iMCaan Posted Monday at 17:38 Posted Monday at 17:38 We have water UFH on ground and first floor and both floors are screeded. In one of the ground floor rooms, the temperature rises to as high as 23 degrees with Salus thermostat set at 8 degrees (same as the other rooms) that's a huge 15 degree difference. In the other rooms the temperature is mostly around 10 degrees. I've taken the room temperature manually and it matches the temperature displayed on the Salus thermostat so it doesn't appear that thermostat is not faulty nor is the Salus auto actuator, which comes on and goes off. So what could be the reason? Why would there be such a high difference between the set temperature and the actual room temperature? Thanks
JohnMo Posted Monday at 18:04 Posted Monday at 18:04 I would check the thermostat settings and your controller. If rooms are 10 degs and you have the thermostat set at 8 degs, where is your boiler call for heat coming from. More details needed
iMCaan Posted Monday at 18:29 Author Posted Monday at 18:29 It's Salus Quantum 230v Programmable Thermostat and Salus CB500 5 Zone wiring centre. @JohnMo I need to think about this. How it works?
JohnMo Posted Monday at 19:03 Posted Monday at 19:03 Which quantum model? There is one for UFH and one for radiators. Do you have self learning stopping starting on or off?
SteamyTea Posted Monday at 19:40 Posted Monday at 19:40 35 minutes ago, JohnMo said: quantum model The Copenhagen model allows for it to be both on and off, simultaneously. The room temperature will only be revealed when it is measured. 1
Nickfromwales Posted Monday at 19:57 Posted Monday at 19:57 Ffs. I googled ‘model’ and ended up back here….. 1
JohnMo Posted Monday at 20:11 Posted Monday at 20:11 15 minutes ago, Nickfromwales said: Ffs. I googled ‘model’ and ended up back here….. Two basic models, WQ610 is for radiators and SQ610 for UFH. If you have a WQ on UFH and you have any self learning functions active, the thermostat loses all control as the algorithm is wrong for the application. A WQ will work with UFH, but only if you use in a simple on off mode. Been there, done it, got the tee shirt.
Nickfromwales Posted Monday at 20:14 Posted Monday at 20:14 15 minutes ago, Nickfromwales said: Ffs. I googled ‘model’ and ended up back here….. 👆 2 minutes ago, JohnMo said: loses all control @SimonD gets what I was looking to achieve.
iMCaan Posted Tuesday at 11:25 Author Posted Tuesday at 11:25 (edited) Thanks all @JohnMo I have no idea how to setup self learning stopping starting or how to enable it. The thermostat model is SQ610 and the wiring centre is CB500 and auto balancing actuators are THB23031. We've not yet moved in. Since there's no broadband yet, I've not installed the Salus gateway therefore I'm not using the mobile app or have anything programmed. The scheduled timer on the thermostat is not set. I've not played with any other settings on any thermostat. Last night, I did some basic testing. Raised the temperature of every thermostat on the ground floor except for the affected room. All actuators came on except the three actuators for the room affected. The 3 flow pipes for the affected room were colder than the other room pipes to touch. After about an hour later I lowered the temperature on all thermostats to turn off the actuators. This morning, the room affected temperature was 11.5 degrees. I raised the temperature to 13 degrees and the three actuators for the room came on. Will check tonight what the room temperature is. Thanks Edited Tuesday at 11:30 by iMCaan
iMCaan Posted Tuesday at 11:31 Author Posted Tuesday at 11:31 Yes, I still do. I'm testing to figure out what is triggering the high temperature. Why it went as high as 23 degrees.
JohnMo Posted Tuesday at 13:55 Posted Tuesday at 13:55 You have self balanced actuators, maybe it was just going through a learning period, some can take quite awhile. With SQ610, you have a setting that optimises control to the Salus self balancing valves. Go on to Google and search for the full instructions for the SQ610, not the quick guide that comes with the thermostat.
iMCaan Posted Tuesday at 18:27 Author Posted Tuesday at 18:27 (edited) Thanks, will read the manual Edited Tuesday at 18:28 by iMCaan
iMCaan Posted Thursday at 12:51 Author Posted Thursday at 12:51 A little bit of progress. Could well be a wiring issue. I've found that the affected room (let's call it Sitting room) thermostat triggers Lounge zone. The Lounge room temperature keeps rising even though the temperature is set well below the actual room temperature. The Lounge thermostat only triggers it's own heating zone. There's only 5 zones (including sitting and lounge rooms) on the ground floor. I've tested all 5 zones, one at a time, but none of them have started the Sitting room zone. Also, turned on all the zones on the first floor (each floor is a separate heating zone), radiators in the attic and hot water but not triggered the Sitting room zone. Investigation continues.
JohnMo Posted Thursday at 13:13 Posted Thursday at 13:13 Where is your boiler controller is it the sitting room?
JohnMo Posted Thursday at 13:15 Posted Thursday at 13:15 But I would just delete all the zones, it's just going to make your heat source cycle and use more energy anyway. Zones add no value
iMCaan Posted Thursday at 14:54 Author Posted Thursday at 14:54 (edited) 1 hour ago, JohnMo said: Where is your boiler controller is it the sitting room? No, it's in the garage. It's a big house (so he says) so don't want to heat up the entire house/floor. Will test and remove the zones as necessary. I did notice this morning that in the Lounge (L shaped), the dining and kitchen were also warm by couple of degrees. So it's likely, I reduce that one zone instead of three. Edited Thursday at 14:58 by iMCaan
JohnMo Posted Thursday at 15:00 Posted Thursday at 15:00 3 minutes ago, iMCaan said: No, it's in the garage. It's a big house (so he says) so don't want to heat up the entire house/floor. Will test and remove the zones as necessary. Depending on the controller it may be configured as the master thermostat unless it's just a time switch. Your sitting room maybe has no zone control it's just an open zone. The controller may be asking the system to do stuff based on what it sees in the garage?
iMCaan Posted Thursday at 15:05 Author Posted Thursday at 15:05 (edited) There's no thermostat in the garage. I'm not sure whether the controller has a built-in thermostat. Edited Thursday at 15:14 by iMCaan
JohnMo Posted Thursday at 15:29 Posted Thursday at 15:29 23 minutes ago, iMCaan said: controller has a built-in thermostat What make model - boiler or heat pump?
iMCaan Posted 21 hours ago Author Posted 21 hours ago Boiler - Valiant ecotec plus 635 I've found the exact cause of the problem. After weeks of investigation, I found that raising the temperature on the thermostat in Sitting room didn't trigger the Sitting room zone instead it triggered the Lounge zone. However, raising the temperature on the Lounge thermostat didn't trigger the Sitting room zone. Furthermore, I noticed, the Sitting room zone's three auto actuators wouldn't come on now. They came on before. One of the thermostats must had triggered them on/off before so why not now? I started focussing on the Lounge zone. If the Sitting room thermostat is triggering the Lounge zone then Lounge thermostat is the likely one that should trigger the Sitting room zone but why isn't it? So I finally did what every computer user does, at least once in there life time Reboot. I pulled the Lounge thermostat out of it's casing on the wall and then re-seated it. Recycling the power to the Lounge thermostat resolved the issue, well, I mean I found the actual problem. The Lounge thermostat switched on the Sitting room zone and the temperature of sitting room slowly started rising. The problem: The Sitting room thermostat is triggering the Lounge zone and vice versa. So in conclusion, the Sitting and Lounge room zones wiring need swapping. The technician is coming out next week. Thanks to all. 1
bmj1 Posted 21 hours ago Posted 21 hours ago 3 minutes ago, iMCaan said: Boiler - Valiant ecotec plus 635 I've found the exact cause of the problem. After weeks of investigation, I found that raising the temperature on the thermostat in Sitting room didn't trigger the Sitting room zone instead it triggered the Lounge zone. However, raising the temperature on the Lounge thermostat didn't trigger the Sitting room zone. Furthermore, I noticed, the Sitting room zone's three auto actuators wouldn't come on now. They came on before. One of the thermostats must had triggered them on/off before so why not now? I started focussing on the Lounge zone. If the Sitting room thermostat is triggering the Lounge zone then Lounge thermostat is the likely one that should trigger the Sitting room zone but why isn't it? So I finally did what every computer user does, at least once in there life time Reboot. I pulled the Lounge thermostat out of it's casing on the wall and then re-seated it. Recycling the power to the Lounge thermostat resolved the issue, well, I mean I found the actual problem. The Lounge thermostat switched on the Sitting room zone and the temperature of sitting room slowly started rising. The problem: The Sitting room thermostat is triggering the Lounge zone and vice versa. So in conclusion, the Sitting and Lounge room zones wiring need swapping. The technician is coming out next week. Thanks to all. Been there - had a plumber cut off all the wiring labels and run almost every zone wrong... It's all fixable, fortunately.. just time consuming