scottishjohn Posted October 27, 2019 Share Posted October 27, 2019 interesting alternative to ASHP they claim its cheaper to run than electric only + it can provide real hot water at 65-70c with no penalty . maybe good choice for old big house where you need rads as well as UFH and lots of bath rooms http://www.roburheatpumps.co.uk/products/heating-only/robur-k18-mini-air-source/ http://www.roburheatpumps.co.uk/wp-content/uploads/2019/01/Robur-K18-brochure.pdf whats your thoughts guys ? Link to comment Share on other sites More sharing options...
ProDave Posted October 27, 2019 Share Posted October 27, 2019 That link is short on details, so I did some googling. I assume it works on the absorption principle like a gas powered fridge? A bit about that here https://www.energy.gov/energysaver/heat-pump-systems/absorption-heat-pumps If so I am surprised it is only 38% more efficient than an electric heat pump. Given that gas is about 1/4 the cost of elctricity, I would have expected an astoundingly low cost per KWh of heat from a gas heat pump? Of course it has all the gas disadvantages of another standing charge to pay and the need for a gas safe installer. Link to comment Share on other sites More sharing options...
scottishjohn Posted October 27, 2019 Author Share Posted October 27, 2019 you need to change the costs to uk prices and it could end up better but 38% better than ASHp --your getting greedy now .LOl and you can have real hot water .Idid see inoen of thier downloads you can run the ufh water down to 20c -- that would give some more savings proably in a well insulated house maybe Link to comment Share on other sites More sharing options...
PeterW Posted October 27, 2019 Share Posted October 27, 2019 1 hour ago, ProDave said: That link is short on details, so I did some googling. I assume it works on the absorption principle like a gas powered fridge? A bit about that here https://www.energy.gov/energysaver/heat-pump-systems/absorption-heat-pumps If so I am surprised it is only 38% more efficient than an electric heat pump. Given that gas is about 1/4 the cost of elctricity, I would have expected an astoundingly low cost per KWh of heat from a gas heat pump? Of course it has all the gas disadvantages of another standing charge to pay and the need for a gas safe installer. Depends which one they are talking about as they have two models, one is a gas booster on the end of a standard air source heat pump. Uses the heat pump at max CoP (so A7/W35) then uses a small modulating gas boiler to pull the temperature up from W35 to W65. It can use the low return temp to manage the condensing on the gas so it’s basically maximizing both energy sources. The gas absorption ones are ok but they need to be big - think 18kW is the smallest they do. Link to comment Share on other sites More sharing options...
ProDave Posted October 27, 2019 Share Posted October 27, 2019 4 minutes ago, PeterW said: Depends which one they are talking about as they have two models, one is a gas booster on the end of a standard air source heat pump. Uses the heat pump at max CoP (so A7/W35) then uses a small modulating gas boiler to pull the temperature up from W35 to W65. It can use the low return temp to manage the condensing on the gas so it’s basically maximizing both energy sources. I can't figure how that would work. Typically when heating DHW I observe a flow temperature of about 55 degrees and a return temperature of about 47 degrees. Under that scenario the HP would be doing nothing and it would just be a gas boiler heating my DHW. On that basis the HP would only operate when heating the UFH, and if that is the case surely you might argue to have 2 separate systems for UFH and DHW? What I am saying is these systems that claim to heat first by the HP then boost it with another heat source require a massive delta T that never happens in practice. 1 Link to comment Share on other sites More sharing options...
Ed Davies Posted October 27, 2019 Share Posted October 27, 2019 (edited) 1 hour ago, ProDave said: If so I am surprised it is only 38% more efficient than an electric heat pump. Do they say that? I can see where they say it's 38% more efficient than a condensing boiler. (BTW, it''s “kWh”, not “KWh”). Edited October 27, 2019 by Ed Davies Add link for kWh. Link to comment Share on other sites More sharing options...
Ed Davies Posted October 27, 2019 Share Posted October 27, 2019 2 minutes ago, ProDave said: On that basis the HP would only operate when heating the UFH, and if that is the case surely you might argue to have 2 separate systems for UFH and DHW? Agreed, I've been puzzled by such things in the past. The only way I can see it working is if you run two systems in series so the flow from the HP goes first to the DHW tank then to another cooler heat user before returning to the HP. The cooler heat user could be a DHW pre-heat tank or UFH. Link to comment Share on other sites More sharing options...
joe90 Posted October 27, 2019 Share Posted October 27, 2019 1 hour ago, scottishjohn said: and you can have real hot water Not sure what you mean, @ProDave and I run our DHW at 48’ and we don’t need it hotter and tank losses are minimal. (Accepted that DHW tank may need to be slightly bigger). Link to comment Share on other sites More sharing options...
ProDave Posted October 27, 2019 Share Posted October 27, 2019 6 minutes ago, joe90 said: Not sure what you mean, @ProDave and I run our DHW at 48’ and we don’t need it hotter and tank losses are minimal. (Accepted that DHW tank may need to be slightly bigger). Indeed. I arrived at 48 degrees as that is the hottest I can (just about) hold my hands under for any length of time. I see no point in having it hotter than that. If I need really hot water for some specific and unusual task I will boil the kettle. 1 Link to comment Share on other sites More sharing options...
PeterW Posted October 27, 2019 Share Posted October 27, 2019 So “real hot water” has a maximum temperature of 47c as set by building regulations (in Scotland) via a TMV2 mixing valve so any hotter is pointless ... I store at 62c and then accept the losses but also use a lot of hot water. Link to comment Share on other sites More sharing options...
Onoff Posted October 27, 2019 Share Posted October 27, 2019 To have one of these I'd first need gas. Link to comment Share on other sites More sharing options...
scottishjohn Posted October 27, 2019 Author Share Posted October 27, 2019 3 hours ago, PeterW said: So “real hot water” has a maximum temperature of 47c as set by building regulations (in Scotland) via a TMV2 mixing valve so any hotter is pointless ... I store at 62c and then accept the losses but also use a lot of hot water. as in if you need to run raditoars as well on big old house and or large volumes of dhw your ashp is not good at getting hig temps for DHW Link to comment Share on other sites More sharing options...
PeterW Posted October 27, 2019 Share Posted October 27, 2019 So an ASHP will get to 48c on DHW without a problem. It will also get to 56c if you let them a keep going but the CoP will drop toward 1 the higher the temperature. And if you have a big old house, an ASHP isn’t the ideal solution anyway ... Link to comment Share on other sites More sharing options...
SteamyTea Posted October 27, 2019 Share Posted October 27, 2019 (edited) 13 minutes ago, PeterW said: And if you have a big old house, an ASHP isn’t the ideal solution anyway Can you explain why not? 1 hour ago, scottishjohn said: your ashp is not good at getting hig temps for DHW It may loose the CoP as temperature rises, but if you have enough storage at the lower temp an ASHP can easily deliver at, where is the problem. Edited October 27, 2019 by SteamyTea Link to comment Share on other sites More sharing options...
ProDave Posted October 27, 2019 Share Posted October 27, 2019 1 minute ago, SteamyTea said: Can you explain why not? Heating my modern well insulated house with low temperature UFH works very well. Thinking back to a previous 1930's house I owned, and how much heat it needed, and how quickly it cooled down, I very much doubt you could get enough heat out from UFH to keep it warm in the middle of winter, so it needs radiators to pump enough heat into it, which a heat pump is not really suitable for. I am glad not to be pumping that much heat into a leaky box any more. 1 Link to comment Share on other sites More sharing options...
SteamyTea Posted October 27, 2019 Share Posted October 27, 2019 9 minutes ago, ProDave said: Thinking back to a previous 1930's house I owned, and how much heat it needed, and how quickly it cooled down, I very much doubt you could get enough heat out from UFH to keep it warm in the middle of winter, so it needs radiators to pump enough heat into it, which a heat pump is not really suitable for. If he heat pump and the emitters (radiators, UFH, forced air or whatever) are size correctly, there will not be a problem. I think the problem is, that as a nation, we are used to the idea of a gas boiler. There is nothing inherently wrong with a gas boiler, they are cheap to buy and install, are small, can throw out a lot of heat, but also throw out a lot of pollution. There is nothing to stop a house having UFH and radiators, even in the same room, if that is what is needed (what is wanted is another thing). 1 Link to comment Share on other sites More sharing options...
PeterW Posted October 27, 2019 Share Posted October 27, 2019 The issue is how quick an ASHP can get heat into the water - even an 18kW will struggle as it’s about a small volume of water getting the heat so the response time is slow. With a gas boiler, you’re getting a rapid heat up which is what is expected with rads. 1 Link to comment Share on other sites More sharing options...
Ed Davies Posted October 27, 2019 Share Posted October 27, 2019 (edited) 1 hour ago, PeterW said: With a gas boiler, you’re getting a rapid heat up which is what is expected with rads. Maybe it's that expectation that's broken. The house I'm in now is not large (haven't measured but a bit less than 80m² I guess) but it's not particularly well insulated and not airtight but still the 18 kW oil boiler cycles and short-cycles madly however cold the weather is. Last December (which included a week when I ran the heating continuously) the boiler only ran 25% of the time so the equivalent of a 4.5 kW full-time boiler. The average flow temperature to my study radiator over the whole month was 30.37 °C. Running, say, a 6 or 8 kW continuously ASHP with some modulation would give an equivalent effect. On the other hand, if the house did cool down for any reason (e.g., if you were away over Christmas (I wasn't)) then heating up again afterwards would be painfully slow. So an ASHP might be suitable for such a pile if it's more-or-less continuously occupied - kids, people working at home, retired, sick, whatever. Edited October 27, 2019 by Ed Davies Link to comment Share on other sites More sharing options...
Nick Thomas Posted December 18, 2022 Share Posted December 18, 2022 Bit of thread necromancy, but I was researching these a bit today. Strictly hypothetically, something like https://www.remeha.co.uk/products/heat-pumps/gas-absorption-heat-pump#product3 could be interesting as a district heating solution for a small group of houses, or a block of flats. With a SCoP of 4.28, you're looking at ~2.3p/kWh of heat output if you fire it from natural gas at current prices. Worth noting that in principle you could fire one of these from anything, not just natgas - fuel oil, wood, solar thermal, they're all options. It's very loud and emits NOx in operation, but still, interesting. They could also be useful for heating municipal swimming pools, etc? Anyone aware of existing deployments? Link to comment Share on other sites More sharing options...