Depth for buried DC cables

Featured Replies

Does anyone have a reference for the depth that DC cable needs to be buried - I assume the same as armoured AC (0.5m in general) but wanted to double check.

 

I was going to use the specific armoured stuff 

  • Replies 72
  • Views 3.2k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Roger440
    Roger440

    After much deliberation, going to run DC. Will add a year to payback time though   Cracking on    

  • So 3.86kW, so not pence.    3.86kW exported over 6 hrs is 22kWh. A 10kWh battery in winter would be filled from the grid. You basically get a time of use tariff so you get cheap perio

  • JohnMo
    JohnMo

    If you don't really need to bury l wouldn't - would surface run, then you can see them.

Posted Images

If you don't really need to bury l wouldn't - would surface run, then you can see them.

  • Author
3 hours ago, JohnMo said:

If you don't really need to bury l wouldn't - would surface run, then you can see them.

For at least some of the run they will go across an agricultural field (sheep) that is occasionally flail mown and then also across a lawn which is regularly mown and trafficked.  Also across a tarmac drive.  It's (hopefully) a single ground mounted array that serves several houses.

 

The other alternative is overhead poles but that has issues too. 

You need to bury below deep plow depth. Although sheep today, you have no idea what will occur in year. So that is 910mm to 1000mm

  • Author
9 hours ago, JohnMo said:

You need to bury below deep plow depth. Although sheep today, you have no idea what will occur in year. So that is 910mm to 1000mm

Good point.

 

Though I can guarantee the field isn't going to get ploughed anytime due to the slope and it also being an orchard.

 

It's a short run from the array site to the edge of the field so I could mount it above ground on some timber rails.  If I run it behind the hedge in a similar manner I could minimise the distance underground as @JohnMo suggests.

 

Looking at the site I realise there already is a telephone line overhead along the fence.

 

I wonder if I could run the cables overhead for a good chunk.

If it's an armoured cable and you have a route along a fence, why not clip it to the fence rails or tywrap it to a strand of fencing wire.

  • Author
8 hours ago, Dillsue said:

If it's an armoured cable and you have a route along a fence, why not clip it to the fence rails or tywrap it to a strand of fencing wire.

I don't have a fence only a hedge, and at one point I have to pass a gate and another a drive way.  In the field I could see effectively building a fence to carry the cable - i'll probably do that.  at least the buried sections will then not be in a field.  the biggest bugger is there are a ton of other services around, gas, mains, water and sewage plus some telephone.

 

Potentially I could go overhead the whole way, it's just passing over the drive way and gate are a bit untidy.

For this distance, sending DC back is nuts. Abandon this is my 2 cents, as you'll need huge CCA of the cables.

 

Put the inverter out with the array and send AC back; same we did a while back on a ground mount some 135m away from the house, where the client wanted the array in a meadow vs the untouchable roof of his listed home.

  • Author
5 hours ago, Nickfromwales said:

For this distance, sending DC back is nuts. Abandon this is my 2 cents, as you'll need huge CCA of the cables.

 

Put the inverter out with the array and send AC back; same we did a while back on a ground mount some 135m away from the house, where the client wanted the array in a meadow vs the untouchable roof of his listed home.

Not a bad idea, it would definitely cut cable costs but I think i'd I be giving up the power cut backup function?

 

And is there a problem with exporting the earth? The panels will all be earthed together by virtue of being fixed to a metal frame stuck to the ground.  But the houses they supply are 50 to 100m away. 

 

wouldn't the same issue with car chargers and remote earth/faults raise it's head?

4 minutes ago, Beelbeebub said:

Not a bad idea, it would definitely cut cable costs but I think i'd I be giving up the power cut backup function?

 

And is there a problem with exporting the earth? The panels will all be earthed together by virtue of being fixed to a metal frame stuck to the ground.  But the houses they supply are 50 to 100m away. 

 

wouldn't the same issue with car chargers and remote earth/faults raise it's head?

 

Im doing exactly what nick suggested. Mines 130m away. Trencher is booked!

 

What is is your thinking around the power cut back up function. Assuming you will have a battery?

Doing long distance AC can lead to inverter switching off depending on the voltage of the grid at the house(s). Taking a voltage drop on the DC has zero effect.

 

When doing the AC over the distance the inverter has to produce more volts to overcome the AC line voltage drop. 

 

One of my arrays has 80m of DC cable zero issues and cable isn't that large. If doing DC make sure the voltage is high, low voltage DC for a given amps is big, high voltage for a same amps gets smaller

6 hours ago, Nickfromwales said:

For this distance, sending DC back is nuts. Abandon this is my 2 cents, as you'll need huge CCA of the cables.

 

Put the inverter out with the array and send AC back; same we did a while back on a ground mount some 135m away from the house, where the client wanted the array in a meadow vs the untouchable roof of his listed home.

 

Surely this depends on the voltage the array/string is at? With modern inverters often wanting arrays of 800-900v, you'd need less CCA on DC than AC. Even the older but common 350v arrays/strings would be better over DC than AC.

 

DC is more efficient at long distances. The conversion between different voltages and safety of the system.

Edited by -rick-

  • Author
48 minutes ago, Roger440 said:

 

Im doing exactly what nick suggested. Mines 130m away. Trencher is booked!

 

What is is your thinking around the power cut back up function. Assuming you will have a battery?

In favour hybrid systems so the battery generally needs to be next to the inverter.

 

If I use the AC method then there is one AC line (a line, neutral and earth) going to the remote inverter connecting to the meter tails between the meter and the consumer unit and I need a switchover box at the house to isolate from the mains in a power cut so I don't energise the mains.

 

I could arrange for power cut cover but there would need to be a Comms line as well which cuts onto the cost savings.

 

 

  • Author
6 minutes ago, -rick- said:

 

Surely this depends on the voltage the array/string is at? With modern inverters often wanting arrays of 800-900v, you'd need less CCA on DC than AC. Even the older but common 350v arrays/strings would be better over DC than AC.

 

DC is more efficient at long distances. The conversion between different voltages and safety of the system.

 

48 minutes ago, JohnMo said:

Doing long distance AC can lead to inverter switching off depending on the voltage of the grid at the house(s). Taking a voltage drop on the DC has zero effect.

 

When doing the AC over the distance the inverter has to produce more volts to overcome the AC line voltage drop. 

 

One of my arrays has 80m of DC cable zero issues and cable isn't that large. If doing DC make sure the voltage is high, low voltage DC for a given amps is big, high voltage for a same amps gets smaller

Good point 

 

The array will be fairly large (maybe 8+ panels for each house) so the voltage will probably be higher than mains so the current lower.

 

Plus we have had high voltage issues in the past.

I've been mulling this situation over too. I don't think it's that uncommon with e.g. (a) panels on a roof, (b) modern all-in-one stacks which tend to have all the bits (inverter, battery, gateway, car charger etc) all at the same location. And as batteries can't be an an attic these days, it suggests the stack is outside or in an outbuilding and maybe some distance away from the panels - which implies a longish DC connection. Either that, or the inverter is in the attic and the battery some distance away, which implies likely an ac connection, but then a split stack.

>>> maybe 8+ panels for each house

 

So maybe 400V max (at low temperatures) & 15A max (in summer sun). 

Edited by Alan Ambrose

Modern panel open circuit voltage is often ~45v so 8x45 is 360v

So, for the OP @Beelbeebub that suggests 2-core 4mm PV ultra SWA (PV-ULTRA2C4.0SWA) rated at 52A and £9 p.m. 

 

Power loss at 15A is 15^2 * 5 (ohms per km) * 2 conductors i.e. about 220W per 100m (and you're carrying ~4kW at that point, so 6%). Voltage loss 15 x 5 / 10 * 2 = 15V i.e. ~4% (per 100m again). Not insignificant.

 

>>> And is there a problem with exporting the earth?

 

Good question.

Edited by Alan Ambrose

 

 

13 minutes ago, Alan Ambrose said:

Power loss at 15A is 15^2 * 5 (ohms per km) * 2 conductors

DC circuits use resistance calculations only. This makes voltage drop simple and linear: V = I × R.

 

Definitely do minimum of 6mm² any smaller you are wasting power. Then you are at or below 3% voltage drop and for a minor uplift in cost. Most panels these days come with 6mm² tails not sure why you would down grade them with 4mm².

 

Screenshot_2026-08-02-13-02-11-55_40deb401b9ffe8e1df2f1cc5ba480b12.thumb.jpg.b3351c83fa2ccaedca578b26db013c10.jpg

 

Do multi core then one cable will carry multiple strings, so 4 core two strings etc. easier to route one cable instead of loads.

8 minutes ago, Alan Ambrose said:

>>> And is there a problem with exporting the earth?

 

No an electrician but I thought over the distances we are talking about you need to install a local earth rod. Earthing would only be for the metal work and wouldn't touch the DC AFAIK.

2 minutes ago, JohnMo said:

Definitely do minimum of 6mm² any smaller you are wasting power. Then you are at or below 3% voltage drop and for a minor uplift in cost. Most panels these days come with 6mm² tails not sure why you would down grade them with 4mm².

 

This is news to me, I thought 4mm was standard. Either way I agree with you, for the long run 6mm makes much more sense for the small cost uplift and it makes sense whether the tails on the panels is 6mm or 4mm as the upsize is purely for voltage drop/efficiency not load carrying capacity.

 

2 minutes ago, JohnMo said:

Do multi core then one cable will carry multiple strings, so 4 core two strings etc. easier to route one cable instead of loads.

 

Disagree strongly*. If you are planning multiple strings then it would be better to install an inverter that supports 800v and run one string of 16 panels rather than 2 of 8. Current and therefore voltage drop on the cable would stay the same but you'd be transmitting twice the power and hence improve efficiency.

 

* @Beelbeebub mentioned multiple houses, in which case I'd guess it's not possible to put them all on one string as there will be separate inverters. I'd also think in those cases you wouldn't want to use a single cable (or even a single trench) to allow proper separation of responsibilities.

1 hour ago, -rick- said:

Disagree strongly*. If you are planning multiple strings then it would be better to install an inverter that supports 800v and run one string of 16 panels rather than 2 of 8

Would agree normally, but multiple houses was mentioned, so would assume one string per house with it's own inverter. Unless @Beelbeebub is doing lots of kW per house. But not knowing the full layout logistics will decide the final cable spec 

  • Author

There are 4 houses in a loose crescent around a "green".  A field backs on to the "green" to the north with a high hedge 

 

The panels are being fitted to comply with the EPC regulations and get each property to. "C" grade 

 

1 house is a good candidate for normal E/W roof solar being a bungalow with a low pitched concrete roof.

 

The other 3 have problematic roofs. Either not good aspect (shaded) or not good enough condition to allow solar to be fitted with out a new roof first or both 

 

But a ground mounted array could be fitted in the "north" field out of sight (and far enough back so it's not shaded by the hedge.

 

I figure it's easier and cheaper to install and maintain one array in a field than 3 arrays on 3 roofs.

 

And then for the bungalow I have to decide if it's cheaper/easier to put panels on the roof Vs chuck some more up in the field array and run a cable to it (that would be the 100m one.  The others are closer to 50m)

 

Strictly speaking the batteries are not needed as the EPC system currently only accounts for the panels and inverter - you get no points for batteries.

 

But it gives so much extra benefit to the tenants it's hard not to justify it beyond the purely mercenary view.

Edited by Beelbeebub

  • Author

If I did an AC transmission system the temptation would be to make it a non battery system and leave fitting of batteries to soak up the excess something for the tenants to do if they wish.

 

This might be easier with plug in battery systems.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.