John Carroll
Everything posted by John Carroll
Insufficient flow rate for Samsung ashp
John Carroll replied to Simon Brooke's topic in Underfloor Heating
Just wonder if there is a actual interlock via a flowswitch, etc, it just says the unit can stop, page 23, I think they can trip if the flow/return dT is too low, some alarm is surely flagged if the unit refuses to start. Could be something else stopping this unit from starting. There should really be a ABV between the flow&return anyway. -
Agree, also, the Wilo Yonos Pico is the RR in pump control because it's head (and output) in CP mode can be incrementally changed in 0.1M steps to give almost infinite control, assuming of course that it can achieve the ASHP minimum requirement of 17.0LPM. @SimonD, where did you get this dP of 0.5M at 17LPM from and is 17LPM written in stone or can it be changed?, if it can, and could be reduced to say 14.5LPM to get the ASHP away, even as a temporary fix just now before any plumbing changes, then maybe worth looking at. -
The (my) last suggestion is to just fully shut/open the TMV, the shuttle may be partially jammed/seized, it will always shut off due to the hydraulic pressure exerted by the controlling pin but only spring force opens it. -
If it means, which I'm sure it does, fully open to hot, then can't see that being the problem although I would still remove the setting knob and have a look. What model mixing valve is it, might be on the label. The 4/40W shows it is a 6M pump, you should still be able to see (but maybe it doesn't display this any more now) the actual power displayed. There's not much else you can check out except see if you can find the ASHP pressure loss, SimonD says "Your heat pump at the required 17l/min has a pressure drop of 0.5m head" so that definitely will not be the source of any restriction, the dP at a flowrate of 22.5LPM would still only be 0.9M. Its a bit strange as you now have 2 powerful pumps running in series at 5M head each and still only getting 15LPM? -
Rough Schematic below of how I imagine the system is now configured, a UFH circ flowrate of 15.0LPM is only possible now vs 22.5LPM with the original UPS pump circulating from a "heat store"??, despite the Wilo running at a 5M head when pumping water through the the ASHP, it would appear that the restriction is caused at the ASHP side since both pumps are/should now be in series. It would be useful if the ASHP heat exchanger pressure loss is known. On the other hand, the mixer is now calling for full hot water so it might be possible to make a adjustment by removing rhe setting knob and increasing this port's opening as it may be restricting the flow, when mixing, there is only ~ 25% hot mixing with 75% cold -
Simon said "The loops are pretty much fully open, in fact one completely undid to much merriment!. Pumps on max." so not much more scope there for improvement?. 90M of 16mm/12mm ID pipe has only a loss of 0.61M and the UPS 2 when using sun amp was circulating a total of 22.5LPM, at this flowrate a UPS 2 will run with a 4.3M head, At the present set up it will be running at 5.3M at a total flowrate of 15LPM (1.5LPM/loop), similar to the Wilo if (a 6M), I would check that the Wilo is orientated correctly, ie pumping in the "right" direction, by looking at the arrow on the pump body, also as requested earlier, check the power in watts which will identify whether a 4M or 6M pump. -
Your Wilo pump should also display the power W (watts), not sure if it alternately switches from flow, m3/hr to power, W but there is certainly some method of having a look quite easily, I have a 6M Wilo (Yonos) Pico that only displays the power W but quite easy to read off the flowrate from the pump curves. If its the 4M model then the power at 0.9ms/hr is only ~ 17W, if its the 6M model, then the power at 0.9m3/hr will be around 40W + a quite hefty pump head of ~ 5M. (speed 3, C3) What is the UFH manifold pump model and setting? What are the flow indicators showing in LPM?. What dia are the Loop pipes and roughy the loop lengths? -
Might find this simple Spreadsheet handy for EV sizing calcs etc, or just for interest Expansion MASTER Vessel Calculation extract rev0.xlsx
Can see this now more clearly on my Laptop, the relief valve that is lifting is the expansion relief valve, while not a safety issue this should not be rated the same (6bar) as the TPRV which is stated on the cylinder data as being 6.0bar (& 95C), just ensure ASAP that the TPRV rating IS stamped 6.0bar as labelled on the cylinder. (Your Caleffi combination valve does appear to be plumbed correctly, as you described) Normally a UVC with a 6bar TPRV would/should have a 4.5bar expansion relief valve and if the precharge/filling pressures are 2.8bar/3.0bar then the final pressure when UVC is heated to 60C will be 4.0bar or 4.24bar with precharge/filling pressures of 3.0/3.2bar. You can see from the screenshot that the expansion relief valve setting is 4.5bar.
Havn't read all the posts but a 22L EV should be OK for a 248L UV cylinder. Assuming a (now) cold mains temp of 10C and a final HW temp of 60C and a full cylinder reheat each time, then...... precharge/filling pressures of 3.0/3.448bar = final pressure of 4.63bar. No problem. precharge/filling pressures of 3.0/4.25bar = final pressure of 6.0bar. Assumes PRV is passing and rises to 4.25bar precharge/filling pressures of 1.31/3.448bar = final pressure of 6.0bar. Assumes EV air end pressure (precharge) has fallen to 1.31bar. (50psi = 3.448bar) If the TPRV is set to 6.0bar, then the expansion relief valve should be set lower and should have lifted first, what is this set to??, it should be stamped on the end of it (red). Is the pipe from the EV connected in at the "bottom" of this expansion relief valve??. Also what is the Caleffi PRV model, it may not be drop tight. The Caleffi 535 is drop tight The Caleffi 533 is not drop tight
Top Mounted Vertical Immersion
John Carroll replied to John Carroll's topic in Boilers & Hot Water Tanks
The devil is in the detail. They obviously don't make them like they used to. No pesky rod thermostat in mine, still working perfectly after exactly 53 years. Sink/Bath c/o switch conveniently on top of the Immersion. -
Can you press (Newheat) pins down to see if they spring back up?, which is I presume what they should do, is the manifold circ pump running?.
@OldSpot will see almost immediately though what effect changing to Auto Adapt does as he can read off the loop flowrates. I have 8 rads on TRVs (old "mechanical" type), I have a 6M Wilo Yonos Pico circ pump where the CP&PP settings can be incrementally changed in 0.1M steps, I have run it for years in PP mode set to 4.6M which gives me the required flowrate of 12.0LPM at a 3.6M head with all TRVs fully calling for heat, the displayed power will then drop from ~ 22W to ~ 15W when the TRVs are throttling down, works very well, havn't adjusted it for years.
Yes, correct, I don't really see though why it should be required or even work on a UFH manifold, where, each system will have its own manifold pump so, irrespective of how many zoned systems are on or off, the flowrates shouldn't change?, why don't you switch over to (CP) Auto Adapt and see what effect it has on yout loop flowrates.
I have never seen any Grundfos Pump working properly in Auto Adapt mode, these had a Auto Adapt mode in PP (proportional pressure) only and generally appeared to run at the lowest PP head which circulated very little through the rads due to the very low head. UFH systems run with a fixed CP head and the loop flowrates are set up manually and are generally fixed, if there are a number of zoned UFH manifolds then the flowrates will probably change slightly depending on the number in service. This is the UPM3 Auto.
Changing the pump mode should result in increased flow, interesting to see if it actually does.
@marshian probably answered your query re continuous heating. You might check the Stuart Turner circ pump mode&setting, it has three constant curve settings and three proportional pressure settings, ensure its on constant curve setting 3, if not sure of the modes, tahe a photo of the pump switch or LEDs while running.
22LPM at a dT of 1C gives a UFH output of, 22*60*1/860, 1.54kW, pretty hopeless for a 11 loop system. Normally one might expect a dT of at least 4C/5C at a flow rate of 2.5LPM/loop even with a low flow temperature, this then gives, 2.5*60*(say) 4.5/860, 0.785kW per loop, in your case, ~ 8.6kW. Increasing the flow rate decreases the dT but should result in a greater output, but something definitely wrong when you are only getting a dT of only 1C. You also posted that when you shut down the GF that the FF flowrates almost doubled with the same dT, this, theoretically doubles the UFH output, can you post the total flow through the GF, can then look at the pump curve, if available, for that 8M ST pump, you might be able to get a suitable circ pump to give you 3.5/4.0LPM. How is the ASHP supplying the UFH, has it got its own pump?
To calculate any UFH output, kW = (total loops flowrate (LPM) X 60 X UFH (flowtemp-returntemp))/860. For example a UFH manifold with a total Flowrate of 15LPM with flowtemp-return dT of 1C will have a output of (15*60*1)/860, 1.05kW.
Have attached two files which combine the UFH+Rads, the other just shows UFH only but you or anyone can play around with the values and you can see the effect, hopefully, more easily. You can configure any one of S.Sheets for UFH only, Rads only or UFH+rads. by just changing the values in yellow. UFH ONLY Sumo Extract Rev0.xlsx UFH + Rads Sumo Extract Rev0.xlsx
No, its the boiler return temperature that primarily determines the Boiler efficiency, the colder the return temperature, the colder the boiler flue gases are, leading to greater efficiency, if you could lower the retur temperature to say 20C then you would have a almost 100% boiler efficiency. The flow through the loops will always and only be greater than the ASHP return flow when the required Loop flow temperature is less than the ASHP flow temperature, for example, with loop flow/return of 36C/26C and ASHP flow/return of 48C/26C, the % ASHP flow is (36-26)/(48-26), 10/22, 0.4545, 45.45%, a loop flow of 7.5LPM will return 7.5*45.45%, 3.41LPM to the ASHP and recirculate/mix , 7.5-3.41, 4.09LPM with the 3.41LPM from the ASHP at 48C to give the 7.5LPM at 36C loop flow temp, (3.41*48)+(4.09*26) = 7.5*36. If, both the flow/return temps are the same for both the loops and the ASHP, then both flowrates exactly the same. The bottom, 4th fom top screenshot below shows this, the 3rd from top screenshot shows the bypass required to give your required ASHP flowrate of 20LPM. The 2nd from top screenshot shows the data if you run with loop and ASHP flow/return the same at 36C/26C and the top screenshot just below shows the bypass required to give that required ASHP flowrate of 20LPM. Hope this is of some help.
No LLH required here (oil fired boiler) the TMV (Tapstat) does the job.
I don't know how how you can reduce the heating loss through the manifold, the only heating loss that I'm aware of is radiation losses which can be improved by insulating the manifolds?, In my (daughter's) case, as long as the water returned to the boiler is less than 40C then it doesn't matter whether like your set up its at 36C or 26C (if you had a conventional UFH where some of the UFH loop outlet water is returned to the boiler. Her boiler has a TMV set to keep the boiler return at 40C, it just mixes some of the boiler flow water with the return water, obviously more HW required if the return is 26C vs 36C, there are also no losses associated with this TMV. For example, if her system had a UFH total flow of 7.5LPM, then its output (and the boiler's) at a dT of, 36-26, 10C, is 7.5*60*10/860, 5.233kW.. With a boiler flowtemp of 54.5C and a return of 36C, then the boiler return (before the TMV) flowrate is 7.5*(36-26)/(54.5-36), 4.05LPM, 1.12LPM of water at 54.5C must be added to give a boiler return flow of 5.17LPM at 40C, if the return is 26C, then the return (before the TMV) flowrate is 7.5*(36-26)/(54.5-26), 2.63LPM, 2.54LPM of water at 54.5C must be added to give boiler return flow of 5.17LPM at 40C, boiler output 5.17*60*(54.5-40)/860, 5.23kW, equals UFH output?. You can see it doesn't matter what the mixing ratios are, same with the UFH mixing. What have you done to improve your own ASP COP? You can theoretically run that at 36C/26C, flow/return with no mixing to improve it, this has nothing to do with the mixing though.
Upnor apparently sell (or did, in 2023) a system something like the subject one and don't even use a TMV, they simply use a Tapstat with some the mixed water also returning to the boiler/ASHP. First screeshot below shows a live system with a ASHP. The manifold pump is pumping Upwards.