  1. OK running out of time because we are going on holiday for two weeks but I’ll answer what I can Pump speed 1 10-11 W in normal operation Head is 1.8 m flow rate is 0.7 m3/hr on HW and 0.6 m3/hr on CH ( it can get down to 0.3 m3/hr as room TRV’s shut down Boiler flow temp 40 return temp 30 on pump speed 1 Most rads have a 9 to 10 deg drop between flow and return Pump speed 2 15-18 W in Normal operation 3.0 m head Flow rate is 0.8 m3/hr on HW and 0.7 m3/hr on CH (again it can get down to 0.3 m3/hr as rooms TRV’s shut down Boiler flow temp 40 - return temp 34 most rads have a 6 to 7 deg drop between flow and return House has 13 rads 2 ladder towel rails (toilet and utility) 2 med size verticals (Bathrooms) 1 large vertical (kitchen) 4 T22 500 x 1200 (bed rooms) 2 T22 500 x 1400 ( Dining and main hallway) 1 T22 600 x 600 (front hall) 1 T33 700 x 1400 (living room) Re pipe calcs (just saying whilst the height of the vent was as stated the length of the pipework to the vent is probably 7m from where it is below the pump to the outlet above the F&E tank. So there is a fair bit of water in the pipe) Automatic air vents are open all the time but when air is introduced the aerated water tends to stay in the pipes - never hear them expelling air unless it’s a system refill then they hiss away a lot if I shut the bottle vents for a day or so I’ll get a 1 sec hiss when re-opened so I know they work ok - I just think when the circuit gets a slug of air in it they aren’t very effective at getting it out due to flow of water in the circuit I think that’s all of your questions answered Better picture of the pump and pipe configuration below (with all the lagging almost complete it just looks like a sea of grey) I’ve not lagged the bypass leg because I’m still trying to find a good compromise setting that doesn’t allow too much return when all rads call for heat but does allow a little flow when some TRV’s start to close
  2. Current set up Filter, pump assembly is all same From pump T to bypass valve to HW return then T splits to go right for CH (NO zone valve) or goes left to HW (NC zone valve) coil in tank Both CH and HW legs have bottle type air bleeds Boiler is 1m below the pump I will try to do the new glass trick today Your calcs on volume of water in 22mm pipe assume that the height of the vent is also the length of the pipe but thats not the case the pipes go thro the ceiling of the airing cupboard and into the loft space - there they travel horizontally 3m along the loft before rising up to the F&E tank. the tanks were relocated a while back because they made access to the loft space difficult
  3. I guess this means whatever problem I have it's always been there - I just put something in that masked the issue Now it's set up as X plan and has bottle vents on both HW and CH legs* they aren't as effective removing air as a 1.5 M length of 15mm copper right above the pump *sighs
  4. Oh that is such a long story I don't want to go there........... Set up was a Y plan with a 3 position valve HW HW&CH and CH only The whole system was controlled by a sunvic set up and when the 3 postion valve failed I converted to a drayton - however that was incompatible with the wiring centre and so an adjustable spanner was deployed to switch from HW to CH and Nope I'll stop there................. The pipe you want to know where it's going was to a manual vent - I've always had an issue with air in the system since we bought the place in 1991 it used to accumulate over time so I put a stupidly long leg of 15mm copper pipe up the side of the airing cupboard and just used to bleed it every month...................
  5. Yes to both The F&E tank is only feeding the CH Circuit - nothing is T'd off it - there is one isolation gate valve in the line but it's fully open The vent for the CH circuit is vented to above the F&E tank There is another vent from the HW cylinder that is vented to above the Cold Water Store Tank but there is no connection to it. The pump is installed the correct way round and as I thought the magnaclean filter has no flow markings and according to the destructions can be installed either way up The distance from the bottom T where the Vent is to the top of the pump gate valve is 58 cm it's as compact as it can be From the pump to bottom of the F&E tank is exactly 3.4 M The vent pipe is at it's highest point before it comes down to just above the surface of the header tank water is another 0.6 M Huge apologies to @Little Clanger for the threadjacking
  6. Just looked at the instructions - not sure there is an orientation requirement on the Magnaclean but I will look carefully at the body when I'm home tonight
  7. I'm not aware of an arrow in the filter body but I'll check that too Filter is checked every three months and rarely has much on it - below is as bad as it gets
  8. Yes exactly that - 99.9% sure the pump body has an arrow pointing up but I'll check again
  9. They are effectively stacked (with the absolute min of pipe between all items) Top Zone Valves Pipework Gate Valve Pump (130 mm flange to flange) Gate Valve Magnaclean Unit 22mm T (15mm inlet) Cold Feed 22mm equal T (22mm Vent Pipe) 22mm Flow from Boiler Bottom I can do exact measurements if required but it's all very tightly packaged
  10. Ahh so one 22mm pipe feed from F & E to below the pump and then the vent tee's off close to the tank outlet - that would be do-able with existing pipework Attached is picture of set up before recent changes to pump filter configuration and valving
  11. Glass of water results (might have to repeat it with a larger glass) pump on - level stable pump off - load of bubbles followed by a level drop pump on - all the water stolen from the glass Just for info when on HW both cold feed and vent pipes below the pump get hot for a few feet up the wall so there is a level of water in them When refilling the system from a drain down it fills fairly quickly so I think the cold feed is clear I would have expected the vent pipe to have water in it to the same level as the F&E tank
  12. Yeah I’ll try the glass of water trick the filter is a magnaclean unit
  13. Ok see below
  14. Really good explanation and makes total sense My Pump is above the cold feed (so 2.0 M plus 3.0 M Head = 5.0 M) so there shouldn't be much chance of air being drawn in - I'll continue my search for why I get occasional slugs of air in the circuits I have turned the pump down from Speed 2 (3.0 M Head) to Speed 1 (1.8 M Head) to try and reduce the system noise and it all seems good on first pass (morning heating - selected rads)
  15. Sorry to thread jack a smidge but thank you for that information - I've got a pump head of 3.0 m but the actual height of the F&E tank water level to the pump is closer to 2.0 m Might explain why I get occasional issues with air in the system with no apparent signs of leaks I think I'll see if I can drop the pump speed and maybe open up the flows thro a few rads to keep the circulation rate the same
  16. Wow that's a heck of a flow rate for a shower - last time I checked ours when looking at water consumption it was 9L per min and I regard that as a decent shower I my concern for our house water usage I did fit a restrictor to reduce the flow to 6L per min and that was fine for me I couldn't notice the difference SWMBO who also didn't notice started whining that it was taking longer to rinse her hair (shampoo and conditioner) so the pump must be going and I should replace it asap................. I timed her showers with flow restrictor and without and it was a tiny reduction in water usage but it did increase the time in the shower by 50% and as I have to wait for her to finish in the shower before I can get in there I decided life was too damn short and I'd look for water savings elsewhere.
  17. I thought that too
  18. Is that the right way round and is it fully open? - stop cock is a fairly convoluted path for water - gate valve (fully open has very little resistance to flow - obv they get a little noisier as you shut them down)
  19. I found using WIser Hub and Smart TRV's I have you could get one rad calling for heat setting the boiler off for a very reduced circuit and a shot while later another rad would call for heat - I think in one particularly cold night I burnt 23kW of gas for no appreciable increase in room temps overnight So I use it to schedule heating periods with a fairly aggressive set back temp at night (almost frost stat setting) this stops individual rads from calling for heat at night What I do like about the Wiser Smart TRV's is they do stay open for a really small trickle of flow and only shut down in the event of a considerable overshoot - so as I'm experimenting with a Weather Compensated flow temp it's actually helped me "tune" the flow thro individual rads especally at the weekend when I have the CH on all day
  20. You have fridge and or freezer? - they randomly top up and cause a spike without you even noticing you are doing anything different. Difference from 0.15p per hour to 0.22p per hour based on say a 35p per kWh for electric is around 200W so it's not enough to be an immersion heater
  21. ^ what @Mike said - get a turbo nozzle for the jet wash lance - that makes short work of even the toughest lichen/moss/green
  22. I had a concrete lorry as a garden ornament for a few hours - I'm sure I've got a picture - driver backed it into the garden to shoot a load of concrete into the footings - when it came to driving out he gave it all the beans and as a result dug himself a bit of a hole Ended up pulling it out with chains attached to another concrete lorry
  23. That is a little poor (understatement) PS thanks for sharing the journey
  24. In other news Gas Engineer has had it confirmed from Viessmann that boiler (in current configuration) needs a switched live from the programmer to the boiler - at bloody last!!!
  25. Well my old school plan had a flaw - it wouldn't have been a problem if the gas engineer had used my 3 port valve as I proposed with no mid position in the old airing cupboard arrangement because I only had a bypass fitted for the CH side - HW didn't need one because the flow rate was always far higher (easiest path and all that) However now I have a bypass that will work if pressure in the system is high with CH or HW - closing the gate valve to increase the amount of time the water stays in the coil and reduce the return temp to the boiler is enough pressure to cause the bypass to want to play (By play I mean get involved) So tonight I've been experimenting with pump parameters to see if I can find a pump setting that Provides a min of 0.4 m3/Hr so that the boiler is happy with the level of flow (below 0.4 m3/hr the boiler gets a bit fussy and throws the odd "low flow" fault) when circuit is at it's smallest (ie just one or two rads in circuit) And provides a max of 750 - 800 l/hr (0.8 m3/hr) when all the rads are calling for heat so the boiler can ramp up and get the circuit up to temp Because the alternative plan is fit a NO zone valve in the bypass line so it closes at the same time as the CH NO zone valve........... Anyway no one wants to see a load of tables of what pump results in terms of watts, head and m3/hr is like for 3 different pump operating modes each with 3 different speed settings for both all rads calling for heat and a very tight circuit where I'm left with just two rads still calling (Bypass was closed for this) so I'll just say I've found a setting that meets the requirements but I haven't done HW on it yet.
×
×