Trying to live with Airsource

Featured Replies

4 minutes ago, Alfapat said:

I have set the flow to 51 and cylinder to 49 , so will see what happens.

A bit more of a difference say flow 56 for cylinder 48

  • Replies 98
  • Views 15.2k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • The HW cylinder and buffer appear to be in a cold loft space with minimal OEM insulation. Could this be why it struggles so much?

  • Nothing looks immediately wrong other than it's is a presumably cold loft so heat losses will be greater and you need more insulation on ALL the pipes you don't want to be seeing any bare copper up th

  • means it’s not fitted properly and not had clips or tape applied.. 

Posted Images

5 minutes ago, Alfapat said:

Black isle renewables , who have washed their hands to repairing or looking after this. 

So "Air Source 1" let you down?

  • Author
7 minutes ago, ProDave said:

So "Air Source 1" let you down?

Yes to be blunt , they agreed to take the system on with the approach of Freedom Pumps , charged me 4500 to correct the system installed by a Central belt company who went bust a year after install , and when I asked them to service it and find out  about a fault it had E920 if I recall , they said they didn’t know enough about Samsung , so I didn’t phone them again!

  • Author
15 minutes ago, ProDave said:

A bit more of a difference say flow 56 for cylinder 48

Ok , so I’m watching Smart meter!

 

15 minutes ago, ProDave said:

A bit more of a difference say flow 56 for cylinder 48

 

  • Author
6 minutes ago, Alfapat said:

Ok , so I’m watching Smart meter!

Done

 

 

53 minutes ago, Alfapat said:

Yes to be blunt , they agreed to take the system on with the approach of Freedom Pumps , charged me 4500 to correct the system installed by a Central belt company who went bust a year after install , and when I asked them to service it and find out  about a fault it had E920 if I recall , they said they didn’t know enough about Samsung , so I didn’t phone them again!

Just what exactly did they do for £4500?

25 minutes ago, ProDave said:

Just what exactly did they do for £4500?

Barbados is nice this time of year.

1 hour ago, ProDave said:

So "Air Source 1" let you down?

 

Eyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyy

  • Author
50 minutes ago, ProDave said:

Just what exactly did they do for £4500?

So original plant was two pumps , not required they said , sold 9kw , reset 16kw with larger copper flow pipes instead of plastic, and further from wall. , better insulation , magnetic filter and glycol in fluid , plus a number of small things........ nightmare . Well you would wouldn’t you if you thought , finally it might work properly.

9 hours ago, Nick Thomas said:

 

Eyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyyy

Black Isle renewables have "Air Source 1" painted on their vans.

  • Author
50 minutes ago, ProDave said:

Black Isle renewables have "Air Source 1" painted on their vans.

Didnt see the vans often enough lol.

  • Author
12 hours ago, Alfapat said:

Ok , so I’m watching Smart meter!

 

 

So Midnight after setting the flow to 55 degrees which is maximum with no hot water used the House 21.4 Outside 3.8 Hot water 39.2  Circ. 48 degrees

Bath run  !

Morning - House  8.30  21.5  Outside 3.8   Hot water 39.8   Circ. 41.5

 

Something not right. What else. I will check parameters/field settings.

I think you need to establish that it is switching from DHW to space heating and not trying to do both at the same time.

 

It is normal, because of the limited power of a heat pump vs a gas boiler,  to only do one at a time.  So I would expect when it is heating the water tank, the space heating (I can't remember if it is UFH or radiators) goes off.  Can you confirm that is the case?

 

 

or radiators. You can't heat the DHW and the central heating simultaneously

9 minutes ago, Alfapat said:

UHF ?

Under Floor heating.  How is the house heated?  The point is working correctly when heating the hot water, the radiators or whatever heats the house should go cold.

  • Author
12 minutes ago, ProDave said:

Under Floor heating.  How is the house heated?  The point is working correctly when heating the hot water, the radiators or whatever heats the house should go cold.

Ah OK, so no underfloor heating here.

I will try and check that . 
 

I don’t know if this helps me or you guys. 2BAEF5E6-8D2E-42B6-8382-A7CEEF1D0A42.thumb.jpeg.c16f4a3bc9879ffb396c2110c196bbaa.jpeg

Edited by Alfapat

  • Author
2 hours ago, ProDave said:

I think you need to establish that it is switching from DHW to space heating and not trying to do both at the same time.

 

It is normal, because of the limited power of a heat pump vs a gas boiler,  to only do one at a time.  So I would expect when it is heating the water tank, the space heating (I can't remember if it is UFH or radiators) goes off.  Can you confirm that is the case?

 

 

To determine the switch over then ,there should be no heat icon showing at top right of controller , would that be correct , similarly the water tank symbol should not be active if rads/heat is on ?

Yes I believe that is how it works but I have not used that controller.

 

Confirm by the fact the radiators should go cold when it is heating the water tank.

  • Author

Ha, they are cold just now as no requirement for heat but monitoring.

  • Author
4 hours ago, Alfapat said:

Ha, they are cold just now as no requirement for heat but monitoring.

4hours on Circ. 49.6 Hot water 39.6 . Just saying. Outside 1.8 c

Radiators on 20 c

NOT CORRECT . I will leave 55 flow and 48 DHW FOR a while.

Where are you measuring the temperatures and with what?

 

If the water really is flowing into the cylinder at 49.6 then after 4 hours you would expect the hot water to be more than 39.6

  • Author

The temps are from the controller GEN 5

  • Author

Ha, they are cold just now as no requirement for heat but monitoring.

 

21E72D59-B97B-4483-B27F-3771B40D560C.thumb.jpeg.f8230737ee1231cf0f93eed03e72dc9a.jpeg

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.