@Temp writes: "The void under the membrane can also be reduced to 25mm just to allow the membrane to drape correctly". This is the 'rule' used by many membrane companies and by most roofers retrofitting insulation over a room-in -the-roof, and what I have used for many attic bedroom retrofits, but the most recent government guidance (https://www.gov.uk/government/publications/room-in-roof-insulation-riri-best-practice) suggests 50mm if I remember rightly.
- 20 replies
-
- ridge board
- ventilation
-
(and 1 more)
Tagged with:
-
If the ridge height is really a problem could you have a mainly-vaulted ceiling with just a tiny dropped area at the apex to allow an air-passage/'plenum chamber'?
- 20 replies
-
- 1
-
-
- ridge board
- ventilation
-
(and 1 more)
Tagged with:
-
Eaves-to-eaves ventilation works for a huge number of roofs, but it may not work for your BCO... My house has no ridge ventiulation and no moisture issues (well, not in the roof....)
- 20 replies
-
- 1
-
-
- ridge board
- ventilation
-
(and 1 more)
Tagged with:
-
Chat GPT for building regulations - insane!
Redbeard replied to GaryChaplin's topic in Building Regulations
"I’d compare ChapGPT to a very recent joiner at an accounting firm". Ah well, that's where they're going wrong! They need an accountant. -
As @ProDavesaid, try ringing from a number he will not recognise. If he puts the phone down when he realises it's you then you have a pretty good idea of where the land lies, but it *may* be that you have time to explain that you want to resolve this in a way that works for both of you. Worth a try...
-
It was a little less straightforward for us since (a) every extension had to be birdsmouthed and (b) the roof has spread in the middle. At that point I was glad I wasn't doing that bit. Less glad when I got the roofer's bill! We had to extend eaves x 1 elev and verge x 1 elev (we only EWI'd 2 sides). We bolted rather than nailed.
-
Detached garage foundation insulation - worth doing?
Redbeard replied to Kelvin's topic in Garages & Workshops
If you want it to be useable I would bump up the 40mm PIR straight away and yes, insulate your floor. If you are looking for quick warm-up, however, you may be better with a floating floor on top of the slab rather than insulating the slab. -
An external pic with context would be good - for my part so that I can see whether external wall insulation (EWI) might be an option. You say "the roof definitely needs changing, but again is this something that would require completely starting from scratch? Would an experienced builder recommend a new flat roof or a pitched roof?". Again, pics will help, and heights (from surrounding ground to current top of roof) so that we can look at it in relation to Permitted Development (Planning) rules.
-
MVHR Loft Installation - Inspiration
Redbeard replied to richo106's topic in Mechanical Ventilation with Heat Recovery (MVHR)
@Mr Punter, as I read it I think that when @richo106 says 'over the top' it means 'underneath', as the next things are VCL and plasterboard. @richo106, can you confirm? -
MVHR Loft Installation - Inspiration
Redbeard replied to richo106's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Agree with @ProDave. You *might* find a manufacturer's tech dept might suggest a lay-up, but I should have thought they would fight shy of 'designing', in terms of the potential liability. -
MVHR Loft Installation - Inspiration
Redbeard replied to richo106's topic in Mechanical Ventilation with Heat Recovery (MVHR)
That's not what I'd call a Warm Roof, whatever the caption says! A 'full' Warm Roof has all the insulation above the rafters. A 'hybrid' WR has some above and some between, but beware of interstitial condensation risk. -
MVHR Loft Installation - Inspiration
Redbeard replied to richo106's topic in Mechanical Ventilation with Heat Recovery (MVHR)
I think you really, definitely, want an air/vapour-tight layer at FF ceiling level. Detail it with say Intello membrane (See Buildhub Market Place for a cracking bargain!) and air-tightness tape. If you have to have the MVHR unit up there how about 'engineering' an 'MVHR house' ? You decide on the size needed and you stop the insulation for that square/rectangle. Build a stud 'MVHR house' (with a maintenance door) and make it air-tight and well insulated. Don't insulate the bottom (at FF ceil level). It wants to be in the heated envelope. For aesthetic reasons of course you will still have plasterboard across at FF ceil level (golden rule of pragmatic eco-build - the end result must not look stupid!) but there will be no insulation there to impede heat tfr. There will be a good, tight connection between the surrounding loft insul'n and that on the 'walls' and 'roof' of the 'house'. -
Walls are '70mm solid wood'. How can you run cables 'inside the wall blocks to hide it away'? Or do you just mean stapled to the inside of the wooden wall and sandwiched between it and the insulation? Is it too late to suggest you insulate externally? That way there's no interstitial condensation risk. You said in your OP 'We just purchased a summer house'. Does that mean that any of us who are suggesting tweaks (roof sheets, for example, or EWI) are advising you to change something you can't change? (If you wanted EWI your roof would have to be bigger, and if your bought building already has a roof you won't want to be buying pre-insulated metal sheets.) Can you give us more on what's possible to change and what's a no-go? Thanks.
-
Not quite what you mean as this is a plug, but at 85mm it may work: https://ewistore.co.uk/shop/external-wall-insulation/spiral-anchors/
-
8R Value sufficient for this basement ceiling?
Redbeard replied to Babugaa's topic in Heat Insulation
Are you installing the insulation from the top (lifting the floorboards) or below? -
Adding an extension … do we need self-build insurance
Redbeard replied to KayleyH's topic in Self Build Insurance
I did EWI and small extension last year (and this year, but I haven't re-started yet!). Already had my own PL ins'ce as I had only just given up regular contracting. Changed home insurers before I began as my exg insurer was being silly. Can't remember all the detail, but it felt less than helpful. Paid for P.L insurance for my chosen 'helpers' . -
+1 to @Nickfromwales. I was about to ask if you had considered the 'Critical Friend' route? I worked with ('between'?) clients and their architect, the 'cut of whose jib' they liked, but who was not 'an energy architect'. Effectively he did the design (I cannot design my way out of a paper bag) and I 'did the energy bits'. We also had a few hours with a PH consultant mid-way through the process. It is not (and was not intended to be) PH, but it's a nice 'tight' house.
-
Hello. You say "There's a gap between the existing ceiling (which is of lathe and plaster construction) and the floor of the extension (which is suspended insulation under TNG etc..). I wanted wanted to ensure this gap is well insulated internally (so where it meets the staircase) as well as externally (which I assume will be stud / block work / guttering etc...). " I don't quite understand that explanation, because you refer to 'plans for an extension' (which implies it is not there yet) but you also refer to "a gap between the existing ceiling (which is of lathe and plaster construction) and the floor *of the extension*". I am guessing that when you say extension in the second example you actually mean the loft conversion. (Maybe...) Can you enlighten me? Pictures/drawings would be good. Apologies if I am just being obtuse.
-
@Conor posted while I was writing mine, but I wonder if PD regs in NI are different to the mainland and still refer to PV on 'roofs' in CAs?
-
Planning Portal says this: " All the following limits must be met: Panels should not be installed above the highest part of the roof (excluding the chimney) and should project no more than 200mm from the roof slope or wall surface. The panels must not be installed on a building that is within the grounds of a listed building or on a site designated as a scheduled monument. If your property is in a conservation area, or in a World Heritage Site, panels must not be fitted to **a wall** which fronts a highway." (My emphasis). This seems to me to imply that they are (may be) PD on a **roof** fronting a highway. This apparently does not stop my LA discouraging PV on the front of properties in conservation areas. I am sure this will hinge on individual interpretations of 'so far as is practicable' (below). My memory says that some years ago PD rules *did not* allow PV on front roofs in CAs but as far as I remember that changed (probably somewhere around 2010) to the current position. See GPDO Part 14 A.1 and A.2. https://www.legislation.gov.uk/uksi/2015/596/schedule/2/made Conditions A.2 Development is permitted by Class A subject to the following conditions— (a)solar PV or solar thermal equipment is, so far as practicable, sited so as to minimise its effect on the external appearance of the building; (b)solar PV or solar thermal equipment is, so far as practicable, sited so as to minimise its effect on the amenity of the area; and (c)solar PV or solar thermal equipment is removed as soon as reasonably practicable when no longer needed.
-
Curtilage listed Stable Conversion in Dorset, built in the 1800's
Redbeard replied to TPickford's topic in Introduce Yourself
+1 for Back to Earth. They will do a WUFI assessment. -
Curtilage listed Stable Conversion in Dorset, built in the 1800's
Redbeard replied to TPickford's topic in Introduce Yourself
...and if you don't knock it down... I would use rigid wood-fibre, and get a WUFI (or similar) dynamic condensation risk analysis done first to inform the 'safe' depth you can use. Some say only 60-80mm, some say 100 OK in some circumstances, but bear in mind that, depending on the exg fabric the resultant U value will be worse than 0.3W/m2K, probably. Some would say use plastic ins (PIR nearly twice as good for a given thickness as some rigid WF) and just get the vapour control right. It is this bit - getting the VC layer right - which, while hardly rocket science, can often be done badly. Difficult for you to control from abroad! My stance on wood-fibre is that if it is designed to operate without a VCL that's one VCL not to get messed up. I have used it a lot, internally and externally. Is the pointing done in lime, by the way? -
@Jimbo23 said: ''@redbeard You're correct, 1920s exactly. 15-20 years lifespan is fine. Does that mean leaving it completely alone or does that include repairs (i.e. re-add missing hip/ridge tiles, repointing etc)?'' The 15-20 years was my latest target for *my* (slate) roof. No, it's definitely not leaving it compeletely alone! I don't think any 100+ year-old roof can be expected to be fine if left alone for 15-20 years. Even if it's just minor fettling it will need some TLC. My latest target for my roof is after a lot of trips up the roof. Till I started getting old I went up every year for a darn good look round. I cannot make a guess at yours from the pics, but you need to look at it critically, like you are *expecting* the tiles to be knackered. Let them prove to you if they are not. Appreciate you don't own it yet, but I think someone really needs to go up there to have any degree of certainty.
-
You'd get longer out of it, almost certainly, but we cannot see the condition of the tiles. I am guessing circa 100 yrs old (?) - looks '20's - and I don't know the life of Rosemary clay tiles. Certainly I have seen some 'dying' in less than that time. My (slate - so almost certainly 'destined-for-a-longer-life' roof had, I reckoned, 5-10 years left when we moved in. 35 years (and a goodly bit of maintenance) later I reckon it's got 15-20 years. If you want 30 years and don't want to re-roof I suspect you might look elsewhere. If you want something which is not too bad, will last while you save the money and will improve a lot when you re-roof it then this may be for you.