Beelbeebub Posted Friday at 14:42 Posted Friday at 14:42 Does anyone have a reference for the depth that DC cable needs to be buried - I assume the same as armoured AC (0.5m in general) but wanted to double check. I was going to use the specific armoured stuff
JohnMo Posted Friday at 15:53 Posted Friday at 15:53 If you don't really need to bury l wouldn't - would surface run, then you can see them. 1
Beelbeebub Posted Friday at 19:38 Author Posted Friday at 19:38 3 hours ago, JohnMo said: If you don't really need to bury l wouldn't - would surface run, then you can see them. For at least some of the run they will go across an agricultural field (sheep) that is occasionally flail mown and then also across a lawn which is regularly mown and trafficked. Also across a tarmac drive. It's (hopefully) a single ground mounted array that serves several houses. The other alternative is overhead poles but that has issues too.
JohnMo Posted Friday at 19:47 Posted Friday at 19:47 You need to bury below deep plow depth. Although sheep today, you have no idea what will occur in year. So that is 910mm to 1000mm 1
Beelbeebub Posted yesterday at 05:53 Author Posted yesterday at 05:53 9 hours ago, JohnMo said: You need to bury below deep plow depth. Although sheep today, you have no idea what will occur in year. So that is 910mm to 1000mm Good point. Though I can guarantee the field isn't going to get ploughed anytime due to the slope and it also being an orchard. It's a short run from the array site to the edge of the field so I could mount it above ground on some timber rails. If I run it behind the hedge in a similar manner I could minimise the distance underground as @JohnMo suggests. Looking at the site I realise there already is a telephone line overhead along the fence. I wonder if I could run the cables overhead for a good chunk.
Dillsue Posted yesterday at 06:24 Posted yesterday at 06:24 If it's an armoured cable and you have a route along a fence, why not clip it to the fence rails or tywrap it to a strand of fencing wire. 1
Beelbeebub Posted 19 hours ago Author Posted 19 hours ago 8 hours ago, Dillsue said: If it's an armoured cable and you have a route along a fence, why not clip it to the fence rails or tywrap it to a strand of fencing wire. I don't have a fence only a hedge, and at one point I have to pass a gate and another a drive way. In the field I could see effectively building a fence to carry the cable - i'll probably do that. at least the buried sections will then not be in a field. the biggest bugger is there are a ton of other services around, gas, mains, water and sewage plus some telephone. Potentially I could go overhead the whole way, it's just passing over the drive way and gate are a bit untidy.
Nickfromwales Posted 8 hours ago Posted 8 hours ago For this distance, sending DC back is nuts. Abandon this is my 2 cents, as you'll need huge CCA of the cables. Put the inverter out with the array and send AC back; same we did a while back on a ground mount some 135m away from the house, where the client wanted the array in a meadow vs the untouchable roof of his listed home. 1
Beelbeebub Posted 2 hours ago Author Posted 2 hours ago 5 hours ago, Nickfromwales said: For this distance, sending DC back is nuts. Abandon this is my 2 cents, as you'll need huge CCA of the cables. Put the inverter out with the array and send AC back; same we did a while back on a ground mount some 135m away from the house, where the client wanted the array in a meadow vs the untouchable roof of his listed home. Not a bad idea, it would definitely cut cable costs but I think i'd I be giving up the power cut backup function? And is there a problem with exporting the earth? The panels will all be earthed together by virtue of being fixed to a metal frame stuck to the ground. But the houses they supply are 50 to 100m away. wouldn't the same issue with car chargers and remote earth/faults raise it's head?
Roger440 Posted 2 hours ago Posted 2 hours ago 4 minutes ago, Beelbeebub said: Not a bad idea, it would definitely cut cable costs but I think i'd I be giving up the power cut backup function? And is there a problem with exporting the earth? The panels will all be earthed together by virtue of being fixed to a metal frame stuck to the ground. But the houses they supply are 50 to 100m away. wouldn't the same issue with car chargers and remote earth/faults raise it's head? Im doing exactly what nick suggested. Mines 130m away. Trencher is booked! What is is your thinking around the power cut back up function. Assuming you will have a battery? 1
JohnMo Posted 2 hours ago Posted 2 hours ago Doing long distance AC can lead to inverter switching off depending on the voltage of the grid at the house(s). Taking a voltage drop on the DC has zero effect. When doing the AC over the distance the inverter has to produce more volts to overcome the AC line voltage drop. One of my arrays has 80m of DC cable zero issues and cable isn't that large. If doing DC make sure the voltage is high, low voltage DC for a given amps is big, high voltage for a same amps gets smaller 1
-rick- Posted 1 hour ago Posted 1 hour ago (edited) 6 hours ago, Nickfromwales said: For this distance, sending DC back is nuts. Abandon this is my 2 cents, as you'll need huge CCA of the cables. Put the inverter out with the array and send AC back; same we did a while back on a ground mount some 135m away from the house, where the client wanted the array in a meadow vs the untouchable roof of his listed home. Surely this depends on the voltage the array/string is at? With modern inverters often wanting arrays of 800-900v, you'd need less CCA on DC than AC. Even the older but common 350v arrays/strings would be better over DC than AC. DC is more efficient at long distances. The conversion between different voltages and safety of the system. Edited 1 hour ago by -rick- 1
Beelbeebub Posted 1 hour ago Author Posted 1 hour ago 48 minutes ago, Roger440 said: Im doing exactly what nick suggested. Mines 130m away. Trencher is booked! What is is your thinking around the power cut back up function. Assuming you will have a battery? In favour hybrid systems so the battery generally needs to be next to the inverter. If I use the AC method then there is one AC line (a line, neutral and earth) going to the remote inverter connecting to the meter tails between the meter and the consumer unit and I need a switchover box at the house to isolate from the mains in a power cut so I don't energise the mains. I could arrange for power cut cover but there would need to be a Comms line as well which cuts onto the cost savings.
Beelbeebub Posted 1 hour ago Author Posted 1 hour ago 6 minutes ago, -rick- said: Surely this depends on the voltage the array/string is at? With modern inverters often wanting arrays of 800-900v, you'd need less CCA on DC than AC. Even the older but common 350v arrays/strings would be better over DC than AC. DC is more efficient at long distances. The conversion between different voltages and safety of the system. 48 minutes ago, JohnMo said: Doing long distance AC can lead to inverter switching off depending on the voltage of the grid at the house(s). Taking a voltage drop on the DC has zero effect. When doing the AC over the distance the inverter has to produce more volts to overcome the AC line voltage drop. One of my arrays has 80m of DC cable zero issues and cable isn't that large. If doing DC make sure the voltage is high, low voltage DC for a given amps is big, high voltage for a same amps gets smaller Good point The array will be fairly large (maybe 8+ panels for each house) so the voltage will probably be higher than mains so the current lower. Plus we have had high voltage issues in the past.