We're prepping to dig foundation and drainage out and wondering about depths for the (approx 5m) run that is going to be under the insulated raft and how low to set the foot for the main stack which exits straight out. 

Any idea what that depth needs to be? Is it 600mm below the mot 1?

 

Also, how far out from the edge of the raft do the drains need to run - I'm reading 1m min is the part H requirement if pipe is below foundation but, as our raft is only 450mm into the ground makes interpreting the regs a bit tricky as, pretty much any drain will be below the raft level.  I'm not sure if it's interpreted the same as obv the weight is spread over the raft rather than down through strip foundations so, does this make a difference?

 

Or, do I just ask BC?!

Posted

On the current MBC project I'm consulting on, we have soil pipes in the 150mm MOT1 layer directly under the 50mm sand blinding, and some others like comms and landscape power are lower to avoid these. I designed all this ahead of MBC's arrival, making sure there were the least number of services crossing over/under each other.

 

As you're under a raft, there is no minimum depth THB, but for power and water you do need to drop down towards the periphery to comply with the 750-900mm that these authorities will mandate.

Posted

@lizzieuk1 Our insulated raft sat on 250mm compacted type1 with 50mm granite fines on top. The insulation was 300mm thick. The inspection chamber was around 3m from the edge of the raft. The pictures show before and after sub-base was laid.

 

P7260010.thumb.JPG.ebdd1cf0eba26ca3d80d904fbb12525c.JPG

 

P7280013.thumb.JPG.c497e1b6cc885d8791cad41e56f1470c.JPG

Posted

Our soil pipes are in the compacted type 803 and sand blinding. A 1m length close to one of the stack foots comes up about 20-30mm into the 250mm  insulation.

Posted
12 hours ago, Nickfromwales said:

On the current MBC project I'm consulting on, we have soil pipes in the 150mm MOT1 layer directly under the 50mm sand blinding, and some others like comms and landscape power are lower to avoid these. I designed all this ahead of MBC's arrival, making sure there were the least number of services crossing over/under each other.

 

As you're under a raft, there is no minimum depth THB, but for power and water you do need to drop down towards the periphery to comply with the 750-900mm that these authorities will mandate.

Many thanks Nick, that's really helpful. 👍 

Posted
3 hours ago, Gone West said:

@lizzieuk1 Our insulated raft sat on 250mm compacted type1 with 50mm granite fines on top. The insulation was 300mm thick. The inspection chamber was around 3m from the edge of the raft. The pictures show before and after sub-base was laid.

 

P7260010.thumb.JPG.ebdd1cf0eba26ca3d80d904fbb12525c.JPG

 

P7280013.thumb.JPG.c497e1b6cc885d8791cad41e56f1470c.JPG

Thankyou 😊  do you know if there's a reason the Chambers needed to be so far out? Or was it just 'on the way' to the mains connection?

Posted
30 minutes ago, BotusBuild said:

Our soil pipes are in the compacted type 803 and sand blinding. A 1m length close to one of the stack foots comes up about 20-30mm into the 250mm  insulation.

Thanks 👍  sounds like we are OK to be in or just below the MOT then. 

Posted
12 hours ago, Nickfromwales said:

On the current MBC project I'm consulting on, we have soil pipes in the 150mm MOT1 layer directly under the 50mm sand blinding, and some others like comms and landscape power are lower to avoid these. I designed all this ahead of MBC's arrival, making sure there were the least number of services crossing over/under each other.

 

As you're under a raft, there is no minimum depth THB, but for power and water you do need to drop down towards the periphery to comply with the 750-900mm that these authorities will mandate.

Have you topped the pipe with pea grit then mot on top? Thinking in the 150 layer there's not much room for both!

Posted
17 minutes ago, lizzieuk1 said:

Have you topped the pipe with pea grit then mot on top? Thinking in the 150 layer there's not much room for both!

Yes. Shingle goes under / around / atop, and then the sand blinding goes in.

 

17 minutes ago, lizzieuk1 said:

Thinking in the 150 layer there's not much room for both!

Groundworkers will just shoot through this, but if there's any major backfill over the shingle then they may well use a bit more type 1, then the sand (usually dependant on how far they have to walk to either pile of 'stuff' ;)).

 

21 minutes ago, lizzieuk1 said:

Thankyou 😊  do you know if there's a reason the Chambers needed to be so far out? Or was it just 'on the way' to the mains connection?

I've set this up so the chambers are dead centre of the hard standing (walkway) around the house. Seen way too many jobs where these are half in the slab and half into the grass etc, which looks shite.

 

Have you allowed for all the requisite ducts / services etc?

Posted
1 hour ago, lizzieuk1 said:

Thankyou 😊  do you know if there's a reason the Chambers needed to be so far out? Or was it just 'on the way' to the mains connection?

I put it in the most convenient position on the way to the sewage treatment plant. I don't think there are any set distances.

Posted

It’s just about when 2 pipes need to converge, where you’ll need IC’s at each instance or any time there’s a change in direction.

 

You can run one pipe from A>B for some distance, but getting most BCO’s to agree to it is another thing. IIRC the last one wouldn’t let us go more than 8m (in a perfectly straight line)….. so ended up with 3 IC’s between the house and the road. 