lookseehear Posted October 1, 2024 Share Posted October 1, 2024 Hi all, hoping for a nudge in the right direction. Our house was two 1800ish miners' cottages which were knocked together with limestone/rubble filled 500mm thick walls. It was extended in the 1970s to the rear with a block cavity wall, albeit only a 50mm cavity, and faced with limestone. The roof has poor/negligible insulation currently and the floors are mostly solid/uninsulated concrete. We put in a worcester bosch external oil boiler with an unvented cylinder about 3 years ago because the old boiler was 30+ years old and we couldn't keep it going any longer. The windows are mostly blown aluminium DGUs which are draughty, and in general it's a draughty house. When we put in the new boiler I also put in a Wiser heating control system with smart TRVs which has helped keep heating bills down because we only heat the rooms we need when we need them, but in general it's a cold house. We've just started an extensive extension/renovation which will result in some big changes. We're going 'upside down' with bedrooms downstairs and living space upstairs to take advantage of better views increase ceiling height and natural light with vaulted ceilings/roof lights and allow us to open up the living space more easily We'll replace all windows with new TGUs and all doors will be replaced We're replacing the roof, so will insulate to building regs (0.15 U value) We're having a new ground floor extension which will have our bedroom in, which we will put wet underfloor heating in as we'll be insulating floor, walls and ceiling to modern standards We're replacing kitchen and bathrooms I'm in a bit of a bind about what to do with the heating at the moment. My ideal solution would be an ASHP driving wet UFH throughout the downstairs, but this means we would need to dig out and replace the floors to add insulation. I'd like to use an air to air heat pump upstairs to heat the open plan living space, and also provide cooling in the summer. If we decide not to dig up the floors, that means putting rads in the other rooms downstairs or using an overlay wet UFH heating system, but if we're keeping radiators, maybe we also keep the boiler given it's only a few years old. I know that the improvements we're making will make a huge difference to the heating performance in the house, but I'm still unsure what the best option is, and what the second best might be if the best option proves too costly. Based on the estimates on the heatgeek website, a heat requirement of 50W/m2 would seem reasonable, which would mean we need roughly 5.5kw for downstairs and 4.5kw upstairs. Probably some kind of heat loss calculation would be helpful, but I'm not really sure where to go for this, or how accurate it would be given the renovations are evolving and not set in stone. Should we just keep it simple and stick with rads everywhere but in the new extension which is fully insulated? I'd rather not do this if possible, as we'd like to move to an ASHP and get rid of the boiler, and like the idea of UFH in bedrooms and bathrooms. Another option is to insulate the solid stone walls, and we had looked at EWI but decided against it for now due to the cost, change of appearance and apparent risks involved with getting it right. Literally any thoughts and opinions are valid here, other than about the layout, which we're very set on at this point. Link to comment Share on other sites More sharing options...
Conor Posted October 2, 2024 Share Posted October 2, 2024 Controversial suggestion, but you could save the £15k+ you'd need for a new heating system and spend it on insulating the walls and keep the oil boiler. Spending more on insulation will make more of a difference than anything else. UFH is more costly to run than rads, and is a no goer unless you've a decent amount of insulation in the floor (150mm+).Do you have the room inside for internal wall insulation? 1 Link to comment Share on other sites More sharing options...
ReedRichards Posted October 3, 2024 Share Posted October 3, 2024 On 02/10/2024 at 06:54, Conor said: UFH is more costly to run than rads Not wet UFH, surely? Link to comment Share on other sites More sharing options...
Conor Posted October 3, 2024 Share Posted October 3, 2024 28 minutes ago, ReedRichards said: Not wet UFH, surely? Yes, been covered here before. You're directly heating the ground, essentially. Applies only to ground floor of course. Link to comment Share on other sites More sharing options...
ReedRichards Posted October 3, 2024 Share Posted October 3, 2024 Surely it depends on how much insulation you have under your slab? And you can probably run your UFH at a lower temperature than radiators which should reduce the running cost? Otherwise why on earth does anyone go to all trouble of installing UFH and the risk of having to dig it up later should anything go wrong? Link to comment Share on other sites More sharing options...
lookseehear Posted October 3, 2024 Author Share Posted October 3, 2024 On 02/10/2024 at 06:54, Conor said: Controversial suggestion, but you could save the £15k+ you'd need for a new heating system and spend it on insulating the walls and keep the oil boiler. Spending more on insulation will make more of a difference than anything else. UFH is more costly to run than rads, and is a no goer unless you've a decent amount of insulation in the floor (150mm+).Do you have the room inside for I ternal wall insulation? You've got me thinking about internal insulation again, but given that the walls of the old part of the house are solid/rubble filled limestone I'm a little nervous due to condensation risks. It would also change the thermal mass of the building somewhat, as we'd only be heating internal air and furniture etc vs now having some thermal mass in the walls. I wouldn't try to get the best U value from these walls, as I understand going below 0.3 is where the highest risks are for interstitial condensation, so improving to something like 0.4-0.6 might be sensible with some breathable internal insulation which also wouldn't take up too much floor space. The overwhelming reason for wanting UFH though is because we currently wear slippers from September to April/May due to cold floors, and for both my wife and I it would be a huge improvement to thermal comfort to have warm feet, particularly in bathrooms, but bedrooms would be lovely too. Although quite a lot of heat would be lost through the floor, warming the bedrooms in the morning would mean that heat would move upwards through the house into the living space during the day, which reduces the heat requirement of the living space fairly significantly (I would imagine). Link to comment Share on other sites More sharing options...
lookseehear Posted October 3, 2024 Author Share Posted October 3, 2024 20 minutes ago, ReedRichards said: Surely it depends on how much insulation you have under your slab? And you can probably run your UFH at a lower temperature than radiators which should reduce the running cost? Otherwise why on earth does anyone go to all trouble of installing UFH and the risk of having to dig it up later should anything go wrong? It seems that anecdotally people with low profile UFH heating systems with not much insulation still really like them, despite the idea that they increase heating costs. Maybe the backlash will come in a year or two as it feels like low profile UFH is still relatively new to market. I've seen calculations referenced multiple times on BH that even with 300mm of EPS, 10% of heat from UFH is lost through the floor. This seems high to me and (I believe) is based on the assumption that the ground is always at 8 degrees C, which it will be if you go low enough, but I suspect is not the case directly under a floor slab. These things are complex and trying to navigate a path between the science and the experience of people who live with the systems is difficult without going insane! Link to comment Share on other sites More sharing options...
Iceverge Posted October 3, 2024 Share Posted October 3, 2024 (edited) 1 hour ago, ReedRichards said: Surely it depends on how much insulation you have under your slab? And you can probably run your UFH at a lower temperature than radiators which should reduce the running cost? Otherwise why on earth does anyone go to all trouble of installing UFH and the risk of having to dig it up later should anything go wrong? It's fashionable. It's cheap to do on a new build. You don't have to juggle furniture with radiators. People love the feeling of a hot floor,however....... Hot floors are a sign of very inefficient UFH. An efficient UFH system with a huge chunk of insulation underneath will feel the same as a non heated floor with a huge chunk of insulation underneath. Not hot - Not cold. By all means stick some electric UFH just under the bathroom tiles for a little bit of luxury in the morning post shower. My 2p worth, install big pipes and rads and continue with the boiler. It'll run more efficiently at low flow temps anyway I think . Calling @JohnMo? When it dies swap for an ASHP. Get some insulation on the walls, anything is worth it. Parged brick, battened service cavity with mineral wool and then plasterboard my favourite method at the moment. Get your airtighess strategy nailed.. Install some kind of continuous mechanical ventilation. Even a few dDCV fans will make a world of difference to the health of the occupants and the building. Good luck and welcome to the forum. Edited October 3, 2024 by Iceverge 1 Link to comment Share on other sites More sharing options...
Iceverge Posted October 3, 2024 Share Posted October 3, 2024 1 hour ago, lookseehear said: You've got me thinking about internal insulation again, but given that the walls of the old part of the house are solid/rubble filled limestone I'm a little nervous due to condensation risks. It would also change the thermal mass of the building somewhat, as we'd only be heating internal air and furniture etc vs now having some thermal mass in the walls. I wouldn't try to get the best U value from these walls, as I understand going below 0.3 is where the highest risks are for interstitial condensation, so improving to something like 0.4-0.6 might be sensible with some breathable internal insulation which also wouldn't take up too much floor space. The overwhelming reason for wanting UFH though is because we currently wear slippers from September to April/May due to cold floors, and for both my wife and I it would be a huge improvement to thermal comfort to have warm feet, particularly in bathrooms, but bedrooms would be lovely too. Although quite a lot of heat would be lost through the floor, warming the bedrooms in the morning would mean that heat would move upwards through the house into the living space during the day, which reduces the heat requirement of the living space fairly significantly (I would imagine). I think I'm going to start a therapy group for confused DIYers regarding thermal comfort, energy usage and building health. Don't worry, I too was once afflicted. Symptoms include using the phrases "Thermal Mass" "Breathable/Breathability" "My old builder/architect said" "ASHP/Gas/Solar is always or never either excellent or terrible" "It's Eco isn't it!" Confusing and conflating Airtightness and breathability (whatever that is) and ventilation. Mixing up environmental pollution, climate change, embodied carbon, recyclability running costs and things that are green and indeed greenwashed. Don't worry, you are not alone. 1 Link to comment Share on other sites More sharing options...
Mike Posted October 3, 2024 Share Posted October 3, 2024 On 02/10/2024 at 07:54, Conor said: you could save the £15k+ you'd need for a new heating system and spend it on insulating the walls and keep the oil boiler. Spending more on insulation will make more of a difference than anything else. UFH is more costly to run than rads, and is a no goer unless you've a decent amount of insulation in the floor (150mm+). +1. Take a look again at the EWI & IWI options. 59 minutes ago, Iceverge said: Get your airtighess strategy nailed Install some kind of continuous mechanical ventilation +1 again. If you still have spare cash after all the above, then consider UFCH, with plenty of insulation below the slab. Link to comment Share on other sites More sharing options...
Nickfromwales Posted October 3, 2024 Share Posted October 3, 2024 If introducing a single zone of UFH to an existing oil boiler, you may also run in to issues with short cycling. This would require either certain rads coming on in unison as heat loss (hall / stairs / bathrooms), or a buffer tank being added to the UFH circuit, or the UVC being swapped out to a thermal store (with DHW coil inside it for hot water). You'll also need independent (additional) heating controls for the UFH'd areas to 'zone' them; these will need set-back times that start sooner / end sooner than the areas with rads. Ahhhh....the joys.... UFH here would be a 'want' vs a 'need', so forget any savings or economics tbh. You either do an overlay system and suck up the inefficiencies or dig out and fit lots of insulation, either option will have cost and performance impacts / pros / cons / caveats to swing each argument for / against, so choose wisely. UFH well installed is the best thing of all, but poorly installed (then poorly performing) UFH is utter garbage to live with. Dealing with draughtproofing will be your No.1 priority in any of these cases, to lower the amount of heat required in the first place, so always consider a fabric-first approach at all times. Further note that the closer you get to 'airtight' the closer you get to needing to fit mechanical (forced) ventilation too, so yet another can of worms to then consider for Part O....! Link to comment Share on other sites More sharing options...
ReedRichards Posted October 3, 2024 Share Posted October 3, 2024 8 hours ago, lookseehear said: I've seen calculations referenced multiple times on BH that even with 300mm of EPS, 10% of heat from UFH is lost through the floor. This seems high to me and (I believe) is based on the assumption that the ground is always at 8 degrees C, which it will be if you go low enough, but I suspect is not the case directly under a floor slab. No, it will be hotter because you are heating it with your UFH. Or even if not you will still be losing heat through the floor but if it's 10% with UFH it must be about 5% without; given the same floor covering. I suppose the worst case would be if the heat that penetrates the insulation can escape laterally to something that is colder than 8 degrees C. So you would have to level the ground, cover that with an appropriate membrane then insulation but around the edge of that insulation you need to dig a trench down to where the ground really is 8 C and fill that trench with insulation. Link to comment Share on other sites More sharing options...
SteamyTea Posted October 4, 2024 Share Posted October 4, 2024 On 03/10/2024 at 12:23, Iceverge said: I think I'm going to start a therapy group Do it. Be fun to see how sustainable it is. Link to comment Share on other sites More sharing options...
SteamyTea Posted October 4, 2024 Share Posted October 4, 2024 On 03/10/2024 at 11:11, lookseehear said: I've seen calculations referenced multiple times on BH that even with 300mm of EPS, 10% of heat from UFH is lost through the floor. This seems high to me and (I believe) is based on the assumption that the ground is always at 8 degrees C Not going to be far out as you only need to heat at the coldest, and generally wettest, times of the year. As for going with radiators, how much area can you fit, can you easily fit larger radiators (maybe a total of 60% of the floor surface area as you don't totally pipe out all the floor area). How about plinth/fancoil units, they can give a quick boost and some are pretty quiet. Easy and cheap solution is below, it is only Canadians that make it law to take your shoes off indoors. 1 Link to comment Share on other sites More sharing options...
lookseehear Posted October 4, 2024 Author Share Posted October 4, 2024 9 hours ago, SteamyTea said: Not going to be far out as you only need to heat at the coldest, and generally wettest, times of the year. As for going with radiators, how much area can you fit, can you easily fit larger radiators (maybe a total of 60% of the floor surface area as you don't totally pipe out all the floor area). How about plinth/fancoil units, they can give a quick boost and some are pretty quiet. Easy and cheap solution is below, it is only Canadians that make it law to take your shoes off indoors. Good point about time of year - you're probably right. We haven't thought about where radiators would go, but that was part of the reason for wanting UFH, so that we didn't have that to think about. I'd need to go back to the plans and see where the best place would be in each room. One issue we have is that we are on heating oil, so we are more restricted vs even gas where you can lower flow temperatures to improve efficiency. I imagine that we might need some kind of thermal store/buffer to run the UFH in the main bedroom (which will be fully insulated) on oil, which means it isn't just reusing the boiler and hot water tank and sticking in some new radiators. I've seen some of the discussion about fancoil units but I assume they would also require a ASHP or thermal store? I like the idea of air heating because of how quickly you can change the temperature, which is why I was leaning towards having an air to air unit in the open plan living space. On 03/10/2024 at 11:46, Iceverge said: Get some insulation on the walls, anything is worth it. Parged brick, battened service cavity with mineral wool and then plasterboard my favourite method at the moment. Is this method suitable for solid stone/rubble filled walls (sorry but I have to use the word 'breathable')? Is there more detail on what you're proposing? On 03/10/2024 at 11:46, Iceverge said: My 2p worth, install big pipes and rads and continue with the boiler. It'll run more efficiently at low flow temps anyway I think . Calling @JohnMo? When it dies swap for an ASHP. I'm not sure this is the case with oil boilers. The installer of ours said that downregulating the burner too much isn't good for it. Oil boiler tech seems a bit behind gas boiler tech in terms of regulating the power output. On 03/10/2024 at 13:25, Nickfromwales said: If introducing a single zone of UFH to an existing oil boiler, you may also run in to issues with short cycling. This would require either certain rads coming on in unison as heat loss (hall / stairs / bathrooms), or a buffer tank being added to the UFH circuit, or the UVC being swapped out to a thermal store (with DHW coil inside it for hot water). I like the idea of a thermal store to use excess solar for example (imagine guilt free long showers 😆) but I've been following the HeatGeek YouTube channel and they seem to believe that to have a really efficient ASHP system you need to have no buffer tank, just run weather compensation with no zoning, keeping the lowest flow temps with the highest uptime possible, so I don't want to buy into a system that if we do upgrade to ASHP in the future becomes redundant. You've got me fairly convinced on the idea of investing in insulation rather than UFH, however we still won't be putting in EWI for a variety of reasons, so I think we'll be putting EPS bead CWI in the existing extension (50mm cavity between blockwork) and I need to work out what we're going to do with the solid limestone walls. If we can avoid lime plaster that would work well with our builder, who says he 'likes to throw a handful of cement in just to make it go off', so I need to find a system that Doesn't wreck the 'breathability' of the walls Doesn't encroach too much into the room (the walls are already 500mm+ downstairs so I'd want to avoid making them significantly thicker) Ideally uses conventional plasterboard Can be worked into an airtightness strategy (answers on a postcard) I'm also nervous about IWI because of potential cold bridges in the void between ground floor ceiling and first floor floorboards. So much to learn and investigate and so many potential pitfalls! Link to comment Share on other sites More sharing options...
Jilly Posted October 5, 2024 Share Posted October 5, 2024 I made a post called ‘Interrelated Concept Confusion’ when I was at your stage. You are doing the right thing making sure you are completely up to speed on the pros and cons (and be aware of the head explosion it will cause via sleepless nights) so you can stand your ground with your builder on the compromises/decisions you have made, and check back here when they throw up objections. Take your time. 1 Link to comment Share on other sites More sharing options...
JohnMo Posted October 5, 2024 Share Posted October 5, 2024 On 01/10/2024 at 23:29, lookseehear said: UFH throughout the downstairs Not sure that would be the best solution, the floor takes an age to heat up then an age to cool down. So chasing your tail to get the right temp for sleeping. Upstairs if going A2W no need for A2A, just use a fan coil connected to A2W HP. Then you have heat and cool in a single unit. On 01/10/2024 at 23:29, lookseehear said: Probably some kind of heat loss calculation would be helpful Yep If you keep oil, consider a thermal store, to provide DHW and a buffer for the oil boiler to give a decent run time, especially if you have zoned heating. Pul the CH water direct from buffer. On 01/10/2024 at 23:29, lookseehear said: When we put in the new boiler I also put in a Wiser heating control system with smart TRVs which has helped keep heating bills down because we only heat the rooms we need when we need them, but in general it's a cold house. This would be rubbish with a heat pump. You will also need to be careful with the oil boiler short cycling, with lots of zones On 03/10/2024 at 11:05, lookseehear said: overwhelming reason for wanting UFH though is because we currently wear slippers from September to April/May due to cold floors Good UFH doesn't equal a warm or hot floor, poorly installed does. Well insulated, you are flowing mid to high 20s, maybe low 30s on a very cold day. On 03/10/2024 at 11:46, Iceverge said: My 2p worth, install big pipes and rads and continue with the boiler. It'll run more efficiently at low flow temps anyway I think . Would agree. On 03/10/2024 at 11:11, lookseehear said: These things are complex and trying to navigate a path between the science and the experience of people who live with the systems is difficult without going insane! I would step back Decision 1 - keep or dump oil. Once made every thing else starts to fall in to place. Just jump one side or the other, don't keep jumping. UFH downstairs - not the best solution, simple low temp radiator, with a manual TRV to manage room temp. Good for Oil or HP Same upstairs if oil and A2A. Or fan coils for A2W. Thermal store for Oil, HP UVC for A2W HP. 1 Link to comment Share on other sites More sharing options...
JamesPa Posted October 5, 2024 Share Posted October 5, 2024 15 hours ago, lookseehear said: I like the idea of a thermal store to use excess solar for example (imagine guilt free long showers 😆) but I've been following the HeatGeek YouTube channel and they seem to believe that to have a really efficient ASHP system you need to have no buffer tank, just run weather compensation with no zoning, keeping the lowest flow temps with the highest uptime possible, so I don't want to buy into a system that if we do upgrade to ASHP in the future becomes redundant. If all you want from your thermal store is long showers, then thats just a big domestic hot water tank, its nothing at all to do with buffer tanks. Link to comment Share on other sites More sharing options...
Nickfromwales Posted October 5, 2024 Share Posted October 5, 2024 48 minutes ago, JamesPa said: If all you want from your thermal store is long showers, then thats just a big domestic hot water tank, its nothing at all to do with buffer tanks. +1. Bigger tank, lower temps, less losses, no brainer. Link to comment Share on other sites More sharing options...
ReedRichards Posted October 5, 2024 Share Posted October 5, 2024 16 hours ago, lookseehear said: I've been following the HeatGeek YouTube channel and they seem to believe that to have a really efficient ASHP system you need to have no buffer tank, just run weather compensation with no zoning, keeping the lowest flow temps with the highest uptime possible That's not wrong but you would have to carefully balance every radiator in the house for it to work. Efficiency is great, it saves you money. But you can save even more money by wearing lots of clothes and not bothering to heat your house. So be aware that you may be sacrificing convenience for the sake of efficiency. Link to comment Share on other sites More sharing options...
Mike Posted October 5, 2024 Share Posted October 5, 2024 (edited) 8 hours ago, JohnMo said: Good UFH doesn't equal a warm or hot floor, poorly installed does. Well insulated, you are flowing mid to high 20s, maybe low 30s on a very cold day. +1. However without UFCH the floor will be several degrees below air temperature in mid-winter, so it's not surprising that floors feel cold. With UFCH (provided the house is air-tight and well insulated, and provided all rooms on the floor are heated to the same temperature) there is also typically 2 or 3°C less variation in air temperature between floor and ceiling, compared to using radiators. All other things being equal, UFCH can therefore provide better thermal comfort but, as mentioned above, it shouldn't be the priority - airtightness, insulation and MVHR should come first. Edited October 5, 2024 by Mike 1 Link to comment Share on other sites More sharing options...
lookseehear Posted October 7, 2024 Author Share Posted October 7, 2024 (edited) Thank you all for the incredibly helpful replies! I've come up with a rough plan, which still needs some development, but I'm feeling optimistic about it. The Plan: Thermal Store for Heating and Hot Water I'm considering installing a large thermal store (around 400-500L) to handle both heating and DHW while keeping the existing oil boiler. Solar PV Integration We’ll be installing solar PV, but likely without a battery for now. Excess solar energy can be diverted to the thermal store for heating and DHW. Electricity and Oil Cost Comparison We're on an EV electricity tariff, which gives us cheap electricity at 8.5p/kWh from 00:30 to 05:30. Currently, oil costs about 60p/litre, which contains 10.2 kWh of energy per litre. However, with the boiler’s 85% efficiency, the cost of heating from oil is around 7.5p/kWh. So, we can use cheap electricity to 'charge up' the thermal store overnight at roughly the same cost as heating with oil. Of course, this may change with fluctuating oil and electricity prices. Heating in Bedrooms We plan to install large radiators or FCUs in the bedrooms and avoid UFH in areas without insulation. Main Living Space In the upstairs living area, we’re thinking of large radiators, and perhaps plinth FCUs in the kitchen to provide an extra heating boost if needed. Bedroom in New Extension For the new extension, we’ll install wet UFH. However, instead of embedding it in screed, we might use an overlay system on top of a well-insulated slab. This would allow the room to cool overnight and heat up quickly when needed, making the UFH act more like a radiator - any pros/cons here? Bathrooms We have two downstairs bathrooms (en-suite and main bathroom) in the older part of the house. I’d like to install UFH for extra comfort underfoot. With 100mm of PIR insulation and 50mm of screed, head height shouldn't be too compromised. A wet overlay system over 100mm PIR might be the best option here. Additional Insulation 1970s Extension: Considering using EPS beads in the 50mm cavity. External Insulation: I’m tempted to install 150mm of EPS around the foundation downstand (about 600mm deep) to reduce heat loss through the floors over time. This wouldn’t go around the entire property but could cover about 50%. Internal Wall Insulation (IWI): For the external rubble limestone walls, we might use wood fibre or hemp insulation between studs/battens with lime plaster on top. If we decide to excavate back to the stone inside, this could be a practical option but I'm open to others. Airtightness and MVHR I’m learning more about airtightness and plan to incorporate this along with an MVHR system. Instead of an ASHP, we’ll invest in the MVHR. Ducting should be fairly straightforward as the MVHR unit would sit in an insulated roof space, with easy access to the plant room. Questions I Still Have: Fan Coil Units (FCUs) Noise: How noisy are FCUs compared to radiators? My wife is particularly sensitive to noise, so this is a concern for us. Radiators vs. FCUs: Are there any downsides to using FCUs over radiators? When would you choose a radiator if an FCU is smaller, quicker to heat a room and runs at a lower flow temp (therefore more efficient)? Heat Stores Compatibility: Do thermal stores work well with radiators, FCUs, and wet UFH systems? My assumption is that the oil boiler could act as a fallback (e.g., if the store drops below 60°C), and the solar PV could power the immersion heater when we have excess electricity. Combined with using off-peak electricity I'd hope we can reduce our oil usage to the point that we could downsize from the 1200l tank we have currently in the garden. Flexibility: Am I right in thinking that with a heat store, it would be just as easy to put an UFH loop as an FCU or radiator, assuming there would be a small manifold required too? Controllers Ease of Use: Are there controllers that work well with a mix of UFH, radiators, and FCUs? Ideally, the system should be simple enough for my wife, who prefers not to deal with complex controls, even though she’s very capable. Any other feedback on this as the basis of a solution? Thanks in advance. I've attached some floor plans for reference. Edited October 7, 2024 by lookseehear Images Link to comment Share on other sites More sharing options...
Gone West Posted October 7, 2024 Share Posted October 7, 2024 (edited) @lookseehear It's amazing how similar our properties and heating solutions are. Ours started as a pair of 1840s sandstone and cob cottages. In the 1970s they were knocked into one and the cob first storey removed leaving a sandstone/rubble walled bungalow. This was then increased in size with a concrete block, cavity walled, extension. Currently heated with an old oil fired Aga, we will be updating to an external condensing oil boiler heating a thermal store connected directly to the radiator heated central heating. We already have PV and solar thermal to help heat the TS. It will use a plate heat exchanger for DHW. The cavity walls, 70mm, will have EPS beads CWI and the 600mm stone walls will have hempcrete type IWI. The cold loft will have 400mm insulation. Good luck with your project. Edited October 7, 2024 by Gone West Added more details. 1 Link to comment Share on other sites More sharing options...
sharpener Posted October 8, 2024 Share Posted October 8, 2024 23 hours ago, lookseehear said: Do thermal stores work well with radiators, FCUs, and wet UFH systems? We have a 270 litre custom TS from Newark Cylinders to time-shift so we can run the rads from night rate electricity. Working well so far. I assume you will be having one with a coil for the HW like the new Heat Geek cylinders? You will need a lot of solar PV to make much of a dent in a 400 litre tank! 1 kWh is only 860 litre-degrees. Link to comment Share on other sites More sharing options...
lookseehear Posted October 8, 2024 Author Share Posted October 8, 2024 20 hours ago, Gone West said: @lookseehear It's amazing how similar our properties and heating solutions are. Ours started as a pair of 1840s sandstone and cob cottages. In the 1970s they were knocked into one and the cob first storey removed leaving a sandstone/rubble walled bungalow. This was then increased in size with a concrete block, cavity walled, extension. Currently heated with an old oil fired Aga, we will be updating to an external condensing oil boiler heating a thermal store connected directly to the radiator heated central heating. We already have PV and solar thermal to help heat the TS. It will use a plate heat exchanger for DHW. The cavity walls, 70mm, will have EPS beads CWI and the 600mm stone walls will have hempcrete type IWI. The cold loft will have 400mm insulation. Good luck with your project. I love this! I can have a look back through your posts to see if there's anything relevant, but I'd love to hear in particular why you decided on hempcrete vs another type of insulation for the solid walls. 15 minutes ago, sharpener said: We have a 270 litre custom TS from Newark Cylinders to time-shift so we can run the rads from night rate electricity. Working well so far. I assume you will be having one with a coil for the HW like the new Heat Geek cylinders? You will need a lot of solar PV to make much of a dent in a 400 litre tank! 1 kWh is only 860 litre-degrees. Glad to hear this system is working well for you. Maybe we don't need 400L, but I'd rather put in a larger heat store than a smaller one. It would be more efficient in terms of heat losses because of smaller surface area to volume/mass ratio, and I'd rather not be hitting the max temp from solar on a regular basis if I can store it instead, although arguably on sunnier days with more solar gain we'd be more likely to use the solar energy to power some kind of cooling system. In terms of the calcs - 1kWh = 860litre-degrees which means that it takes 1kWh to raise a 400l tank by 2.17 degrees. We have a good orientation for solar PV and no shading, so my guess is that we'd generate between 5 and 30 kWh/day between a shady December day and a sunny July day, which would raise the temperature of a 400l tank between 10 and 60 degrees. Not that bad I think! Link to comment Share on other sites More sharing options...