Based on my experience with containers (and box trailers) the condensation issue is driven by swings in temp and zero ventilation My concern for tools and furniture clothes and books is even ventilated there is a risk that the ventilation is defeated by a large change in temp. Before I insulated my single skin brick garage - big swings in temp would result in condensation on tools and cars/motorcycles. 200 mm of loft insulation fully plasterboarded and boarded loft area - SUDG Window and side door - plus insulated roller shutter door and I no longer see any issues when temperatures swing rapidly. In fact the garage is cool in summer and always 4-5 deg warmer than OAT in winter. So I think I would insulate the sides and roof internally? If they were long term keepers I'd have suggested spray foam for speed and cost but I'm guessing you want to use and then sell on so I think I'd use PIR and protect it with OSB - probably don't need a huge thickness to cover off all but the most extreme change.
-
-
Absolutely correct - most of the time it is impossible to tell from the flue gases that the boiler is running - When you can tell it's running is below 5 deg C OAT when a very thin plume is visible or when it's re-charging HW as the flow temp and modulation level is much higher (it starts on 50% modulation and ramps up to 100% before slowly ramping down to maintain a 7 deg delta between flow and return at whatever target flow temp I've set it to) - and after the first 10 mins of the HW cycle the return temp exceeds 55 deg C and the boiler is no longer in condensing mode and my boiler flue looks like all the other boiler flues around me - chucking out a white plume but that's mainly due to a small coil in the current HW tank meaning I can't heat HW to target temp without leaving the condensing mode. It's on the list to sort - just haven't made up my mind to go with a new HW Cyl and ASHP coil or install a PHEX and circulation pump with the existing tank but we are a bit off topic now........
-
so OAT 7.0 Deg C - Weather Compensation curve says boiler should be targeting 27.4 deg C 3 mins after start boiler sitting happily with 7 deg delta (flow temp on left - return temp on the right) and maintaining a 28.7 deg flow temp at min modulation (10.4 %) at 13 mins after start boiler reaches the overshoot temp (target temp plus 3 Deg C or return temp delta below 7 deg C - I haven’t worked out which it’s using it may even be using both on either or basis) either way the boiler shuts down and waits for restart temp (Flow = Return - at 7.0 deg OAT this will be around 20.8 to 21.2) this will be in about 50 mins time It’s the 3 Deg hysterisis of the boiler that allows me to run low flow temps - it will keep a burn going for as long as it can as long as target flow temp doesn’t climb too high or delta between flow and return doesn’t drop below 7 deg.
-
Hmmm - that sounds like you are mixing up with an issue that would be a result of running a non condensing boiler at condensing temps. The aim of the condensing process is to recover latent heat from the exhaust gases. This process is not a fixed value of say 55 Deg C flow temp it's a scale of recovery The lower the return temp the higher the % of heat recovery in the zone of condensing mode. I'm targeting flow temps in the mid 20's to low 30's and I've validated the boiler efficiency to be 97 % (that's quite a fun thing to do once you get your head around how) Anyway the boiler has a stainless steel heat exchanger with a radial burner in a boiler designed to run low flow temps - the condensing process keeps the products of combustion off the heat exchanger and sends them out via the condensate drain - it really doesn't matter to the boiler if you are condensing with a return temp of 50, 40, 30 or 20 deg - the only impact it has is on the volume of condensate produced. It had it's first service a month or so back and the gas engineer commented how clean it all was inside the heat exchanger (he was as interested in the boiler condition as I was) I'll post up my flow temps from this morning
-
It's interesting to read that someone else did a lot of background study and was very selective (and prescriptive) about what they wanted installed and how. I "chickened" out of an ASHP - I didn't have enough data to prove to myself that an ASHP would work - despite being told by a well known plumbing youtuber I was already targeting flow temps that would work with an ASHP (even if the boiler at that time couldn't cope with them very well) I made the decision to go low temp gas boiler and look again at ASHP when the latest boiler needs replacing. In hindsight maybe a poor decision but Mrs Alien and I both like cooking with gas which meant no opportunity to be rid of the standing charge and that tipped the balance further in favour of a replacement gas boiler. Incidentally the chosen Gas Engineer didn't get everything right first time but was diligent enough to work with me and requirements and get it right in the end. (I wouldn't chose me a customer if I had plenty of other less demanding customers but he took it as a challenge and he'd never had the opportunity to fit a gas boiler that needed to target 30 - 40 deg flow temps based on Heat loss calcs that was pretty much where I thought I'd end up - I was out by 5 deg)
-
Unlimited hot water with 4 bathrooms - is it possible?
marshian replied to Indy's topic in Boilers & Hot Water Tanks
I guess because the kids aren’t paying the bills they aren’t bothered about wasting energy and water I’d be going one boiler and two tanks - a smaller one for the kids bathroom - when the shower goes cold they’ll soon learn to be less wasteful with energy and water 🙂 On a more serious note one boiler - with a good turndown rate for the CH demands of the house but a decent output for water reheat times to be quick urban plumbers did a set up a while ago with a fairly small tank that could be re-charged almost as it was used - worked like a giant storage combi but not a combi was how he described it at the end. -
Oh how well I remember those days - as if it was yesterday (was actually just 14 mths ago) Full Wiser system with smart TRV's on every rad Micromanaging schedules to individual room temps to control heat loss Boiler had a 10kW min output and wouldn't cope with a flow temp below 45 Short cycled like a complete twat at anything below 50 Deg C flow temp (My record was 19 cycles in 1 hour) When short cycling it chewed thro gas putting pretty much zero heat into the house and was fundamentally puking the heat out of the flue House was either too hot after too long or too cold after spending way too long waiting for it to warm up Ahhh happy days............... PS They bloody weren't!!!!
-
No that’s the flow temps the boiler is running based on my WC curve - No thermal store, no volumiser or buffer just 135 litres of water spread across 13 rads in the CH circuit. Flow rate is 8.5 Litres per min. example below only time it goes to conventional gas boiler temps is when it’s recharging the HW tank then it ramps up to 68 Deg C says “to hell with condensing efficiency - lets get back to space heating” Viessmann boiler 100W “heat only” 16kW with WC and HW demand box I’m basically running it at ASHP temps for CH
-
Your logic to me is totally sound - you want a nice big UFH slab with capacity to buffer temp swings outside if they are typically installing 50mm flowscreed in fairly modern builds with occupancy only outside working hours It would make sense - scheduled heating needs quick response in terms of warm up and a big chunk of screed is going to be much slower to respond. Perhaps that’s where they are coming from? I know I’m doing low temp (currently 21 to 27 deg C depending on the OAT) with a gas boiler and rads (no UFH and ASHP) but low and slow 24/7 to meet the needs of the house (or heat loss) makes so much more sense to me and I’m using less energy than I was last year when I was running scheduled heating with 50 deg flow temps and only heating when the house was occupied - everything is at room temp. last year when the heating went off the room temps rapidly fell this year I turned the heating off for 10 hours and the house lost just 1 deg C in the 10 hours it will take at least that time again to recover unless I raise the WC curve but it’s still comfortable so I’ll let it sort itself out
-
Upgrading upstairs pipework – 22mm vs 28mm
marshian replied to hyso80's topic in Central Heating (Radiators)
Neat solution but alternatively either Danfoss RAS-B2 will also offer fine tuning of the flow rates from 10 L/Hr to 135 L/Hr which is what I am fitting next. I'm currently using Drayton EB4 bodies which have 6 presets and in the main they've been pretty good at providing a system that is nicely in balance but I've a few rooms where one setting is too slow and the next one too fast so need a little more fine adjustment. -
-
You’ve replace google for me
-
Unfortunately from a stealing heat perspective both bathrooms 1. share a wall with the stairwell (18 deg set point) 2. share a wall with the landing (same 18 deg) 3. One shares a wall with a heated bedroom (20 deg) the other with a box room (18 deg) this box room has 3 external walls and a much higher heat loss hence the lower target temp 4. Both have an external wall and small window (plus extractor fan) 5. Both have 300 - 325mm of loft insulation above This conversation has stopped me making a big error and doubling the size of the rad based on 50% of wattage required - I just need to either buy slightly taller one 1800 v current 1600 or same height doubled but a reduced width. I really want to make sure I don’t end up bouncing along the top temp with TRV intervention - currently I have a DAB pump set to lowest speed on constant pressure watts 9.5 head 1.8 m m3/hr 0.5 (so 8.5 litres per min flow rate) in the shoulder seasons with current set up Boiler fires for ~12 mins in every hour and with a nice open circuit all rooms stay nicely at close to target temps again thank you for the help
-
I've not designed for any DT - I believe the expression is I am where I am with this house I've been using DT 10 compensation factor of 0.123 to work out what the rad output is v the heat loss at -2.5 OAT and two of my rads are coming out as undersize (both bathrooms with vertical column rads) This confuses me because the room temps are actually way closer than they should be (no matter what the OAT and room temp is just 1 deg below what I want it to be 21 although on bath nights Mrs Alien would like it a bit warmer.) so before I upsize them to hit the target temp I want to be absolutely sure of the factor to apply so I don't end up going to large and then restricting the flow to trim the temps. Set up if it helps Viesmann 100-W 16kW "Heat only" range rated to 4kWh on CH with external OAT sensor running WC (DHWP takes care of HW) Heating 23.5/7 (HW cycle once a day 30 mins does what we need 6 out of 7 days 2 x HW on her bath night) So at -2.5 my boiler flow temp is 36 Deg C (that worked fine last winter and the WC curve is nicely dialed in for pretty much all circumstances) DT at the boiler is a pretty stable 7 Deg (regardless of flow temp determined by the WC curve) Two rads concerned have a DT of 6 Deg between flow and return (Pretty much all the rads run similar DT T22 and K33 are a little bigger but other towel rails are a little narrower - all the rads are set up with the correct flow to meet the room requirements using Drayton EB4 TRV bodies) Now I understand the calculation (and I take the worst case of -2.5 OAT) 36 - 6/2 = 33 33 - 21 = DT 12 13/50 = 0.240 So Heat loss of Bathroom is 210 W Current rad is 800W at DT50 This at 0.123 is 98.4 W (Just under 50% of the output I need based on heat loss calcs) 800W @ new correction factor of 0.240 is 192 W That's much closer and kinda fits with the reality I need to upsize it but not by much ( a 1000 W similar rad with a DT 50 rating should give a little more wiggle room for the Bath night ). Thanks for your help
-
I keep coming back to this thread to make sense of the calculations in Bold I can't make 35-5/2-20 = 12.5 It's driving me a bit cranky @JamesPa My issue is my heat loss calcs were done room by room and in some rooms the rads currently fitted shouldn't provide the heat required at -2.5 Deg OAT if I use the std DT10 factor for T50 Rad so I'm trying to work out what they will actually output based on my own flow, return temps Flow 35 Return 25 Room 20 DT 10 Correction 0.123
-
Put the floorboards down and make a coffee 😉 Whats the joist spacing - they look quite close together in the picture but maybe that's the camera/phone lens
-
Last year at the start of the heating season I was running scheduled heating and manually setting flow temps. I transitioned to full WC flow temps during Dec moving to 23.5/7 heating (0.5 is HW recharge) and refined the curve in Jan, Feb and Mar with a really small tweak in Apr to fix overheats on warmer days (so bottom of the curve stuff). This year I used the same WC setting I was using at the end of the heating season Comparison of kWh/HDD (based on 16.5 Deg C base line) for first 6 days of this house heating season Day Last year This year Day 1 2.3 0.6 Day 2 4.9 1.8 Day 3 3.5 4.1 Day 4 2.7 2.0 Day 5 5.5 2.4 Day 6 7.6 2.3 Avg 4.4 2.2
-
50% of my CH circuit is under the suspended ground floor - it's lagged to within an inch of it's life as it is outside the heated envelope 45% of my CH circuit is between the floors - ie it's within the heated envelope and is not lagged at all 5% of the CH/HW circuit is from the Boiler to the HW tank and CH zone valve and back - this is lagged to within an inch of it's life to keep the heat in the pipes because in summer as @JohnMo says that contributed to an increase in room temps whenever water was heated Use something like Tubolit and the largest wall thickness that you can - the glue if you buy it in 250ml cans has a dispenser brush which makes it really easy to run along a split and seal it up - I'm not sure with a decent wall thickness pipe insulation you'd get much improvement from wrapping in rockwool
-
Not going to make it - still at work.........
-
You raise a really good point - thank you If you mean those officials who partied whilst the country was locked down - we should trust them right? Or perhaps you mean the officials who line their pockets on PPE equipment that was effectively useless - we should definately trust them? Or maybe the Media who with a country locked down and little in the way of revenue from advertising eagerly lapped up the official advertising revenue - totally trustworthy? Or maybe we should trust the businesses that profited from the lack of competition - supermarkets that could sell anything v small retailers that had to shut their doors - we should trust them? Nothing passed the sniff test for me during covid - if it passed yours then fine - you do you I'll do me Earlier contributor calling me a conspiracy theorist for having views that they didn't agree with is pretty much the way of the world - Everyone I don't agree with is Hitler. On average 1,600 people die a day in the UK yet the national news outlets during covid announcing 50 deaths from (or with) Covid like it was an extra-ordinary event I was labelled an "anti vaxer" for not "getting vacinated" - I'm not and have never have been anti vax - my reason was specific - having a holiday in North Vietnam on the Chinese boarder in very late 2019 I caught something that knocked me sideways and took me 3 months to recover - My reasoning for not getting vaccinated was simple - damn sure I've had Covid so why do I need a vaccination for something that didn't kill me and I'm pretty sure my body would recognise quicker next time - that's how post infection immunity works. (I do hate the term natural immunity as it implies you have it like a blessing from god or some other crap) Of course in 2019 it couldn't be Covid - it didn't exist then because everyone in authority says it didn't exist. Never had it since and during the pandemic working in my industry unfortunately I had to test for it a lot. PS I didn't get to enjoy the summer sitting at home on 80% salary - that would have been nice and I can understand why some would have a rose tinted view of the pandemic and the massive over-reach of the Government. Anyway That's my last contribution to the conversation around Covid in this thread.
-
Regarding Covid (Which was what I was referring to) quite a few obvious ones Pretty sure you don't need me to point them out It wasn't a "lab leak" but from a wet market from someone eating an uncooked Pangolin We were told there was no such thing as "natural immunity" - only the vaccine can end the pandemic (Post infection based immunity has served mankind effectively since the very beginning - to deny that is crazy) Minimal risks to the Vaccine - yeah that worked out well. Covid risk to the elderly and those with co-comorbidities was as high as a bad flu season but we never previously locked down for that what was different for Covid. The risks from the vaccines increased as they vaccinated younger and younger people but the benefits from vaccination weren't there to justify the vaccination but they still carried on. Masks and social distancing were based on science Lock down was the only answer - the vilification of the Great Barrington Declaration and the authors who dared to question the official narrative and suggest a more moderate path. The increases deaths post pandemic can easily be explained by the shutdown of the NHS for a large number of screening processes and focus on one aspect. In short my view is simple "The Cure was worse than the disease" Problem is those in government will never allow that to be a conclusion (It doesn't matter which colour rosette they wear).
-
I'm quite impressed it's been "foamed" - most window/door fitters bang in the window or door and then cover the gap with a bit of trim held there by a thin bead of silicone I think most "Expanding Foam" products break down with UV so left exposed like that it will degrade over time - so needs covering with suitable silicone/mastic I especially like that the packers are still in place!!!!
-
I have no doubt that man on this earth has had an influence on the climate - can we reverse it - maybe - should we try absolutely? However is the current path the right one? Can we discuss this? No......... What I really have an issue with is trust in authority (AKA Government) and MSM is broken and their reaction to Covid caused it - it was pretty shakey before but Covid broke it - utterly broke it in my opinion - I'm sure other opinions are equally valid What broke it - the total suppression of discussion - there was no alternative opinion or direction of travel allowed What was it Elizabeth Arden Said "We are your one point of truth - nothing except what we say is true" Jesus Christ!!! How many statements have been proven to be be false How many conspiracy theory's ridiculed are now grounded in fact Good luck all because IMO this is all going to end very very badly and no one in power is going to be happy about that