Jump to content

Wrong lintels used - mould risk ?


bmj1

Recommended Posts

Hi all,

 

We're at ridge level now, which is super exciting... however, I've hit a bit of a snag when reviewing progress to date.. we've had some material substituted by the main contractor to use regular cavity wall galvanised steel lintels, instead of the hi-therm/insulated. We've now paused all progress on site while we review state of play.

 

My question is as follows:

 

- Putting aside all the impact on thermal performance, and SAP, etc, which we can compensate for (and live with), in practice, how much of an issue is this likely to be in terms of causing mould ? If this is a problem, is there a solution that doesn't involve replacing all the lintels ?

 

Many thanks in advance.

 

image.thumb.png.6578cd6887aac90eb89ce9bf49d04486.png

Edited by bmj1
Link to comment
Share on other sites

  • bmj1 changed the title to Wrong lintels used - mould risk ?

The Hi Therm lintels have a fairly long lead time and are quite a bit more expensive.  I can't work out from the picture what has been used.  If they used a separate lintel for inside and outside leaf they will be just the same thermally, but just more effort to build with.

Link to comment
Share on other sites

Looks like a pair of lintels there - can’t see the stickers properly. As long as the SEng is ok with substitution then insulating the gap (PIR foamed and trimmed) will be better than the standard EPS inserts anyway. 
 

Also seems to be an additional Concrete lintel on the inside - what’s going on there or is that a very deep reveal ..??

 

Mould risk..? Zero if you’re ventilating correctly.

Link to comment
Share on other sites

I wouldn't worry too much about the mold. So long as it's not behind something that prevents airflow, like fitted furniture.Especially if you have MVHR. 

 

If your contractor has substituted the lintels on every window and they had clearly been specified as thermally broken I would be expecting them to find a solution to fix the problem. 

 

If you have say 20m of lintels at a PSI of 0.55W/mK Vs a thermally broken lintel at 0.05W/mK that's an additional heat loss of about 20m X 0.5W/mK X Dt20deg or about 200w extra peak heating load. 

 

I don't know how this fares in your overall scheme but it'd be 14% extra for our (passive) house. 

 

 

 

 

 

Link to comment
Share on other sites

That is extra load on the assumption there is no internal insulation though and it’s exposed ends. 150mm cavity isn’t close to passive levels so it’s probably negligible and not going to get any impact on SAP - air tightness score will be the biggest impact with a build like that. 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...