6 Months with the Ecocent


Recommended Posts

Hi, I hope everyone is well, I just thought I would provide an update on how things are going with our Ecocent after 6 months use, and now that I have some data for the past few months where we have had below 0 temperatures.  For those that can remember there was a debate over potential big temperature drops when the ecocent came on over on ebuild, here is the link http://www.ebuild.co.uk/topic/18060-i-have-bought-an-ecocent-and-everything-else-esp-do/

 

Well I am pleased to say that we haven't experienced anything like that, I am monitoring the temperature via the 12 Heatmiser Themostats we have installed around the house and there is nothing more than a degree of temperature varitaition during a 24 hour period, from any of the thermostats with house set around 22 degrees, we also are using the Earthsave Varimax ASHP to heat our 280m2 ground floor slab. I am waiting on our Electricity usage to come through so can't give the numerical figures yet but so far we are very happy, and only once have we run out of DHW from the 300 litre tank but we did have around 9 adults all trying to shower in the space of an hour.

  • Like 2
Link to comment
Share on other sites

Yes, useful to know, as it means that the UFH can pump enough extra heat in to the house to make up for the heat removed by the Ecocent, something that bothered me in terms of response times.

 

Out of interest, what's the UFH flow temperature?  We keep ours at around 24 to 25 deg C maximum, as any higher tends to cause a fairly large (greater than 1 deg C) temperature overshoot after the thermostat's satisfied.

Link to comment
Share on other sites

Just like @Mikey_1980 we are running an Ecocent. It is in our rental cottage which we now use whilst new house is built. Picking up on @JSHarris point of flow temperature i have been reducing the temperature gradually from 40 to 35 as we were having the temperature overshoots mentioned. Its been at 35 for 4 weeks now and we still find that it is overshooting late evening so needs to drop some more. There has been no noticeable change in the time the Ecocent comes on. Our Ecocent is set to come on when there is a temp drop in the water so it extracts the heat from showers etc (our wet room can go from 21 to 26 after a shower). I don't have the monitoring systems in place to measure anything accurately its more about comfort. Last night we had -5.5 deg and have had -9 this year and both systems have coped well and have not been working flat out as i had expected.

I am currently looking at how to simplify the control down stairs so it acts as one large circuit to even out the heat rather than having 4 zones and trying to match the on off and temps 

 

Link to comment
Share on other sites

I'd not expect the slightest problem with an Ecocent drawing heat from a house with that much heat input; your UFH is pumping many times more heat per unit area into the floor than our is, so the additional heating requirement imposed when the Ecocent turns on is pretty small in comparison with the other heat losses. 

 

That's the sort of application where exhaust air heat pumps, or room air draw heat pumps, work fairly well for DHW.  Where they don't work well is where the house heating requirement is so low that the additional heat loss when the Ecocent turns on cannot be quickly accommodated by the heating system ramping up to push extra heat into the house.

 

The Ecocent doesn't "make heat", it only sucks low grade heat from the house, that's been heated by some other means, upgrades it and heats hot water with it.  That means it always has to draw around three quarters of the heat it puts into the hot water from the inside of the house, and that heat has to come from somewhere.

Link to comment
Share on other sites

So answers to questions are

Our UFH is running at 28 degrees.

I haven't been monitoring the electricity usage closely and we have been doing alot of work still so the next 3 months will give the best indicator for usage, we are also only just moving from business rates to residential as it is something I never got round to doing.

The install cost was less than £20k, this was for the Ecocent, MVHR and ASHP, all pipework/controls/installation everything taking the bare UFH pipes to a full functioning Heating/MVHR/DHW system and our plumber ran all the Hot and Cold pipes back for the Ecocent to be connected to

Link to comment
Share on other sites

52 minutes ago, gravelld said:

Someone should create a spreadsheet to work out the sweet spot... is it doable with given space heating loss and DHW requirement?

 

 

Not sure there is a sweet spot, really.  It largely comes down to the response time of the house heating system in being able to put back the heat sucked out by the Ecocent.

 

If you're using a heat pump as the heat source for the house, then what you achieve with the Ecocent is a two stage heat pump, with a stack of losses, in effect, in the intermediate stage (the house heating requirement).  To work OK, then the house heating system has to be able to respond to any heat loss quickly enough to not impact on the room temperature too much (there has to be some impact on room temperature as usually room temperature controls the "first stage" of this two stage system).

 

You need to design the total system (heating and hot water) so that the heating system can deliver the extra  power needed to provide the heat input to the Ecocent (a couple of kW or so) when it turns on.  The idea above, of timing it to come on when there is an excess of room heat from the shower having been run is a good one, although it would naturally tend to come on then anyway because of the hot water use.

 

To give a specific illustration, our house needs a few hundred watts of heat at most to stay at around 20 to 21 deg C.  If we had an Ecocent we'd have to find a way to put three to four times more heat into the house whenever the Ecocent was running, and do it quickly.  I could turn the UFH flow temp up; turning it to 28 deg C would definitely do the job OK in terms of additional heat input, but then I'd hit the snag I've already found; at 28 deg C flow our room temperature overshoots  a fair bit when the heating switches off because the thermostat is satisfied.  I dare not turn up our flow temperature above 25 deg C, and ideally I'd like to keep it around 24 deg C if I could, because of the overshoot problem.

 

The problem is that the slab response time is pretty long, so when you start pumping heat into the pipes it takes a fair time for it to reach the surface and start heating the house.  If the heating turns off, because the house is warm enough, heat continues to be released by the slab for several hours, as the warmer core of the slab slowly transfers heat to the surface and thence to the rooms.  The less warm the core of the slab gets from the UFH, the smaller the overshoot problem.

Edited by JSHarris
typos
Link to comment
Share on other sites

I can totally understand it won't work for your house Jeremy, I meant that I wondered whether there's a sweet spot with less performant dwellings.

 

The sweet spot may also relate not just to the technical questions of balancing the heat loss and DHW demand, but also the woolier demands of an overall building project. For example, might this be a good fit for a refurbishment project with reasonable aims at low-ish energy (let's say AECB Silver), if it also ticks the ventilation box, without having ducting which might otherwise by overly disruptive.

 

I don't know the answers to these questions and my examples are purely speculative.

Edited by gravelld
Link to comment
Share on other sites

25 minutes ago, gravelld said:

I can totally understand it won't work for your house Jeremy, I meant that I wondered whether there's a sweet spot with less performant dwellings.

 

The sweet spot may also relate not just to the technical questions of balancing the heat loss and DHW demand, but also the woolier demands of an overall building project. For example, might this be a good fit for a refurbishment project with reasonable aims at low-ish energy (let's say AECB Silver), if it also ticks the ventilation box, without having ducting which might otherwise by overly disruptive.

 

I don't know the answers to these questions and my examples are purely speculative.

On it's own, it won't meet the ventilation requirements, for two reasons.  Firstly, it only sucks air from the house when it needs to heat water, and that may or may not coincide with when you need ventilation.  As an example, you may be cooking, so need extra ventilation, but the hot water tank may already be hot, so the ecocent won't run.

 

ESP can combine it with a simple MVHR (like a few other systems that are available), which is sort of OK.  When the Ecocent isn't running the MVHR works as normal, with the flows balanced and the flow rates set to those needed to meet the ventilation requirement.  However, when the Ecocent runs the flow rates massively increase, and the MVHR goes way out of balance.  The consequence of this is that heat recovery to the room air during these periods is very low, far lower than when the system is running normally.  That's just a function of the way heat exchangers work, and can't be avoided. 

 

However, the impact this has may not be that massive, as you don't need to heat water all the time, only for a few hours a day, so most of the time the MVHR works normally, with normal heat recovery rates.  The fact that the MVHR loses efficiency a lot for a few hours is still better than no MVHR at all, by a long way.

 

To be fair, we should also include the other combined systems, like the Paul and the Genvex that are also MVHR units with an added exhaust air heat pump to heat hot water, as they all operate in the same way and have the same pros and cons.

 

They are absolutely ideal if you have a house that has somewhere that's consistently too warm.  As an example, we stayed in a well-insulated log cabin, with a wood burning stove.  There was a mezzanine storage area in what could have been a small loft, and up there it was always like an oven.  Drawing air from there to run an exhaust air heat pump for hot water would have been ideal, as it would have made use of what was probably a fair bit of otherwise waste heat.

 

Someone on another forum has an Ecocent and (IIRC) they feed it with air that comes indirectly from a workshop (heated with a wood burner in winter) that's connected to  a glazed sun room (that tends to get warm in summer) alongside the house and that feeds the air to the Ecocent.  This results in virtually no impact on the house temperature, by making use of otherwise wasted heat to deliver hot water.  I think the only issues I've heard of with this set up was the stainless tank in the Ecocent corroding and failing.  IIRC there is a protective anode that needs to be regularly inspected and replaced when corroded, just like many stainless tanks.

Edited by JSHarris
Link to comment
Share on other sites

Put another way, is it that fast recovery is the issue? I think I naively thought that leaving it to run through the day would slowly build up enough energy in the tank, but then as I think ST's calcs showed in the other thread, there just wouldn't be enough air or high enough exhaust temperature to provide enough energy. But this definitely wouldn't work if the tank was depleted and needed immediate energy.

 

If the ventilation rate was increased as you say and the energy was exchanged back into the water, it's not being wasted is it, other than the losses of the heat exchanger?

Link to comment
Share on other sites

49 minutes ago, gravelld said:

Put another way, is it that fast recovery is the issue? I think I naively thought that leaving it to run through the day would slowly build up enough energy in the tank, but then as I think ST's calcs showed in the other thread, there just wouldn't be enough air or high enough exhaust temperature to provide enough energy. But this definitely wouldn't work if the tank was depleted and needed immediate energy.

 

If the ventilation rate was increased as you say and the energy was exchanged back into the water, it's not being wasted is it, other than the losses of the heat exchanger?

 

Yes, it is the "on/off" nature of the heat pump in these things that is a part of the problem (and it's not just the Ecocent, the Genvex and Paul units similarly have a non-modulating heat pump). 

 

The basic units are extremely common in China, where there are literally hundreds of companies making them, and they are all very similar in design.  The Ecocent was originally just a badged Chinese unit, but when I spoke to the guys from ESP (who are very helpful and technically pretty switched on) they told me that it was all made in the UK now.  I have to say I have a few doubts about that, as there are physically absolutely identical units still on sale on Alibaba etc, and ESP has a long history of importing Chinese equipment, getting it approved to EU regs, and then re-badging it.  However, where it's made doesn't matter, it's the "all or nothing" nature of the heat pump that's key.

 

The reason for this is two fold.  Firstly, these units are designed to replenish the hot water tank as quickly as possible after use, so there is always hot water available.  Secondly it is a heck of a lot cheaper to build a non-inverter controlled heat pump, that only runs at a single speed.

 

Depending on the pattern of hot water usage, an inverter-controlled version might well be a good option.  For example, our major hot water demand is first thing in the morning for showers, then there is virtually no demand at all through the day, with a small demand in the early evening for washing dishes (just the stuff that doesn't go in the dishwasher) and very rarely an evening bath.  A unit that could very slowly recharge during the day, drawing only as much heat from the exhaust of the MVHR as allowed by normal MVHR flow rates, would be fine for us, as our available recharge periods are always going to be 8 to 10 hours or more.

 

The alternative, for those that need the maximum recharge rate, is to have a heating system that is responsive enough to increase its heat output in time with the additional demand that the water heating heat pump needs (I'm trying to be non-brand specific here, as this applies to all exhaust air to water heat pumps).  There is loads of available energy in the MVHR exhaust, but to extract it at normal flow rates needs a very small capacity (or variable capacity) heat pump.  The alternative is to increase the ventilation rate to get enough mass flow of air through a larger air to water heat pump.

 

However, if the ventilation rate is increased, then the MVHR heat exchanger efficiency will drop, a lot, as heat exchange efficiency is very closely tied to flow rate.  This means that incoming cool air won't get warmed anywhere near as much and so will be a lot cooler, and tend to cool the house down more than it would when the ventilation heat recovery system is working at normal flow rates.  There is no good way around this.  One sort of fix (and one that I think some systems use) is to draw outside air in and mix it with the MVHR exhaust, so that the MVHR doesn't end up delivering cold air.  The downside with this method is that although the MVHR efficiency then ends up OK, the efficient of the air to water heat pump drops, as its inlet temperature is reduced by mixing outside air with the MVHR exhaust (which is always a couple of degrees warmer than the outside air).  I've seen another fix where there was a valve fitted to the MVHR external inlet to just throttle the incoming fresh air, and allow air leakage to deal with the resulting flow imbalance.  Clearly any incoming leakage air will be at outside air temperature, so will cool the house, but because it would probably be distributed over a lot of small, tiny, leakage points the effect may not be as obvious.

 

For me, a small, inverter controlled, variable output, exhaust air to water heat pump could work well, as I could easily accept long recharge periods.  I've looked around, and so far I've not found a modulating unit like this.  My guess is that this is just down to demand.  There is a massive demand in China for these things, do a search on Alibaba and you'll probably be as surprised as I was at how many manufacturers of them there are.  Nothing in the Far Eastern market is driving manufacturers to invest in inverter controlled units, and I have to say that it's really only people with low energy homes, plus a pattern of hot water usage that allows for fairly long recharge times, that would really benefit from such a unit.

Edited by JSHarris
  • Like 1
Link to comment
Share on other sites

15 hours ago, JSHarris said:

...

 

Depending on the pattern of hot water usage, an inverter-controlled version might well be a good option.  For example, our major hot water demand is first thing in the morning for showers, then there is virtually no demand at all through the day, with a small demand in the early evening for washing dishes (just the stuff that doesn't go in the dishwasher) and very rarely an evening bath.  A unit that could very slowly recharge during the day, drawing only as much heat from the exhaust of the MVHR as allowed by normal MVHR flow rates, would be fine for us, as our available recharge periods are always going to be 8 to 10 hours or more.

 

The alternative, for those that need the maximum recharge rate, is to have a heating system that is responsive enough to increase its heat output in time with the additional demand that the water heating heat pump needs (I'm trying to be non-brand specific here, as this applies to all exhaust air to water heat pumps).  There is loads of available energy in the MVHR exhaust, but to extract it at normal flow rates needs a very small capacity (or variable capacity) heat pump.  The alternative is to increase the ventilation rate to get enough mass flow of air through a larger air to water heat pump.

 

...

 

For me, a small, inverter controlled, variable output, exhaust air to water heat pump could work well, as I could easily accept long recharge periods.  I've looked around, and so far I've not found a modulating unit like this.  My guess is that this is just down to demand.  There is a massive demand in China for these things, do a search on Alibaba and you'll probably be as surprised as I was at how many manufacturers of them there are.  Nothing in the Far Eastern market is driving manufacturers to invest in inverter controlled units, and I have to say that it's really only people with low energy homes, plus a pattern of hot water usage that allows for fairly long recharge times, that would really benefit from such a unit.

 

Thanks Jeremy.

 

Another approach may be to solve the problem at a different point. Is the system too closed to not allow other heat inputs, or different ways of drawing hot water?

 

For example, PV or solar thermal could top up the temperature, or even a system boiler might be a good idea if you can have a modern gas boiler installed.

 

Also, you could make do with lower temperature in the tank if you had inline modulating heaters like yours, right?

 

However, that still assumes you can just have a exhaust air heat pump which doesn't go into overdrive, and will just through the day trickle energy in at the ventilation rate.

Link to comment
Share on other sites

I'm pretty sure there's an immersion heater element in some of these systems, to allow for PV top up, and a couple also allow for solar thermal input too, via a high efficiency coil, and that could be used with other low grade heat sources too.

 

The bottom line is that really all these things are is a fixed speed air to water heat pump fitted to a water tank.  They don't care where the inlet air comes from or the outlet air goes to.  They are technically no different at all from a conventional (but rather small) monoblock ASHP, and work in exactly the same way.  They do select a refrigerant that works better at higher air input temperatures, because the principle design point for these things (direct from an ESP bloke I was talking to, ages ago) is an air input temperature of 25 deg C and a hot water temperature of 50 deg C, where they will deliver a COP of better than 4.

 

Like any ASHP, increase the temperature differential between inlet air and output water and the COP goes down, and also you start hitting the double whammy of getting  defrost cycling.  They get the high heat pump efficiency by drawing in warm air from the house, which maintains the low temperature differential needed.

 

The key thing is to work well the house has to have a heating system that can provide the heat needed to feed the air inlet of the unit.  There are several ways of doing this, but the major stumbling block is that when running these things use a LOT of warm air, far more than a normal sized MVHR exhausts.   That has to come from somewhere.

 

When you do the numbers, an exhaust air fed heat pump is barely better than an outside air fed heat pump in cold weather.in terms of efficiency, because, within reason, intake air temperature has only a small impact on the heat energy available for the heat pump to extract.  For example, air at 2 deg C contains about 1% more heat energy than air at -1 deg C, or air at 20 deg C has about 7% more heat energy in it that air at 0 deg C. 

 

Right now the air coming out of our MVHR exhaust is only 3 deg warmer than the outside air temperature, and frankly that makes the difference in COP between an outside air fed heat pump and an exhaust air fed one negligible, and not worth the additional expenditure, in my view.  I get a far, far bigger difference in COP from having an inverter controlled, variable output, ASHP, as that can modulate down and avoid the defrost penalty, something a fixed speed unit can't do.  The variable speed advantage in efficiency terms is probably well over 10%, and that exceed any difference from feeding the thing with warm air.  The downside is that all heat pumps only have a limited temperature differential over which they work very efficiently, and that's typically around 30 to 40 deg C.  Any more than this and efficiency falls off, rather non-linearly I've found..

 

These integral water tank and heat pump units were designed for homes where there was plenty of heat available inside the house, and they work very well under those conditions.  As other companies have found, trying to make them work well in a house that doesn't have a good heating system that is separate from the unit is challenging.  Paul, for example, got caught out (or, more accurately, a UK agent selling Paul stuff who got his/her sums badly wrong) got their fingers burned when they installed a load of their very similar (functionally) exhaust air heat pumps in social housing.  They found that the electricity usage was excessively high, because poor system design meant that the air temperature going into the unit was too cool and the unit was compensating by running its internal immersion heater a lot of the time to make up for this (the Paul and Genvex systems have an internal immersion that's automatically controlled by the built in controller).

 

 

Link to comment
Share on other sites

  • 2 months later...
  • 1 year later...

Hi All

My experience of the Ecocent may be of interest to forum members.

I had one for 4 1/2 years when it started to struggle heating our hot water. EarthSave were called out and for a charge of £300 informed me that the heat exchanger gas had leaked out. The Earthsave engineer suggested that we turn the Ecocent off & use it as a hot water tank as it was already connected to our boiler for backup contingency.

Earthsave don't have a gas refill service, so I called out a refrigeration engineer who found that the gas was leaking inside the tank & so it wasn't possible to get it working again.

The Ecocent has a sacrificial anode which needs replacing every year to 18 months at a cost of around £300 to get Earthsave to change.

I had the first one replaced after 18 months & the next one 2 years later. My thoughts are that the heat exchanger pipe was being corroded causing it to fail.

Earthsave don't mention the anode replacement to customers, but this has a huge impact on running costs & longevity of the Ecocent.

Earthsave  give an estimated life of 15 years for the Ecocent compared with my experience of 54 months.

 

In my experience it would have been much cheaper to have a good quality hot water tank heated by a central heating boiler.

 

 

 

Link to comment
Share on other sites

7 minutes ago, RLightbown said:

Hi All

My experience of the Ecocent may be of interest to forum members.

I had one for 4 1/2 years when it started to struggle heating our hot water. EarthSave were called out and for a charge of £300 informed me that the heat exchanger gas had leaked out. The Earthsave engineer suggested that we turn the Ecocent off & use it as a hot water tank as it was already connected to our boiler for backup contingency.

Earthsave don't have a gas refill service, so I called out a refrigeration engineer who found that the gas was leaking inside the tank & so it wasn't possible to get it working again.

The Ecocent has a sacrificial anode which needs replacing every year to 18 months at a cost of around £300 to get Earthsave to change.

I had the first one replaced after 18 months & the next one 2 years later. My thoughts are that the heat exchanger pipe was being corroded causing it to fail.

Earthsave don't mention the anode replacement to customers, but this has a huge impact on running costs & longevity of the Ecocent.

Earthsave  give an estimated life of 15 years for the Ecocent compared with my experience of 54 months.

 

In my experience it would have been much cheaper to have a good quality hot water tank heated by a central heating boiler.

 

 

 

 

 

Thanks, you're not the first case I've heard regarding the cost of getting the sacrificial anode changed, and I know of one case where the tank split, possibly because the anode wasn't changed.  I put a lot of thought into fitting one in the early stages of our build planning, but despite the good communications with ESP, decided it was not the best solution for our house.  I also found many near-identical looking units for sale on the Chinese marketing site Alibaba, and despite the fact that I know ESP have said that they manufacture these units, I do suspect that they are imported from China, with perhaps some modifications done here for the UK market, to comply with our regulations etc.

 

I'd like to be proved absolutely wrong, with hard evidence that these are not in essence Chinese made units re-badged, tested and certified for the UK, but I had a look inside one when we were looking at fitting one and was also sent a few internal photos by one of the many Chinese vendors of near-identical looking units, and have to say they looked pretty much the same to me.  If they really are wholly made in the UK, then I'd be happy to be corrected.

Link to comment
Share on other sites

Quite apart from the failure issue,  a product designed with an 18 month £300 service schedule would be ruled out by me as too expensive.  It is either a bad design requiring a lot of man hours to change the part, or a simple case of rip off labour rates if it is an easy item to change.  Assuming the anode is £50 (a guess) then they are charging a good man day of labour to replace it, and I just cannot believe it would take a whole day.

Link to comment
Share on other sites

Just now, RLightbown said:

I was told by ESP at the time of purchase that the Ecocent  is made for them in China

 

Interesting, as when I asked the same question, having seen loads of near-identical units on the Chinese marketing site, they told me (when chatting on their stand at the Swindon self-build centre I think) that they were made by them in the UK, and weren't just imported from China.

 

I can't criticise the company on the grounds of helpfulness, they were very good at letting me have all the information I asked for, but I have always believed that they were a bit like Navitron, just UK importers of stuff from China, albeit with a bit of added value from some UK testing and certification.

 

This is a bit like a lathe I bought a few years ago, although at least the UK importer in that case was dead straight with me about their origin.  When the lathe was delivered there was severe corrosion on the tool post and cross slide, so I took photos and sent them to the UK importer.  He was great, in that he sent me replacements, but they didn't fit.  It turned out that the Chinese manufacturer had changed the spec and the lathe hadn't even been looked at by the UK importer at all - it was delivered to me in the crate that it was in when it left China.  It got sorted in the end, with a replacement lathe, but frankly the wiring, motor and motor controller was garbage.  After replacing three controllers and two motors, all under warranty, I decided to redesign the whole drive system and fit a decent quality brushless motor and controller.  That, together with several hours spent lapping the gibs to get things to run accurately and smoothly, and stripping the whole thing to reassemble it as it should have been in the first place, resulted in a pretty good machine.  The main failings with Chinese made stuff seems to be a tendency to cut corners to save a few pennies and poor finish and attention to detail at final assembly. 

 

I guess it's really a case of trading reliability for price, when it comes down to it.  The Ecocent is relatively cheap (although you can import virtually the same unit from China for a fair bit less), so it's inevitable that there will be some trade off's.  To be fair, there are several other companies importing stuff direct from China and selling it in the UK, so I'm not in any way singling ESP out.  They provide a product that is at the "value" end of the market, so when  noting shortcomings it's worth looking at the price for roughly equivalent systems from companies like Nibe or Genvex, which are two or three times the price of the ESP kit.

Link to comment
Share on other sites

13 minutes ago, RLightbown said:

When I called out the refrigeration engineer to regas the Ecocent he was very surprised that the heat exchanger pipe appeared to be aluminum which is more likely to be eroded by galvanic action.

 

 

Doesn't surprise me. There has to be a very good reason for the high rate of erosion of the sacrificial anode in these units, as it seems far too high than that from the PD of stainless steel and copper, which would be a normal budget option.  Higher quality units might use stainless steel and monel, or even all stainless steel construction.  Using aluminium, which is a long way from stainless steel in the electrochemical series, sounds like a sure-fire recipe for relatively rapid corrosion.

Link to comment
Share on other sites

We fitted a laser cut aluminium roof on the back end of a cruise liner, and the steel / stainless and Aluminium were all kept 3mm apart with nylon or rubber bushings. That'll last decades now, but would have lasted a few years without such separation. 

This thread is of extreme value, as I, for one, didn't know about the anode :( !!! Thank you @RLightbown for your feedback, and a shame your in the situation you are. Have you any alternate solutions to escape the circle of maintenance / cost / repair ?

 

@JSHarris, it seems utter madness to save the few £ with the Alu components given the cost of manufacturing the boss for the anode and the cost of the anode. This is a serious design FU and so easily avoidable. 

I shall now go and check the component makeup of the Genevex 185 as I am considering specifying one for an ongoing project.

"It was all going so well...." 

Link to comment
Share on other sites

1 minute ago, Nickfromwales said:

We fitted a laser cut aluminium roof on the back end of a cruise liner, and the steel and stainless elements were all kept 3mm apart with nylon or rubber bushings. That'll last decades now, but would have lasted a few years without such separation. 

This thread is of extreme value, as I, for one, didn't know about the anode :( !!! Thank you @RLightbown for your feedback, and a shame your in the situation you are. Have you any alternate solutions to escape the circle of maintenance / cost / repair ?

 

@JSHarris, it seems utter madness to save the few £ with the Alu components given the cost of manufacturing the boss for the anode and the cost of the anode. This is a serious design FU and so easily avoidable. 

I shall now go and check the component makeup of the Genevex 185 as I am considering specifying one for an ongoing project.

"It was all going so well...." 

 

It is madness, but it's also an intrinsic part of Chinese business culture. 

 

A friend builds custom bicycles, and has to import a lot of parts from China (strictly speaking Taiwan, but the culture is the same) as practically all the big name bike component manufacturers now source them from Taiwan.  He would send the factory in Taiwan a specification, and they would produce sample components for him that were fine.  They'd give him a price, then when he placed a larger order he'd find that they changed the material specs, but also charged him a lower than agreed price, thinking they were offering him good service. 

 

Price over rides quality, as price is a matter of "face", something you just have to get used to when dealing with China.  In the end he had to employ a local British ex-pat living in Taiwan to be his quality assurance manager and inspect every batch of components before it was shipped, to make sure they were made to his spec.  This seems to be the only way to guarantee consistent quality.

 

I doubt the Genvex will have any issues.  All the refrigerant piping on mine is copper, and it looks very well made internally.

  • Thanks 1