Temp Posted yesterday at 00:11 Share Posted yesterday at 00:11 (edited) After some info/advice on breaker curves and/or soft start/in-rush limiting.. Our local village hall is having issues with its IR electric heaters tripping at switch on. There are 6 heaters each on their own C16 30mA RCBO. I don't currently know the wattage of each heater but it looks like they have 6 elements in each so I'm assuming they are quite powerful units. My background is in electronics rather than electrical engineering so I've just been asked to "translate" what the electrician is saying when they can get him to visit next time. For the moment I'm assuming they are tripping due to inrush current rather than Earth leakage but will ask if he's checked that. The wiring doesn't look too old. It looks like last time he visited he switched one of the RCBO for a B20. That one seems to be OK but three others on C16 are tripping. As I understand it.. C curve trip between 5 and 10 times rated current within 1 second. So a C16 trips between 80 and 160 A. B curve trip between 3 and 5 times rated current between 1 and 5 seconds. So a B20 trips between 60 and 100A. Q1: So tentatively it sounds like the issue is the duration of the inrush current rather than the magnitude of the inrush current? Q2: The whole lot are on one 100A RCD (I think) so I suspect he can't switch them all to B20 because 6 x 20A = 120A. They are normally all on at once so can't apply diversity? Or am I talking bollocks 🙂 Q3: Would it be reasonable to try 6 x B16 instead of C16 as they tolerate overload for a bit longer or am I misunderstanding how they work? Have heard conflicting info from the Village Hall committee. One said the electrician was considering adding in-rush current limiting at £25 to £100 per heater, but another added "or rewiring". I think each heater is on a 2.5mm^2 radial. Part clipped, part loose in the roof and part in metal conduit. I think a 2.5mm^2 radial is typically limited to 16-20A. Any suggestions for how to diagnose the problem ? Do electricians carry a fancy meter that can measure in-rush peak durations ? I suspect not. Edited yesterday at 00:14 by Temp Link to comment Share on other sites More sharing options...
Nickfromwales Posted yesterday at 01:18 Share Posted yesterday at 01:18 1 hour ago, Temp said: Do electricians carry a fancy meter that can measure in-rush peak durations ? I suspect not. A simple clamp meter wouldn’t suffice. This will be measured within a human ‘blink’. 1 hour ago, Temp said: Or am I talking bollocks 🙂 Oi!!!! Get your own job A C curve breaker is usually the more tolerant of “surge current”, caused by “shunt resistance” in motors usually, or lots of fluo lights etc. I would have thought C curve would be a ‘pikey’ solution but @ProDave and @Onoff are the books on this vs my less qualified understanding. 1 hour ago, Temp said: The whole lot are on one 100A RCD (I think) so I suspect he can't switch them all to B20 because 6 x 20A = 120A. They are normally all on at once so can't apply diversity? Look at a domestic CU, where quite often or not (usually always) the total amps of each circuit massively outweighs the rating on the front of house isolator. I would suggest these were brought on by contactors which had programmable ‘delay on’ or even Shely’s perhaps, to bring them on one after the other. Depends on how they’re then used / turned on & off when room temps are achieved. Link to comment Share on other sites More sharing options...
Temp Posted yesterday at 01:28 Author Share Posted yesterday at 01:28 3 minutes ago, Nickfromwales said: I would suggest these were brought on by contactors which had programmable ‘delay on’ or even Shely’s perhaps, to bring them on one after the other. Depends on how they’re then used / turned on & off when room temps are achieved. As I recall you have to walk around the room switching on each heater in turn so I don't think the issue is multiple heaters being turned on at the same instant. 1 Link to comment Share on other sites More sharing options...
Onoff Posted 19 hours ago Share Posted 19 hours ago Is this a new issue? Is the B20 RCBO he's fitted the same make as the C16 one it replaced? The type of RCD section within RCBOs can vary: https://www.electrical-installation.org/enwiki/Types_of_RCDs The individual RCBOs should have an RCD test applied to gauge tripping and also their ramp times. The fact that it's been upped to a 20A and not tripping is perhaps telling. B curve is for low inrush currents, C for medium and D for high. If it's an inrush issue then it's usual to go from B to C curve or even D not the other way. If the cumulative load is too much for the incoming supply then you might need to think about spreading it across phases if you have 3P coming in. Or timers. As for diversity on heating then in a domestic premises this would be 100% up to 10A + 50%. There are other ratings for other than domestic in the OSG. Find out the rating of each unit. Link to comment Share on other sites More sharing options...
Temp Posted 9 hours ago Author Share Posted 9 hours ago @Onoff & @Nickfromwales I think it started getting worse as the weather got colder but then again they aren't used much in summer. I was able to speak to the electrician briefly today. He confirmed.. Each heater is 3kW (approx 12.5A). The insulation breakdown tests he did recently passed ok He plans to change the RCBOs from C16 to C20s but might not be able to do them all. Think he said he needed to check the wire impedance to ensure they would trip if there was a short? He also mentioned he's considering investigating NTC devices to limit inrush. Ive used these before as auto resettable fuses at much lower currents. But not for high power applications like this. I know they can be a bit tricky to get the right spec. Dimplex who sold the heaters say they aren't made/supported now. Link to comment Share on other sites More sharing options...
Alan Ambrose Posted 8 hours ago Share Posted 8 hours ago (edited) OK hold my beer.... Get your sparks to disconnect and measure the cold resistance of a heater and the voltage you actually have there on no-load (or if they're lazy, just assume 230V). Divide one by the other and that's your inrush current. If you've ever seen an old fashioned resistance heater heat up, you'll remember it takes a minute or so to do that. That is, much longer than any RCBO curve, which are designed for machinery in-rush currents. While it's heating up, the resistance goes up and the current goes down ... until it reaches a steady state. Measure the current at this stage with a clamp meter and you'll know the steady-state current (and hot resistance come to that). Now you've got inrush current and steady-state current. Just size your MCBs/RCBOs accordingly to fit the inrush current (actually cold-state current - there's not really an inrush currrent - that is usually associated with sub-1s timescale). Yeah, probably 20A, but worth checking to avoid further problems. BTW, worth the sparks checking the nominal power of the heaters - on a 16A trip, each is probably 3kW. Yeah, I appreciate they probably dont glow... Edited 8 hours ago by Alan Ambrose Link to comment Share on other sites More sharing options...
Nickfromwales Posted 8 hours ago Share Posted 8 hours ago 20 minutes ago, Temp said: He plans to change the RCBOs from C16 to C20s but might not be able to do them all. Think he said he needed to check the wire impedance to ensure they would trip if there was a short? I’d want to hear from a governing body and then have a method statement in place if doing something ‘bespoke’ and pushing these boundaries, given this is for a 3rd party public venue. I’d prob say go for B20’s not C20’s as there should be no need for the C capability. Link to comment Share on other sites More sharing options...
Onoff Posted 8 hours ago Share Posted 8 hours ago 6 minutes ago, Nickfromwales said: Think he said he needed to check the wire impedance to ensure they would trip if there was a short? Did he say earth loop impedance? Link to comment Share on other sites More sharing options...