flanagaj Posted yesterday at 21:02 Posted yesterday at 21:02 I want to simplify the installation of the Radon membrane and if I can do the below, eg run the lower DPC under the inner leaf and across the cavity and then up the inner face of the outer leaf. If I can go with this approach, it completely negates me having to use pre formed door openings OR having to try and bodge it together. The only required detailing will be the 4 corners. The standard Visqueen detailing is shown below, but if you go with this approach, then you have to mess around at door openings. I just want to avoid as many taped joints as possible.
Mr Punter Posted 13 hours ago Posted 13 hours ago Why have you lapped it up the brickwork? Just leave it flat.
Russell griffiths Posted 12 hours ago Posted 12 hours ago As @Mr Punter said lay it across the full width and build up from that. if you had of brought your concrete up higher you could have just laid it flat across that.
flanagaj Posted 11 hours ago Author Posted 11 hours ago 1 hour ago, Mr Punter said: Why have you lapped it up the brickwork? Just leave it flat. Because it’s a Radon barrier and has to span the cavity
Mr Punter Posted 9 hours ago Posted 9 hours ago 1 hour ago, flanagaj said: Because it’s a Radon barrier and has to span the cavity So can't you do this?:
JohnMo Posted 9 hours ago Posted 9 hours ago Your white blocks make a nice cold bridge. Just replace with thermolite or similar and it's gone.
flanagaj Posted 5 hours ago Author Posted 5 hours ago 3 hours ago, Mr Punter said: So can't you do this?: What would that provide over and above the detail shown?
flanagaj Posted 5 hours ago Author Posted 5 hours ago 3 hours ago, JohnMo said: Your white blocks make a nice cold bridge. Just replace with thermolite or similar and it's gone. I didn’t show it, but the second course (inner leaf) is a Marmox block
Oz07 Posted 5 hours ago Posted 5 hours ago 4 minutes ago, flanagaj said: What would that provide over and above the detail shown? Zero folds
Tony L Posted 5 hours ago Posted 5 hours ago 22 minutes ago, flanagaj said: I didn’t show it, but the second course (inner leaf) is a Marmox block I'm not thinking that's wrong, but I'm interested to know if there's any reason why you made the middle white brick Marmox, rather than the lowest of the three white bricks?
Mr Punter Posted 5 hours ago Posted 5 hours ago 31 minutes ago, flanagaj said: What would that provide over and above the detail shown? The green line would be your gas membrane, laid flat with no folds or laps, supported on the slab and external walls. You can add whatever other DPCs you may need, safe in the knowledge that the gas membrane is continuous save for correctly detailed service penetrations. 1
flanagaj Posted 2 hours ago Author Posted 2 hours ago 3 hours ago, Mr Punter said: The green line would be your gas membrane, laid flat with no folds or laps, supported on the slab and external walls. You can add whatever other DPCs you may need, safe in the knowledge that the gas membrane is continuous save for correctly detailed service penetrations. That is a clever option, but I would need to protect the membrane whilst the shell is built.
flanagaj Posted 1 hour ago Author Posted 1 hour ago 3 hours ago, Tony L said: I'm not thinking that's wrong, but I'm interested to know if there's any reason why you made the middle white brick Marmox, rather than the lowest of the three white bricks? I could be wrong, but my understanding is that the marmox block simply needs to sit at the same level as the PIR insulation.
JohnMo Posted 1 hour ago Posted 1 hour ago That works, but save some money and just use Thermolites. They are in a nice dry area, so will.work well.