Bramco
Everything posted by Bramco
Choice of ASHP for near-passivehouse
Bramco replied to DInwood's topic in Air Source Heat Pumps (ASHP)
Useful guidance - thanks. Just out of interest, if you are cooling in the summer, then I assume you have a bypass round the buffer tank and blender? Or are you not cooling the slab in the summer? Simon -
The part of planning that validate applications have little or no time or on the ground local knowledge unless they happen to live round the corner and even then... I'm sure they take a site location plan as gospel unless someone local complains. So the onus is on you or neighbours to point this out. Probably called democracy but .... Local councillors can be really helpful with this kind of thing, except maybe they're thick as thieves with the perpetrator - it is the time of backhanders. As @PeterW said the council solicitors are on the hook if it's wrong. So an anonymous email/letter should work. From experience don't bother calling the case officer.... Simon
Integrating an MVHR to our build
Bramco replied to djcdan's topic in Mechanical Ventilation with Heat Recovery (MVHR)
We had heat loss calculations done for both 0.7 and 1.2 and the difference in terms of heating required was actually quite small. Walls will be 1.4 and roof and insulated slab 1. You have to weigh up the additional cost of going to 0.7 against the expense in terms of lekky for the ASHP with 1.2. When you work it out, it's not a lot - for us it would be £100 a year but a LOT more to do the windows at 0.7. Having said that we may well go the extra mile to get an A rating - daft?!!!.... Simon -
ASHP, UFH and solar thermal, or ASHP, UFH and MVHR????
Bramco replied to Dicky's topic in Air Source Heat Pumps (ASHP)
Agree wholeheartedly - we installed solar thermal when PV was too expensive - it's great in the summer for hot water but you need a few panels for it to be effective. In the winter it doesn't really do a lot, so no use for hot water, which in your question would mean an immersion heater if you didn't use the ASHP. If you use the ASHP for hot water as well as UFH then it should be up to a third cheaper than an immersion heater due to the COP of the ASHP. MVHR will simply mean you don't lose a lot of heat through the air changes you need for air quality. When PV came down in price we installed some PV - sadly we didn't remove the solar thermal and replace it with PV - wish we had!! PV is much more versatile as you can divert any excess through an immersion heater into your hot water tank - and when that's had enough it will supplement the power needed for any other electrical devices and if they aren't using anything into a battery for later consumption, or your EV. And hopefully in a couple of years more vehicle manufacturers will get 'enlightened' and allow V2H or V2G - in which case you won't need a house battery as you'll have one on 4 wheels parked up outside. (Only the Leaf does this currently). Batteries are great for some of the new electricity tariffs like Octopus agile - if you can avoid the peak times, rates are cheap and last summer they were paying you to fill up your EV or battery storage overnight - yes a few p per kW to take electricity off their hands!! Kerching!! Simon PS We're also about to start a new build - ASHP (UFH and DHW), MVHR and a 4kW PV array (and when the SAAB convertible dies an EV...) PPS I saw a table comparing prices of batteries on Naked Solar (was put on to this by a Mesh Energy presentation) Tesla come out as one of the cheapest in their comparison which wasn't what I expected -> https://nakedsolar.co.uk/storage/ scroll down a bit to see the comparison table. -
They do and I think the IOTCricket is based on either the original or the ESP32. But of course you need the software to handle the sleep, awaken and manage the wifi to send the data. The IOTCricket seems to have solved this, although it's worth reading Pete Scargill's blog. For us the ESPs were in a place where power wasn't an issue, so they ran continuously without using the sleep functionality - it's a lot easier if you can do this. Tsk tsk - and you've had many months of Covid idling when you could have ....... ? Simon
That's a route I've been down as well. Feeding the data to an emoncms system running on a pi. These though wouldn't be battery powered and you'd need some software. Another option are the sonof devices (we have some of the switches and a temperature switch in the shed to turn on the heating when it gets too cold). Sonof devices can also relatively easily be reprogrammed with the Tasmota IOT software which is much more versatile and doesn't use a Chinese cloud server. If you need a battery powered device instead of the esp 01, there's a UK company thingsonedge.com with a new device called iotcricket. Not tried one yet but Pete Scargill has -> https://tech.scargill.net/the-iotcricket-from-thingsonedge-com/
I've had a lot of pleasure from installing an energy monitor. Another great aspect of these designs is that you can monitor temperatures as well as the electricity flow, so we have our thermal store all wired up. For the new house we're planning to do a DIY thermostat monitoring the temperature of the slab as well as the room temperatures. The guys that developed things are also doing a lot of great work on the open ESVE, so software to manage when to charge your EV using data on the Octopus Agile and Go tariffs. PM me if you are interested in what we have done in the current house. Simon
You need to install a system that will tell you. Take a look at the open energy monitor site -> https://openenergymonitor.org/ They sell a simple system based on a Rasberry pi which will monitor your overall usage and your PV generation - there are tools included to allow you to create your own dashboard. There's also instructions on how to build a PV diverter to divert any excess into an immersion heater. These will only divert when there is excess PV over and above your consumption, so automatically will stop diverting if say you turn on the dishwasher and you aren't generating enough to run it (there are commercial units that do this as well). There are also some apps for android and apple so that you can see what's happening and on the community there's lots of additional info and ideas - for example with a fairly simple bit of code you could light an LED when you are generating enough to run a big appliance - of course you could just look out of the window ?. Also follow the advice about running big appliances round midday and only one at a time - you'll get the best self consumption that way. Simon
Ours is only there in the current house because solar PV and solar thermal as the only energy source wouldn't cover the needs of an old fairly draughty house in terms of heating in the winter. For the house we're building which will be very well insulated with MVHR we'll only need an ASHP for both heating and DHW. We'll still use a PV divert into the DHW tank I think, so as not to waste the generated energy. Simon
New build water calcs - I don't get it
Bramco replied to dysty42's topic in General Self Build & DIY Discussion
But the calculators work through how many showers, loos etc you have and there is nowhere to put in how many people there are...... I can only use one loo obvs but our new house will have 3 en-suites and according to the calculators we'll be massively over the 110l per person. Simon -
Agreed - not that you're going mad of course - but the calculators take no account of the number of people. We have to do the 110l/per person limit but if you add up all the toilets, showers, a bath, washing machine etc in the calculator then it comes out as way above 110l. Where on earth does the per person bit get factored in? Simon -
We can too. We've had them in our homes since we lived in Holland in the 80's. We've had Howdens and IKEA in rental properties and IKEA are much better. It might be a small point but with IKEA you have oodles of holes in the sides of the cabinets to set your shelf height - with Howdens (at least in the past) you get a choice of 2 or 3 positions, so lots of potentially wasted space and then there's the 'utilities space' at the back of the Howdens and other base cabinets I've seen, maybe great for the installer but an absolute waste of space. IKEA are very well thought out. For the new house we've already speced IKEA cabinets - the work surfaces we'll get from somewhere else though. We'll also get IKEA appliances. Our own kitchen is on it's 2nd set of doors and as @SimonD said when anyone comes round they are always wowed by it (it's not that wow really), it just still looks pretty new. Simon
Thanks I'll take a look. Simon
Here's a graph of a sunny day. I should say that our thermal store in now 10 years old and is a DPS store - they were notorious for not being lagged well - it does make for a great drying room though!! The zig zags are the boiler kicking in. So at 7:30 or so because the tank temp has dropped low enough, then there's another one, when one of us took a shower. The big drop in the afternoon is both of us taking showers - it's a rain shower, so uses a lot. From 9am the rising red, grey and orange lines are due to the solar PV divert and the blue line due to the solar thermal going into the bottom of the tank. The PV divert goes into the middle, so only heats the top half. Graphs are all from the open energy monitor software emoncms which is excellent for this. If you look to the left you'll see it with the heating on the previous evening - the boiler only fires when temperatures drop enough. There's actually two setpoints on the tank controls, so the backup boiler is set to fire at a higher setpoint when the heating is on, i.e. the tank is a bit warmer - this prevents the flow to the rads dropping too much (we have both rads in the old part of the house and UFH in the extension. Hope that is of use. Simon
We have a thermal store and heat exchanger in our current house on which we have a number of sensors. There is always a gradient on the tank (210l), so v hot at the top, getting gradually cooler as you go down the tank. As you draw off hot water, the hot water is extracted from the top through the heat exchanger and returned lower down. If the temperature at the middle drops enough, then the backup boiler kicks - we have solar thermal and PV divert to harvest as much solar energy as we can. I'm guessing that an ashp or gshp wouldn't be able to kick in with the same amount of energy as the gas boiler does, so wouldn't maybe be able to give you several showers and a bath. Having said that I can't see how a how water tank would be any different from our thermal store. The hot water generated by the heat pump surely enters the tank at the top as cooler water is drawn off at the bottom to be heated up. So the tank won't be all hot, there will be a gradient, so as hot water is drawn off at a shower or tap it will eventually get cooler as again the heat pump won't be able to keep up. So it would seem that each solution will behave in a similar manner and depending on sizing might be behave exactly the same as each other. The reason we went for the thermal store in our current house was to make use of solar thermal and diverted PV and to have mains pressure potable hot water through the heat exchanger without having to worry about legionnaires. For the new house we'll have to decide whether we go the same way again or go for a hot water tank and make sure it goes through a hot cycle for the legionnaire treatment. It would be interesting to know the relative sizes of a thermal store and standard cylinder to get the same behaviour, i.e. amount of hot water before it begins to run cooler. Assuming I'm right about the heat pump not being able to keep up. Simon
We would but I read here -> https://www.edie.net/news/11/Government-planning-to-replace-RHI-with-Clean-Heat-Grant/ that in the budget it was extended to 2022. If not, then we'll have and ASHP in a field!!! EDIT: Here's the official notice -> https://www.gov.uk/government/consultations/future-support-for-low-carbon-heat PHEW!! Simon
@Dan F @Oldsteel I'm assuming you have both completed the build by now, or are nearly there. Any chance you could let us know how you decided to manage your projects and any insights on how they went? We're about to start ours, structuring it an a similar way to @Dan Fs, groundworks, foundations and timber frame from MBC, metal roofing and cladding and the MVHR and ashp as packages and then a builder to do the internals. Trying to keep things as simple as possible. Simon
And we're at J24 - Batman country if you know the area. Simon
MVHR - list of questions/thoughts
Bramco replied to mjward's topic in Mechanical Ventilation with Heat Recovery (MVHR)
We were intending to do that as well on the first floor. So only UFH in the slab on the ground floor. -
This is something that has got me thinking. Assuming we have our bathrooms warmer than the rest of the house and also have heated towel rails in the bathrooms, won't the returned warmth that an MVHR recovers as the air flows from the living spaces through the bathrooms to the outside keep the living spaces warm. So you can imagine that the heated towel rails are actually doing the heating which if these are electric are at a COP of 1.... Is this an issue? And if so how do you prevent it happening. Simon -
Hi there, wish I'd found this forum earlier!! Not that we're in need but there's loads of great experience here which could have kept informed and entertained as we ground through the planning process. We finally got permission a week or so ago after 3 years - I'm sure there are plenty of members whose trials and tribulations were worse than ours but I'm sure it's a pain for almost everyone. Our build is in the Green Belt and is obviously infill, therefore not inappropriate - the officer that dealt with our pre-app decided that the plot, was too wide at 32m. She then went on to give permission to another application in another village stating that their frontage of 100m was fine for infill. Beggars belief.... Anyway, we won the appeal with ease and then had the haggle of getting our design through (oh and another officer on the reserved matters decided the outline permission red line wasn't correct, so we had to put in a full application). So here we are 3 years down the line, when we should have been living in our German kit house for 2 years, being unable to afford the Germans because of the exchange rate, watching materials prices shooting up due to Covid and Brexit, as well as possibly a housing market slump in a years time when we want to sell our existing house....... The upside is that we'll be much more involved in the build which should be interesting... Our permission is for a 3/4 bed timber frame house to passivish standards but not certified - although we may need to be when it's done. Metal roofing and cladding with some wood and render, ashp, mvhr, solar at the top of the field, triple glazed windows etc. Simon & Jane PS We're just south of Nottingham which seems to be a bit of a desert as far as self builds go...
Hi Bozza, That's not going to work.......... I probably don't need to say any more....... Thanks for the info though. Simon
Hi, We've just been granted planning permission - the 'granted' bit makes it all sound a bit medieval - which it is - took us 3 years and an appeal..... That aside, we now need to make sure the finance is in place. We can cover all but about £100k and have been looking at how to find this part. We own our current house outright and it's worth about £450k, so naturally we would look to a mortgage on this rather than a self build mortgage as the rates are much better. So the question is how do you convince a bank or building society to loan you that kind of money on a new mortgage on the current house? Speaking to brokers some time ago, as soon as we mentioned financing a self build, there was much sucking of teeth and quotes for bridging loans at extortionate rates. I noticed someone on a post a couple of years ago saying they had said they wanted to buy a 2nd home. We have rental properties, so I guess we could say it was for a deposit on a new rental property. Is there any experience of raising money on your own home and if so how did you do it? And which bank/building society did you use? Thanks in advance for any help. Simon