Gus Potter Posted Saturday at 19:23 Posted Saturday at 19:23 5 minutes ago, flanagaj said: So apparently, it's 60mm box section welded at 600 centres, to join tHe two sections together. I'll of course get her to provide a drawing. Ok. If you fancy let us see the drawing (include the weathering detail if possible) and a few photographs of what's been built so far. What's the beam span and confirm the loads if you can. Has your SE provided calculations? 1
flanagaj Posted Saturday at 19:31 Author Posted Saturday at 19:31 2 minutes ago, Gus Potter said: Ok. If you fancy let us see the drawing (include the weathering detail if possible) and a few photographs of what's been built so far. What's the beam span and confirm the loads if you can. Has your SE provided calculations? The SE basically provided a lintel schedule for all openings. I have just ordered lintels as per her spec. Builder has installed dpc cavity trays and weep vents according to building regs. I will ask her for calculations. I submitted the lintel schedule to BC and I didn't even receive an acknowledgement. I don't think they have actually looked at a single spec that they have been sent.
Gus Potter Posted Saturday at 19:51 Posted Saturday at 19:51 11 minutes ago, flanagaj said: I don't think they have actually looked at a single spec that they have been sent. This may well be the case. The English BC system can be much less rigorous then the Scottish system for example. But in all cases BC are not their to check or take liability for calculations for example. Their role is to exercise reasonable skill and care to determine if your submissions generally appear to be sufficient to meet the regs in the round. If you read the fine print of BC approval you'll find that the real liability rests with you and your appointed designers. If you miss something then BC are pretty much off the hook. @saveasteading has written at length about this in the past. I've suggested you post some info, photographs etc. It's up to your how much you want to explore. I'm curious as to how the box section is going to be buildable, the orientation for example and how it works. 1
flanagaj Posted Saturday at 19:58 Author Posted Saturday at 19:58 3 minutes ago, Gus Potter said: This may well be the case. The English BC system can be much less rigorous then the Scottish system for example. But in all cases BC are not their to check or take liability for calculations for example. Their role is to exercise reasonable skill and care to determine if your submissions generally appear to be sufficient to meet the regs in the round. If you read the fine print of BC approval you'll find that the real liability rests with you and your appointed designers. If you miss something then BC are pretty much off the hook. @saveasteading has written at length about this in the past. I've suggested you post some info, photographs etc. It's up to your how much you want to explore. I'm curious as to how the box section is going to be buildable, the orientation for example and how it works. I will post some images tomorrow. But thanks for showing an interest. Ideally, I expect SE to be totally responsible for all calcs and drawings. I'm just the end client who knows nothing about that discipline.
saveasteading Posted Saturday at 22:14 Posted Saturday at 22:14 2 hours ago, flanagaj said: expect SE to be totally responsible for all calcs and drawings. That depends what you've asked for and they have offered. E.g there is a big difference if you ask simply what size of lintel or please visit site and design the lintel and draw up all working details with specification, as this may well be carried out by a highly competent contractor. Did you find out their stated qualifications. I'm not especially doubting it but interested.
flanagaj Posted yesterday at 07:21 Author Posted yesterday at 07:21 9 hours ago, saveasteading said: That depends what you've asked for and they have offered. E.g there is a big difference if you ask simply what size of lintel or please visit site and design the lintel and draw up all working details with specification, as this may well be carried out by a highly competent contractor. Did you find out their stated qualifications. I'm not especially doubting it but interested. She is a registered Civil Engineer and her details are on the register. I was very clear in the brief as to what I wanted. All of my woes stem from using a cheap Architectural Designer, who was solely focussed on building reg drawings. If doing this again, I'd pay a good architect who handles the liaison with the SE and ensures that all of this is done up front. 1
saveasteading Posted yesterday at 08:54 Posted yesterday at 08:54 1 hour ago, flanagaj said: registered Civil Engineer Not "chartered"? I'm one of them. MICE or FICE. And CEng comes with it. 4 years uni and 4 years min real world training. I'd never use the word 'registered'. A huge element of gaining that professional status is communication and collaboration. That's why it seems strange to me that you say that is lacking. It's possible they are a technician rather than Chartered. Nothing wrong with that, but their experience may be limited, as may be their insurance. Unfortunately the term civil engineer is not protected, as witness the white vans. 1 hour ago, flanagaj said: doing this again, I'd pay a good architect who handles the liaison But would you? Probably 3 or 4 x the cost at minimum brief. It's all learning. Glad to hear it's moving along. 1
carlos21 Posted yesterday at 09:39 Posted yesterday at 09:39 Id reach out to a local metal fabricator who deals in this sort of thing, i know it will be adding another opinion, but they will most likley be fabricating and fitting these kind of details on a weekly basis. Onsite welding can tricky to acheive consistent results, bolted connections are often easier to retrofit. 1
JpManning Posted 6 hours ago Posted 6 hours ago Thanks for the shout Gus Potter, and a good explanation of the deflection side of it. From the timber yard side, two practical things for flanagaj. First, if the C24 that turned up is badly twisted or bowed, photograph it with the grade stamps and send it back. Any decent merchant will swap timber that isn't fit to use, and twisted joists will only get worse as they dry out on a long span. Second, I'd hold off ordering anything bigger or swapping to I joists until the SE has been to site and confirmed the design in writing. 47 x 225 at nearly 6m is well past what the usual span tables show, so whatever she comes back with, ask for the joist size, grade, centres and the deflection limit she's used, plus the fall you'll keep once it's loaded. Then the merchant can quote exactly to that and you're not paying twice. Good luck with the site visit.
ProDave Posted 5 hours ago Posted 5 hours ago Just for info I used 47 x 220 C24 at 400 centres for my 6M car port. The span tables I looked at said for a flat roof, it was good up to 5.7 metres but not 6. My design has the support pillars inside the 6M width and allowing for further structure my clear span is 5.5 metres, so close to the limit but not over it. My joists arrived straight and dry with no obvious defects and have remained straight.
saveasteading Posted 4 hours ago Posted 4 hours ago 31 minutes ago, ProDave said: My joists arrived straight and dry You were lucky , or your merchant is unusual in keeping treated timber covered. It's a good point. Due to receiving 60 large and wet joists which bent so much in drying that 60% were rejected, I looked into the storage. All the merchants keep their treated timber outside and uncovered "because it is treated for outdoor use". This is contrary to their industry guidance but saves warehousing. So do tell your supplier that it is important that it is dry and straight. Maybe get them to set it aside under cover, to bend there rather than on your site. At this time of year they should all be dry. On a positive note, I haven't checked numbers, but most timbers are critical for acceptable deflection before strength. It would be worth reminding the designer of this. Nobody is going to be nervous because your timber is moving up and down a few mm in wind or under snow.
Oz07 Posted 3 hours ago Posted 3 hours ago Does anyone ever set these joists up with the required 150mm fall instead of using firing strips?