1:40 drainage fall for W.C's

Featured Replies

I'm just digging for the drainage and I think I can just about get away with a 1:40 fall everywhere. While reading something about drainage, it says that any drainage that has W.C's attached should be a 1:80 fall. Is that strictly true?

 

Cheers

 

Vijay

  • Author

Thank you. Looks like 1:40 will be fine for 100mm pipe :)

  • Author

I've just about got 1:40 (with a bit of work), so I'd really struggle to get 1:80 without core drilling a hole through foundations................

10 hours ago, Vijay said:

I've just about got 1:40 (with a bit of work), so I'd really struggle to get 1:80 without core drilling a hole through foundations................

 

Vijay, I think you've got this the wrong way round.

If you've got 1:40 then 1:80 is already available, i.e. a lot less fall.

If you overdo the fall then the liquids disappear too quickly and leave the solids sat in the pipe, that's why @PeterW suggests 1:80

Edited by RichS

I thought the issue with 1:80 was it is the absolute minimum allowed, so you have to be really careful that nothing happens to allow a bit of pipe to sag. Some say when doing 1:80 under the ground you should concrete it in for that reason.  If you have enough room I would go as close to 1:40 as you can. It's not one or the other, it's anywhere in between.

BC was happy for me to use 1:80 but only with 150mm pipe & concrete.  I stuck to 1:40.

1:80 shouldn't sag if it's packed properly and bedded - it does if you don't support it in situations such as internal soil pipes. Polypropylene pipe sags worse than uPVC as it has a slightly lower melting temperature. 

19 minutes ago, PeterW said:

1:80 shouldn't sag if it's packed properly and bedded - it does if you don't support it in situations such as internal soil pipes. Polypropylene pipe sags worse than uPVC as it has a slightly lower melting temperature. 

A bit close to the wind though, and allows little for error? 

  • Author
On 16/08/2017 at 08:15, RichS said:

 

Vijay, I think you've got this the wrong way round.

If you've got 1:40 then 1:80 is already available, i.e. a lot less fall.

If you overdo the fall then the liquids disappear too quickly and leave the solids sat in the pipe, that's why @PeterW suggests 1:80

 

 

Not if the foundations and manholes fitted by the developer are are already in place - I would need to drop the foundation or raise the manhole :(

Edited by Vijay

  • Author

How should any pipework running under the B&B floor (and on top of the cleared ground) be supported? Do I just use a concrete slab under the rest bends or do I bed any pipework and restbend in concrete?

If the ground is not great, use a flagstone as a pad, then wet concrete pads on those to actually hold the pipe. Come 1/2 way up the pipe, no need for more than they afaik. Just make sure it's benched either side so it can't move. 

Get a laser and work out the fall over the distance. That'll tell you your fall. 

  • Author

Cheers Nick. How often should a pipe run be supported to stop sag?

Edited by Vijay

Isn't the whole point of b&b that the ground inside can move and heave? I've never been a fan of long runs underneath beams for this reason. I think it would be preferable to dig a trench filled with pea gravel allowing a big of movement without upsetting the falls. 

  • Author
2 hours ago, Oz07 said:

Isn't the whole point of b&b that the ground inside can move and heave? I've never been a fan of long runs underneath beams for this reason. I think it would be preferable to dig a trench filled with pea gravel allowing a big of movement without upsetting the falls. 

 

Can't do that as the foundations are in and the pipes are to be ontop

On 16/08/2017 at 08:29, ProDave said:

I thought the issue with 1:80 was it is the absolute minimum allowed, so you have to be really careful that nothing happens to allow a bit of pipe to sag.

 

Shit sticks.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.