epsilonGreedy Posted August 6, 2021 Share Posted August 6, 2021 I am about to order some lead flashing and cannot decide on the best code for load soakers to be fitted at a pitched roof abutment. The online guides say soakers can be made from code 3 or 4 but there is no indication of a preference. My roof has a 30 degree pitch with a natural slate covering. Code 3 is 1.32mm thick and Code 4 is 36% thicker at 1.8mm. Some say code 4 might kick the slate up a bit more. My greatest concern is that a code-3 soaker might tear at the upstand bend if the roof structure flexed away from the wall abutment during a storm force gust. Link to comment Share on other sites More sharing options...
PeterW Posted August 6, 2021 Share Posted August 6, 2021 If the roof moves that much during a storm you’re going to have bigger issues than lead tearing ..! I use lead clips and leadmate rather than mortar these days to remove any issues with minor movement cracking mortar. 2 Link to comment Share on other sites More sharing options...
Temp Posted August 6, 2021 Share Posted August 6, 2021 I doubt you would notice an extra 0.5mm from the ground. Link to comment Share on other sites More sharing options...
joe90 Posted August 6, 2021 Share Posted August 6, 2021 My take on this is if the soakers are under the slates (as I prefer not to see too much lead) then code 3 is fine. If the lead is open to being “picked up by the wind” then I would use code 4. 1 Link to comment Share on other sites More sharing options...
tonyshouse Posted August 6, 2021 Share Posted August 6, 2021 3 for me Link to comment Share on other sites More sharing options...
Conor Posted August 6, 2021 Share Posted August 6, 2021 Our excellent roofers used code 4 for everything. Think it cost me about £500 ? Link to comment Share on other sites More sharing options...
Oz07 Posted August 7, 2021 Share Posted August 7, 2021 15 hours ago, Conor said: Our excellent roofers used code 4 for everything. Think it cost me about £500 ? You only spend it once Link to comment Share on other sites More sharing options...
Roys Posted August 7, 2021 Share Posted August 7, 2021 I bought a roll of code 4, 2 years ago, told to go and just take it from the pallet, oh how I laughed when I thought they had stuck it down, they hadn’t, it was just a lot heavier than I thought it was going to be, if my memory is correct I think it was 40kg. 1 Link to comment Share on other sites More sharing options...
epsilonGreedy Posted August 9, 2021 Author Share Posted August 9, 2021 On 07/08/2021 at 12:20, Roys said: I bought a roll of code 4, 2 years ago, told to go and just take it from the pallet, oh how I laughed when I thought they had stuck it down, they hadn’t, it was just a lot heavier than I thought it was going to be, if my memory is correct I think it was 40kg. A 6m x 210mm roll of code-4 lead flashing about be 26kg according to this page. https://www.roofgiant.com/code-4-lead-flashing/midland-lead-code-4-roofing-lead-flashing-roll-6m/ And in my case a 6m x 450mm wide roll for the ridges & hips in code 5 is 68kg. That is 2.5 bags of cement in a small package. Link to comment Share on other sites More sharing options...
epsilonGreedy Posted August 9, 2021 Author Share Posted August 9, 2021 On 06/08/2021 at 19:47, joe90 said: My take on this is if the soakers are under the slates (as I prefer not to see too much lead) then code 3 is fine. If the lead is open to being “picked up by the wind” then I would use code 4. I assume the slates will be cut to within 5 or 10mm of the abutment facing brick wall and the stepped cover flashing will protect some of this joint, so there will be very little of the soakers exposed. Link to comment Share on other sites More sharing options...
epsilonGreedy Posted August 9, 2021 Author Share Posted August 9, 2021 On 06/08/2021 at 15:56, PeterW said: If the roof moves that much during a storm you’re going to have bigger issues than lead tearing ..! I was only thinking of a few mm of movement and was concerned this might tear paper thin code-3 soakers that would be constrained a little by the code-4 stepped cover flashing. During in the Boxing Day storm of 2020 I was working on the ridge of the main roof tying down the temporary tarps, as the storm built up I was surprised to feel the (incomplete) hipped truss structure moving a bit. On 06/08/2021 at 15:56, PeterW said: I use lead clips and leadmate rather than mortar these days to remove any issues with minor movement cracking mortar. I plan to use home-made lead roll clips but I need to point up in a light sandy colour mortar to match the rest of the brickwork. That leadmate seems like a simpler material to use but think it only comes in a mid grey colour. Link to comment Share on other sites More sharing options...
PeterW Posted August 9, 2021 Share Posted August 9, 2021 Lead rolls are pointless - just buy a bag of clips and forget about it forever. You can point up but consider finding a pale cream external silicone in that case as it’s more stable. Link to comment Share on other sites More sharing options...
Oz07 Posted August 9, 2021 Share Posted August 9, 2021 Doesn't silicone rot lead? Hence leadmate. Honestly @epsilonGreedy your worrying too much about the colour. Just use lead mate it looks fine when done. Particularly 3 winters later when half the compo isn't missing. Link to comment Share on other sites More sharing options...
joe90 Posted August 9, 2021 Share Posted August 9, 2021 55 minutes ago, epsilonGreedy said: concerned this might tear paper thin code-3 soakers Code 3 is not paper thin, it’s 0.5mm thinner than code 4. What is Code 3 lead? Code 3 lead is the thinnest gauge of lead used in commercial roofing and is suitable for light applications such as soakers at the abutment.. Link to comment Share on other sites More sharing options...
epsilonGreedy Posted August 9, 2021 Author Share Posted August 9, 2021 2 hours ago, Oz07 said: Doesn't silicone rot lead? Hence leadmate. Honestly @epsilonGreedy your worrying too much about the colour. Just use lead mate it looks fine when done. Particularly 3 winters later when half the compo isn't missing. Definitely advice I will take seriously for the chimney flashing on the main 2 storey roof. However this particular abutment which is the first challenge will be just above the principal house entrance. Link to comment Share on other sites More sharing options...
epsilonGreedy Posted August 9, 2021 Author Share Posted August 9, 2021 1 hour ago, joe90 said: Code 3 is not paper thin, it’s 0.5mm thinner than code 4. What is Code 3 lead? Code 3 lead is the thinnest gauge of lead used in commercial roofing and is suitable for light applications such as soakers at the abutment.. Yes fair point, as I mentioned in the opening post "Code 3 is 1.32mm thick and Code 4 is 36% thicker at 1.8mm. Some say code 4 might kick the slate up a bit more.". 1.32mm does sound paper thin to me but I have not actually handled lead flashing before. The fact that the industry equally approves of materials with a 36% difference is something I cannot reconcile in my head. Neither would be a mistake it seems. There is always the breather membrane if the soaker fails! Link to comment Share on other sites More sharing options...