Chanmenie Posted March 28, 2022 Share Posted March 28, 2022 Hi guy’s I’ve read just about everything I can find on the forum but I’m still not clear on the best method. What is the best way to build up to floor level in a ground bearing slab, as far as the Underfloor heating pipes are concerned. On the insulation or tied to the mesh ? I get the impression that using clips or staples directly on the PIR is easier than cable tying to the mesh, but which is more efficient when using an ASHP. I am also concerned about walking on A193 mesh with ufh pipes attached it’s only 7mm so will it bend. Slab make up as this from bottom up. 100mm compacted type 1 sand blinding enough to fill and smooth type 1 25mm EPS ( should this be 100 rather than 70) DPM 150mm Celotex XR4000 UFH pipe clips with pipes 40 / 50mm rebar chairs A193 mesh 120mm Concrete The SE specified the A193 Link to comment Share on other sites More sharing options...
AliG Posted March 28, 2022 Share Posted March 28, 2022 MBC just installed a slab for us and the UFH is in the slab attached to the mesh. There were no issues walking on the mesh to install the pipework. It was 252 which is 8mm. The main issue is keeping your balance. I think if you have mesh the expected way is to attach to the mesh. I haven't seen that kind of makeup before. What's the 25mm of EPS for? It won't provide a lot of insulation. 150mm of Celotex is roughly the same as 220mm of EPS. It only took two guys around 5 hours to install 140 sq metres of UFH pipe tying it to the mesh. They used a gun which applied the ties, MBC said they would have used cable ties by handing taken similar time. Is a PIR strip specified around the edge of the slab? Without it you can get a cold bridge. Link to comment Share on other sites More sharing options...
Chanmenie Posted March 28, 2022 Author Share Posted March 28, 2022 The 25mm EPS is to protect the DPM, better than just using sand blinding. I have around 145 m2 so similar size yes there will be a vertical strip around the perimeter Link to comment Share on other sites More sharing options...
AliG Posted March 28, 2022 Share Posted March 28, 2022 Thought it might be. Sounds all good to me. Our UFH company didn’t care what way the pipes were attached. As far as they were concerned it was the same job. Link to comment Share on other sites More sharing options...
Nickfromwales Posted March 28, 2022 Share Posted March 28, 2022 1 hour ago, Chanmenie said: The 25mm EPS is to protect the DPM, better than just using sand blinding. I always did this, seemed a no brainer. 1 Link to comment Share on other sites More sharing options...
Olf Posted March 29, 2022 Share Posted March 29, 2022 12 hours ago, Chanmenie said: I get the impression that using clips or staples directly on the PIR is easier than cable tying to the mesh It may be, but you need a tool and extra spend on clips. Also it would have to be planned carefully to not to collide with the chairs for rebar, so I think tying to the mesh is the way to go. Not sure about your shoe size, but 15cm between the bars is enough to put a foot on 2 adjacent, you can easily go forwards and sideways, bigger issue is reversing and not stepping on the pipes 12 hours ago, Chanmenie said: which is more efficient when using an ASHP Irrelevant, flow temperatures are the same. Saying that, my thinking is that rebar would help to transfer heat from the pipes attached to it initially. Mind that with pipes at insulation level, the same will happen once the heat reaches the mesh above, and considering UFH heating is all about slow and steady, it should not matter in the end. Also my thinking is that UFH pipes at mesh level should result with slightly lower losses: at 35°C flow temperature I get 25°C surface temperature. With pipes roughly in the middle of the slab I'd expect bottom of it (where it touches insulation) will also be at ~ 25°C. Pipes attached directly to the insulation means something close to the flow temperature is reached there, and so higher heat flow happens downwards. 12 hours ago, Chanmenie said: DPM 150mm Celotex XR4000 UFH pipe clips with pipes 40 / 50mm rebar chairs A193 mesh 120mm Concrete You need another layer of membrane (thinnest DPM you can find) on Celotex to stop reaction of aluminium facing with concrete, also prevent any leaks between the panels (just in case, even if foamed). As mentioned earlier, apart from compression lagging around, do install perimeter insulation to prevent bridging to the walls. Put it between DPM and the 2nd membrane, otherwise it will float away. I've seen opinions that EPS is 'soft' enough to act as both, though PIR will have better properties. Also all the services going through the slab will benefit from being wrapped in lagging And last but not least make expansion joint in any doorways, otherwise they'll form naturally. Through those places make sure UFH pipes are bent (even forcing S shape) and covered in pipe insulation, so they can move a bit within once the slab is settling. 1 Link to comment Share on other sites More sharing options...
Bitpipe Posted March 29, 2022 Share Posted March 29, 2022 Our build up was 150mm compacted type 1 50mm sand blinding 300mm EPS 200 (could have got away with 200mm) - 200 grade specced by SE, you may get away with 150 (which is same compressive strength as your EPS). DPM Concrete construction. We did not have UFH in the basement slab, but if we had it would have just been tied to the mesh. Using just EPS would simplify your slab sandwich and remove need for second sheet of DPM. Link to comment Share on other sites More sharing options...
Chanmenie Posted April 5, 2022 Author Share Posted April 5, 2022 (edited) Thanks for the replies and info guys I'm still undecided on where to fit the pipes, I am considering upping the Celotex XR4000 to 200mm, should give U value of 0.10 W/M2k Edited April 5, 2022 by Chanmenie Link to comment Share on other sites More sharing options...
Rishard Posted November 8, 2023 Share Posted November 8, 2023 Where did you decide to tie your UFH pipes in the end? Link to comment Share on other sites More sharing options...
Chanmenie Posted November 9, 2023 Author Share Posted November 9, 2023 13 hours ago, Rishard said: Where did you decide to tie your UFH pipes in the end? I used fibre reinforced easy flow concrete in the end, so stapled the UFH pipes to the insulation. much easier and cheaper than using rebar mesh 1 Link to comment Share on other sites More sharing options...
garrymartin Posted May 15 Share Posted May 15 Apologies for updating a couple of older topics but if you're like me and have been diligently combing through old threads for nuggets of wisdom, the following might be helpful. Short version, out of three scenarios (pipes at 19mm centres below surface of slab, at 50mm centres below surface of slab, and pinned to the insulation); the pipes at 19mm give the best performance, but obviously very close to the surface (~79.2 W/m²) the pipes at 50mm showed a small decrease in performance against those at 19mm (~75.1 W/m²) the pipes pinned to the insulation showed a much larger performance hit (~56.2 W/m²) So when considering in-slab UFH and choosing between tied to rebar or pinned to the insulation, tied to the rebar will win from a performance perspective every time. Longer version, in Imperial measurements (US-based author) https://www.pmengineer.com/ext/resources/PME/2019/July/014-017-pme-0719_siggy.pdf 1 Link to comment Share on other sites More sharing options...
JohnMo Posted May 15 Share Posted May 15 See my other response. Plus below on the article From the article "This increases the time required to warm the floor surface to normal operating temperatures following a call for heat. It also lengthens the cool-down time after heat input is interrupted by system controls. A fully “charged” slab can hold several hours worth of heat that will continue to flow into the space as long as the air temperature and / or interior surface temperatures are cooler than the floor surface. This can be a real problem in buildings with significant internal heat gains from sun-light or other sources." Comments With batch heating the long storage time constant is what you want. Heat for 7 hours, live off the heat for next 17 hrs until next heat cycle. Charge with a low hysterisis thermostat ensure little temp overseeing in the rooms. Well insulated ensures heat doesn't escape and also floor surface is only a couple of degrees warmer than the room so the floor output self modulates. One of the FEA models I constructed is shown in Figure 1 (on Page 14). It consists of a 4-inch concrete slab sitting on 1-inch-thick extruded polystyrene insulation. Comments - 25mm of polystyrene insulation is a joke and undermines the whole premise of the article. Link to comment Share on other sites More sharing options...
gavztheouch Posted May 18 Share Posted May 18 On 15/05/2024 at 19:58, JohnMo said: See my other response. Plus below on the article From the article "This increases the time required to warm the floor surface to normal operating temperatures following a call for heat. It also lengthens the cool-down time after heat input is interrupted by system controls. A fully “charged” slab can hold several hours worth of heat that will continue to flow into the space as long as the air temperature and / or interior surface temperatures are cooler than the floor surface. This can be a real problem in buildings with significant internal heat gains from sun-light or other sources." Comments With batch heating the long storage time constant is what you want. Heat for 7 hours, live off the heat for next 17 hrs until next heat cycle. Charge with a low hysterisis thermostat ensure little temp overseeing in the rooms. Well insulated ensures heat doesn't escape and also floor surface is only a couple of degrees warmer than the room so the floor output self modulates. One of the FEA models I constructed is shown in Figure 1 (on Page 14). It consists of a 4-inch concrete slab sitting on 1-inch-thick extruded polystyrene insulation. Comments - 25mm of polystyrene insulation is a joke and undermines the whole premise of the article. @JohnMo how would I calculate how much extra heat loss I would have if I tied my UFH to the lower layers of mesh rather than the upper? i have 250mm eps and 250mm concrete the lower layer will be at 70mm from the bottom and the upper layer will be 170mm from the bottom. Link to comment Share on other sites More sharing options...
JohnMo Posted May 18 Share Posted May 18 34 minutes ago, gavztheouch said: @JohnMo how would I calculate how much extra heat loss I would have if I tied my UFH to the lower layers of mesh rather than the upper? i have 250mm eps and 250mm concrete the lower layer will be at 70mm from the bottom and the upper layer will be 170mm from the bottom. That's a lot of concrete to heat up. My 100mm takes 24 hrs at the start of the heating season to get going and heating the house. I would just put on the top layer of rebar, otherwise you will be heating the floor for days to get heat out. Basically the heat radiates from the pipe in all directions and looses temperature in a informed manner, until it hits a resistance (insulation, heat flux from another pipe, surface). 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted May 18 Share Posted May 18 sytem used in my house has been subfloor with refeforcing mesh - then dpc whcih stands up the walls to finished floor hieght 140mm of celotex boarding next is UFH piping then final 75mm screed to finshed floor height 1 Link to comment Share on other sites More sharing options...