We’ve removed an open fire (in one room) and a gas fired back boiler in another. My wife wants a wood burner installed in each opening (I’ve tried to win the ‘take down chimney’ argument, and lost)…. All fine you would think.

 

However, I went on an air tightness drive when we did the knock through rear extension (one of the fireplaces is now in this larger room) and sealed as much as a I could up with tape and fm330.

 

The plan was always to buy stoves with external air input and draw from under the timber floor (we maintained ventilation to this floor void even though we built on the back with the extension) but I was working away when the builders did the floor and hearth, and there’s no pipework/vent through the hearth into the void.

 

1. Am I worrying about this for nothing and will the general air infiltration into the property (trickle vents on the windows, 1946 block/block rendered construction, triple glazed) be sufficient for 2x <5kW stoves?

 

2. If I’ve screwed this up, is there a concentric flu liner that I can install to provide combustion air from outside?

 

3. Failing 2, is it possible to draw combustion air from the cavity around the flue liner via a second opening in the register plate?

 

I don’t anticipate these stoves ever being lit, as we have a perfectly functional central heating system that I installed new about 18months ago that does a fine job of heating the place to 22-23 in the depths of winter.

 

But if they do (we have a power cut or a heat pump problem) then I’d like them to work safely.

Edited by HughF
Link to comment
Share on other sites

1 hour ago, HughF said:

1. Am I worrying about this for nothing and will the general air infiltration into the property (trickle vents on the windows, 1946 block/block rendered construction, triple glazed) be sufficient for 2x <5kW stoves?

Well it would be against the Building Regulations - though you'd only be prosecuted if you survived the carbon monoxide poisoning.

 

You'd need a 'room sealed' stove installed in according to the manufacturer's guidance - I've only seen horizontal of under-floor supply pipes. The alternative is to knock a hole in the wall and install a permanently-open vent, in accordance with the dimensions in Part J of the Building Regs.

 

If it's only a decorative effect you want, block the flues, install a TV screen inside an old stove and set it to show a flame video.

Link to comment
Share on other sites

The stoves are in the middle of the property, no way to knock through to an outside wall.

 

Stoves <5kW are assumed to be able to use the air in the room, no? That’s what I though the regs said.

 

Wife does want a backup heat source…. So they need to work. 
 

I guess the only option is a grill in the floor in front of the hearth, or core drill through the slate hearths and the concrete underneath, at an angle, to intercept the floor void 🤦‍♂️

Edited by HughF
Link to comment
Share on other sites

50 minutes ago, HughF said:

I guess the only option is a grill in the floor in front of the hearth, or core drill through the slate hearths and the concrete underneath, at an angle, to intercept the floor void 🤦‍♂️

tend to agree, my experience with wood burners is trickle events just don't allow enough supply air. Just opening the window slightly usually provides a near instant combustion improvement and kindoff proves the point. Something to think about if you're not having the fire lit much is whether there's a risk of mice in the floor void deciding to nest in the pipe? If so how will you provide a louvre or the like to prevent that?

Link to comment
Share on other sites

1 hour ago, Temp said:

I'm sure there are wood burning stoves on legs that are designed to draw external air in at the bottom/rear so perhaps you could drill through the slab at the back?

 

Try Clearview stoves.

I’ve already got the stove with an external air supply inlet on the back, the ductwork up/down/left/right is no issue. The issue is where to take the external air supply from now that there’s no pipe installed in the hearth.

Link to comment
Share on other sites

As I think it is unrealistic to core down through the hearth retrospectively and  get a duct into the floor void, I think we’ll have to settle for a grill/grating in front of the hearth.

 

It’s a real shame a concentric flue liner system isn’t an option.

Link to comment
Share on other sites

If you don’t have passivehouse levels of air tightness, I think you’ll have ample air supply as it is. If you want, have a blower test done - maybe with and without the trickle vents open.

 

We have a barn conversion done 7 year’s ago (not by me) with double glazing, trickle vents and (I assume) minimum BC standard insulation and air tightness. I put in a woodburner as I wanted it done right (I didn’t like the look of the standard flue hangers and had a custom SS plate bent up to fit). (BTW DIY is fine with BC involvement.) No external air supply - I leave one trickle vent open near the stove and that’s it. We have a nest combined smoke & CO alarm and, as I have asthma, I have a Davis particulate detector as a check. We use the stove a lot and everything is good.

 

Yeah in the new place we’ll be passivehouse-like insulation and air tightness … and therefore have external air supply for it.

Edited by Alan Ambrose
Link to comment
Share on other sites

On 23/01/2025 at 10:57, HughF said:

Stoves <5kW are assumed to be able to use the air in the room, no? That’s what I though the regs said.

If you have a stove <5kW, and if it doesn't have a flue draft stabiliser, and if the design air permeability of your house is >5.0m3/{h.m2), and if the manufacturer doesn't say otherwise, then the Building Regs say you don't need a permanent vent. Though why they use the design air permeability instead of the actual air permeability, I don't know.

 

However you are planning to have more than one stove, so logic dictates that you'd need to add the outputs together and still be <5kW - which seems unlikely.

Link to comment
Share on other sites

51 minutes ago, Mike said:

If you have a stove <5kW, and if it doesn't have a flue draft stabiliser, and if the design air permeability of your house is >5.0m3/{h.m2), and if the manufacturer doesn't say otherwise, then the Building Regs say you don't need a permanent vent. Though why they use the design air permeability instead of the actual air permeability, I don't know.

 

However you are planning to have more than one stove, so logic dictates that you'd need to add the outputs together and still be <5kW - which seems unlikely.

Dangerous thing, logic.  As is assuming that regulations are sensible.  I think you’ll find each stove in each room is viewed individually. 
 

On 23/01/2025 at 11:42, HughF said:

I’ve already got the stove with an external air supply inlet on the back, the ductwork up/down/left/right is no issue. The issue is where to take the external air supply from now that there’s no pipe installed in the hearth.


As you have said stove already why not hitch it up and see?  You can leave the air supply pipe open at the back. My guess is that you are likely to discover that it works just fine.  Mid century house with trickle vents I would guess won’t be that airtight.  
 

Alternatively, as a precursor to trying it you could test the draft on your flue.  Shut everything, everywhere, including all other flues/chimneys, ideally on a cold and windless day, and see what a smoke match does in the fireplace below the open flue. The warmth of your house should generate a gentle draft (hence cold and windless) which mimics least draft conditions. Betcha the smoke slips straight up that flue. 
 

However….

 

having two flues connected does give the opportunity for a strong draft in one sucking smoke down the other (as I’ve experienced). If you’ve bought fires that shut off the airflow well then it should be ok using one then shutting the other off.   I wouldn’t, however assume without investigation that you can use both at once. 
 

What stage are you at re flue liners?

Link to comment
Share on other sites

Roof, including chimney stack, is being scaffolded for flashing repairs and I want to make the most of the scaffolding, so I’m planning on getting my hetas guy to drop the liners at that point.

 

4 chimney pots on the top - each fireplace had a separate run up the chimney. I will have two liners installed, one per appliance.

 

I cannot drill through the hearth and access the floor void so the external air supply will have to draw from the room. Unless, as I said earlier, I can draw from outside using a concentric flue liner, if such a thing exists.

Link to comment
Share on other sites

On 26/01/2025 at 09:37, Alan Ambrose said:

If you don’t have passivehouse levels of air tightness, I think you’ll have ample air supply as it is. If you want, have a blower test done - maybe with and without the trickle vents open.

 

We have a barn conversion done 7 year’s ago (not by me) with double glazing, trickle vents and (I assume) minimum BC standard insulation and air tightness. I put in a woodburner as I wanted it done right (I didn’t like the look of the standard flue hangers and had a custom SS plate bent up to fit). (BTW DIY is fine with BC involvement.) No external air supply - I leave one trickle vent open near the stove and that’s it. We have a nest combined smoke & CO alarm and, as I have asthma, I have a Davis particulate detector as a check. We use the stove a lot and everything is good.

 

Yeah in the new place we’ll be passivehouse-like insulation and air tightness … and therefore have external air supply for it.

DIY is fine with BC eh, interesting. I haven’t found a hetas guy I trust yet. The local one who has done a few in our area didn’t fill me with confidence when he casually suggested he didn’t need to measure up for a register plate and would just cut something on site and fix it with silicon.

Link to comment
Share on other sites

9 hours ago, HughF said:

DIY is fine with BC eh, interesting. I haven’t found a hetas guy I trust yet. The local one who has done a few in our area didn’t fill me with confidence when he casually suggested he didn’t need to measure up for a register plate and would just cut something on site and fix it with silicon.

Many BCOs won’t sign off a woodburner install however perfect, and insist on. Hetas person signing it off.  
 

9 hours ago, HughF said:

4 chimney pots on the top - each fireplace had a separate run up the chimney. I will have two liners installed, one per appliance.

So the perfect arrangement for recirculating smoke down a flue.  Hmmmm. Maybe it is worth running some duct to the outside, perhaps even up to ceiling level then outside somehow. 
 

Are you sure you can’t pick just one woodburner as your emergency hear source?

Link to comment
Share on other sites

19 hours ago, HughF said:

DIY is fine with BC eh, interesting. I haven’t found a hetas guy I trust yet. The local one who has done a few in our area didn’t fill me with confidence when he casually suggested he didn’t need to measure up for a register plate and would just cut something on site and fix it with silicon.

 

9 hours ago, G and J said:

Many BCOs won’t sign off a woodburner install however perfect, and insist on. Hetas person signing it off.  

 

My BCO signed off my self installed stove with ducted direct air intake.  They were over it like a rash with a tape measure comparing clearance distances to what it said in the installation manual.  Once happy with that they signed it off.

 

 

Link to comment
Share on other sites

9 hours ago, G and J said:

So the perfect arrangement for recirculating smoke down a flue.  Hmmmm. Maybe it is worth running some duct to the outside, perhaps even up to ceiling level then outside somehow. 

I had that in a previous house.  A 1930s semi.  It did not have much heating when I moved in and still had an open fire in the living room.  On a still cold ight I lit the fire.  Later I went upstairs, only to find smoke everywhere.  Being a windless night, the smoke was not being blown away from the chimney and it turned out the easiest way for the air drawn by the fire to be replaced, was by sucking air down a bedroom chimney down the stairs and under the living room door, and that was drawing smoke with it down the bedroom chimney.

 

There was no proper vent anywhere for the fire, only leaks in the building.

Link to comment
Share on other sites

26 minutes ago, ProDave said:

I had that in a previous house.  A 1930s semi.  It did not have much heating when I moved in and still had an open fire in the living room.  On a still cold ight I lit the fire.  Later I went upstairs, only to find smoke everywhere.  Being a windless night, the smoke was not being blown away from the chimney and it turned out the easiest way for the air drawn by the fire to be replaced, was by sucking air down a bedroom chimney down the stairs and under the living room door, and that was drawing smoke with it down the bedroom chimney.

 

There was no proper vent anywhere for the fire, only leaks in the building.

In a cottage in Norfolk I installed a fan in the kitchen flue which we had to have running to stop smoke being drawn down when we first lit the lounge fire.  It was usually ok once the fire and thence chimney git going nice and warm, presumably because the warm gases simply rose up past the other chimney pots.   
 

Oddly, a tiny whiff of woodsmoke I find comforting.   Any more than that is nasty.  

Link to comment
Share on other sites

On 23/01/2025 at 09:53, Mike said:

You'd need a 'room sealed' stove 

I'm of the opinion that this is a good, though expensive, way of reducing heat loss yet keeping ventilation. 

Ignoring fire lit times, Outdoor air flows up the chimney and keeps it dry. Perhaps that reverses sometimes.

Indoor, heated air cannot rush up and out. 

It is shocking how much warm  air  is flying out of  our chimney without a fire lit.

I had one of those umbrella thingies in our open fire but lost it...you know how.

 

That would have been even messier with a bin bag of fibreglass, which I may stuff up. Payback about 10 minutes. Risk??

  • Like 1
Link to comment
Share on other sites

11 hours ago, G and J said:

Many BCOs won’t sign off a woodburner install however perfect, and insist on. Hetas person signing it off.  
 

So the perfect arrangement for recirculating smoke down a flue.  Hmmmm. Maybe it is worth running some duct to the outside, perhaps even up to ceiling level then outside somehow. 
 

Are you sure you can’t pick just one woodburner as your emergency hear source?

If I had my way, I’d take the chimney down to open up the loft and block the chimneys up, but wife is insistent - ‘you had your way on the heat pump vs combi argument, you’re not winning this one’. Two solid fuel (we’ll never run them on wood, if I’m going to buy fuel, I’ll buy smokeless ovoids) stoves it is, unfortunately.

Edited by HughF
Link to comment
Share on other sites

>>> Many BCOs won’t sign off a woodburner install

 

FYI my install was one on an existing dwelling rather than a new build and with LA BC. I sent in some drawings, highlighting the safe distances, materials, suppliers etc. Installed the stove. Sent a doc with narrative & photos, testing etc. BC guy visited, asked me about the CO detector, and signed it off.

 

I do agree though that BCOs are moving to the stage where they don't check or sign off much at all. They just check that someone else has signed it off.