3 hours ago, Dillsue said:
I did a quick heat loss calc on a ground floor stone building 12m x 6m x 2.5m without any insulation and rooms above which gives a 5kw heat loss @-2. If the rooms above are of a similar size and insulation level then a 9kw heat pump is going to heat the place. That's physics. If you know someone you trust who has studied physics then speak to them and see if they can explain it to you in a way that works for you.
That's pretty much what I came to as well. Glad to see it verified.
2 hours ago, ProDave said:
If you are only paying £70 per month for electricity then there is no way you can be putting enough energy into that house.
At this time of year I am paying that much for heating a very well insulated and air tight house.  If I put that level of heating into an old cold stone building it would be cold.
The only way you are going to solve this impass, is to turn your heating on 24/7 for at least a week to try it.  Once you have been shown how to do this, please give it a try.  For the first week or 2 the bills WILL be high as it will be heating the mass of the building and drying it.  Bills will go down once the building has warmed up and dried out as you will then only be replacing lost heat.
Until you get over your conviction that it is not going to work and actually try it, you will never know.
Hi ProDave,
as Ive said I just kinda left both systems for the installer to set, last thing.
On Monday, I can certainly ask the engineer (come to fix HW issue) to set it a certain way. But I have no idea what to ask.
When you say 'leave it on 24/7' I'm not quite understanding what you mean: you see I know that my system is working 24/7, what I mean is it's connected up to receive power, but obviously doesn't produce rad heat overnight. But it's still 'on' nevertheless.
So this word "on" is hugely ambiguous. Are you suggesting I leave all the rads to be warm for 24/7 ? Surely not as I wouldn't be able to sleep, it seems massively wasteful, environmentally ridiculous, when just 1 person living here.
So you might be suggesting some kind of setting -between- these two situations. If so, isn't that what I had it set ti before with my prior system with the rads dipping on-off all day?? I've tried that. The try failed. The cottage remained freezing.
I'm also not understanding the thermostat suggestion thing. The suggestion to place it somewhere other than where the installer put it. Why, would the installer put it anywhere other than a sensible place? How can I override his decision, & ask him to place it some other room, when I can't even understand the system?
Afaik, the thermostat needs to be close to the cylinder. Close to the other interface box too, which itself has to be close to the cylinder. Cylinders are typucally found in spae bedroom cupboards. I know this to be true, as Ive seen them with my own eyes, in almost all the houses Ive ever set foot in. An orange foam covered tank, warm, usually in a tiny cupboard often called 'airing cubboard' residing within an upstairs bedroom. Usually the smallest, least used bedroom. When I call up saying 'another fault' the Vaillant fix team person asks me to look at the screen on the interface, then go to the controller (I think this smallest box is also referred to as the thermostat). So I have to dart between them. I can't do that, if the thermostat, has been rewired (a huge length of cable running 15m away from where it is) to be in one of my cold rooms downstairs.
Thanks Zoot
Yes, I mean ON as in running and radiators hot ALL DAY AND NIGHT until the house reaches the temperature set by the thermostat.
You need to get the installer to show you how to change the settings between off, on, controlled by a timer and on all the time.
Only when you actually try it on all the time, will you really know if the house is capable of being heated by the heat pump.  Try it for a week.  It might annoy you with some noise at night, it might cost you more, but that is the only way to know if it is actually capable of heating your house and if so how much it might cost to do so (remember costs will go down after the initial heat up and dry out period)
Get the installer to show you how to change the settings, take notes so you remember, and if you don't understand ask him to explain it again.
As an aside, one thing I dislike about heat pumps is to the average user, they are so different to a gas boiler.  Almost everyone is familiar with a normal central heating programmer on the wall from where you can set on off times or easily turn it on all the time.  But every heat pump I have seen the timer functions are way more complicated but more important are nothing like operating the sort of programmer that everyone is used to.
When I installed mine, I made it a non standard install by ignoring all the timer functions built into the controller that came with the heat pump, and instead connected a standard central heating programmer so anyone could understand how to change it from on all the time to on a timer etc.
@S2D2 Your £700 figure has polaxed me. I've no comprehension why you'd pick such a figure (unless you live in a castle?!).
I know I pay £70 odd, each month. Now this is likely not an actual figure of useage in winter, because it's compromise/ average/ I forget the word, figure.
When I call up Octopus to ask why my 'balance is £300 in credit' & what this means, I ask them to please speak very slowly, to explain, to please use simple analogies, to help me understand, what on god's name this figure means. Just this.
They do so, but I cannot understand a word they say; I have to politely say thanks but I still haven't a clue what this figure even is at the end of the call. It's economics. My brain doesn't compute economics.  So much so, that the very fundamental lesson 1/ page 1 example of  'supply & demand'... is 100% counterintuitive, to my brain. I do not understand economics. It seems you need to have a basic grasp of it, in order to pick the bones out of these super-complicated (to me) electricity bills. So I don't. I set up a direct debit, & £70 is taken each month. I often put in a meter reading, but still, it takes £70 each month (IE it seems my putting in meter reading, makes zero effect, on what is taken each month.. so I never know why on god's earth am I even being asked, to put in meter numbers at all?? A rhetorical question).
I just pay £70. And enough already. Whether that is a correct figure, or wildly incorrect, I have no clue whatsoever. I dare not ask, or rather there's zero point me asking an Octopus person, because I won't understand a word of their reply.
Thanks Zoot
Edited by zoothorn
Most people use more energy in winter because they are heating their house,  and less in summer when they are not.  Your electricity meter gives  reading all the time of how much it has used.
Most suppliers, like Octopus prefer you to pay the same amount each month.  So in the summer months you are paying for more than actual use so your balance with the company builds up.  In the winter you are probably using more than the £70 per month you are paying and your balance comes down.
If you still have an account balance of £300 at near the end of winter then you are paying more than you need to.  That makes your £70 per month even more astonishing.  I can't get my summer monthly usage that low, I would have to stop using the washing machine and dishwasher and watch a lot less television to achieve that.
So all it shows is just how little you are using on heating which is why your house is always cold.
Octopus will change your monthly payments to actual usage each month if you prefer rather than the same average all year round.  Or you can ask for surplus balance to be returned to you if you want to.  In that respect they are a lot better and easier to deal with than most other suppliers.
@-rick-
I can certainly give him your wording here, to the engineer, on Monday.. despite not understand some of what you're asking me to ask him
For eg. Always on?? Why would I want the heating always on?? (Why would anyone want their heating always on??) I don't want to wake up sweating, besides, you & I were on the same page grumbling about Storage heaters being on at 3:53 am when you absolutely least want them to.
So the very first thing, you're asking me to ask him here, I don't understand whatsoever as to why you'd want me to request this. From then on, I'm further confused.
But I can show him your reply, record his answer on my iPad's audio, & write down what he said. But then type it on here, for it to be "translated", by you guys. I mean I'm exhausted enough. But if that's the only way.
TRV's which iirc are independent thermostats.. plus separate thermostats.. & my head explodes. I cannot understand an iota of this principle. Apologies.
How to be ready:
1. Get the engineer on Monday to show you how to:
a. turn heating to
- "always on"
- "always off"
- "timer"
b. adjust the set temperature
c. adjust the timer
2. Deal with the bedroom external walls as discussed.
3. If needed, arrange for the thermostat/heatpump controller to be moved to a cold part of the house
4. Possibly, get TRVs installed on the radiators in the warm part of the house (this is something that couldbe done if needed at a later date).
50 minutes ago, -rick- said:
parents to upgrade their storage heaters as it didn't make any difference
Why would it if they were the same energy storage and similar power delivery.
Workmate of mine did the same. Found out the problem is the way she used them i.e. turns the fan in when she gets home and leaves it on.
I can't explain past decisions. What's important is to solve the problems now.
Not at all. Traditional Gas systems usually have a controller (that might be near the cylinder) but a seperate thermostat somewhere central in the house.
Heat pumps often by default have the thermostat inside the control screen. This should be installed in a place that is exposed to the coldest indoor temperatures (so it doesn't switch the heating off until the coldest place is warm).
From what you've said your thermostat is near your cylinder, which explains your problem. The cylinder is mostly likely the hottest part of the house, so the thermostat is sitting there thinking it's 18C when you are sitting in the sitting room freezing.
So either you need an engineer to attach a remote thermostat to your existing system or to move the existing thermostat.
Ok.
Simple to explain, as follows.
You are using less than £70 per calendar month on electricity / heating and hot water etc.
The bills are estimated at the moment, and they must have a way of knowing where you're at in terms of consumption because they are slowly racking up a credit (hence they are saying that you are currently £300 in credit; this means your over-paying at £70, and giving Octopus more money PCM than you are using.
Do you not have someone in the family who can speak to Octopus on your behalf to get some clarity?
You should be submitting a meter reading to Octopus, at least once a year, so they can adjust your charge rate and credit.
Do you have a smart meter?
£700 PCM for energy consumption during winter is nothing to do with a castle-sized property. A "castle" would probably need £7000 PCM so please stop thinking that say £350 PCM in winter for a poorly insulated and draughty house is expensive, it is not.
I'm doing probably close to £15 a day in winter, stone walls, 2G doors and windows, and draughty as feck. Gas boiler with rads, and they do not turn off day or night (we sleep just fine because we don't over-heat the house, we just heat it so it's not cold or 'chilly') so for me atm close to £450-500 PCM depending on how much we use the tumble drier.
Summary:
You cannot possibly think you will be able to feel even marginally warm in your exact house if you do not run the heating for longer. You are being told (asked by frustrated, helpful people on here) to set the thermostat to a temp that is simply acceptable to you, and to leave the heating system on constantly (24/7 means 24 hours a day, 7 days a week) and allow the house to heat itself throughout and arrive at an ambient.
You are cold because you are not putting enough heat into the house, simple as, nothing to do with the heating system being effective you are just not using it for long enough each day.
My thermostat is set to a comfort temp during the day, but that's probably only 1.0 - 0.5 degrees C higher than the night time temp, so I am saying that I do not turn my heating off all winter.
If I turned the heating on and off (night to morning) and then on and off again Evening to night) every 24hrs like a timer as you're set up like at the moment then my house would be horribly cold and probably twice as expensive to heat.
If you don't want to freeze at night just set a low temp for the nights, and a slightly warmer temp for the days, then the heating system won't cook you, it'll regulate and just give you a minimum temp that you don't want to be colder than. Running the heating constantly doesn't mean it's constantly heating, it just means you wont get cold.
You need to look on YouTube for the controller for your heat pump and watch, listen and learn how to use it from there, as that will show you the short cuts to get your heating on as you need it.
Currently the short heating programs are useless and that's why you are cold. It's also why your heating bills are so small, because you're not using any heating.
Once you learn how to control this thing, which will become easier the more you try, and learn by making mistakes, the problem will go away. You can then time the hot water to be hot when you want it to be hot.
Hi ProDave,
honestly thanks for trying to explain it, but if I can't understand "If you still have an account balance of £300 at near the end of winter then you are paying more than you need to".. I just can't do this. I've tried & tried for so long so many times with this stupid electric billing system. But I can never get it. Not even with childlike analogies. It just doesn't compute.
If my prior HP was (& afaict this is what you mean by 'always on' but I don't know) set to go on-off all day long, then afaict it was, in all normalcy, 'always on'. That is if you can't be suggesting in a 3-bed cottage just me living here, that I have all my 12 rads on continuously overnight: I just can't bring myself to believe that is what you are suggesting as it makes no logical sense.
So if my prior system was always on, for weeks on end set like so, during the winter & despite what my expense on electricity.. then the test is done, surely. The 'put your HP set to always on' test (which you're asking me to set the new HO to) has been done. It failed. The cottage remained freezing. Bar two newbuild rooms that is (sod's law being the least used rooms).
I'm in a perpetual cycle of non-understanding here. And the number of subjects I cannot understand, is increacing, with now mention if electric bills. I'll have to bail out, tbh, & with huge respect to all here, simply because I can't cope. I'm getting increacingly confused, leading to increasing kinda creeping mild stress.
Thanks, Zoot
This is the problem with hit and run installers, just fitting the stat where they can easily get a wire to it.
They've also done a shit handover, and it's programmed to run completely ineffectively, as such a short heating window (unless @zoothorn told them it must be only on for a couple of hours to save money??).
Yes always on, the radiators should be hot/warm until the house is warm. Once the house is warm then you would expect the system to automatically turn on and off to maintain that temperature.
You need to keep the system on to maintain a relatively steady temperature in your house. With thick walls like you have, once the heat is lost it takes an enormous amount of time and energy to heat up again so the key is to stop them getting cold in the first place.
I've suggested you get a TRV fitted to your bedroom radiator. This way you can set your bedroom temperature independently from the rest of the house and set it a couple of degrees lower. But the system will still be on, pushing heat into the rest of the property.
Can't you ask a friend or family member to be in attendance to help you understand and decipher what is being said / how to use the controller?
Loom on YouTube as I have said, and see if that helps. May be good homework for you before the chap arrives Monday as you will then begin to learn by watching this repeatedly until some of it begins to make sense.
Pause the video, take screenshots, write notes.
Does it not already have a TRV on it? @zoothorn, do all the rads have TRVs on them?
On 16/02/2026 at 21:45, zoothorn said:
You mentioned before, about TRV's, as if you expected them to be on my rads. But I don't have any on my rads. When I had them on a property before, I found them infuriatingly impossible to understand. One minute the rad is on flatout, & I was too hot, then half an hour later the rad wasn't seemingly on (but it was within the block time the heaters were meant to be on) & the room was pretty cold again.
Thank @-rick-
This goes from a bad situation to a worse one then. WTF were these guys smoking when they thought this would self-regulate and not have any requirement for individual room temp control?!?
Hi Nick,
alas I'm not blessed with family to help, 86/90 yr old frail parents, brother 200m away not close-brothers either. I don't even know anyone in wales to ask to tea, let alone ask to come & decipher some engineer's spiel!
I can spin the wheel on the controller though, know how to zip around it's menu (having to on phone to Vaillant, yet again, due to some minor fault). I'm even adept at it.
But look I don't know what is being meant, by "set the heating to always on". I must try & establish what, exactly, is being asked here. Everyone seems to all know what is meant; but Ive repeatedly said that I do not, & no-one answers.
Thanks, Zoot
No, none have. The installer asked this question too. I have no idea why this question would be asked, by you, or by him, if the room's rads are ultimately defined by the 'controller thermostat small box'.. therefore cannot for the life of me comprehend why any discussion of extra thermostats/ TRV's, makes any logical sense. Their mention merely adds further confusion for me.
So here Rick, you -are- unless I'm mistaken, saying all my rads, should be set to 'on', overnight.
In my life I've never known any house, any heating system, anywhere, in any country Ive been to including cold NZ, to have the rads on overnight.
I cannot possibly believe this is what you or anyone is suggesting. I just can't sorry. Ive never heard anything suggested being so preposterous.
All 12 rads, to be on, when I'm alone for 9 hours in one room.. when not only do I not even want heat (because I'm under a duvet), but also when I open a window to sleep, needing a bit of cold air/ how I prefer.. is such daftness I can't believe this is  being suggested.
How can I possibly run my house like this? I can't sorry, this is sheer madness to me. The wastage, the expenditure, just no way.
This may be how you like your bedroom overnight, maybe in a family of 4, with all your rads on, but never in my life have I ever heard of it before, by anyone, anywhere. You yourself agreed with the storage heater ridiculousness, of them belting out heat at 3:45am. You agreed. No-one could ----possibly, possibly----  disagree either. It's like having a car sat in the driveway idle, but left on & somehow using up MORE fuel, than you do when actually driving it. "Yes that's logical, keep it on running idle in the drive overnight, that's what they do". You'd commit that person to a mental asylum.
Maybe this helps:
The Thermostat/controller is there to put heat into the system whenever the coldest room needs heat (to do this it needs to be located in the coldest room)
The TRVs are there to set the hottest temperature you want the individual rooms to reach.
There are ways to make systems work without TRVs but your house is a long way away from that. So you need TRVs in rooms that would otherwise get too hot as the system is heating up the cold rooms. You don't really need TRVs in the cold rooms.
In my flat I have removed the TRVs from everywhere but the bedrooms and it works fine, but if I remove the TRVs from the bedrooms then the bedrooms overheat as the system is trying to warm up the cold other rooms. (My bedrooms have much better thermal properties - like your new bedroom in the old house)
I'm saying the rads should be hot whenever the room is colder than your set temperature, including overnight.
This is how I run my system, how @Nickfromwales runs his, ditto @JohnMo@marshian and many many more.
With a TRV you can set the temperature in your bedroom lower, but the heat is required in the rest of the house to prevent the stone walls getting cold. Once they are cold then warming them up again is super difficult.
Once your house is warm, the radiators will only be on as needed to maintain the warmth, but to get the house warm they need to be on continously, likely for many many days because your house is so cold right now.
As I said many posts ago, I've found running my system 24x7 seems to be using less energy than running my system on a timer. The reason is that it takes a lot more energy to heat a cold space up than it does to maintain a constant temperature.
1 minute ago, -rick- said:
Maybe this helps:
Please forgive me Rick, I just can't understand a word of this.
It would take me a week of brainache, tk puck through just this one post, reading it 150x to maybe glean 1/4 of understanding from it.
Look, all I can do, is ask the engineer to set the rads to go on during the day. Not overnight, sorry but I cannot entertain this idea as anything but nonsensical, if I catagoricallly & absolutely do not ever want to have any radiator on during the night time in my house.
I've got your set of listed things to ask him. Apparently there's a 'Setback temp' (which I don't quite understand why hasn't been mentioned as it seems pretty fundamental to the rads switching on situation) that I guess in principle, I could have set to say 10*Cmax if that's what someone mentioned the 'see your breath' cutoff temp is. But no more than that.
I'll also ask if the 'controller- thermostat' can be moved.. but the logistics of doing so, with it being wired (not wireless) would be very costly & needing a cable of maybe 30m to be fed through an attic, down through a ceiling.. 3 hours work min costing me £100's, which I can't afford tbh. I could conceivably do it, if I knew how to remove the cable, replace with 30m of new stuff, but then my warranty will likely be compromised wouldn't it.
But then even if I did run it downstairs, to one of the 3 freezing cold rooms, it would be running overtime, & totally out of kilter, just being left to trip the rads on, pretty much all day long. The average day room temp in these 3 rooms, I'd hazard a guess is about 14*C, they can never ever get any higher than that, that's even with their room rad or rads producing heat, because (& pretty blindingly simply & also as blindingly obviously) so much cold is coming up from uninsulated cold floor & in through uninsulated cold walls.
I honestly think we're at an impasse here, whereby I say the cause of the cold is fundamentally due to the uninsulated nature of the rooms, & you say the cause is the heating system isn't introducing enough heat. I'm absolutely adamant, & you guys are. But look, I live here, the doctor analogy is applicable/ you know your own body best analogy.
I will do my best with the engineer though. I'll record his voice saying the answer to each thing you suggested to ask.
Thanks, Zoot
Thanks, Zoot
OK, calm down.....we're only discussing options and explaining ourselves to you, based on your feedback and the fact you're living in a bitterly cold house when you have a full, brand new central heating system installed.
You're reporting that it is useless, but you're not giving it a chance to prove that it works, in actuakity.
The part you can't fathom is that my house is cheaper to heat by not turning the heating off, at all, all winter.
None of us are sweating, none overheating, none are shivering cold and wrapped up in a duvet on an electric blanket.
If you don't want a heating bill, don't turn the heating on. That means accepting you live in a stone fridge.
If you don't want that, but something a bit less like a fridge, you need to turn the heating system on (timed to come on at 06:00 and to go off at 22:00 maybe) and TRY and see if that is better.
Then try that for a month and see what the meter reading has jumped by. Number of units x the price per kwh that you pay, and divide by 2.5 for your COP and that'll give you a rough guide as to what your heating bill will actually be.
If you don't (or won't) try then you'll never know.
For completeness, I don't know anyone, anywhere, who will sit all winter freezing their arses off, even more so if they're saying that they're cold, or the house is borderline unacceptably cold to live in.
We may have a breakthrough after all!!! Hoorah :)
Yes, ask them to do this, and then see if it makes a difference. As above, choose a setback time (maybe the times I suggest above or think about this before the installer arrives to save time), but ask for this to be 15 degrees not 10!!!
You need to open up to trying a few things and getting actual results to consider.
You may not want the house to be heated per-se during the night, but you don't want it to be left to go stone cold, so a setback temp sounds like you may find a middle ground.
If you want me to speak to the engineer with you, I am happy to support, we'd just need to be on the same page before their attendance or it'll be a shit-show. You can give the chap my mobile number and ask him to ring me.
  • Like 2
But Rick.. the difference here between your house & mine (& it's massive/ it's so absolutely fundamental/ the crux of all this issue here)..
.. is you (& all those members you collectively listed earlier in the post) have decent insulation. It goes without saying, that with your knowledge, this priority structural factor, you WILL have up to par. Likely beyond-par up to a very decent standard.
I
do
not
have
insulation.
Practically.. none.
This is the cause of the cold. This is why so much cold enters. This is why a HP which typically produces medium-warm rads, cannot hold a candle to making any inroads, here.
The only way I can affect the insulative factor of my kitchen & bathroom (in their terrible construction 80's extension I sit here with nose & feet freezing cold as I type this, with it 14*C & mild outside..) is to knock it down. Rebuild it. Not by running each of these two room's small rad on for countless & pointless wasting hours.
I cannot afford to rebuilt this extension. If I could, my main sittingroom is still in need of effectively the same treatment. I can't knock that down. I can affect a tiny perimeter cold ingress, but that's merely a sticking plaster solution.
it's just a cold house, it will always be so. Unless 2 jet engines are introduced. Still I'd pee & huff my breath one side, even with the afterburner singing my arse the other.
thanks, Zoot
The physics is the same, to get a comfortable house you will undoubtably have to spend more on bills than I do but the same principles apply.
My mums house does not and she is able to heat that perfectly fine. Yes it costs her approx £2000 a year but its not cold (so long as the heating is on)
Medium warm rads on 24x7 will output much more heat than hot rads on for short periods of time. 12 rads designed for heatpump temps should be able to output the full capacity of your heatpump without issue. The fact your energy bill is only £70 shows that this hasn't been tried yet. For you to get a warm house it will cost substantially more than £70 per month.
If my mums leaky, mostly uninsulated house can be kept warm then so can yours.
Take @Nickfromwales up on his offer. TRY to run your house in a different way. Physics and experience from people on this forum says it's possible. Unfortunately you've had a bad experience with previous installers putting a system in that wasn't set up right and gave the impression that your house is unfixable. Try to set that experience aside and start with a blank sheet of paper.
