Does aerobarrier negate need for airtightness detailing?


Recommended Posts

Posted
29 minutes ago, SBMS said:

Do you mind me asking how much they charged (per sqm?)

Here's an excerpt from the email that came with a quote I received in August 2025, if that's any help:

 

"Pleased to provide a quotation for the airtightness works in your project - to view in full, please click the Quotation link above. For the supply and installation of the AeroBarrier system in your 190m2 project in [my postcode], your installation would be £2,538.40 (ex VAT but zero rated on new builds). This price is inclusive of travel, labour and materials and we do not charge a premium or any added fees for you end airtightness target (even to high performance levels)."

  • Like 1
  • Thanks 1
Posted
4 hours ago, SteamyTea said:

Half a cubic metre per hour per square metre of exposed area is considered quite good.

Has anyone managed that without filling the house up with glue?

Seem to remember that someone got a 0.23 m3.h-1.m-2.

 

................... sprints to trophy cabinet.........🏃‍♂️🏃‍♂️🏃‍♂️🏃‍♂️🏃‍♂️...............

 

.........unpacks golden framed airtightness cert................

 

............. Yells "I told you someone would care" at nonplussed family........

 

.......Tear runs down cheek.......... Tears of joy, tears of pride .....

 

 

 

 

Screenshot_20260108_224342_com_hihonor_hnoffice_PDFPhoneActivity0.thumb.jpg.f5d9c276282b1d1245413f0b7bbf77df.jpg

 

 

.......Children roll eyes and crank up some yank making funny with the Minecraft on TV......

 

  • Like 1
  • Haha 4
Posted
16 hours ago, crispy_wafer said:

Start and end, not measured in ACH, but once we get volumes the conversion can be made.

From 3.9 to .5 and you think that needs improvement?  I think i must have missed something on mine to end up at 1.4. Which i thought was reasonable actually.  The lads from AB  did say the windows and door sealing was very good. Wonder where i was still losing air from.

Posted
14 minutes ago, Post and beam said:

From 3.9 to .5 and you think that needs improvement?  I think i must have missed something on mine to end up at 1.4. Which i thought was reasonable actually.  The lads from AB  did say the windows and door sealing was very good. Wonder where i was still losing air from.

 

No, not really, .5 is more than good enough for me, originally I said 1.5 and I'd be very happy, just a bit pee'd off at the windows because it's so obvious.  My fault for being soft as shite and not inspecting 100%.

Posted
5 hours ago, crispy_wafer said:

and not inspecting 100%

I guess you didn't tape the windows & doors yourself then.

 

The only place i can think of that might have let down my score was the fact that the floor screed did not flow as hard to the edges as i imagined it would and the sole plate being a little suspect. I can imagine that once pressurised, air was getting down past the edges of the screed and out through the sole plate gaps.

Either way its costing me no more to heat than i was paying for my old 3 bed semi at less that half the size.

Posted

When I was designing my last house I used the PHPP, and I ran some iterations to determine the sensitivity of infiltration on the space heating requirements. There are the results for my particular design. This was back in 2009 using the 2007 version.

 

Pressurisation Test Result (ACH)    Specific Space Heating Demand (kWh/m2)
               0.2                                                   12.1
               0.4                                                   12.3
               0.6                                                   12.5
               0.8                                                   12.7
               1.0                                                  12.9
               2.0                                                  14.0

Posted
2 hours ago, Post and beam said:

I guess you didn't tape the windows & doors yourself then.

Yeah I’d done the taping myself, but that is not an issue, it’s the epdm seal in the opening that’s either shrunk or was cut too short when installed, it’s just something I’ve noticed as AB has left a nice witness mark, how much it adds up to over say 14 openings I don’t know, probably not a great deal but now I see it, makes some sense to try and fix it

Posted
1 hour ago, Iceverge said:

 

Chimney? 

 

 

Would have been a much worse score if that was open!?

 

Plus the AB team look for 'major faux pas' before testing. An open chimney would have not passed grade, I am sure.