I'm shopping around for foundations for a timber frame structure with brick outer leaf. I don't plan to do it myself but will engage a ground works company to do the install.

 

I've not had a ground investigation yet, but indications are that I have good ground conditions, about 600 mm top soil with compacted gravel and sand below. I've had to dig holes and trenches down to about 1.2 m around the plot for various reasons, and never seen water.

 

I'm most interested in speed of installation, simplicity and cost. Regarding energy efficiency my expectation is that whatever foundations I go for, they can be made be good enough.

 

So I'm not wedded to any particular type of foundations and have been getting prices and talking to installers, suppliers and structural engineers to make my decision. I had been talking to AFT and an installer they had recommended, but as I mentioned in a previous post, AFT have ceased trading in the UK. The recommended installer is looking at carrying on his business with a different insulated form work supplier and is looking at Build Lite. 

 

I'd be interested in thoughts or comments on my approach but also on the Build Lite insulated raft system. I've attached their sketch from their website.

 

Thanks

Typical-Cavity-Wall-Detail-4-Layers.thumb.png.0a6d078691817db183f7e7e9f3e0e0fb.png

 

That's a pretty stonking great thermal bridge there. Not keen. Both AFT + Kore systems have thermally breaks between the inner and outer leaves.

 

With that thermal bridge I'm not sure why you would bother with the extra cost of an insulated raft vs traditional foundations.

 

What U value are they claiming?

  • Author
13 minutes ago, -rick- said:

That's a pretty stonking great thermal bridge there. Not keen. Both AFT + Kore systems have thermally breaks between the inner and outer leaves.

 

@-rick- Thanks for your comment. Just checking, did you see the whole image? For some reason, after I uploaded it, I only see the whole image if I click on it and open it. Here it is uploaded a different way. Does that answer your question? They have a toe on the raft which the bricks sit on, but with a course of Marmox blocks. 

image.thumb.png.e2442562eaa178d6becbf617b11f6315.png

I missed that before, sorry. Still not sure it really changes my view. Marmox blocks are good but they are still much lossier than the other mentioned solutions. There is also nothing stopping using marmox blocks with a traditional foundation and save all the custom eps/engineering costs (use it on the inner leaf and ensure the non-load bearing floor slab is thermally broken from the foundation).

Edited by -rick-

Expanding on my thoughts. If you have ground that suitable for this solution and are happy with the performance then it's a valid option if it is cheaper/quicker/easier to install. But I suspect you can get the same performance from a traditional foundation with somewhat lower cost (can get any groundworker to do it vs a specialist) and the industry is just much more comfortable with the engineering of traditional slabs which may make other things (insurance, future sale, warranty, etc) easier.

You have basically taken a passive slab and killed all its benefits. You have no continuity of insulation. Take a look below, you can follow the insulation in the floor and up the walls. The slave takes the structural loads the block work sits outside the insulation. Your Marmox block works but is an expensive bodge. 

 

image.thumb.jpeg.5ba3b67999cebdd673186e63bff99d73.jpeg

 

2 hours ago, JohnMo said:

You have basically taken a passive slab and killed all its benefits.

In a nutshell.

 

A lot of mis-information and simply "bad" ideas here, with a significant price tag to boot. 

 

400mm of EPS means a load more unnecessary excavation and muckaway......... Buildlite, erm, no thanks, I'll pass. 

Not for me. 

8 hours ago, LnP said:

speed of installation, simplicity and cost.

Reasons to support that system?

IF  the ground doesn't need to be excavated and tipped to get to that level

IF there are no experienced builders available or it's diy

 

Reasons against?

The holistic cost is likely to be high,

A local builder may be suspicious of some new trendy system

A local builder can do traditional build much more readily.

300mm of eps on the middle areas where it isn't so important but 200 at the critical perimeter is weird.

 

you have great ground conditions  so don't waste it on a floating slab.

 

I have an inherent dislike for a heavy structural beam to the perimeter ( compare it to a big floor beam holding an upper car park floor?) sitting on top of 200m of eps. 

 

trench footings and masonry to Floor level

masonry or timber above. 100-150  mm concrete slab with crack control only

150mm pir or 250mm eps then a screed.

 

that will likely save you half your cost to floor level.

 

 

  • Author
4 hours ago, JohnMo said:

You have basically taken a passive slab and killed all its benefits. You have no continuity of insulation. Take a look below, you can follow the insulation in the floor and up the walls. The slave takes the structural loads the block work sits outside the insulation. Your Marmox block works but is an expensive bodge. 

 

image.thumb.jpeg.5ba3b67999cebdd673186e63bff99d73.jpeg

 

@JohnMo One insulated form work system provider I spoke to, said that NHBC and other warranty providers are not comfortable with having the masonry outer leaf sitting on a different foundation than the timber frame. They're concerned about differential movement. They could supply their system with a separate outer ring beam for the masonry, but recommended a toe off the raft similar to the Build Lite one I shared, for an easier ride past BCOs and warranty providers.

 

20 minutes ago, saveasteading said:

Not for me. 

Reasons to support that system?

IF  the ground doesn't need to be excavated and tipped to get to that level

IF there are no experienced builders available or it's diy

 

Reasons against?

The holistic cost is likely to be high,

A local builder may be suspicious of some new trendy system

A local builder can do traditional build much more readily.

300mm of eps on the middle areas where it isn't so important but 200 at the critical perimeter is weird.

 

you have great ground conditions  so don't waste it on a floating slab.

 

I have an inherent dislike for a heavy structural beam to the perimeter ( compare it to a big floor beam holding an upper car park floor?) sitting on top of 200m of eps. 

 

trench footings and masonry to Floor level

masonry or timber above. 100-150  mm concrete slab with crack control only

150mm pir or 250mm eps then a screed.

 

that will likely save you half your cost to floor level.

 

 

One such local builder I spoke to came by with a machine with a large (1.5 m long?) augur and drilled some holes to see what kind of ground conditions I have. He was polite about my interest in insulated raft, but was of the opinion traditional foundations would be a doddle.

 

I'm aware that there are those on here who say that insulated raft is cheaper, when you account for not needing screed, can fix the UFH pipes to the rebar etc. And I've heard it from insulated raft suppliers. I'm getting quotes both ways so will soon find out how it is in my case.

 

Maybe insulated raft is best suited when you don't have the masonry outer leaf to worry about.

11 hours ago, LnP said:

'm shopping around for foundations for a timber frame structure with brick outer leaf. I don't plan to do it myself but will engage a ground works company to do the install.

Do you do this as a day job / business or are you a genuine self builder?

 

The build light system shown is not compatible with a timber frame. 

Edited by Gus Potter

On 30/07/2026 at 00:10, LnP said:

@JohnMo One insulated form work system provider I spoke to, said that NHBC and other warranty providers are not comfortable with having the masonry outer leaf sitting on a different foundation than the timber frame. They're concerned about differential movement. They could supply their system with a separate outer ring beam for the masonry, but recommended a toe off the raft similar to the Build Lite one I shared, for an easier ride past BCOs and warranty providers.

 

One such local builder I spoke to came by with a machine with a large (1.5 m long?) augur and drilled some holes to see what kind of ground conditions I have. He was polite about my interest in insulated raft, but was of the opinion traditional foundations would be a doddle.

 

I'm aware that there are those on here who say that insulated raft is cheaper, when you account for not needing screed, can fix the UFH pipes to the rebar etc. And I've heard it from insulated raft suppliers. I'm getting quotes both ways so will soon find out how it is in my case.

 

Maybe insulated raft is best suited when you don't have the masonry outer leaf to worry about.

Rubbish. Raft foundations are designed with the EPS basket extended to allow the pour of a second mini ring foundation to accept the masonry.

 

Don’t take this the wrong way, but you’re entering an area of major misadventure here, and what you’ve arrived at independently is already falling on its ass.

 

Stick with ‘tried & tested’ and an experienced contractor / SE to solve this correctly. It’s “kinda important” :) :D 

  • Author
6 hours ago, Gus Potter said:

Do you do this as a day job / business or are you a genuine self builder? 

There are two ways for me to understand your question. If it's a straight one, the straight answer is, no I don't do it for a day job/business and yes I'm a genuine self builder, whatever that is. But since I opened my post by explaining why I'm asking my question, the straight answer should already have been clear. So I'm wondering if your question was rhetorical and intended to demean and denigrate, which would be a pity.

6 hours ago, Gus Potter said:

The build light system shown is not compatible with a timber frame. 

Thanks for your comment. Useful to get your opinion..

  • Author
On 30/07/2026 at 07:26, Nickfromwales said:

Rubbish. Raft foundations are designed with the EPS basket extended to allow the pour of a second mini ring foundation to accept the masonry.

 

Don’t take this the wrong way, but you’re entering an area of major misadventure here, and what you’ve arrived at independently is already falling on its ass.

 

Stick with ‘tried & tested’ and an experienced contractor / SE to solve this correctly. It’s “kinda important” :) :D 

Yes, I get it. Thanks for your alert. Choosing the foundations is one of the most important decisions in the project. The best one can hope for is to become an "intelligent customer". That's why I'm talking to people and asking questions on here.

7 hours ago, Gus Potter said:

Do you do this as a day job / business or are you a genuine self builder?

I read that as..." how much detail do we need to go into?

For examples:

A builder may have been asked to do this for the first time.

A self builder may have been "sold" the idea at an exhibition, without having the pros and cons explained.*

 

*there is a reason I see such systems at  self build exhibitions but not at trade exhibitions.

Not that it's bad, but that there are options and there is more to know.

 

  • Author
46 minutes ago, saveasteading said:

I read that as..." how much detail do we need to go into?

For examples:

A builder may have been asked to do this for the first time.

A self builder may have been "sold" the idea at an exhibition, without having the pros and cons explained.*

 

*there is a reason I see such systems at  self build exhibitions but not at trade exhibitions.

Not that it's bad, but that there are options and there is more to know.

 

Fair point and thanks for your helpful interpretation. 

Not being overly familiar with this type of design I find this interesting. That thermal design asks a lot of the Marmox thermal blocks as they are the only line of defence between the cold bricks of the outer leaf and the warm concrete of the raft.

 

The Marmox blocks have vertical columns of epoxy/stone concrete surrounded by XPS, so the vertical direction is the worst from a thermal transfer perspective, but only 6.3% [1] of that sectional area looks to be solid concrete. I am not a thermal expert by any stretch - just trying to ballpark the numbers. Assuming an XPS lambda of 0.033 W/m.K and a concrete lambda of 2.3 W/m.K [0] results in an average vertical lambda of 0.176 W/m.K [2] which is noticeably higher than the value they advertise of 0.05 W/m.K. That may be because the horizontal performance is much better and they quote that value. If using the 65mm Marmox thermal blocks that's going to create a vertical thermal bridge of 0.379 W/m.K . There would also be a lesser thermal path out sideways trough the Marmox block to the soil, but using a total value of 0.4 W/m.K would probably be indicative. This is similar in magnitude to a standard steel lintel, as used above a window. At an average 10C difference for 6 months that would loose 17.3 kWh/m or £1.21/yr per metre based on a heating system COP of 3 (low) and electricity price of 21p/kWh (high).

 

The overall thermal bridge would have to consider the thermal transfer through the slab as well, which I have ignored, but that feels reasonable given the high thermal conductivity of concrete and rebar.

image.thumb.png.97b4c4859e8444ca6394c74bd35a4dcb.png

[0] IMPORTANT TO NOTE: the Marmox epoxy concrete may be thermally better than standard concrete and mean this value, and subsequent values, should be lower.

[1] (pi*(30/2)^2) / ((50+30)*140) = 6.3%

[2] (2.3*6.3%) + (0.033*(100% - 6.3%) = 0.176 W/m.K

[3] 0.176*(0.140*1) / 0.065 = 0.379 W/m.K

[4] 0.4*10*(24*180)/1000 = 17.28 kWh/yr.m

 

I have a make up on my garage raft which is essentially the same without the Marmox thermal block. That's an oversight, but it is a garage rather than a house. However, I think I can improve matters by putting a thin layer of XPS between the blockwork and the soil. The blockwork at the bottom of the outer leaf is a course of engineering bricks and a course of Stranlite 140mm 10N blocks. With the change as pictured below, ignoring horizontal heat flow through the insulation (yellow) and assuming perfect thermal conductivity in both the slab concrete (light grey) and engineering brick (brown), I can consider just the vertical heat flow through the Stranlite block (dark grey). It has a lambda of 0.43 W/m.K , so that works out as a thermal bridge of 0.43*0.140/0.215 = 0.28 W/m.K which is actually comparable to the Marmox thermal block. Interesting. Looks like I have an improvement worth making there.

 

Tweak to include horizontal heat loss through the added XPS: 50mm of XPS would have a sideways thermal bridge of 0.033*0.215/0.050 = 0.14 W/m.K which can probably be halved assuming a linear temperature gradient across the height of the Stranlite block. 0.28 + (0.14 / 2) = 0.35 W/m.K , so still similar to the Marmox thermal block.

 

Now:

image.png.349b0527c34b559cffa7bed2188be667.png

 

Improved:

image.png.8c7a0bbd0dc80abc370fafd84003924d.png

 

Just found the BBA certificate (BBA 19/5617 PS1 Issue 2) of the BuildLite product and that gives a psi value of 0.4 W/m.K for similar make up but different geometry (100mm wide Marmox) :

 

image.png.0a8d0c58f9f7b1db3f0a6e23d01e576e.png

 

image.png.93f8d47f6933d79d8828b7f31d90d02c.png

 

On 30/07/2026 at 08:23, LnP said:

There are two ways for me to understand your question. If it's a straight one, the straight answer is, no I don't do it for a day job/business and yes I'm a genuine self builder, whatever that is. But since I opened my post by explaining why I'm asking my question, the straight answer should already have been clear. So I'm wondering if your question was rhetorical and intended to demean and denigrate, which would be a pity.

Yes it was a straight question. I was just asking as I design insulated rafts as part of my day job. Some of the stuff I do has a lot of my intellectual property built in. I'm happy to share some of my knowledge on BH, just don't want folk ripping it off whole sale for commercial advantage. 

 

As an offer if you want to have a chat on the phone then give me a call on 0771 308 1597, text me first so I know it's you, I'm also a bit deaf! We can chew the fat for a bit, happy to chat with you for up to an hour..  and you can pick my brains for free. If you want to take up my offer then send me some drawings and so on first. These of course will be kept confidential at my end. 

On 30/07/2026 at 09:03, LnP said:

The best one can hope for is to become an "intelligent customer".

Great approach. I enjoy teaching and informing Clients. I find it a lot of fun actually. My starting point is to listen to you find out what you know and don't, then fill in the gaps in your knowledge and explain what often can be quite technical things in terms a lay person can understand.  The objective is to give you enough information to allow you to make informed decisions. This sort of thing gives me a bit of a refreshing break, from drawing details / to structural calculations etc. once you have designed your first few hundred beams the novelty kind of wears off. You still have to concentrate though. 

 

In my day job I do this when pitching for business. If you inform a Client and explain the issues, how you might deal with them, highlight the things they may not have thought about,  put forward other solutions, buildability cost and risk then it makes it hard for your competitors, you set the bench mark.

 

If my competitors come in at lower fee rate, the Client is often now aware of what constitutes value for money. It works most of the time but some Clients are really stupid / just don't listen and go with the lowest price without valuing the service, ongoing support etc They will also then go with the lowest builders tender and end up nine times out of ten getting truly ripped off. 

7 hours ago, Gus Potter said:

Yes it was a straight question. I was just asking as I design insulated rafts as part of my day job. Some of the stuff I do has a lot of my intellectual property built in. I'm happy to share some of my knowledge on BH, just don't want folk ripping it off whole sale for commercial advantage. 

 

As an offer if you want to have a chat on the phone then give me a call on 0771 308 1597, text me first so I know it's you, I'm also a bit deaf! We can chew the fat for a bit, happy to chat with you for up to an hour..  and you can pick my brains for free. If you want to take up my offer then send me some drawings and so on first. These of course will be kept confidential at my end. 

Great approach. I enjoy teaching and informing Clients. I find it a lot of fun actually. My starting point is to listen to you find out what you know and don't, then fill in the gaps in your knowledge and explain what often can be quite technical things in terms a lay person can understand.  The objective is to give you enough information to allow you to make informed decisions. This sort of thing gives me a bit of a refreshing break, from drawing details / to structural calculations etc. once you have designed your first few hundred beams the novelty kind of wears off. You still have to concentrate though. 

 

In my day job I do this when pitching for business. If you inform a Client and explain the issues, how you might deal with them, highlight the things they may not have thought about,  put forward other solutions, buildability cost and risk then it makes it hard for your competitors, you set the bench mark.

 

If my competitors come in at lower fee rate, the Client is often now aware of what constitutes value for money. It works most of the time but some Clients are really stupid / just don't listen and go with the lowest price without valuing the service, ongoing support etc They will also then go with the lowest builders tender and end up nine times out of ten getting truly ripped off. 

Hasn't there been issues here before mixing business interests with forum advice? I know thats not where you're coming from with it but I seem to remember some aggro previously. 

On 01/08/2026 at 09:00, Oz07 said:

Hasn't there been issues here before mixing business interests with forum advice? I know thats not where you're coming from with it but I seem to remember some aggro previously. 

Hiya.

 

You are absolutely right to raise this point, which is valid. I use my own name on BH, a quick search on the internet will show that I run a design business. I was attracted to join BH as I felt it was non commercial. Initially I never mentioned that I do this as a day job, but as time passed I felt I could not bring my knowledge and advice to bear effectively without actually saying I do this as a day job.

 

In light of that I wrote to the moderators and asked for their advice. I definitely don't want to get banned from BH as I enjoy sharing what I know and helping folk. I see your valid comments were possibly prompted by my response to @LnP. I spent some time earlier today just chatting on the phone with him. Once piece of advice I gave him was that he should employ a local Engineer and provided reasons why he should do this. However, occasionally once in a while members chat with me they write to me formally and ask if I will undertake their design. This is arguably a breech of BH rules, which is why I asked for moderator advice. 

 

I'll leave it at that for now as the moderators may wish or not add to my response. 

 

 

  • Author
On 01/08/2026 at 09:00, Oz07 said:

Hasn't there been issues here before mixing business interests with forum advice? I know thats not where you're coming from with it but I seem to remember some aggro previously. 

I can confirm that the advice I got from Gus was helpful, and the more so because he does it for a living.

I'm sure the administrators are well able to spot when people are on the forum motivated by commercial interest rather than collaboration.

2 hours ago, LnP said:

I can confirm that the advice I got from Gus was helpful, and the more so because he does it for a living.

I'm sure the administrators are well able to spot when people are on the forum motivated by commercial interest rather than collaboration.

He's definitely one of the good guys

6 hours ago, LnP said:

commercial interest rather than collaboration.

Although I'm qualified I still engage expert SEs because I can't keep up to speed on all aspects.

I might 'know' that something will work but have lost the calculating skills and haven't kept up with the changes to codes.

 

It is normally prudent to engage a  local practice because they know the ground, the local preferences, and are available for site visits.

Equally an Engineer doesn't usually want work far from home, for the same reasons.

 

That can change if the work is purely academic as in the analysis of a beam or truss. But that will be an unuusual case.

 

So we can rest assured that Chartered Engineers are not going to use BH to tout for business, and free advice should normally be received as well intended and without any strings .... with the unstated subscript that the project has not been visited or examined in detail and no liability can be inferred.

 

Which leads me to emphasise that a concerned owner might not be noticing the underlying problem or cause*, and a site inspection is recommended in mot instances.

 

*That's why we ask so many questions which can annoy some correspondents who simply want an easy answer.

 

Gus is not touting for business, but his advice is rounded and pragmatic and up to date.

 

 

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.