Hi guys

 

I'm rewiring my 177 sqm house. I will carry out first fix.

Electrician to make final connections at consumer unit.

 

I would be gratefully if you could give me feedback on my circuit design:

 

🏠 SOCKET CIRCUITS


1. Ground floor ring (32A)
lounge 1
lounge 2
hall
WC sockets

One external socket at front of house.


2. Kitchen ring (32A)
all kitchen sockets including oven.

One external socket at rear of house.


3. First floor (32A)
Bed 1
Bed 2
Bed 3
Bed 4 (extension)

Bathroom
first floor landing
home office (light load)


4. Loft ring (32A or radial)
Bed 5
loft office (light load)
Loft bathroom sockets


5. Outhouse radial (20–32A SWA)
36 sqm outhouse
One external socket.

 

6. Basement sockets (20–32A)

2 rooms, currently damp. To be waterproofed within the next 10 years.

Most critical infrastructure here. Eg router 


🔥 HIGH LOAD / INFRASTRUCTURE CIRCUITS


7. Cooker (32–45A radial)


8. Heat pump (dedicated radial)

9. EV charger (40A dedicated)

10. MVHR (small dedicated supply / FCU)

11. PV inverter AC circuit
grid-tied feed into CU
protected by dedicated MCB/RCBO


12. Battery storage system feed

 

13. Fire Alarm (6A Radial)

 

14. Security PIR (6A radial)


💡 LIGHTING CIRCUITS

 

15. Basement lighting (6A)

 

16. Basement Emergency light at consumer unit (6A) 


17. Ground floor lighting (6A)


18. First floor lighting (6A)


19. Loft lighting (6A)


20. External lighting front and back (6A)

 

Is any of the above insufficient or overkill?

 

Thanks in advance

 

P

Posted

Are you intending to have a hob - that will need its own feed. 

5 hours ago, Pappa said:

Loft bathroom sockets

What are these for - bathrooms have very specific restrictions? 