fatgus Posted 3 hours ago Posted 3 hours ago Weāre about to start our passive-ish build. Our heatpunk calcs suggest heat loss of 10W/m2, assuming we hit our airtightness target Ā Original plan was for ASHP & UFH downstairs, just some towel radiators upstairs. Weāre keen to have some form of cooling too, so we started looking at ducted A2A. It would appear that we could potentially switch to that and eliminate the UFH entirely. Missing out on the warm floors doesnāt bother us at all. In fact, losing the UFH could be a benefit as weāre contemplating a kind of earthen/clay floor (thatās another story entirely). Ā Would love to know what people think? Stupid idea? Or worth pursuing, maybe with an eye on potential āgotchasā? It would be great to hear of any first hand experience⦠Ā
SteamyTea Posted 3 hours ago Posted 3 hours ago I have lived in a number of places with forced air heating/cooling. It works well. It can be combined with the MVRH, and maybe an exhaust air recovery water heating as well. Ā The two downsides are that it can be noisy, so needs to be sized properly, and not just thermally. The other, more serious problem, is cross talk between rooms via the ductwork.Ā I know someone who was sitting in his kitchen bitching to his mate about his mental wife. She heard everything in the bedroom. He got his own bedroom after that, and eventually his own, smaller, house. You also get some ugly grills in the rooms. But it can be done and I think all the problems are easily overcome.
fatgus Posted 2 hours ago Author Posted 2 hours ago Thanks @SteamyTea The more I look into it, the more appealing it becomes. Ā Althoughā¦Ā Ā 39 minutes ago, SteamyTea said: I know someone who was sitting in his kitchen bitching to his mate about his mental wife. She heard everything in the bedroom. He got his own bedroom after that, and eventually his own, smaller, house. ā¦could be quite a crucial issue to eliminate š Ā Ā
JohnMo Posted 2 hours ago Posted 2 hours ago 10W/m2 ties into passivhaus heating requirements, that can be done via MVHR if you want, but doing any cooling via MVHR is not really that successful. Ā A2A could do both. Do DHW via direct immersion heating. Not really cost effective to do much else with A2A. Even with an ASHP I do direct anyway, not noticed any uplift in electric cost since I changed over. Ā But for primary heat source, buy carefully, do your research as performance can vary hugely. As can the I'm fukced off with air always blowing at me factor. Ā Maybe if doing A2A look at ducted systems.
JohnMo Posted 2 hours ago Posted 2 hours ago 48 minutes ago, SteamyTea said: The other, more serious problem, is cross talk between rooms via the ductwork.Ā I know someone who was sitting in his kitchen bitching to his mate about his mental wife. Or maybe don't do ducted, do wall mounted and no cross talk
fatgus Posted 43 minutes ago Author Posted 43 minutes ago 1 hour ago, JohnMo said: Or maybe don't do ducted, do wall mounted and no cross talk Iām thinking wall mounted makes sense for the bedrooms thenā¦Ā
fatgus Posted 35 minutes ago Author Posted 35 minutes ago 1 hour ago, JohnMo said: A2A could do both. Do DHW via direct immersion heating. Not really cost effective to do much else with A2A. Even with an ASHP I do direct anyway, not noticed any uplift in electric cost since I changed over. I think direct DHW definitely makes sense⦠weāll have a decent PV array and batteries, so electricity should be mostly āfreeā and worst case itāll be off-peak.
fatgus Posted 31 minutes ago Author Posted 31 minutes ago 2 hours ago, JohnMo said: As can the I'm fukced off with air always blowing at me factor. That would would indeed be a bad thing š¬