JohnMo Posted August 29 Posted August 29 Trouble is they are just making pretty pictures. There is zero balancing of room output. All designed around a thermostat controlling the room temperature.
Nickfromwales Posted August 30 Posted August 30 4 hours ago, JohnMo said: Trouble is they are just making pretty pictures. There is zero balancing of room output. All designed around a thermostat controlling the room temperature. Plus, it’s just dogshit (pretty pictures).
Mulberry View Posted August 30 Author Posted August 30 12 hours ago, JohnMo said: Trouble is they are just making pretty pictures. There is zero balancing of room output. All designed around a thermostat controlling the room temperature. Awesome! Anyone up for productively helping out with this for some beer tokens?! 🤣🍺 This guy is primarily a screeder by the way (and one that came highly recommended by someone I really trust), so I'm not holding it against him too much. I also think he'll be a good supplier for the kit, perhaps just not so much the design!
Nickfromwales Posted August 30 Posted August 30 12 hours ago, JohnMo said: Trouble is they are just making pretty pictures. There is zero balancing of room output. All designed around a thermostat controlling the room temperature. It’ll be running such low temps that it won’t matter imho. Balancing on the manifold is fine to get flow rates fettled in, and after that it should be plenty good enough. I’ve never done loops by room, and I only make overall adjustments for changes like this (200mm cc or 150mm cc or 100mm cc) for different types of heat sources. The only time I change loops per room (or space) is for adding tighter loops in bathrooms, or for hallways where the area is open to the 1st floor etc and needs a little more ‘oomph’.
Nickfromwales Posted August 30 Posted August 30 1 hour ago, Mulberry View said: Anyone up for productively helping out with this for some beer tokens?! 🤣🍺 Send me a PM if you’re stuck. It really doesn't need to be this hard .
JohnMo Posted August 30 Posted August 30 Computer models just use some basic science. This chart and room by room heat loss calculation is about all you need. You then vary spacing to suit your needs. Start in living room with say 200mm to 300mm spacing and then move the spacings around to W/m2 based on heat loss and target room temperature. Your flow temp max shouldn't be above 30 degs. Key to this knowing room heat loss. @SimonD has a tool in boffins corner I think. As @Nickfromwales says loops don't need to be by room. One of mine partly heats hall, bathroom and kitchen.
Tetrarch Posted August 31 Posted August 31 20 hours ago, JohnMo said: This chart and room by room heat loss calculation is about all you need. You then vary spacing to suit your needs. Start in living room with say 200mm to 300mm spacing and then move the spacings around to W/m2 based on heat loss and target room temperature. Your flow temp max shouldn't be above 30 degs. I have jacked my UFH to ~40 degs. We already have a slow-responding UFH system as my pellet boiler takes ~25 mins to ignite and get to operating temp, and whilst it is very clever in maintaining its internal efficiency it means that on cold winter mornings it takes a while to really get going, also it is a little noisier so starting super early in the morning can be disturbing Am I doing any real harm in running my UFH at that temperature? Regards Tet Additional info: UFH Pipes in eggboxes so 100mm centres 80mm screed 100mm PIR (I know, I know)
JohnMo Posted August 31 Posted August 31 You are really running your UFH like a radiator system, it's your system your choice, but keep an eye on floor surface temperature. Actual flow temp doesn't mean much, floor surface temp does.
SimonD Posted September 1 Posted September 1 On 30/08/2026 at 12:34, JohnMo said: Key to this knowing room heat loss. @SimonD has a tool in boffins corner I think. Yep. https://openheatloss.com. It will do all the UFH output calcs room by room based on flow/return temps, room heat loss, pipe spacing and floor covering etc. and provide floor surface temps and over temp warnings.
Super_Paulie Posted September 1 Posted September 1 On 31/08/2026 at 09:29, Tetrarch said: I have jacked my UFH to ~40 degs. i run mine at 42 at the manifold. Any lower and its short cycle city from my combi which is at 50.
Mulberry View Posted September 2 Author Posted September 2 20 hours ago, SimonD said: Yep. https://openheatloss.com. It will do all the UFH output calcs room by room based on flow/return temps, room heat loss, pipe spacing and floor covering etc. and provide floor surface temps and over temp warnings. I've only just clicked on this, looks like a comprehensive tool, thank you. What steps do I need to complete for the UFH calcs?
Mulberry View Posted Saturday at 16:26 Author Posted Saturday at 16:26 Just to update this, I've put it with an independent heat-loss consultant who has done a much more thorough heat-loss analysis. Very comprehensive and far more believable. I'll be sharing his details on here once I have the full work in hand so I can make a proper recommendation. I realise many can do this themselves, but there are clearly some out there with far more knowledge than I can hope to attain in the short time I have to get this sorted. Good news is that he makes our total heat loss a more respectable 5.45kw and has already hinted at 300mm pipe spacings with a 5kw heat pump. I hope to have eyes on the UFH layout plan next week. 1
Oz07 Posted Saturday at 16:56 Posted Saturday at 16:56 29 minutes ago, Mulberry View said: Just to update this, I've put it with an independent heat-loss consultant who has done a much more thorough heat-loss analysis. Very comprehensive and far more believable. I'll be sharing his details on here once I have the full work in hand so I can make a proper recommendation. I realise many can do this themselves, but there are clearly some out there with far more knowledge than I can hope to attain in the short time I have to get this sorted. Good news is that he makes our total heat loss a more respectable 5.45kw and has already hinted at 300mm pipe spacings with a 5kw heat pump. I hope to have eyes on the UFH layout plan next week. What kind of fee do these heat loss consultants charge? Do they also do the ufh layout?
Mulberry View Posted Saturday at 18:20 Author Posted Saturday at 18:20 1 hour ago, Oz07 said: What kind of fee do these heat loss consultants charge? Do they also do the ufh layout? I've paid £195 for a heat loss analysis with a hefty report. £295 for the UFH layout and for that he's going to route the manifold supply and returns too. Honestly, I think he'll pay for himself in what he's looking like he'll save us on kit already. 2
SimonD Posted Saturday at 20:44 Posted Saturday at 20:44 2 hours ago, Mulberry View said: I've paid £195 for a heat loss analysis with a hefty report. £295 for the UFH layout and for that he's going to route the manifold supply and returns too. Honestly, I think he'll pay for himself in what he's looking like he'll save us on kit already. That's cheap.
Oz07 Posted yesterday at 08:54 Posted yesterday at 08:54 14 hours ago, Mulberry View said: I've paid £195 for a heat loss analysis with a hefty report. £295 for the UFH layout and for that he's going to route the manifold supply and returns too. Honestly, I think he'll pay for himself in what he's looking like he'll save us on kit already. What do you mean route the supply and returns? As in physically put them in? Is it the same person doing heat loss and ufh layout?
Mulberry View Posted yesterday at 09:08 Author Posted yesterday at 09:08 11 minutes ago, Oz07 said: What do you mean route the supply and returns? As in physically put them in? Is it the same person doing heat loss and ufh layout? Each manifold needs to have an MLCP supply and return, these were something I didn't understand at all in terms of when they are installed in the sequence. These are separate from the heating loops and, as I understand, need to be insulated. Yes, the same person is doing both elements and will also be helping me to spec the whole heating and ventilation system by the looks of it. Probably PV too. 1
JohnMo Posted yesterday at 10:31 Posted yesterday at 10:31 UFH loops connect to manifold. Heat source connects to end ports on UFH manifold. Heat source feeds in and is returned by the pipes on the left, loops are the pipes in the vertical. You can do UFH loops first and connect to manifold. Then once you have the ASHP run the pipes from it. Or you do everything together once UFH is in position, it's pretty flexible how you do it.
Nickfromwales Posted yesterday at 14:52 Posted yesterday at 14:52 5 hours ago, Mulberry View said: Each manifold needs to have an MLCP supply and return, these were something I didn't understand at all in terms of when they are installed in the sequence. These are separate from the heating loops and, as I understand, need to be insulated. Yes, the same person is doing both elements and will also be helping me to spec the whole heating and ventilation system by the looks of it. Probably PV too. I think @Oz07 was asking if that was ‘supply and fit’….. methinks not!! If it was, I have a full time job to offer him lol. 22 hours ago, Mulberry View said: I'll be sharing his details on here once I have the full work in hand so I can make a proper recommendation. Please do, and tag me in, as I don’t have enough hours in the day atm (and would be glad to outsource this if he’s robust). 1
Mulberry View Posted yesterday at 19:20 Author Posted yesterday at 19:20 (edited) 8 hours ago, JohnMo said: UFH loops connect to manifold. Heat source connects to end ports on UFH manifold. Heat source feeds in and is returned by the pipes on the left, loops are the pipes in the vertical. You can do UFH loops first and connect to manifold. Then once you have the ASHP run the pipes from it. Or you do everything together once UFH is in position, it's pretty flexible how you do it. @JohnMo How far are your manifolds from the ASHP? Do the pipes from the ASHP run in the floor insulation or...? Edited yesterday at 19:20 by Mulberry View Typo
Oz07 Posted 12 hours ago Posted 12 hours ago 16 hours ago, Nickfromwales said: I think @Oz07 was asking if that was ‘supply and fit’….. methinks not!! If it was, I have a full time job to offer him lol. Please do, and tag me in, as I don’t have enough hours in the day atm (and would be glad to outsource this if he’s robust). I just meant supply and fit of the supply and returns not the ufh loop. I didnt realise a plan or drawing was needed to route these 2 pipes thinking you'd just take them straight to where they need to go but sounds like @Mulberry View has to run through the floor?
Mulberry View Posted 12 hours ago Author Posted 12 hours ago 23 minutes ago, Oz07 said: I just meant supply and fit of the supply and returns not the ufh loop. I didnt realise a plan or drawing was needed to route these 2 pipes thinking you'd just take them straight to where they need to go but sounds like @Mulberry View has to run through the floor? Although the design isn't done yet, in my case, the consultant has talked about 3 manifolds, none of which will be adjacent to the ASHP and each one is on a different GF height level, so routing is on my mind. it might be common sense, but it seems as though he's going to include this in his design.
JohnMo Posted 7 hours ago Posted 7 hours ago 17 hours ago, Mulberry View said: @JohnMo How far are your manifolds from the ASHP? Do the pipes from the ASHP run in the floor insulation or...? About 14m at a guess. Mine are fully insulated but most are outside and or underground, I also do cooling. Pipes come through the wall. And are insulated in the house (1.5m long) 1
saveasteading Posted 3 hours ago Posted 3 hours ago 8 hours ago, Mulberry View said: routing is on my mind The vendors of this kit will do a layout. I liked that they called the cluster of flow and returns a "highway". On the ground floor, with 300 insulation, we put the big blue and red pipes ( from heat pump to manifolds,) inside the insulation. That was a fiddle. The highways are on the surface. ie in the screed.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now