  1. I actually went down the sequential route as part of the discovery phase for my ASHP. I first reduced my boiler temp to the lowest it would go (50C), then started operating 24x7. That was as far as I could take it without changing radiators, in fact I needed to up the FT to 55 in the depth of winter. I also limited my boiler output to the minimum possible (8.5kW in my case). This arrangement was indeed more comfortable, and used less gas (it wasn't cheaper because prices went up at the same time, but it used less gas). Upsizing radiators, swapping to an ASHP (obviously with WC) and thus getting max FT down to 45, and FT most of the time to 35 or less, together with removing all but one TRV head made the big difference in comfort though. One day I will tot up how much I have spent on wholly unnecessary heating control equipment over the years (yes I too was suckered into trying 'smart' TRVs at one point - what a waste of time and money!).
  2. I don't think you wont have to wait long. My 4 year old Kia e-Niro reliably does >240miles in the worst of winter, 300 in summer. That's not much less than you need and thats a car from 4 years ago.
  3. ... and the heating industry is content not to inform them, because it is so easy to whack in a 28kW boiler without thinking and let the controls 'sort it out'. This is of course at considerable cost to the customer both in comfort and expense, and with the added benefit to the industry that they get to sell lots of unnecessary controls! We are stunningly backward in the UK. Some continental european countries mandated weather compensation decades ago. I presume our heating industry lobbied against and unfortunately our Government wouldn't have had the technical knowledge to overrule them. I confess that, despite having a degree in physics, I was ignorant of this myself until I started researching heat pumps (and thus heating systems in general) about 3 years ago. Its only slowly dawned on me how misled we have been by the industry in this country and how backward it is. For the avoidance of doubt Im not saying we are unique, but we could be a lot better.
  4. I know that and acknowledge it in my post - I quote: 'Low temperature heating (the conversion to which makes up a major part of the differential cost) is just so much better, but how many people who haven't experienced it know that?.' However the cost comparison that you do is with your typical 'shove in a 28kW boiler, whack the flow temp up to 75, ignoring the fact that it wont condense, and let it cycle like mad on the TRVs and Thermostats, with the consequent temperature gradients across rooms and temperature swings with time' crap that our heating industry has been installing, its not the well put together low temperature system you speak of above. The latter needs the same care, and mostly the same components, as an ASHP system. So yes if you want a crap heating system that costs more to run than it should go for the cheapest to install, which is undoubtedly to shove in a 28kW boiler, whack it up to 75C, and let the TRVs 'sort it out'. If you want a system that keeps you comfortable then go for something much better, which will cost about the same to install whether the heat source is ASHP or gas and, if you get it right, will be a bit cheaper to run in the latter case (a lot cheaper if you have batteries and/or solar PV) and much greener. Obviously there are many that can only afford the capital for the first of these, but equally there are many who would happily pay for better if (a) they knew the option existed and (b) our heating industry were capable of delivering it at scale, which at present I doubt it is.
  5. As a recent ASHP owner I would probably agree (although I do save a significant amount of money with mine) However I would also say that, if you want a much better heating experience with a house the whole of which is comfortable 24*7 for about the same or possibly less running cost then do bother. (Obviously also if you want to reduce the carbon footprint of your heating by a factor of 3 they do bother) Low temperature heating (the conversion to which makes up a major part of the differential cost) is just so much better, but how many people who haven't experienced it know that?. Just be sure to do your research so you avoid the cowboys, as you must for absolutely anything which involves any of the building trades which, lets face it, are in parts about as dodgy as it gets.
  6. It hasn't. However in the thread concerned the complainant was blaming his ASHP (because thats what people do) for problems clearly caused by a poorly insulated circulation loop running continuously. I suppose with a boiler the problems wouldn't be so easily noticed, because the boiler would just carry on chucking heat into the loop.
  7. Transmission losses and power station efficiency etc are all accounted for on the published figures for carbon intensity of fuels, which are updated annually. The carbon footprint from UK domestic electricity per kWh is about 10% less than that of domestic gas, furthermore it's falling as we move to renewables. That means that a heat pump with a cop of 3 causes less than one third the carbon emissions (actually it's a bit better still than that because most has boilers are set up by the heating industry in a way that makes them less than 100% efficient). This stuff is well established and the carbon case for heat pumps irrefutable.
  8. Fair enough if you make it that sophisticated. Is that what your average plumber does or do they just have it running continuously? There is a running 'ashp' thread elsewhere in which it's obvious that the main problem is in fact a circulating loop (IE nothing at all to do with the ashp).
  9. Really don't go down the recirculating loop route. In summer it heats your house continuously when you dont want it to, so you will pay to heat and pay to cool. In winter it heats the house at high cost when you could be heating it for one third of the cost. For hotels, fine, for houses no. Instead design out the need by locating dhw storage near points of use. If necessary use point of use heating for everything other than baths and showers. Unless of course neither money or carbon footprint matters to you and you can get joy by showing off about having instant hot water everywhere.
  10. That's very perceptive! Also spot on and a better description.
  11. So long as installers do a reasonable job of heat loss calcs and emmitter sizing Unfortunately the evidence is that a significant proportion don't, instead many slavishly follow the MCS rules which are highly likely to overestimate, but give ironclad protection to the installer. My house may be an extreme example, two surveys each taking 3 Hrs said 16kW whereas it's actually 7kW. Fortunately the better guys understand that the MCS calculations strictly applied may give seriously wrong results, and exercise due judgement, whilst foregoing the ironclad protection that following the mcs rules offers (to installers not customers!).
  12. It was only 2.5:1 in 2011 and its been steadily growing since (until the Ukraine war made the ratios volatile.) I find it very difficult to believe that this wasn't a largely political decision by the previous government.
  13. I'll drink to that (and I'm in the pub so I can!)
  14. Not if you get a sensible tariff. Also don't forget gas boilers are rarely set up to run efficiently because our heating industry never really bothered to understand condensing boilers. Practical break even is more like 3.5. Some may wish to factor the significant added comfort of an ASHP based system.
  15. I think householders do need to understand WC at least a bit. The probability that an installer has correctly set it up is small (particularly if the installation is in summer) and even if the installer has set it up correctly if the householder doesn't understand a bit about WC they wont understand why their radiators are rarely warm. Its hardly a difficult concept though, water circulating through system, is hotter when it colder outside and colder when its warm outside. They dont need to understand scheduling of the CH though, just leave it on! I do think interfaces need to get better. The likes of Vaillant, who have had to cope with boilers featuring WC for a couple of decades (because its been compulsory in some mainland European countries), have more or less got it; the interfaces for some of the far eastern machines are really poor.
  16. Sorry Im genuinely confused, which stupid regulations are these? Is it the fact you can only have one under PD (two on a detached house?) or is it something else in the regulations that causes a problem?
  17. Indeed, and performance/features People bought Teslas because they are cool, because they work, and because they could show off, not because they are cheap. Of course their CEO's antics has rather messed that up. It could be similar with heat pumps. Done properly they will give you much more comfortable heating for less money (like mine does!), for which people will pay a considerable premium. Furthermore done properly is actually the easiest and cheapest way to do it! Heat pumps might even be 'cool'. The installation industry needs to get its act together. European heat pump manufacturing ditto IMHO. I expect the Chinese could knock out a perfectly good heat pump for £500 and sell it for maybe sub £1000. Its basically three motors, a low end processor, a bit of pipework and some bent steel. I have a Vaillant which sells for >4K, Ideal about the same, and what planet are Stiebel Eltron and Nibe on with their pricing? Im not advocating removing grants at the current time, but the fact is that even if it doesn't happen in the next couple of weeks it will happen in the next few years and the industry needs to work out how it will carry on on its own two feet.
  18. I monitor it from time to time through home assistant (which solves the graphing problem) more than I do on the app. It's definitely interesting, but I'm not sure I can honestly say I have made changes to my settings as a result. That said my system worked well from day 1. If it hadn't I don't doubt the data as presented in HA would be very useful in diagnosis. It does provide handy real time information on OAT though, which has uses beyond heat pumps. I can't comment particularly definitely on accuracy. The electricity consumption appears to be good, heat delivered is definitely in the right ball park, but I can't be certain to better than perhaps 20%. I would expect temperatures to be pretty good but have no evidence to back this up.
  19. Eon next drive, but locked in Dec 2024 for 12 months so soon to be re-contracted. There current offer is not as good, but still better than octopus.
  20. Ahh. The install got put on hold and I ended up eighteen months later with a different installer who went down the heat pump cylinder route (by then I had decided definitely to replace my existing vented cylinder). Sorry
  21. 100% agreed. But few will fit auto bleeds on every radiator and @Potatoman was asking if air would find its way to the automatic bleed valves. My reply was no it won't, you may need to use in the manual bleeds on individual radiators in addition to whatever automatic bleeds you have.
  22. Only if the bleed valves are at any high points Even if the bleed valves are at the high points air can still get trapped elsewhere. I have a tall radiator downstairs, well below the auto bleed valves, which needed manual bleeding every two days for a month after my ashp installation was done. That's why radiators have bleed points!
  23. Time is another key factor. Dissolved air comes out of solution quite slowly, mine (for example) took a full month. Sometimes you need to be patient.
  24. Nearly. The loss of efficiency comes from the liklihood that cool return water is mixed with warm flow water thus reducing the flow temp to emitters relative to the ft from the heat pump. Since the flow temp to emitters governs their output, you need to increase the ft from the heat pump to compensate. The cop of a heat pump reduces with increased ft hence loss of overall cop. It an be made to work with little or no loss, but for that the water in the buffer needs to be properly stratified, which has implications for buffer design and size, and the pump rates also need to be controlled. This (it seems) almost never happens presumably because the people who know how to do it properly also know how to design out a buffer in almost all domestic situations. The typical dumpy 50l buffer is unlikely to have any material stratification.
  25. It will stop altogether if it detects flow rate too low. Mine did when the filter bunged up. BTW I suspect the mesh filter, normally fitted near the return inlet, has a fairly high pressure loss even when not bunged up. If yours is like mine a model with a larger area may well assist!
×
×