John Carroll
    3
Everything posted by John Carroll
  1. I’ve been asked numerous times to explain the residual pump curves published in some Vaillant Ecotec Boilers MIs, I’ve looked at them several times but afraid I can’t make any sense of them. Someone on here might explain them or/and post similar curves from their (Vaillant) HP circ pump curves, if available. The first screenshot shows my calcs based on a typical 7M circ pump, second screenshot is the Vaillants and the third is unknown but does make sense. The Vaillant’s constant pressure residual default setting is 250mB, 2.5M. At this setting, mine shows a flowrate of 1200LPH (20.0LPM), unknown’s 1300LPH & vaillant’s 1230LPH, much of a much. At 70% pump speed (72% for unknown’s but won’t have any big effect vs 70%) mine = 540LPH (9.0LPM), unknown = 620LPH (10.3LPM), again not hughely different and probably explained by pump differences but Vaillant = 1150LPH (19.2LPM), can’t figure this out but one would think Vaillant have some basis for publishing these figures??. Residual Head.docx
  2. The boiler's behaviour in reaching 100% output seems quite reasonable IMO, 5 minutes to reach 75% and a further 5 minutes to reach 100%, my daughters Vokera Vision 20S is pretty similar except, as it states, in the MIs.... it takes another 10 minutes to increase the output from 75% to 100%., it probably doesn't take quite 5 minutes to reach 75% but ~ 2 or 3, not a whole not different. But it certainly behaves much differently once the targettemp is reached, it immediately ramps down to maintain the targettemp very accurately, if one zone is switched off, the flowtemp might rise by a max of 2C and then returns to exactly its targettemp. This would be my bone of contention with WB. It shouldn't matter where the "flow" temperature is being measured, the controller is looking at this temperature and should modulate the boiler output to maintain the targettemp. What is the offset now between the Boiler displayed flowtemperature and the targettemp? and how does your temperature sensor, (if installed), compare with the boiler displayed one?. If you change the targettemp up or down by say 3C, is the boiler sluggish in responding and is there overshoot and undershoot?. I seem to remember that before the HEX replacement that the targettemp and boler displayed flotemp were withim a degree or so even though way higher than the actual flowtemp?.
  3. It was, on this very boiler, but in another Site/Thread, "Bypass Valve" in DIYnot.com, the pump speed fell to 30% which by my calcs meant a flowrate of 6.3LPM at a head of only 0.35M, shared through 11 Type22 & 4 Triple rads. This was before the boiler HEX was changed, so yes, would be interesting to see a full set of data if tried again.
  4. The 150, 200, 250 & 400mb or whatever settings in the WB are CP (Constant Pressure)settings. At the 400mb (4.0M) setting the pump will be running at 100% to just about achieve 20.9LPM at 4.0M (residual head) at the rads, if TRVs reduced the flowrate to say 10.0LPM then the head will remain the same 4.0M but the pump speed will fall to 81%, if the TRVs throttled down the flow to 5.0LPM then the pump speed will fall to 75% but the head remains the same at 4.0bar. If the boiler pump was like the 8M Wilo Yonos Pico set to 4.8M in its PP mode then that will achieve 20.9LPM at 4.0M, if the TRVs throttle down the flow, the pump speed will reduce to give 10.0LPM at 3.0M & 5.0LPM at 2.7M but the TRVvs will be opened a bit further, obviously if the PP setting is lower then the heads at 10LPM & 5LPM will be lower still and the TRVs will open still further. This boiler has, I think, a variable speed setting, 0?, I think it aims to get the flow/return dT to ~ 20C, the rad output then for any given flow temp, outside temp & room temp will start reducing, the boiler output will then reduce to match this. The latest Vaillant boiler has this, where the dT can be set between 10C & 20C but doesn’t seem to work very well on at least on one user's boiler that I’m aware of.
  5. Like most Boilers, there are several hydraulic options, one of which is pump modulation based on boiler output, this option would not be the one I would recommend for a system with long pipe runs as the pump head then at low boiler modulation might not produce enough head to circulate sufficiently through the furthest away rads, resulting in boiler cycling, one of the options is a constant pressure Residual Head of 4M (400mb) which, because of the Boiler Hex loss and the rads/system loss will/can result in the pump running at 100% to maintain this required residual head. None of the selected options should cause the above problems.
  6. A LLH will not cure a BOILER problem which IMO this boiler clearly has. It reached Targettemp after 25 minutes yet it took another 20 minutes for its output to fall from 36kW (100%) to 23.4kW (65%) but reached a flow temp of 64.8C during this period. It then took another 50 minutes to fall from 23.4kW (65%) to 17.64kW (49%) and finally return to its Targettemp of 60C (59.9C) I would be very embarrassed to look someone in the eye and tell them this is normal operation. On 25 minutes (target temp reached) Flow 60.1 return 39.0 dT 21.10C Burner 100% 36.00kW Pump 100% 21.50LPM dT 24.00C Flowtemp 63.00C On 30 minutes Flow 63.2 return 42.8 dT 20.4C Burner 95% 34.2.00kW Pump 100% 21.50LPM dT 22.80C Flowtemp 65.6C On 35 minutes Flow 64.8 return 46.4 dT 18.4C Burner 85% 23.40kW Pump 100% 21.50LPM dT 20.4C Flowtemp 66.8C On 45 minutes Flow 64.8 return 50.2 dT 14.6C Burner 65% 23.40kW Pump 100% 21.50LPM dT 15.60C Flowtemp 65.8C On 55 minutes Flow 61.9 return 50.7 dT 11.2C Burner 49% 17.64kW Pump 100% 21.50LPM dT 11.76C Flowtemp 62.46C big time gap now as I stopped measuring till it settled to actual target temp of 60'c On 1h35mins Flow 59.9 return 47.8 dT 12.1C Burner 49% 17.64kW Pump 100% 21.50LPM dT 11.76C Flowtemp 59.56C
  7. This is some of your data after the HEX was renewed. The Target Flowtemp was 60C. The bottom line of each set of data are my calcs using the pump flowrate and your dT (as measured with the external sensors), it gives a calculated flowtemp not too far away from your measured temp so will mean that the boiler output based on modulation is quite reasonably accurate but maybe no harm to do that gas meter rate. On for 5minutes Flow 30.6 return 15.6 dT 15.00C Burner 62% 22.32kW Pump 93% 20.00LPM dT 16.00C Flowtemp 31.6C On 15 minutes Flow 50.9 return 29.0 dT 21.90C Burner 100% 36.00kW Pump 100% 21.50LPM dT 24.00C Flowtemp 53.00C On 25 minutes (target temp reached) Flow 60.1 return 39.0 dT 21.10C Burner 100% 36.00kW Pump 100% 21.50LPM dT 24.00C Flowtemp 63.00C On 30 minutes Flow 63.2 return 42.8 dT 20.4C Burner 95% 34.2.00kW Pump 100% 21.50LPM dT 22.80C Flowtemp 65.6C On 35 minutes Flow 64.8 return 46.4 dT 18.4C Burner 85% 23.40kW Pump 100% 21.50LPM dT 20.4C Flowtemp 66.8C On 45 minutes Flow 64.8 return 50.2 dT 14.6C Burner 65% 23.40kW Pump 100% 21.50LPM dT 15.60C Flowtemp 65.8C On 55 minutes Flow 61.9 return 50.7 dT 11.2C Burner 49% 17.64kW Pump 100% 21.50LPM dT 11.76C Flowtemp 62.46C
  8. @SimonD, in your experience of Worcester 8000 system boilers, have you come across this strange? behaviour on both this boiler and others, where, after a HEX change, the indicated flow temperature doesn't match the Target temperature even under steady demand conditions and with the boiler demand well above its minimum output, can you suggest any reason for this behaviour?. and which WB says is normal.
  9. Meant to post these as well a few days ago. If you do choose a 8M UPS2 Pump then you can see from the attached that it should satisfy a flowrate of up to 30LPM based on your present flowrate of 20.89LPM at a Rad head of 3.98M.
  10. Here are the screenshots from your LLH with both balanced and unbalanced primary/secondary flowrates.
  11. Increasing flow rate will have a very small effect on rad output, temperature increase, if possible, is the name of the game, again as said previously, a small increase in flowrate requires a big increase in head which can be very beneficial in balancing rads. You can see, quite clearly below from your set of readings that a flowrate of 20.8LPM with a flowtemp of 59.9C gives a rad(s) output of 16.49kW, increasing the flowrate to 30LPM will only give a 0.96kW increase to 17.45kW, not a lot. IF the flowrate remains at 20.8LPM but the flowtemp is increased to 75C then the rad output increases by a substantial 8.1kW to 24.6kW, if the flowrate is now increased to 30LPM, (flowtemp 75C) then the rad output only increases by a further 1.53kW to 26.13kW. Also, attached, some LLH numbers, for interest. LLH Calcs Extract ET Rev0.xlsx
  12. There's no way a 6.0M or even the "normal" 8M pump will give you 30LPM even with a LLH based on our tests. The Hex loss was 1.54M @ 20.89LPM, this = 3.5M @ 30LPM, The rads loss was 3.9M @ 20.89LPM which will require 8.04M @ 30LPM. Any of the conventional 8M pumps will only give a head of 5.5M ish at 30LPM but the 8M UPS2 which is a giant of a pump at 140W will certainly supply 30LPM and far more at a 8M head, its actually a ~ 10M pump but the "fixed" "CC" speed curves are almost fully CP (constant pressure) curves, no other pump that I'm familiar with will match that performance. If you do think of going for that pump then it might be worth just installing it as a booster pump at minimal installation costs as the boiler circ pump will still have a residual head of ~ 0.66M at 30LPM, enough to avoid cavitation in the UPS2 which requires a minimum inlet head of 0.5M at 75C. The UPS2 other "CC" curves of 7M & 6M can also be useful if the need arises, the LLH can be installed if the above doesn't work out, it's your choice. I will post a few screenshots later of a LLH based on one of your tests to show the effect of balanced & unbalanced flowrates.
  13. Had a look at installing a 6M Wilo Yonos Pico as a booster pump. It should, IMO, provide a modest boost in flow from 20.9LPM to 25LPM or slightly higher, might not seem a lot. but if your problem is getting a higher flow to a few cooler rads then it may be beneficial because the residual pump head now available to the rads should rise from 3.98M (398mb) to 5.7M (570mb), a 1.72M (43%) increase.
  14. Dynamic Head, above should read ~ 570mb, not 510mb.
  15. Their answer(s) is a bit illogical, to me, at least. As stated numerous times before, any control system that is controlling a system that is running under steady conditionds WILL and certainly SHOULD get the process variable (flow temperature) within decimal places of the Setpoint (Target Temperature), and worse, since your flow temperature is apparently being controlled at least > 2.5C above the Target temp then this cuts down the tolerance before the burner trips on overshoot. Again, regarding the maximum 400mb residual pressure setting, this does seem on the low side but now that we know the boiler HEX pressure head loss, (CDI+8000 Chart) its quite easy to see why your system will run at 100% pump speed when set to 400mb. You can see from one of your set of readings, attached, below, that the residual pump head is almost 400mb (398), the pump dynamic head (before boiler HEX loss) is 510mb to give the calculated flowrate of 20.89LPM. I will have another look at installing a second pump but can't see much merit in it just now as it would just reduce (rob) the existing pump's residulal head (when running flat out at 100%) and you could just end up with the same effect as having no extra pump. On 1h35mins Flow 59.9 return 47.8 dT 12.1C Burner 49% 17.64kW. Calculated flowrate, 17.64*860/60/12.1, 20.89LPM Residual Pump Head 400mb OR 100% Speed. ET Rev0.xlsx
  16. Yes, but remember the flowrate is a indicated 21.5LPM at 100% pump speed,a pretty hefty flowrate. If the engineers haven't come and gone please ask them for the boiler HEX pressure loss as I used a assumed one.
  17. Open & shut the pump isolating valves 3 or 4 times, should then hold OK. I have a 6M Wilo Yonos Pico Pump, running fine and silent for the past 7 years.
  18. @EinTopaz I think I may finally have a answer to your query..... " if its 15-70, why is setting 6 (400mbar) show as pump output 100% on the boiler LCD display? Does that essentially mean its got way more head than it's able to use? i.e it's capable of 700mbar, but can only run 400mbar max? I find the manual quite confusing here and it'd be great to understand" The pump appears to be able to calculate the speed required to give a RESIDUAL HEAD of 400mb based on the HEX dP and the system/Rads dP, in your case, with a new clean HEX and because of your system resistance then the pump has to run flat out to achieve this residual 400mb, you can read off the flowrate from the Residual Head chart, which is 20.7LPM at 400mB, the clean HEX dP is only 1.67M at this flowrate. I have based the HEX dP on one I think is correct for your boiler, you might ask them for it sometime.
  19. Did your engineer come back on Friday?
  20. If you are talking about a Immersion then presumably its a Electrical Immersion, if so, the UVC will have somewhere to install this, these immersions have their own integral stats and measure the water temperature where ever they are installed, THe 50%& %75% probes should determine what vol of hot water is used before the HP or boiler is called on to start reheating, HPs might tend to have the probe at 50%, if measuring from the bottom up then the HP might use the 75% pocket.
  21. Below gives a idea of the loss through the boiler HEX, this might be the same as your boiler but try and get the proper one for your boiler. The pump curve above shows that the flowrate (curve A) is ~ 27.5LPM, 1650LPH at a head of 6M, the screenshot, below shows that the boiler HX pressure loss at this flowrate is 3.2M, this leaves a residual pump head of, 6-3.2, only 3.1M, so would require a LLH to allow a secondary pump to suppy enough head to give this flowrate. You could look at installing a booster pump instead of the LLH, far cheaper, even though frowned on by some because a perceived problem that the pumps wouldn't be matched leading to problems, I don't see a big problem with this as pumps like my own Wilo Yonos Pico have virtually infinite head setting (in 0.1M incremants) in CP (and PP) mode, to match the other pump.
  22. If you look at the pump curve above, you will see "H/M" (M is meters) right at the top and it states right at the bottom that H is the Residual head. Residual head is the pump head available after the boiler HEX, you can see the pump head just starts falling, 1200LPM (21.7LPM) @ 7.0M head which indicates to me that the boiler HEX has a pressure loss of 7.0-4.0, 3.0M at a flowrate of 21.7LPM, you are getting very close to this flowrate, 21.5LPM at full pump speed. The residual (remaining) net head of 4.0M is lost through the CH system. If you now install a LLH where the primary pump just circulates through the boiler HEX and a (new) secondary pump circulated through the CH system, then, all the secondary pump head is used to increase the flow through the CH system which will increase the return temp/reduce the dT and get a increase in rad output and a faster warm up. If you install a "6M" secondary pump then the flowrate will increase from 21.5LPM to, 21.5*sqroot(6/4), 26.3LPM, not a lot as the rads dT will only fall from ~ 12C to 10C which only gives ~ 3% in rad output, say a increase of 0.6kW from 18.0 to 18.58. The easiest way to get a faster warm up is to increase the flowtemp to say 75C but would need reducing again when roomtemps reached to maintain reasonable boiler efficiencies. When the engineer next attends ask what the pressure loss through the boiler HEX is, dP & flowrate.
  23. Have you contacted WB re this issue?.