sharpener
    1
Everything posted by sharpener
  1. Yes, if you run the secondary pump off the HW valve supply then it will not de-stratify when you are not heating the water. It will in addition need an NRV so you do not get back flow from cold inlet straight to the hot taps when the pump is not running. For best heat transfer make sure you plumb the HX in the counter-flow configuration.
  2. This web site seems to provide some useful services e.g. comparing Octopus tariffs and checking for missing smart meter readings. Anyone else using this? Is it genuine or just a way of harvesting/selling on your data?
  3. 12kW Vaillant is v conservatively rated so good for a lot more: Don't know about the Mitsi but @JohnMo can probably tell us.
  4. 12kW Vaillant is v conservatively rated so good for a lot more, don't know about the Mitsi but @JohnMo can probably tell us.
  5. HG cheat sheet suggests 30 - 50 W/m^2 so 11.2 to 14 kW, Vaillant 12kW sounds a good match. The 10kW is basically the same unit so has the same minimum output. 2023 of course.
  6. In 2003 it was said to be Chofu (see upthread). Maybe the delay in getting to market was bc of a change of horses.
  7. Had a poke about the web yesterday but couldn't find anything very specific. What is the most appropriate forum on this board to discuss this issue? I am surprised I can't find any recent discussion if the problems are widespread.
  8. Our installer has contacted us to say that (13 months after installation) the MCS want to visit as a random site chosen for QA follow up. It would be useful to know from anyone who has had a visit how long they take, what they want to see in terms of equipment and documentation, whether you get a written report or any other kind of feedback, anything else of note. TIA
  9. Yes and no. On the one hand the Pylon BMS tapers the charging current a good deal as 100% is approached. OTOH I seem to recall most of the physical expansion in the size of the cells (which AIUI is the root cause of degradation) occurs in the top 10% so avoiding that would be good. But would cost me quite a lot in extra peak rate consumption. Victron s/w allows 5 separate Scheduled Charge periods and you have reminded me that I used 3 different targets for the afternoon charge to max out use of solar: 40% by 1400 70% by 1500 100% by 1600. the idea being to allow room for solar without forgoing the chance to fill from the grid if necessary. So runs a bit counter to my declared philosophy upthread. ATM I am more concerned that Octopus are 2 months behind with billing and have rates for Cosy on the app that are different from those on my latest bill (to June 19). Anyone else got similar problems?
  10. If you install a heat pump you will have to find a home for a hot water cylinder anyway bc it is very unlikely you will need an HP big enough to provide "instant" water heating. They can go in the loft if necessary. Then you can get rid of the electric shower for the cost of plumbing in an ordinary mixer shower - which will be small compared with the rest of the project. If you have already got forklift batteries (what chemistry?) and they are or can be wired for 48V then you can use them with a Victron inverter and probably many others. The 8kVA Multiplus is probably the one to get, it has 15kVA surge capacity ? for 2mins? and 100A (23kW) passthrough capability. Charged overnight at cheap rate this would enable you to timeshift/arbitrage your aqua blasting usage as well as providing grid reinforcement.
  11. Yes. The other fly in the ointment is the electric shower. No-one would sensibly keep that once they had had an HP installed. As upthread 80A is sufficient for an EV, a cooker and an HP all at the same time. But evening cooking load falls mainly in a peak rate period, which is where the battery comes in handy and of course that avoids demand on the grid.
  12. Yes, but high energy density! Which is why it is used for storing the energy for launching torpedos from submarines, my sometime employers had contracts for the refurbishment of the pressure vessels which were expoxy lined steel.
  13. Seems to me that storing the energy as compressed air is a plausible solution (and has been trialled at utility scale), what are the economics of fitting a ginormous receiver? Even with a bigger house, a 12 kW (thermal) HP and a zappi 7kW EVCP we have found an 80A connection quite workable. The demand planner here is very useful for carrying out thought experiments.
  14. I'd be tempted to put in my own borehole to be independent of the farmer (and whatever he puts on his land by way of cow muck, fertilizers and pesticides). There was a recent case near us where a village was supplied by a communal borehole but the farmer still got PP for a great new slurry pond near it. Have seen quite a few borehole threads on here and don't have any great personal interest, but high single £ks are what springs to mind (sorry). You would also need to budget for break tank, pump etc and treatment depending on analysis, but present owner may be relying on farmer for adequate treatment anyway. A local co will probably be able to advise on that too.
  15. Has been the received wisdom for decades. I would be particularly hesitant to drink softened water if immunocompromised, have high blood pressure or less than perfect kidney function. Difficult to avoid entirely as our tap water comes ultimately from Dartmoor so quite acidic. A SWW chemist told me they treat it with NaOH to raise the pH. But according to the calculator at www.aqion.de only 0.1 mg/l is required to raise it to pH 8.4 so it is miles below the 200 threshold. Nearly all the outlets in the house are fed from harvested rainwater; to raise the pH we treat it with NaHCO3 at about 100g/m^3, which is quite a lot of sodium. So we have tap water piped to drinking water taps in the kitchen and bathrooms.
  16. born or possibly borne but not bourne
  17. A gas or oil boiler would have failed too. Admittedly to run a heat pump you will need a bigger battery to be useful (or @JohnMo's generator. I have got an interlock which turns my HP off automatically on grid failure, this gives me time to switch it into low power mode or decide to do without it. Also have kept the oil-fired AGA, and for the real extreme case I have one of my grandmother's Aladdin oil lamps.
  18. Not sure I understand the rationale of this. Don't the mini-SoC targets mean that the battery is eventually charged to 100% mostly from PV at 15p per unit not exported rather than the grid at 12.65p (at present Cosy rates)? Why is this better? The battery is still cycled from 100% SoC so the depreciation is the same.
  19. Told NGED (ex WPD) over the phone I had had more panels and a heat pump fitted and wanted the inverter power limit relaxed so it could drive the HP, and the export limit relaxed so I could export any surplus. They agreed subject to a new G99/G100 application but it took a long time to process and much chasing.
  20. Before I managed to get the DNO to remove the export limit I considered how to do this, IIRC it involved holding off recharging the battery until midday so that when there is max generation there is room in the battery to take the excess. This runs the risk however that the predicted sun does not arrive. I could not work out exactly how to automate this but I think it must be possible on a Victron inverter with NodeRed, you might find it easier with your HA setup using solcast or similar. For me the DNO made the problem go away in the end, I assume in yr case that the 3.6 kW is a hardware limitation though.
  21. I think it's more to do with the efficient area of operation of the compressor. It's easier to design a gas burner to work over a wide range of output. The lowest speed the Vaillant 12kW will run at is 27.2% which gives a turndown ratio of over 3:1 and that is typical of better HPs. A preference for matching the behaviour of a (20kW) gas boiler is unrealistic. In most cases it would lead to an extremely oversized HP, with attendant capital cost and inefficiency at low outputs. A longer coil will not help (much). However you do not need to limit yourself to a single tank, you can cascade them e.g. with a feeder tank in the loft space. If you were planning to scrap the existing one doing this might get you more capacity more or less for free. It will not save you capital cost now. It should break even on running cost now, and assuming the govt eventually does something about the cost structure will likely give you worthwhile cost savings in the future. As the cost of solar PV and battery systems continues to fall you will increasingly be able to run an HP off your own power plant. Given the demands on the grid, at some point in the future you may be refused an HP connection by your DNO so best to get in before the rush. As with many incentive schemes the BUS grant may not stay at £7k5 once its initial purpose has been served. You will be able to bask in the glow of the brownie points.
  22. This may well result in infeasibly big rads whatever their construction. But the fancy column radiators do not have as much emitting surface area per unit frontal area as a conventional Type 22 or Type 33. Our installers designed for a flow temp of 45 and used a (conventional) rad size uplift factor of 1.9. This is a compromise with the partial ground floor UFH set to 35C, but a mixed system is going to have very big rads indeed unless you sacrifice some efficiency. As were were migrating from an oil system we are happy enough if it costs no more to run.
  23. OP reads consumption off his solar inverter and 2.5-3.5 kW there would equate to maybe 7.5 - 14 kW thermal output depending on assumption about CoP so is broadly consistent. Can't think of anything other than that the fancoils are undersized so cannot get rid of the heat/coolth. It would be good to know how they were sized, and the floor area and construction of the house.
  24. As others have said if you are already planning to get a bigger one it is perhaps not fair on attributing that requirement to the heat pump! The equation you need is 1 kWh = 860 litre-degrees. So it takes 10 kWh to heat a 215 l tank through 40 degrees. Or a 5kW HP will do it in 2 hrs etc etc. An MCS approved installer (not much of a qualification but you have to use one to get the BUS grant) will use the MCS sizing guide which is 45 litres x (no. of bedrooms + 1) so if yr house has 4 bedrooms that would mean a min of 225l, and with your usage I would go for at least 300. We have a 210 litre OSO cylinder and at 60C it will supply decent showers for two normal ppl plus 2 guests in quick succession. We usually have the HP flow set to 45 which gives just under 40 at the outlet which is enough when there are no guests. There are various claims for fancy tanks such as Mixergy or the new Heat Geek combi boiler substitute but they are mostly spurious and you will do best IMO in spending the money on a bigger conventional tank with a large coil. Have you tried the aerating shower heads which apparently give a full shower experience while using less water? You can download quite good free heat loss s/w from www.heatpunk.co.uk and there is also a quick heat geek cheat sheet which from your description would suggest maybe 65-85W/m^2 is appropriate but you need a more formal method than that. There is a new Heat Geek Zero Disruption process which may be suitable for yr house particularly bc of the existing 15mm pipework. The planning restrictions @SteamyTea refers to have been relaxed so you can put a HP within 1 m of the boundary and do not need PP for even a big twin fan unit like the Vaillant 12kW (which are slimline and extremely quiet). I would not want to install a HP above ground level, though it can be done subject to the manufacturer's requirements about safe access for servicing. HTH
  25. Victron inverters have a Dynamic ESS setup that does something very similar which I tried for a while. As reported by many other people on their forum it had behaviours which had no obvious rationale so I gave up in favour of the very simple strategy upthread. There is not enough difference between Cosy's cheap rate import and 24h export tariffs for arbitrage to be worthwhile so I think KISS applies here. I will have another think when the heating season starts but I can't see anything significantly better atm.