Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Another thing I thought of last night, how on earth do you ensure the elbow is pointing the right way, or would it naturally fall that way?? Rubber washers inside the joint? -
phstore.co.uk stock these, not cheap mind!
-
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
@Nickfromwales Have I missed anything from my list? -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Yeah I know, i can't think of a cheap alternative though? Theres only a small chance of vermin, but i can live with them chewing through insulation vs pipe. -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
the only 16mm pipe insulation i've found is only 6mm thick, so I'm going to see how tight the 15mm fits 15mm pipe, and may use that. Any additions/improvements welcome :-) -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Component Quantity Price Shop Underfloor heating manifold 8 PORT 1 114.2 PSW Trade Suppliers 16mm PE-RT/AL/PE-RT 100m 1 40 PSW Trade Suppliers Pipeplus 22mm x 25m Grey Barrier Pipe 1 24.45 Plumbling and Heating Solutions Climaflex Pipe Insulation - 22mm x 19mm Wall x 2m Length 12 15.70 PlumbNation 10m Pipe Insulation 16mm - Blue 5 23 PSW Trade Suppliers 10m Pipe Insulation 16mm - Red 5 23 PSW Trade Suppliers Sentinel Eliminator Quadra Cyclone Magnetic Filter 1 55.58 PlumbNation STRAIGHT AUTO BYPASS VALVE 22MM 1 9.58 Screwfix Female Elbow 16mm - 1/2'' 8 16.80 PSW Trade Suppliers Pipeplus 15mm x 25m White Barrier Pipe 1 18.50 Plumbling and Heating Solutions Pipeplus, G15SLE,15mm Plastic Pipe Support Sleeve 1 0.15 Plumbling and Heating Solutions Calmag SI-CALCOMBI 15mm & 22mm Magnetic & Electrolytic Scale Inhibitor 1 33.70 Plumbling and Heating Solutions Climaflex Pipe Insulation - 15mm x 25mm Wall x 2m Length 50 89.40 PlumbNation 22mm Manifold connector compression 2 7.20 PSW Trade Suppliers WHITE & CHROME ANGLED TRV WITH LOCKSHIELD 15MM X ½ " 6 40.74 Screwfix Straight Braided Filling Loop - Part L 1 8.97 Toolstation -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Yeah I looked at those, but for any decent size you have to get a double with 2 convectors, and they hang off of the wall quite a bit, plus they are very expensive! Seem a good idea overall though, pumping less heat into the walls. -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
I'd originally seen these to allow the PEX to be horizontal: https://www.plumbnation.co.uk/site/towelrads-15-15mm-pushfit-chrome-elbow/?gclid=Cj0KCQiArYDQBRDoARIsAMR8s_QfgrEpNY7eCR34kmQfaPVRGg4VrQvs3IldRN9lx-_f0OcSlDVMeIsaAu-yEALw_wcB No good for the 16mm like, i'd have to get a converter, or use the bend you suggested above and an adapter, which would be cheaper overall. Yeah not using actuators, as I plan to get Tado Smart Radiator TRVs at some point when they come down in price a bit. The Central entry point for the pipes is for a number of reasons, firstly so I only have to cut one hole in the floor, and secondly so I don't really have to worry about radiator sizes in the future and the pipes then being in the wrong place. PSW Trade Suppliers have a number of very well priced products, I've sent them an email regarding their manifold just to see what it actually comes with, but I've made a list of everything i will need for a 16mm pipe system, with manifold, which comes in at £440 for 7 radiators, which i didn't think was too bad. Actually thinking about it, instead of using the elbow, building on your suggestion, how about these? https://www.pswtradesuppliers.co.uk/en/products.php?product=Female-Elbow-16mm-%2d-1{47}2''-%2d-COMPRESSION-Fit. Not sure what size is on the end of a TRV, they do both 3/4 and 1/2, yours is half hence why i linked this one. That would get me a pretty native 16mm connection in the direction i want off of the TRV and lockshield -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Yeah i've looked at several solutions. The MLCP appeals due to its strength and bending radius, plus there is the chance of mice under the floors here (it has happened before). Emmetti manifolds are nice, but once you have all the bits, very expensive. The oxygen barrier too, isn't really suitable for CH with JG and the like, and most only work to around 50C, which is below where the CH would be. Happy with the plastic look, my idea was to bring both pipes up in the centre of the radiator, up behind the rad, and bend them back down to tails off of the valves, and finally box the pipes coming from the floor to create a robust install which can't be caught by things such as hoovers. Maybe I'm going a little OTT? -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
My other concern over the MLCP, it all seems to mention press-fit, which seems a step backwards from pushfit? The tectite is push fit, so it seems the euro stuff is the press fit. -
Central Heating Manifold system
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Finally got round to measuring all my pipe lengths, need around 100m in 15mm and 25m in 22mm. I'd got everything decided what I was going to get, a disman 8 port manifold, with tectite MLCP Pex-Al-Pex pipe, but my word is it expensive! Looking around £300 just for the pipe alone. My other option is Pipeplus, which has an EVOH oxygen barrier, and is far superior in terms of oxygen penetration compared with the likes of the JG barrier pipe, and is a much better £61 + VAT per 100m, also in the standard 15 and 22mm sizes. The tectite is clearly better overall, but would you spend the extra on it? This is just for wall hung rads, not underfloor heating. If 16mm TRV's existed, it wouldn't be an issue, i'd just go straight for the european 16mm MLCP Pex-Al-Pex pipe, which is very cheap, but I can't seem to find any. I'll try looking for radiator stems with 16mm push fit or compression ends -
Solar PV DNO Engineering Recommendation Code
MikeGrahamT21 replied to MikeGrahamT21's topic in Photovoltaics (PV)
OK, I shall leave it be in that case, thanks for the info -
Hi, We have a 16 panel system equating to 4kW, which I had always assumed was limited by the G83 recommendation, as we have no special permissions with the DNO, however when I've been fiddling around with my inverter settings (just figured out how to connect to it via bluetooth), I noticed that the current setting was on G59 however, and it presumably has been that way since the day it was installed. Just to clarify, what should it actually be set to? Don't want to be burning out the local substation, though I assume if mine is like this, i bet hundreds of other installs are likely the same. Regards Mike
-
Yeah, all i can see is 10mm too: https://www.toolstation.com/shop/Plumbing/d20/Pushfit/sd3143/Radiator+Pipe+Guide+N+Seal/p63699 Can't imagine you'd find 15mm ones, as the PEX pipes wouldn't bend sharp enough, like the 10mm ones do.
-
The other day I found Pegler Yorkshire Tectite, which is a UK made, 15mm MLCP, can be used with ordinary push fit and compression as long as you use their 3PS liners. Its quite expensive, but for me, worth the extra so it works with lower cost fittings.
- 22 replies
-
- thermostats
- stats
-
(and 1 more)
Tagged with:
-
lol, good plan! I'm pretty sure you can take the glazing units out of the door, would turning them round give us any benefits in terms of energy efficiency? Not sure how much the reflective coating actually adds.
-
Lol! I don't mind the light to be fair, saves us putting ours on, it was more a question of if the sensor can pick me up, that means IR radiation is escaping, and therefore heat. Doesn't happen on the windows which are smooth to the inside.
-
Hi Bit of an odd one this one. Our neighbour recently had a new spot light fitted, and it seems very sensitive, so much so that we can turn it on inside our kitchen, through the glass of the composite door, and it got me thinking... It's patterned glass, but the pattern is on the inside,just how it came, but to me that's inside out? We have another exactly the same, and that also has pattern to inside. I've even had a look on other people's and theirs is the same. Is there a reason for this or are they all wrong way round? Pretty sure the soft low e coating can only be on flat glass. They are both doors which can have the glass replaced, so taking it out and turning it round shouldn't be impossible. What do you think? Regards Mike
-
Bypass Radiator Question
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
That's good info thanks, I'll definitely incorporate one of these into the new circuit -
Bypass Radiator Question
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Yeah I'm sure I'll manage that lol. We don't have a hallway radiator, as it's too small, so I'll go with the bathroom on bypass, as it can get as hot as it likes in there. Now all I need is black Friday to come along and hopefully a bit of luck that the evohome has a discount, I can hope lol -
Bypass Radiator Question
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Checked manual, boiler definitely needs a bypass, but that should suffice with both the pipework, and the bathroom radiator, so TRV in the room is possible. -
Bypass Radiator Question
MikeGrahamT21 replied to MikeGrahamT21's topic in Central Heating (Radiators)
Well, I'm not really sure. I also fitted a bypass on part of the pipework a few years back as a just in case all the radiators were turned off for whatever reason, so in terms of flow, there is a path even if everything is off (though the bathroom towel rad doesn't have a TRV currently, so is also a bypass). I was just thinking from a boiler perspective. I'm about to invest in a Honeywell Evohome System with connect radiator TRVs, currently the back of the house tends to be cooler (thermostat lives in living room where the TV and home cinema gives off quite a bit of heat), so ideally i'd want a TRV in the room too (even though its not recommended to have one where the stat is, evohome doesn't really work like that though), to close off the room radiator while still allowing heat into the back radiators, without cooking us -
Hi, Is there a size requirement for the Bypass Radiator? Or can it be any radiator? I was thinking of making it the towel radiator in the bathroom. We have a combi condensing boiler. Thanks for any info. Regards Mike