The heat pump is running, it has some teething problems but it works very effectively at warming the slab. The heat Meter (EMON Pi) is also up and running. So now I want to move on to setting up the Weather Compensation and see what happens. Looks like you choose a curve setting as best guess and then observe what goes on to fine tune. One thing I cannot see anywhere in the system we have is an internal temperature monitor the typical systems seem too open loop to me. I get the system does not use a thermostat but I don't get how it can get away without having some sort of measure of the internal temperature of the house because it doesn't know how the house is being used, what is coming in via the sun or indeed if the house is cooling or heating more than the output is providing for. Still the heating period has a few weeks to run yet and I want to make every day a school day learning how to heat the place so I guess I should just give it a go, any definitive advice as to the process I should follow.
Panasonic uses the wall mounted controller for internal info. How the feck will yours know what's going on indoors if you don't have one? Other than the difference between flow and return, which would be cruder than a semi-sober welsh plumber.
Some simple science
Your floor even on a dull day will not be much hotter than the room, maybe 1 to 3 degs at the surface depending on outside temperature.
Let's assume room is 20 degrees, floor surface 23, sun comes out room increases to 23. Now as floor is 23 and room also 23 the floor no longer transfers heat to room. Sun goes away room temp drops, floor starts giving heat to room. With a thick screed (think you have this) the floor just acts as a huge buffer for energy.
Thick screed doesn't act like a radiator due to its thermal capacity, think more a swimming pool, once up to heat it isn't cooling quickly. Once you allow to cool it takes an age to heat up.
Setting up WC is pretty easy for UFH, start with a gradient of 0.5. so every degree outside temperature drops you increase the flow temp 0.5 degs. Start with a flow temp of around 20 or 22 at 10 degs and 28 to 30 at -5. Ideally let it run for 24 to 48 hrs. Adjust curve up down to suit. Small changes have a big change. System doesn't need to know internal temperature. You set the curve to balance heat loss and heat input. You better starting cool rather than hot.
WC is completely open loop.
It's witchcraft - that's all you need to accept - once you accept that it's really easy to understand 😉
I set mine up to target a flow temp which resulted in my house being stable internally at 0 Deg C OAT (I started high and worked down - probably quicker to start low and work up but Mrs Alien was not keen on "freezing her ass off while I fecked around with the heating" (True statement)
My slope target flow temp at 0 deg OAT ended up at 33 Deg C which in my case was 0.6 as a slope (with no level correction)
Once you have the slope you can then fine tune the level
All the level is doing is compensating for the fact that heat loss is proportional to temp differential - higher the difference between inside and outside the faster the heat loss
example
at -2.5 OAT and 21 deg inside the delta is 23.5 Deg C
at 10 Deg OAT and 21 deg inside the delta is 11 Deg C
So heat from inside moves slower to outside when the differential is lower so proportionally you need to put less heat in to cover for the escape because the escape is at a slower rate
So at 10 deg OAT my target flow temp was 27 Deg C and the house over heated so I needed to drop the level to target 26
When I drop the to -3.0 on the level on a slope of 0.6 it changes the target temp at 0 Deg C OAT to 32 Deg (and I want 33)
So I increase the slope to 0.7 and that gets me back to 33 Deg C at 0 deg C OAT
Told you it's bloody witchcraft :D
WC uses partial differential equations (PDE).
These show a possible solution to a position on a complex curve.  In heat equations, complex curves can be though of as rugby ball.  If you place a rugby ball on a table, and assume it rests level, then you can easily measure the heights along the length from the table.  This will give you a curve.
Now imagine that for every 5mm you move, either left or right, towards the pointy end of the ball, that you measure the circumference.  This will reduce as you move left or right.
So you can see that you have two variables.  Positions on the X and Y axis.
Now imagine that you throw in a third dimension, Z, and you can see that you could recreate the shape of the rugby ball.
This can be written as a PDE with the form:
δ2u/δx2 + δ2u/δy2 + δ2u/δz2 = 0
All that is really showing is that if you know two positions you can deduce the third i.e. Flow dT, OAT.  This is because of the Laws of Energy Conservation.
Easy really.
I get that but it assumes a static envelope if, using your analogy, the rugby ball is shape shifting as you measure the curve would work only when the ball hits the shape it was when you measured it. In my terms if I leave the windows open when it's cold outside the heat will be removed faster than you are making it up so the temperature will drop and once you close the windows the temperature difference will linger for a period which, in a well insulated building, could last a reasonable time. Obviously the reverse also applies so if you have a big party the house will overheat and stay overheated!  Have I got that wrong?
We do have a number of internal temperature sensors and via the BMS connection to the heat pump we should be able to  adjust things if the Weather Compensation (WC) is not effective.
On the whole I suspect when I get it all going that the edge cases I set out above, windows open and parties, will not be an issue but I do think it is important to stress test all the assumptions built into the accepted truth.
Yes, and it is why there are, sometimes, no solutions.
Though you can put a time element into the mix, which you, in effect, be enthalpy.
But as you are working within limits, and tight limits as well, it is probably close enough.
The assumption is incorrect though. Open window you let cold air in hot out, but the thermal capacity of air is very low, building fabric the thermal capacity is very high. You close the window, the air within the building is reheated by the now warmer fabric (especially the floor) pretty quickly. You floor will not lose heat for many hours/days even with heat source off.
The other acceptable running mode is pure thermostat, set a fixed flow temperature of 28, still run as a single zone. Your thick screed will demand very long times and at that temp CoP will be great.
Because your system and house should run at that min outside temp. So run will be proportional to outside temp. Cold day run all the time, 10 degs for a couple of hours.  Lowest temp to do that and get best CoP
1 minute ago, dpmiller said:
Because @JohnMo says so. And if it works for him, nothing else will do?
What boll0cks. I'm running pure WC.  Have run WC, thermostat mode, batch charge mode and hybrids of all three. You could set target flow temp to 35, I've done that also.  But ASHP just runs full load with zero modulation and will most likely never get there before the thermostat trips out.  You get best CoP at a medium load position, so you want the heat pump to hit the target temp and then take control and modulate down. Any UFH with a thick screed, the floor is the dominant force, its temp dominates return temp, return temp dominates max flow temp achievable.  Simple science, not because it works for me. Many on here run a thermostat based system, its just a matter of setting the lowest flow temp you can get away with not the maximum.
‘ckin hell……
”Shots fired!!!!!!!!” 💣 💥
Lol.
I thought it was only me that didn’t get their full 8 hours in last night :D
  • Haha 2
"I don't get how it can get away without having some sort of measure of the internal temperature"
I dont know how your system works but I know our GSHP monitors flow and return temps on the heating circuit so I guess it can extrapolate from that. We have no internal thermostat influence on our GSHP or ASHP systems and they both keep the buildings at very steady temps once you get the curve right.
WC only sets the ASHP flow temp, and I'm pretty sure it does so using only the exterior temperature. When running perfectly, the higher flow temperature completely cancels out the increasing heat loss as it gets colder outside.
Once WC is properly set up, interior temps are solely a function of whatever thermostatic feedback you implement.
For example, I have a 10 year old Panasonic Aquarea. I only have the dumb controller without a thermostat. All interior temperature sensing is handled by my home automation system, which controls a relay across the relevant switched live contact. The ASHP knows literally nothing about the internal temperature of the house other than indirectly via switched calls for heat.
Not quite. Curves for radiators and ufh are different - the output factor of each is calculated as to the power of 1.3 for rads and 1 or 1.1 for ufh, so neither are linear and so heat pump curves aren't either. With the curves, you'll general have a default curve and then you adjust this with a heating curve shift.
Usually, a heat pump manufacturer will supply a heat curve chart which provides you with the initial basis of your settings - this can be in the manual or just on screen on the main controller. Against this curve, all you need to do is draw from the x and y axes,which tell you the outside air temperature (usually on x-axis) and flow temperature (usually on y-axis), until you meet the curve that matches your heating system design flow temperature and corresponding design outdoor air temperature. Fire the system up and wait at least 24 hours, or if the house is cold and has lots of thermal mass, it could take weeks for the house to thermally balance out. Then you can look at how the system behaves as outdoor temperature fluctuates which will then tell you what adjustments you need to make to the curve and shifts.
Useful info. I will havea play over the weekend.
39 minutes ago, SimonD said:
thermal mass
Is that a thing - Steamy will be along shortly, no doubt, with his cosh.
It is on here, if not for any other reason than to get @SteamyTea hot under the collar 😁. But on a tangent, I was talking to my son the other day and I was winding him up by using the term phase change where he insists it's state change. I then explained to him that during school I had 2 physics teachers. One was adamant that centrifugal force did not exist and said the only force was centripetal force and the other would repeat that centrifugal force did exist and it was fine to use the term as long as we knew what centripetal force was. Hope this doesn't now cause a 55 page discussion of the reality of force.
Thermal Mass is just a common way of saying thermal capacity - The SI unit for thermal capacity (or heat capacity) is, joules per kelvin (J/K) or joules per degree Celsius (J/°C). Heavy stuff like concrete the value is high, air the value is low.
But Harris and Steamy through the teddy out the cot because it "Not the Correct term" to use, but ha-ho.
They exist in science they are just taken from a differing view point, an example cut and paste
The centripetal acceleration is the acceleration a body experiences in centripetal motion (moving in a circle or along an arc). Centripetal acceleration always points towards the centre of the circle, hence the direction of the moving body is constantly changing (since its velocity is always tangent to the circle). On the other hand, the centrifugal force is a fictitious (imaginary) force the object experiences during circular motion. The direction of this force is opposite to the direction of the centripetal acceleration. The best example to visualise this difference is to imagine being in a car. If the car takes a sharp left turn, the passengers experience a thrust towards the right (the centrifugal force), whereas the friction between the road and the tyres results in the centripetal acceleration allowing the turn to take place.  So they are equal but opposing forces.
Not quite.
You have to take the thermal conductivity into account as well.  And the thermally exposed areas where potential differences are.
A tonne of concrete will store the same amount of energy as an identical tonne of concrete, but if one is a sphere and another spread over 50m2, they perform very differently.
  • Like 3