SimC
Everything posted by SimC
The flow/pressure chart makes much more sense now with the labels on each axis. Yet you need to be achieving 2095 l/h at 100% pump speed, and according to the the chart you only have around 55 kPa available external to the HP. So a higher flow rate is required, with a lower pressure drop, which is a significant difference to make up with pipe changes to larger diameter and a reduction in the number of 90 degree elbows. From your photo of the rear of the HP, I can see 4 elbows, and assume there are another 2 elbows to direct the pipes through the external wall. These pipes are not well aligned with the ports on the rear of the HP, and once lagging is applied will act as an obstruction to air flow from the rear of the HP to the front. This area could be significantly improved with the suggested larger diameter flexible insulated hoses. With such a flow/pressure difference to make up you may need to be looking at some of the heating pipes after the diverter valve as well. May be think of what flow rate is required down each section of pipe to assess suitability of the current sizing.
Assuming the pump is performing correctly at 100% speed, yes you can use the chart to lookup the reported flow value to determine the pressure generated by the pump. I would have expected the Vaillant technician to have measured the pressure drop of the HP heat exchanger, or at least the residual pressure difference between the flow and return connections to the HP unit with the pump running. The 70 kPa developed by the pump is all lost across the whole circuit including the HP heat exchanger, so if the heat exchanger loss is say 25 kPa then only 45 kPa is available to generate the required flow in your heating pipes and emitter system. The published Vaillant manual should at least provide the expected HP HEX pressure drop at design flow rate, and the residual pump pressure for your system. My work involves interacting with air and water balance specialists usually in commercial buildings who validate by measurement with calibrated instruments that a system is performing as per the design criteria. By just relying on a unit display value, and not by seperate measurement, Vaillant have not proved that their unit including pump is actually performing to specification. Obviously you have also highlighted concerns with sections of the distribution pipework sizing, that should also be resolved to improve the resulting flow rate when heating, but you could be chasing your tail if it turns out there is an issue with the pump not actually generating 70 kPa pressure.
At 1750l/h we have a pressure of 70kPa. Where was the 70 kPa measured? If across just the pump, what was the pressure drop across the HP heat exchanger?
There may be an issue with the 3-phase Sigenergy inverter combined with the 4 panel string, in that the MPPT startup voltage is stated at 180 Volts. In comparison the 1-phase inverters have MPPT startup at 50 Volts, but only size up to 6 kW. The Sigenergy datasheets and install guides provide no information on how the 3-phase unit reacts to unbalanced loads. If the inverter only outputs equal power on each phase when there is an unbalanced load, then the net result is that some phases will be importing from the grid and some will be exporting, rather than all 3-phases being grid neutral. It is not clear whether any specific 3-phase grid meter from a supplier operates with net metering calculations or not for billing purposes. With the 10kW 3-phase inverter, the max output current per phase is 16.7 Amps, which equates to just over 3.6 kW on each phase. If your loads draw more than this on a single phase, then the remainder will be imported from the grid. The Aiko NeoStar 3S 475 W panels will probably only produce around 30 V each in lower light conditions, which only produces 120 V when the 4 are connected in series. This string input is unlikely to start even in the brightest conditions, so is not worth installing with the proposed equipment. These observations may not provide a solution for you, but I hope they are helpful in what to look out for when choosing a new system.
I am interested in how the specific PHE was chosen. Was it based on kW rating, water flow rates required by the boiler and CHP, or some other arbitary parameter? My experience in a work capacity is that the primary and secondary return temps are very closely matched at low flow rates, but when the flow rates increase there is a point when the primary return temp (to heat source) rises significantly which has a knock-on effect on the heat source efficiency.
In theory it could be possible to add an ASHP in parallel with an existing boiler, but both would need to have their own pumps in the correct part of the circuit, and each have a non-return valve to prevent reverse flow through the non-running unit, and the existing plumbing would have to support the required flow rate through the ASHP, and the water teatment used would have to suit both. So quite a lot of dependencies. My 8mm microbore to most of the rads will probably not allow the required flow rate for an ASHP, and I have no idea what water treatment would be required to suit both devices. Thinking about inserting a plate heat exchanger, but then the issue becomes the ASHP does not engage with sufficient volume of water for de-frost cycles etc. The Daikin hybrid schematic does not indicate where any pumps are located to generate flow, so they could be in series, meaning the non-running pump will restrict the whole system flow rate.
Another significant parameter is the current under STC and NOCT conditions. As the new and old panels will be wired in series for each string, the same current value will pass through all the panels in a string. The best match will be if the new and old panels would naturally produce the same current at the various insolation levels say 200W/m2 to 1000W/m2. Some manufacturers show an insolation/current/voltage graph on the data sheet, but not Longi. Have you got the full data sheet for the existing panels? Current of the new panels, Imp = 13.17 A (STC) and 10.78 A (NOCT). The string voltage is then the summation of all the panels in that string which must not exceed the capabilities of the inverter, even under open circuit conditions at low temperature (Voc - (Voctempco * (25 - - 20 degC)). For the new panels this equates to:- 39.33 - ((-0.23% * 39.33) * (45)) = 39.33 + 4.07 = 43.40 V per panel.
Mini Store - Heat Geek / Newark Cylinders for ASHP
SimC replied to Nick Laslett's topic in Air Source Heat Pumps (ASHP)
I would be interested for thoughts on using one of these to convert from a vented hot water cylinder fed by a system boiler via a 3-port diverter valve to a hot water system under mains water pressure. Presumably it avoids the full G3 requirements as the hot water coil must contain less than 15 litres volume within the pressurised circuit from non-return valve to closed hot water taps. Does the G3 requirement for a pressure/temperature relief valve and associated drainage then go away? I already run the boiler at around 50C flow temp for heating, then turn up to around 70C on 1 day per week to heat the full tank for bath day. The remaining 6 days use an Eddi plus immersion for night/solar hot water heating of just the top half of the tank which is sufficent for showers and washing up. Presumably with the MiniStore the boiler flow temp would not need to be so high, and the 15 kW boiler would be able to provide enough top up to be able to fill a bath. The current hot water cylinder is approx 1100 H x 475 D, the same as the Tall MiniStore. Just trying to think outside the box with immersion backup possible by using a Willis heater connected between the heat source flow and return connections to the MiniStore. The existing boiler system is already vented with expansion up to the loft header tank. -
Clean Heat Market Mechanism to incentivise heat pumps
SimC replied to LnP's topic in Air Source Heat Pumps (ASHP)
The PVGIS default value of 14% system losses are not all down to conversion and transmission losses, a proportion is due to the degrading performance of the panels as they age over their lifetime. Many panels are rated at 98% after year 1 and down to 86% at year 25, so you could assume a mean value of 92% (8% loss) over the lifetime. Here is the relevant extract from the PVGIS user manual. -
It does not seem to be best use of hydrogen in a fixed location such as a distillery. Electrification would in my mind be a better solution, and not reliant on a single source of supply of hydrogen. In my day job I have come across a few recent examples of cascaded ASHP and WSHP in order to achieve suitable grade heat for hospitals including for their DHWS which is required at least at 60 C for protection against legionella in areas for vulnerable patients. This must be somewhere near the grade of heat required for distillation.
My concern would be how to modulate/balance the water flow rates through the currently active heat source with that through the total of 5 pumps serving the loads. There would appear to be a total of 7 pumps required in the system, assuming 1 in the outside ASHP and 1 in the system boiler. Too low a flow rate through the heat source, and the manifold ends up containing predominantly cool return water from the loads so not meeting the load heating requirements. Too high a flow rate through the heat source, and the manifold ends up containing predominantly hotter water from the heat source resulting in a high return temperature to the heat source with its knock on effect on the COP/efficiency.
You could have an 8kW inverter with a 3.68 kW DNO export limit. How any inverter achieves this is by having it's own metering device next to your utility meter (or along the route of the main live cable from the utility meter). The inverter then has a live import/export power value that can be limited to whatever value is programmed in. The value is password protected so that only the installer and manufacturer can set or change it. The inverter has power point trackers on the PV string inputs, that it can set for maximum/optimal output from the panels, or when the export limit is being reached the trackers adjust to non-optimal to reduce the electrical power output of the panels. The excess solar energy is then just dissipated as heat in the panels. Solar panels are only around 20% efficient at generating electricity, so already dissipate 80% as heat meaning another few % due to the DNO export limit is not going to cause any damage. Have you got a logical position for the inverter and batteries, bearing in mind there needs to be suitable cable routes for the DC feed from the panels, the ac power cable to a suitable consumer unit breaker, along with a data cable to the metering device? Batteries are very heavy, so ideally on the ground floor. Depending on your building layout, a garage can be the best location, but only you know the layout.
One solar performance website is:- https://re.jrc.ec.europa.eu/pvg_tools/en/#PVP Here is one example of a thread from this forum (the advanced search with 'wall pv' is your friend).
Battery storage (or any storage) comes in to play when your solar generation profile does not align with your consumption profile, instant by instant over each day. If at one instant in time the PV is generating 5 kW, and your consumption is 2 kW with no storage available, then the 3 kW excess has nowhere to go other than export to grid (potentially at 15p/kWh from Octopus). If at a later instance in time the PV is generating 2 kW with a 5 kW load, then you have a 3 kW import from grid (potentially at 33p/kWh on the price cap). The battery storage will save any excess solar generation during the day, for consumption later whilst avoiding the cost of grid import. Whilst waiting for my battery install (on a long lead time), I have a solar diverter (MyEnergi Eddi) connected to the hot water immersion heater and 2 oil filled heaters. As soon as the diverter detects any grid export it diverts just the excess power to the immersion heater. Once the immersion is up to temperature, it automatically switches to the heaters. The diverter is fully automatic, so when the solar gen drops off or a household load is switched on, a grid import is detected so the power diversion drops to 0. Assuming your grid export price is less than grid import (almost always the case), you get the fastest payback on the solar PV when you self consume as much of the generation as possible. Energy storage helps with this, as long as it is suitably sized to your generation and consumption profiles.
For the PVGIS solar output calculator:- Choose your location, even down to your street level. Input the PV peak power (approx 3.0 East, 5.0 West). Slope = angle of roof from horizontal. Typically 30 to 35 degrees for a UK roof. May be your roof builder can provide this figure, or by measurement and trigonometry where the angle = tan[-1] (vertical distance/horizontal distance) of the right-angle triangle formed by half your roof. For example, angle = tan[-1] (2.5m/4m) = 32.0 degrees. Azimuth = angle from due South (so due South = 0, East = -90, West = +90 degrees) Click the 'Visualise results' button to see the predicted kWh output per month. If the azimuth angle is not obvious, you can get a figure to the nearest 10 degrees (possible 5 if between graduations) by using this link, enter your postcode, then move your property under the pointer on the map. Each graduation is 10 degrees, so count from due South. Repeat for each of your roof slope directions. This example is -30 degrees from due South.
As others have said, you really need to understand how your 3 phase supply is going to be utilised and what electrical loads will be presented on each of the 3 phases. It may be a legacy use of the property that powered 3 phase motors/machinery. For example a 3kW 3-phase motor will put an even 1 kW load on each phase, whereas a 2 kW 1-phase washing machine will put the full 2 kW load on 1 specific phase based on which it is wired to. Another brand of 3-phase inverter mentions being able to cope with out of balance loads across the 3-phases, with up to 5 kW output on 1-phase from an 8 kW inverter. https://midsummerwholesale.co.uk/buy/solax/solax-x3-g4-fit-8-tp30 Another consideration is the location of the grid incomer (plus utility meter) in relation to where the inverter will be located. The inverter will require a suitably rated power cable, along with a data cable to it's own 3-phase meter. This is so the inverter knows what loads are present on each phase and also once a battery is added what output it needs to provide in order to target zero grid import which minimises your bills. If you want to be paid for export, the installer will need to be MCS approved and provide a certificate for your installation along with DNO approval for connecting the system to the grid.
Starting with the solar panels part, REC is the manufacturer with a good reputation for reliable products. If they are installed by an 'REC Pro Installer' then you get a 25 year warranty on the panels that includes the labour costs to swap out any that fail. Check this link for your local installers. https://www.recgroup.com/en/installers/search The GSE integration is a mounting system for the panels that fixes directly to the roof slats, so the panels become part of the weather proof cover for the roof with the edges filled in with normal roof tiles. Presumably this is for a new or replacement roof project. With 22 x 365 Watt panels, the peak output in Summer with all at the optimum slope angle on a South facing roof would be 8030 Watts (8.03 kWpeak). But is your roof area all South facing, and big enough to contain all 22 panels, or do you have East and West roof areas big enough for say 10 and 12 panels? To cater for different alignment of roof areas, the inverter has 2 string inputs that operate independantly to optimise the output of the connected panels. So you could have say string 1 of 10 panels for the East roof, and string 2 of 12 panels for the West roof. You can get a prediction of the panel performance for your location and roof layout by using this calculator:- https://re.jrc.ec.europa.eu/pvg_tools/en/ Choose your location, even down to your street level. Input the PV peak power (all 8.03 if all facing in the same direction). Slope = angle of roof from horizontal. Azimuth = angle from due South (East = -90, West = +90) Click the 'Visualise results' button to see the predicted kWh output per month. Run the report twice with different PV peak power and azimuth if you have 2 roof areas, then add the monthly results together.
Is that 100 mm too tall per panel, or for the whole height of 2 portrait panels including the required spacing between (usually around 24 mm)? The JA Solar 395W are 1722 mm tall (in portrait), and the Perlight 295W are much less at 1504 mm and significantly lower output. There is a Perlight 400W panel that is 1646 mm tall, that may fit, and will keep the total output up at your original target.