idunknow Posted April 17, 2023 Share Posted April 17, 2023 hi could you give me your opinions on 110mm waste traveling through 150mm concrete slab, its a garage conversion i have taken floor down allowing for 150mm hardcore 30mm blind DPM 1200 gauge this is where the existing soil pipe bottom level is, i have allowed 200mm for insulation and 70mm screed, and would like your opinions on how to move forward allowing for protection expansion and the possibility of movement due to the clay ground built off. i have checked nhbc & will be changing the toilet access from that T to Y connection, i have been scratching my head for ages on the best interpretation of best practices. thanks for your time Link to comment Share on other sites More sharing options...
Jenki Posted April 17, 2023 Share Posted April 17, 2023 (edited) Is the plan to inbed the pipe in concrete? You need the pipes in the hardcore layer . Also the tee's are a bad / unacceptable idea. Is there any fall on the pipes? A diagram of the build up would be good. Edited April 17, 2023 by Jenki Link to comment Share on other sites More sharing options...
Dave Jones Posted April 18, 2023 Share Posted April 18, 2023 you want to use swept 'Y' not T's https://www.speedy-plastics.co.uk/shop/underground-drainage/110mm-underground-drainage/45d-t-s-swept-y-branch/ Link to comment Share on other sites More sharing options...
idunknow Posted April 18, 2023 Author Share Posted April 18, 2023 hello yeh im going to change t to y, yes there is a 75 mm fall over the length of 2.8mt this is the end of line for sewer run the rest of run is already built over no option for any greater debth, there will be 20mm of concrete cover at the end of run to 95mm cover of concrete at the lowest end. thanks for your time Link to comment Share on other sites More sharing options...
idunknow Posted April 18, 2023 Author Share Posted April 18, 2023 just noticed i wrote DPM where blind is apologise this is the other way round cheers Link to comment Share on other sites More sharing options...
idunknow Posted April 18, 2023 Author Share Posted April 18, 2023 15 hours ago, Jenki said: Is the plan to inbed the pipe in concrete? You need the pipes in the hardcore layer . Also the tee's are a bad / unacceptable idea. Is there any fall on the pipes? A diagram of the build up would be good. yes thats the plan however i sapose i could lay 125mm of insulation first then another membrane then 150mm concrete then 75mm insulation >UHF>then the screed maybe that would be better ? thanks for your time Link to comment Share on other sites More sharing options...
Carrerahill Posted April 18, 2023 Share Posted April 18, 2023 (edited) I am certain your concrete will crack over the pipes, however, does it really matter in this makeup, probably not, you could throw some mesh in but you will then struggle with your 50mm cover. Stronger mix with fibre in it... but then again, thinking about what it is doing and the fact the cracks will be adequately bridged by the PIR, I don't think you will have an issue. Edited April 18, 2023 by Carrerahill Link to comment Share on other sites More sharing options...
ETC Posted April 18, 2023 Share Posted April 18, 2023 Bad idea having all those voids in a slab - move the pipe below - or above - the slab. Where it is above use a concealed system (Geberit) and when it's below get it out of the building as soon as possible, don't over complicate connections (think about blockages and access) and bed all pipes in an appropriate bedding material. Link to comment Share on other sites More sharing options...
jayc89 Posted April 18, 2023 Share Posted April 18, 2023 3 hours ago, idunknow said: hello yeh im going to change t to y, yes there is a 75 mm fall over the length of 2.8mt this is the end of line for sewer run the rest of run is already built over no option for any greater debth, there will be 20mm of concrete cover at the end of run to 95mm cover of concrete at the lowest end. thanks for your time Sand blinding and DPM are the wrong way around. You use the sand to protect the DPM from ripping against the stone. 1 Link to comment Share on other sites More sharing options...
jayc89 Posted April 18, 2023 Share Posted April 18, 2023 (edited) Might be too late for this now, but I would switch it around; 150mm conc (FFL) VCL 200mm insulation DPM Sand 150mm MOT 1 Run your pipework through the insulation. Edited April 18, 2023 by jayc89 Link to comment Share on other sites More sharing options...
saveasteading Posted April 18, 2023 Share Posted April 18, 2023 Making the best of what you have: Best take the dpm out and blind (30mm is rather a lot unless the stone is really rough) then dpm down again. OR Omit the sand over the dpm as it will just mix with the concrete and weaken it. But be very careful not to puncture the dpm. Put a concrete surround to the pipes. I think bring it up to concrete level and float it. Later pour the rest of the concrete. This will protect the pipe and also allow the slab to shrink in a controlled way, with nice straight cracks. The pir and carry on. It isn't ideal but will work. By encasing the pipe you are protecting it in a controlled way. Double check that all the falls are OK in the pipes...they can move during the work. After the spirit level, I put a golf ball in each open end as a practical check: don't drop it though or it will always clatter through. This checks the slope but also that there are no obstructions. And catch the ball before it disappears to the main drain! Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 18 hours ago, Carrerahill said: I am certain your concrete will crack over the pipes, however, does it really matter in this makeup, probably not, you could throw some mesh in but you will then struggle with your 50mm cover. Stronger mix with fibre in it... but then again, thinking about what it is doing and the fact the cracks will be adequately bridged by the PIR, I don't think you will have an issue. yeh thanks that sounds logical cheers Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 18 hours ago, jayc89 said: Sand blinding and DPM are the wrong way around. You use the sand to protect the DPM from ripping against the stone. yeh thanks i stupid make mistake in diagram the sand is under the DPM thanks cheers 1 Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 18 hours ago, jayc89 said: Might be too late for this now, but I would switch it around; 150mm conc (FFL) VCL 200mm insulation DPM Sand 150mm MOT 1 Run your pipework through the insulation. naa not to late never a rush round here yeh i was thinking about the offects of running pipe in insulation because of under floor heating it would be prudent to have say 75mm insulation UFH 75mm screed to finish thanks for time 75mm screed incasing UFH 75mm insulation 150mm concrete 125mm insulation its enough to cover soil pipes DPM blind stone Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 15 hours ago, saveasteading said: Making the best of what you have: Best take the dpm out and blind (30mm is rather a lot unless the stone is really rough) then dpm down again. OR Omit the sand over the dpm as it will just mix with the concrete and weaken it. But be very careful not to puncture the dpm. Put a concrete surround to the pipes. I think bring it up to concrete level and float it. Later pour the rest of the concrete. This will protect the pipe and also allow the slab to shrink in a controlled way, with nice straight cracks. The pir and carry on. It isn't ideal but will work. By encasing the pipe you are protecting it in a controlled way. Double check that all the falls are OK in the pipes...they can move during the work. After the spirit level, I put a golf ball in each open end as a practical check: don't drop it though or it will always clatter through. This checks the slope but also that there are no obstructions. And catch the ball before it disappears to the main drain! thanks for the intresting information i have been very fortunate to have been given such a wide varity of responces thanks for your time Later pour the rest of the concrete. This will protect the pipe and also allow the slab to shrink in a controlled way, with nice straight cracks. The pir and carry on. It isn't ideal but will work. By encasing the pipe you are protecting it in a controlled way. wil do thanks Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 19 hours ago, Carrerahill said: I am certain your concrete will crack over the pipes, however, does it really matter in this makeup, probably not, you could throw some mesh in but you will then struggle with your 50mm cover. Stronger mix with fibre in it... but then again, thinking about what it is doing and the fact the cracks will be adequately bridged by the PIR, I don't think you will have an issue. noice one i think i feel the same cheers thanks for your time Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 17 hours ago, saveasteading said: Making the best of what you have: Best take the dpm out and blind (30mm is rather a lot unless the stone is really rough) then dpm down again. OR Omit the sand over the dpm as it will just mix with the concrete and weaken it. But be very careful not to puncture the dpm. Put a concrete surround to the pipes. I think bring it up to concrete level and float it. Later pour the rest of the concrete. This will protect the pipe and also allow the slab to shrink in a controlled way, with nice straight cracks. The pir and carry on. It isn't ideal but will work. By encasing the pipe you are protecting it in a controlled way. Double check that all the falls are OK in the pipes...they can move during the work. After the spirit level, I put a golf ball in each open end as a practical check: don't drop it though or it will always clatter through. This checks the slope but also that there are no obstructions. And catch the ball before it disappears to the main drain! thanks i am making the best of what i have yeh the previous diagram of build up i wrote DPM and blind the wrong way around blind is under DPM Put a concrete surround to the pipes. I think bring it up to concrete level and float it. Later pour the rest of the concrete. This will protect the pipe and also allow the slab to shrink in a controlled way, with nice straight cracks. i will do this if i pour concrete on pipes thanks for your time Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 1 hour ago, idunknow said: naa not to late never a rush round here yeh i was thinking about the offects of running pipe in insulation because of under floor heating it would be prudent to have say 75mm insulation UFH 75mm screed to finish thanks for time 75mm screed incasing UFH 75mm insulation 150mm concrete 125mm insulation its enough to cover soil pipes DPM blind stone Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 20 hours ago, jayc89 said: Might be too late for this now, but I would switch it around; 150mm conc (FFL) VCL 200mm insulation DPM Sand 150mm MOT 1 Run your pipework through the insulation. Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 20 hours ago, ETC said: Bad idea having all those voids in a slab - move the pipe below - or above - the slab. Where it is above use a concealed system (Geberit) and when it's below get it out of the building as soon as possible, don't over complicate connections (think about blockages and access) and bed all pipes in an appropriate bedding material. yes will do thanks for your time Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 20 hours ago, Carrerahill said: I am certain your concrete will crack over the pipes, however, does it really matter in this makeup, probably not, you could throw some mesh in but you will then struggle with your 50mm cover. Stronger mix with fibre in it... but then again, thinking about what it is doing and the fact the cracks will be adequately bridged by the PIR, I don't think you will have an issue. Link to comment Share on other sites More sharing options...
idunknow Posted April 19, 2023 Author Share Posted April 19, 2023 stunning replies thank you all most appreciated i will post pics of the progression that you all have enabled. Respek. Link to comment Share on other sites More sharing options...
saveasteading Posted April 19, 2023 Share Posted April 19, 2023 You shouldn't need 150 concrete. 100 is plenty. Better spent on more insulation above the concrete, under the screed, where it will havd most effect. Also due to the diminishing effect of insulation lower down, you might use polystyrene at the bottom layer and pir under the screed. Link to comment Share on other sites More sharing options...
idunknow Posted April 20, 2023 Author Share Posted April 20, 2023 22 hours ago, saveasteading said: You shouldn't need 150 concrete. 100 is plenty. Better spent on more insulation above the concrete, under the screed, where it will havd most effect. Also due to the diminishing effect of insulation lower down, you might use polystyrene at the bottom layer and pir under the screed. wow great advice thank you Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now