@Gus Potter& dealing with your previous post:
I am grateful to you for taking the time to explain your thoughts on this - including those I don't like & those I disagree with.
I don’t have time to explain the history of how I got to this point, because I have big demands on my time at the moment, in addition to the self build project, but just taking a few of your points in order, from above.
The SE has been impressive, so far.  He seems completely undaunted by this project.
My architectural technician (& he’s not the first one I’ve had on this project) is a huge disappointment.  If I start to explain why, I’ll be here all night.
Agree: his designed insulation envelope is not good enough.  I am having to work to fix this – not something I expected to have to do.
Rain will fall straight into the cavity behind my cladding (will be composite or Millboard type, so the top of the cladding is OK getting wet)  – some advice says a 6mm gap above the ventilation void (which will be 50-100mm, depending on how much building out we do to get the cladding to where we want it to be, will be enough to vent & will not let much rain in.  I could easily have the drip edge from the flat roof running over the top of the cladding, whilst allowing 50mm vented space all the way out of the top of the vent cavity then under the drip edge.  It’s not the look I wanted, but if it’s necessary, that’s what I’ll put on the drawings.
I’ve got draft drawings from the SE, so I know where all the steels go & this is how I know my rafter depths are different for the two pitched roof sections.
Re: “can I get someone to build & at what cost”.  I don’t see how I can stop & do that now.  I need to get the drawings done properly then I can get a BoQ/build cost.
“blindly” I don’t agree with this characterisation of my approach to this project,  although I don't mind you telling me this is what you think.
“If I go back to the beginning, how much will that cost me?” – difficult to say in financial terms & I'm not going to waste time thinking about this right now, but “going back to the beginning” would cost me the relationship I have with the person who’s paying for the other half of all this.  Due to a looming planning permission deadline, the old house was demolished 2024.  Self building was her idea, fortunately.
2 hours ago, Gus Potter said:
internal clearance for stairs, ventilation at window heads and maybe fire escape /
Stairs have more headroom than building regs require - so no problem bringing the roof at the front back towards the centre of the house.
Ventilation - I'm aiming for good airtightness & MVHR - you have possibly been misled by the MEVs the AT drew in, despite my clear brief, "air tight, + MVHR".
Fire: I read the building regs document.  I think my design is compliant.  My only concern is BC may demand doors across my kitchen, that opens up into the hallway & stairs.  No big problem if the doors have to go in here - it will just be an unwelcome expense.  Also, most of the steels will have to have intumescent paint, rather than be boxed in, because they have joists attached.
34 minutes ago, Tony L said:
Thanks
Hi Tony.
I can see you are putting in a lot of effort into this. I appreciate that your teck may have not "captured" the complexity, but how much are you paying? You get what you pay for to some extent.  You sound like a hands on person so if you have just paid you technician from the neck down then what do you expect?
I thought he'd know how to do all this stuff.
This is a hard thing to learn, it takes years. To provide a bit of context. I was a building Contractor for 20 years, went to uni at the age of 40 to become an SE did training and now I've progressed to the point where I'm confident / competent in both SE, Architectural design, whats buildable and cost aware. That is a 40 year journey and every day is a schoolday for me. BH is a great resource. There are folk like you proposing this kind of innovative design. Your sketchup model looks brillaint!
It's not that hard if you go about it in the right way. Your SE sounds experienced, pragmatic, some SE's are actually sympathetic! We are not all horrible, sometimes we dish out tough love when it's clear that is what is required to give the Client a bit of a jolt and protect their interests.
So what to do? If you want to keep the rest of the team on board then in your own head go back to basics. Bluntly you can probably fix it by reconfiguring what is going on under the bonnet. The planners have no interest in the structure, insulation or what's going on inside the building. All thye are interested in is what it looks like from the outside. If you increase the occupancy that is material as it could impact on the parking provision, but all we are looking at here is seeking a buildable, cost effective design that is not going to fail due to say condensation, water ingress etc.
You asked about cold formed steel joists. You are right they can be a bit of wicked cold bridge, but on a warm roof you keep them on the warm side of the insulation. Dormer roofs tend not to be that big span wise. SE wise we need to check the bearing on the dormer face. But here we only need about 50 - 60 mm, this is driven by the fixing requirement into timber to get enough timber edge distance. The bearing strees does not govern usually on a msdest dormer roof.
You can get some insulation in to stop the ends of the joists getting cold. Also the cold formed joists may be only 1.2 -1.5mm thick. So while the rate of heat transfer in steel may be much more than a timber if you look at an exposed timber joist end which may be 45mm thick cf a 1.5 mm bit of steel exposed is not as bad as you think. Most folk think about big universal steel beams.. but here we are using thin steels that have a small expose cross section.. it's ecclectic but part of the art of design.
I think you can and you need to find a diplomatic way of doing so. It's just a move from the concept to detailed design stage after all! Detailed desin always uncovers unexpected cost elements, design is an itterative process. I pointed out why I think you are going to suffer, all your are doing is developing the design and details as you learn about the best and most cost effective way of achieving what you want.
Post overlapping here Tony.
I'm trying to warn you of the challenges you face. I have not considered your internal ventilation, only that the structure is going to work insulation and ventilation wise.
The fire protection is always a challenge. Your house is only two stories and detached so pretty benign.
In your case so long as any roof steels are not contributing to the stability of a floor or structural load bearing wall they may only need minimal protection. Talk to your SE and you may find it all works boxed in by ordinary plasterboard and buried in the roof dpeth.
Thanks for all this, @Gus Potter.
I've designed all my metal web floor joists so they're inside the inner block leaf; those that meet the outer wall will be hung on ledger boards.  I've done this to make air tightness easier to achieve, & there's a thermal break benefit too.
With the ideas @Iceverge has provided, the tops of the rafters will all be insulated, but at the bottom they'll run from inside to outside over the wall plate, of course.
The SE has specified UB19 for the beam in the section picture you posted.  This is a fair bit chunkier than I was expecting - only because I can lift the mild steel box section back bone chassis of an old Lotus with ease, & they're very strong.  These UB19s (there are 6 of them) are in lengths of max. 4.55m, so that's 86KG to lift into place.   I think the top of a UB19 will be 7.9mm thick & the web will be 4.8mm, so it will be good to have insulation along the edges of these UBs, & it's worth considering what's going on at the beam ends too.  My plan was to wrap the beam ends that penetrate the inner cavity block leaf with VCL membrane, bring the membrane inside & fix it to the wall (I've got notes on how to affix). The cavity between the block inner & rendered block outer leaf is only 150mm & will be filled with EPS beads.  I was thinking it may be worth sticking a rectangle of super insulating something or other inside the cavity on the beam ends.  If anyone has any suggestions please let me know.  & is it worth sticking a block of high R-value something on the top flanges?  There's not much gable end wall going on top of these UB ends.  I looked for high R-value padstones, but I gave up this search & decided to rest the beam ends on regular padstones.
In general once stuff is inside the main insualtive layer then it's not worth worrying about extra minute thermal gains like insulating padstones or the like.
As i can see you'll have 150mm EPS beads outside your UB so any gains would be very small.
I would stop the inner leaf of the wall 100mm short of the external wall and allow the 100mm PIR to oversail the wall and meet the wall EPS beads. This will make a thermally very nice junction.
In general I'm not a fan of too much steel work in domestic construction. It's hard to finish and fix to with typical builders tools.
I would prefer precast concrete or on site poured lintels for the blockwork sections and gluelams for the roof. They're aesthetically quite nice in my opinion and leaving them on show may be cheaper and easier than building in a UB.
In general the more I look at your house I can't but agree with @Gus Potter. There's a lot of obstacles to getting it to the standard you hope. It has the classic hallmarks of something that perhaps began more simple but had bits bolted on to satisfy a desire for something different or with a bit more flair. Then it sounds like planning appeared and imposed some limits that compromised the building.
1 went through 3 sets of planning permissions before we build our house. Each one simpler in turn and it was still a pain as a first time builder to get anywhere close to the standards I wanted with efficiency etc.  Would you consider returning to the drawing board and designing out some of the trickier bits like reverse slope dormers and hidden guttering?
Based in your design constraints a section like this would be much more buildable.
No steps in the upstairs. 45 deg roof into a 3 deg section in the middle for sanding seam. likewise with the dormer. 400mm allowed for the walls and roof for plenty of insulation.
@Iceverge. Thank you again for your work on this.  I'm pleased you support the idea of "flat roofs" being standing seam at 3 degrees.  Let's hope the planners consider this a reasonable fall for my approved flat roof sections (I'm not intending to ask them).
I've been working on some detail drawings for the roof intersections this morning.  I have to go out now, so I'll aim to I'll finish these off & post them this evening, along with responses to the other points from your post above.
Thanks again for this, @Iceverge.  I like what you’ve drawn. Sorry, the roof can’t be at 45 degrees because this would stretch the flat roof section at the top & make the building look very different from the approved plans.
400mm EPS in the walls is appealing, but it would make the inside too small & it can’t happen because [I’ll be in big trouble with you when you read this] the substructure is already built.  For the benefit of anybody reading this whilst researching your possible self build, & to save @Gus Potter & @Iceverge the trouble, l will just explain: building the substructure before your superstructure drawings have been finalised is a very bad idea.
I’m sorry to make the task of resolving these problems more difficult but, there is no way I’m going back for a new planning permission.  I don’t want to spend time explaining the long history of how I eventually achieved PP for something that I actually wanted to build: I need to focus on what’s ahead.
That's not far off what happened, yes.
I don't know anything about site poured lintels.  I think I ought to minimise the number of technologies I must learn about to get this house built - I'd really want to learn about it because I wouldn't trust a builder to do it properly, if he thought I didn't understand the process.  My learnings about works up to DPC (mostly from BH) saved me at least £7,000 after the builder took advantage of BC's requests for changes & tried to rip me off.
I like glulams too.  Are these OK to stick through the inner block leaf, so they're flush with the cavity (wrapped in VCL, of course)?
Sorry, I can't visualise this.  Are you talking about the long inner walls that the rafter ends sit on or the gable end walls (that will have ladders going over them, for some roof overhang)?
I’ve added to a drawing I found online to show how the ventilation & drip edges will work at the apex of a standing seam roof, at 3 degrees .
& here’s a detail for where the 3 degrees centre section meets the 42 degrees section.  I’ve added in some L shaped plates (green) to prevent rain being blown up the roof & into the vent void.
This same detail could be used where the the 42 degrees sections meet the backs of the 3 degrees flat roof sections over the dormers.
9 hours ago, Nickfromwales said:
Can you not use slabs?
Thanks for the suggestion, Nick.  Yes, I could do, but I like EPS beads because:
EPS will fit perfectly into all the awkward shaped edges, on top of cavity trays, into a badly built section of cavity that is 165mm wide (ref: one of my threads from months ago).
If my trench blocks get wet, I think wet/damp EPS will be better than wet/damp mineral wool.
It doesn’t have to be stored on site.
It won’t get wet during installation.
It won’t be installed by the brickie, who’s on a price for the job & who’s motivated to work quickly & cut corners (ie leave gaps in the insulation), so he earns himself a paid day off at the end of the job.
We’ll be able to start putting the roof on sooner.
Perhaps the brickie/brickies will enjoy laying the blocks & do a better job if they don’t have to faff around with fluff.
The internet says EPS will be cheaper (so I’m assuming, if it costs more it won’t be loads more).
The internet says EPS has a better R-value (& that will be as compared to the expertly & patiently prepared mineral wool that was lab tested to deduce its R-value).
I reckon I can procure EPS installation service myself, so I won’t have to rely on the builder to deal with it, nor pay him to watch it being done, nor pay his margin.
I get to choose who does the work & it will be easier for me to arrange to be there to oversee it when it happens
@Iceverge likes EPS & I’m an @Iceverge superfan.
Hahah, I'm going to have to apply for an extension for my house to fit my ego after that!
Beware I'm probably far more disappointing in person than my ~online dating~ build hub profile suggests.
I do like EPS, but mineral wool batts in the wall would be fine too.....
However..... Are you dead set on cavity walls? They work well in simple structures however not having full planning drawings for yours I don't know if something else might be a better fit.
Can you post your full (deidentified) planning drawings, to let the collective masses decide here how to best make this project work for you.
I might be persuaded to use something other than block cavity walls, but I’m under pressure to get my notes on how to fix the draft drawings back to the arch tec’ – under pressure from both the arch tec’ (I can put him in his place if I need to) & from  my partner, who’s paying for half of all this & has become very frustrated that we’re not already much, much further forward with this project; I feel that if I take a step backwards & demand more extra time from her, for a complete structural redesign, this may lead to severe consequences.
I’m also keen to get these drawings finalised soon, so we can get a BoQ/build cost, & following this, if my partner isn’t prepared to commit to spend half of whatever it might take to build this design, we’ll need a re-think.  Building costs are very much higher than when this project was conceived & house values are not that much higher.
I chose cavity walls because, I was told (a long time ago now) this would be the easiest & cheapest way to build.
This project has been going for many years.  It took forever to get PP.   I designed the house before I discovered BH. The PP design has 100mm cavity walls & pre-dates the building regs change to 150mm.  Obviously, my latest design has a 150mm cavity.
I’ve attached the approved drawings.  Since these were approved, I have persuaded my partner she really does not want a wood burner, & I’ve deleted the chimney & some of the windows.  To save money & build complexity, the arch tec’ deleted the 550mm (F to C) loft space in the dormers & reduced the height of the dormers.  I’ve moved some of the walls around inside, to give more space to some rooms & take it away from others; for example, there’s now more space for MVHR & other plant room gubbins (all on the left of the back door as you walk in) & less space in the adjacent room (snug).
I’ve attached the approved plans.  These are really poorly drawn (by me), because I had somebody helping me with construction notes, etc, back when I didn’t understand this so well; he was supposed to re-draw my rough design, but he said my drawings were good enough to use for a planning application, & we just needed to add a scale bar & a few notes.
Also, I'll just mention, the construction drawings show a chunky (215mm blocks laid flat) wall next to the stairs, so I can have a floating staircase for the top flight.  That's if there's any money left when we get to that stage.  All the block inner walls are spec'd to go onto Marmox Thermoblocks.
TonyL_NMA-ELEVATIONS.pdf TonyL_NMA-FLOOR_PLANS.pdf TonyL_ROOF_PLAN__SECTION.pdf
Tony, what's done is done, anyway, there are occasions where you may for one reason or another needed to get some sub structure in place, it's called speculative desgn.
That's actually ok! You have an outside envelope into which you need to fit structure, the external appearance and materials have been established, happens all the time so take that as a positive.
The first thing and I'll say again, what you are doing design wise is really hard especially the detailing! This cavity tray detail for example does not work, not least as the piece of masonry on the inner leaf will just come loose when you bed the cill, probably before that,  there is no insulation under the cill. The shaped insulation is not achievable. What will happen is that you will end up paying for something that does not get delivered on site.
I've looked over your thread and conclude. You have set you heart on the outside, it looks great. You have an established plan for the general internal layout and finish, again good! But you are struggling with the structure, how you insulate that,  do the interfaces work thermally but also provide the lateral structural restaint and connections to the main structure. Now I've distilled your probem down. So all of a sudden that looks a bit more hopeful!
What has happened is that as you have learnt more about the bit inbetween the outside and the inside you are discovering that it is hard and often I think the case here with you is.. you can't see the wood for the trees. This is not uncommon so don't take this as bad.
It happens to many people, even those who do it as a day job! You are not alone!
Consider trying to find someone who has the skills to review your design in the whole, identify a way forward that is buildable, knock heads together when required. That includes knocking you into shape. Many self builders are stubborn! That is ok at times but from time to time it can be to their own detriment. They pay professionals, but only from the neck down!
Someone like this will work with you very closely and explain where your ideas are good and where you are going wrong. At the end of the day it's you paying the wage, it does work!
Now that will cost you but for that you get not least, an advocate, a friend and someone on your side. In my experience the fee you pay is often offset by the savings made and enjoyment you get when someone says.. you are on the right track, always have been, but we need to add this critical bit.
I'll leave these thoughts with you.
Edited by Gus Potter
TonyL_NMA-ELEVATIONS.pdf 226.14 kB · 3 downloads TonyL_NMA-FLOOR_PLANS.pdf 128.3 kB · 3 downloads TonyL_ROOF_PLAN__SECTION.pdf 317.32 kB · 4 downloads
Just saw now. Will have a look shortly.
Sorry - my fault.  I should have quoted or namechecked you when I posted, so you'd have receive a notification.
Thanks very much for pointing out this error - I hadn't spotted that one.  Although, I don't understand which bits are, "the shaped insulation".
I'd expected the air brick periscopes would be drawn, hard up against the outer leaf, & I'd have more EPS beads under the cavity tray & between the periscope & inner leaf, right down to the trench blocks.  As it is, there's a gap on one side of the periscope & some unspecified board on the other side.  The brick sized cross section at the bottom of the inner leaf, on top of the block & beam, is a Marmox Thermoblock.
Now I've distilled your problem down. So all of a sudden that looks a bit more hopeful!
Yes, it does.  Thank you.
What has happened is that as you have learnt more about the bit in between the outside and the inside you are discovering that it is hard
Yes, it's hard for me to learn, especially with the house build being just one of several significant responsibilities I must devote time to. I am keen to learn all about this, but when I began this project, I didn't imagine I'd be forced to learn in so much detail, to mitigate the losses from people who want to rip me off & others who are just incompetent.
I have already been thinking, with his limited talent, this arch tec’ is only going to be able to get us so far & unless I start again with somebody else (4th re-start) with the drawings, I’m going to need to pay somebody who knows what they’re doing to go through everything the current arch tec’ draws & re-work the details he’s not able to design properly.  I know I can’t trust my arch tec’s work, because, even with my very limited understanding of what needs to be done, I can spot many errors & I can see he doesn’t fully understand how to do his job properly.
Even if I start again with somebody else, there’s no guarantee the next person would be any better.
I came across Richard Bendy, who may be the right person to check over the drawings.  I haven’t made contact yet: https://www.thehealthyhome.uk
Ideally, my arch tec’ would pay Richard to show him where he’s gone wrong, & teach him how to do what I’ve contracted him to do, but I know this won't happen.  Richard Bendy's services include training architects.
Re. paying professionals: I had a good meeting with a proper architect, who has designed & overseen the completion of some certified passive houses.  His quote (& this is for a house that has already been designed to PP level & for which PP has been granted) was £28,272 inc VAT. This included 12 hours for electrical layouts, which my current AT’s contract doesn’t specify, & some of the things that my AT has so far failed to include in his drawings, such as door threshold detail & intermediate floor to external wall detail, were specified in the £28k+ quote.  There was also a substantial fee for, “building contract admin, PD & on-site support”, which I negotiated down from the quoted fee to £2,160/month (inc VAT) for the duration of the project. I was told that it would be very unusual to proceed without this monthly fee, but if I chose to do so, I’d be completely on my own once the drawings had been handed over & I wouldn’t be able to call for help with the build (a condition arising from the architect’s insurance policies). So that’s £50k, assuming we pay the monthly fee for 10 months & don’t need any extra drawings.  & this fee was based on me providing the .dwg format drawings (which I had only as .pdf) from the AT that I was about to sack, for being quite a lot worse than the current one.
A prominent member on here explained, many architects overcharge for work that’s often sub-standard.  He highly recommended the AT I‘m trying to work with now.  This BH member gives out good advice here on BH all the time & I trusted his judgement.  Here’s an excerpt from the current AT’s quote:
My fee to prepare a detailed set of construction drawings for a dwelling of this scale and design, including detailed floor plans, 2 x sections, annotated elevations, site plan showing drainage and services, specific details of key elements which require further thought/ironing out such as the cantilevered box and corner glazing and a set of construction notes/specification, would be £6000 plus VAT, 50% of which would be payable upon instruction with the balance payable upon issue of final drawings. This is an all inclusive fee for the complete set of drawings and details. There are no further charges for any amendments required or liaison with structural engineers or building control, or indeed yourself. Therefore there are no nasty surprises further down the line.
Thanks again, Gus.
I’m away from Friday, for 9 days, so I must just explain: any comment anybody posts will be gratefully received, although I won’t respond until the week after next,  because I’ll be having a fantastic time snowboarding & screen time will be limited to essential work comms only.
I thought I'd put up a clearer picture of the poor detail @Gus Potter pointed out so that anybody who's interested can see it clearly.  I'm wondering if the cavity tray went in under a full block (see orange line), this would make the arrangement sufficiently robust.  We could also attach some steel brackets under the window (green line), with bolts into resin & appropriate attention to air tightness detail, behind the brackets. I've only just come up with this idea.  No doubt there will be a proper way to do it, which will work better & cost less - please advise.
The cill projection, at about 100mm, looks vulnerable & is much wider than I want.  I've asked for this to be reduced to 45mm.
The orange 150, above, is supposed to represent the height difference across the orange tray.  I've just realised the top bar is drawn a little low, & my 2 minutes, or whatever is allowed, of editing time has expired.
We had a separate DPC on the external leaf 150mm above external ground level.
There's no need for a tray here. Just let the EPS beads fill to the bottom of the cavity.
Have a close look at the picture above. It's what I suggested for the roof. ( Although you could do the whole house)
It's from the "monopoly framing" system by Matt Risinger on YouTube.
It's a really great concept for air sealing and dealing with thermal bridging in complex house shapes, it's not mine. I rarely have original thoughts!
The timber frame is built with no bits sticking out. Then air sealed externally. In this case taping the sheathing.
Then any overhangs are added and finally a layer of PIR  or maybe Rockwool/woodfiber. Finally the external cladding.
Air sealing from outside is dead easy on a timber frame building like this. 10 times easier than doing it inside. Likewise an unbroken layer of external insulation is simple to do and really performs excellently.
I would be happy to tape 11mm OSB as an airtight layer so long as you could avoid rain until it was covered.