Salus THB23030 Auto Balancing Actuator with Google Nest

Featured Replies

Hi there

 

Currently my UFH & system is setup as the following.

 

Entire ground floor is UFH, i have a 8 port manifold (7 used) this is connected to my boiler and Pump.

 

When i turn the nest up the pump kicks in pushing the water around the loops until temperature is met.

 

Problem is the longer runs take longer to heat up so i purchased the Salus THB23030 - Auto Balancing Actuator. (7 of them!)

 

I dont want to rip out my nest as i like the smart functions of the nest, i presume i can do the following.

 

Install the Salus THB23030's (simple and easy todo) wire them into a Salus KL08NSB 8-zone wiring centre WHICH ONLY has 230v power supplied to it to power the Salus THB23030's.

 

In effect they will be "always on" and will have the power to control the pins/flow as they see fit.

 

Is there any thing im missing here? Would that be a good way todo it? As i say im retro fitting and dont really want to take away the nest or re-wire it.

Probably all you needed to do is balance the system, turn down the flow rate to the shorter loops and turn up the flow rate to the longer loops.

 

can you post a picture of your manifold as it is?

I have those Acutators, my wiring system only powers them up if that Zone calls for heat. Question why an acutator would always be on, seems counter pruductive.

 

Fly

I think the main thing to be aware of if powering them off when nothing is calling for heat is ensure they don't get power cycled off/on too frequently as it puts them into recalibration mode. presumably their wiring centre has a power off delay to avoid that, but it's not clear. (It does have 3min hysteresis for the boiler)

 

1 hour ago, Fly100 said:

Question why an acutator would always be on, seems counter pruductive.

I was consider doing this just for simplicity in getting them commissioned and proven working, at least initially. Curious if there is any downside, except for the 0.5W wastage per actuator 

 

 

  • Author
22 hours ago, ProDave said:

Probably all you needed to do is balance the system, turn down the flow rate to the shorter loops and turn up the flow rate to the longer loops.

 

can you post a picture of your manifold as it is?

 

i have tried adjusting the flow rates and over time they just mess up its a real pain with some rooms getting hot and some not - hence the auto balance.

 

 

2018-12-29_07_29_16.jpg

  • Author
17 hours ago, Fly100 said:

I have those Acutators, my wiring system only powers them up if that Zone calls for heat. Question why an acutator would always be on, seems counter pruductive.

 

Fly

 

BUT if its always on i dont think makes a difference its not always on in the sense its always open, its more it always has power. 

 

The pin will then be able to move into any position the actuator see's fit.

  • Author
15 hours ago, joth said:

I think the main thing to be aware of if powering them off when nothing is calling for heat is ensure they don't get power cycled off/on too frequently as it puts them into recalibration mode. presumably their wiring centre has a power off delay to avoid that, but it's not clear. (It does have 3min hysteresis for the boiler)

 

I was consider doing this just for simplicity in getting them commissioned and proven working, at least initially. Curious if there is any downside, except for the 0.5W wastage per actuator 

 

 

 

yes if they are powered on/off all the time then they do go into calibration mode.

 

hence i wanted to wire them into the wireing control center, porivde 230v to it and thats it so they are always on basically and just open and close as they see fit.

 

the fact they are always on shouldnt make any difference to them ??

Tom,

 

I still cant see the reason to keep them powered on all the time. Mine are off by default and never go into Calibration mode. Im confused why you would want them open. For instance if the UF was to come on in one room the fact they are open it would heat all the other rooms aswell.Unless im missing something you are defeating yourself at step one.

Happy to debate this with you and hear your opinion as we all have differing goals.

 

FLY 

I

1 hour ago, Fly100 said:

Tom,

 

I still cant see the reason to keep them powered on all the time. Mine are off by default and never go into Calibration mode. Im confused why you would want them open. For instance if the UF was to come on in one room the fact they are open it would heat all the other rooms aswell.Unless im missing something you are defeating yourself at step one.

Happy to debate this with you and hear your opinion as we all have differing goals.

 

FLY 

 

Sounds like he only has one stat (a Nest) for whole house. So yes all loops are either on or off together. If the Nest controls the UFH loop pump and boiler then no need for loop actuators at all. If they are just used for balancing it makes sense for them to be powered up (eg open) all the time to avoid accidental recalibration cycles.

 

4 hours ago, tomcoleman said:

 

i have tried adjusting the flow rates and over time they just mess up its a real pain with some rooms getting hot and some not - hence the auto balance.

 

 

2018-12-29_07_29_16.jpg

The original setup did not have any actuators on the mainfold, just manual adjusters.

 

If you want to try the Salus actuators, just connect them all in parallel and connect that to the manifold pump power.  you will probably want another junction box to marshal that number of cables into the existing wiring centre.

 

I will be intertested to see if it makes a difference, I am sceptical but willing to be proved wrong.

  • Author
5 hours ago, Temp said:

I

 

Sounds like he only has one stat (a Nest) for whole house. So yes all loops are either on or off together. If the Nest controls the UFH loop pump and boiler then no need for loop actuators at all. If they are just used for balancing it makes sense for them to be powered up (eg open) all the time to avoid accidental recalibration cycles.

 

 

exactly the above.

 

I have 1 thermostat (nest) which controls the UFH for the entire ground floor.

 

If the actuatorsare powered on all the time then they will just open / close as they see fit to make sure floor is balanced?

 

unless I'm missing something 

 

I was going to wire the actuators into the KL08NSB then just power that with mains power.

 

When the nest calls for heat the loops will start to have water pumped through them, the actuators will then (most likley) close the hottest loops first thus giving more flow to the coolest loops thus having a balanced ground floor ?

Edited by tomcoleman

I wonder if being powered ON all the time will actually slow response tho- even with no flow or energy input aren't they going to close down to try and maintain a deltaT? How will they then respond to a very slow rise in supply temp?

  • Author
12 hours ago, dpmiller said:

I wonder if being powered ON all the time will actually slow response tho- even with no flow or energy input aren't they going to close down to try and maintain a deltaT? How will they then respond to a very slow rise in supply temp?

 

as i understand it they open/shut depending on the reading of the probes.

 

So if they are always powered on, they will always have power - no issue there.

 

Being powered on all the time they will always be "detecting" temp via the problems

 

when the pump/boiler is off the loop will cool down, the probes will tell the actuator "im cold" and the actuator will open (there just wont be any flow or heat as pump and boiler will be off)

 

when pump boiler is on the actuators will already be in an open state it will then close or minimize the flow to the hottest circuit/loops thus giving more flow and heat to the coldest ones

 

exactly what im trying to achive.

 

unless im being stupid? 

I think they just try to maintain a delta of 7 degrees between the flow and return on each individual loops... I would think that they won’t balance between loops because each loop will have their own heat loss rate. For example one room could need more heat input to achieve the same target temp as another room. Would it ever balance? 

  • Author
41 minutes ago, Gav_P said:

I think they just try to maintain a delta of 7 degrees between the flow and return on each individual loops... I would think that they won’t balance between loops because each loop will have their own heat loss rate. For example one room could need more heat input to achieve the same target temp as another room. Would it ever balance? 

 

but if loop 1 gets hot quicker (smaller run) the valve would then close or reduce right?

 

if it does then more flow (i.e quicker hot water) will be pumped to the colder circuits

 

fixing my issue

 

i'll install soon - only one way to find out

  • 4 weeks later...
  • Author

so i got the units installed buy having a nightmare with them.

 

all 7 actuator's are linked into the KL08NSB controlbox which is powered by 240v mains.

 

The all come on and powerup fine, no issues.

 

On first setup as per the manual heating was switched on, actuator's was then powered on and LED's ontop began to blink (i presume this was calibration phase) i left it for around 30mins.

 

During this time the actuator's closed, opened then closed (their boot up sequence) and remained closed.

 

They basically will not open or balance the pump is on, boiler is on heating and i can see the temp rising on the probe and worried it will burst or something if gets stupid hot, which it is because the valves are all fully shut and pump is trying to push water around the circuit.

 

any ideas on what i can do ?

 

i took a video of the boot sequence here you can see at the end they all fully shut and stay shut.

 

 

2021-03-18 14.27.20.jpg

2021-03-18 14.27.22.jpg

2021-03-18 14.27.25.jpg

  • Author
4 minutes ago, PeterW said:

Are all the green LEDs saying lit on the control panel ..??

 

yes, my control panel is wired to be always on giving 24/7 power to the Actuator's.

 

 

  • Author
2 minutes ago, PeterW said:

Have you tested that with a meter and confirmed it..?

 

yes 240v into the control box, LED's green, Voltage going to the actuators, which move (open/close) and RED LED's lit. 

  • Author
7 minutes ago, PeterW said:

And the pump is starting ..?? pipes getting warm..?? Clips the right way round ..??

 

everything working as it should. just valves close and stay closed.

 

clips are 10cm as per manual - not sure they have a way around to go ?

If I've understood correctly you have the actuators powered all the time? What happens if (after calibration) you turn the power to the actuators off then on again?  The manual says it should flash the led for 2min then fully open the valve. 

Edited by Temp

  • Author

 

14 minutes ago, Temp said:

If I've understood correctly you have the actuators powered all the time? What happens if (after calibration) you turn the power to the actuators off then on again?  The manual says it should flash the led for 2min then fully open the valve. 

 

ok it might be fixed!!

 

i read somewhere to leave it on for 60mins "calibrating" and not the 20mins the manual says.

 

So far this seems to have worked and the valves are now open and everything is balanced at 2l/m

 

 

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.