scottishjohn Posted July 30 Posted July 30 my problem is a strange one my cold water is not cold I,m on a bore hole and water comes to plant room into an accumulator where pressure is kept at 3.75 bar it then goes through filters + uv etc the water pipe then goes up into the space between the upper floor and the ceiling the result is my cold water is never cold I checked the ASHP pipes with a heat gun and can see a heat bloom from the ceiling but even now when the low heat is not much to heat the hot water it is still a problem my question what insulation by law if any should have been done to the pipes in that area are there laws about insulating pipes inside the house
JohnMo Posted July 30 Posted July 30 Different bits need different strategies depending on what it is. DHW piping should be insulated, it adds unwanted heat in the summer to house. You may also suffer heat loss at cylinder, think the 2m around cylinder are supposed to insulated anyway. CH piping if you are running WC most parts of the house are going to be a similar temp including voids so any heat gains are fine. If you are running cooling you may need to insulate anyway. Cold water wants to stay cold so you may need to insulate depends on routing. I have the bore hole kit outside in an insulated shed, so stays pretty cool. Pipes in-house are mostly in concrete below my floor insulation, only bit not is encased in roof insulation on its way to hot water cylinder. If your cold pipes are in the void between floors your cold water is likely to be 20 to 21 degs most the time. Insulate to death.
Nickfromwales Posted Thursday at 22:51 Posted Thursday at 22:51 Cold mains “potable” or “wholesome” water needs protecting to prevent it being early to mid 20 degrees. It’s a major health and safety risk due to legionaries disease etc. Any volume of stored potable mains will inevitably acclimatise to the immediate local ambient temp, so this is a thing you can’t avoid, it can only be slowed by insulating the pipe as well as is practicable. If the temp of the plant room housing the accumulator can be insulated then this will pay huge dividends, plus the accumulator itself should be insulated also to maximise the time taken for the local ambient to affect it. What is the temp at the accumulator location? Length of pipe feeding the house?
scottishjohn Posted Friday at 10:31 Author Posted Friday at 10:31 neither of you addressed the question I take it from that there are no regulations about insulation of pipes inside house
scottishjohn Posted Friday at 10:43 Author Posted Friday at 10:43 temp of accumulator and filters etc in plant room today with thermal temp gun 24c when i ran the tap in the kitchen it started off at 23 c then after 1min of running it went up to 30c then eventually it went down to 18c and i also checked where it comes in the house from the borehole--same temp I do have a UV on the system would that not protect from legonella ?
scottishjohn Posted Friday at 10:50 Author Posted Friday at 10:50 I think insulation is part of my problem --too much and the batteries +invertor for the solar are in there == plus washing machine and condensing dryer may be i need some positive ventilation in there? vent at bottom of wall and one at ceiling level but that would not stop it getting hot in the space between floors I suspect they did not insulate the SHP pipes to the controller and tank which is upstairs in center of house house is 22m long granite with TF built inside it
scottishjohn Posted Friday at 10:52 Author Posted Friday at 10:52 12 hours ago, Nickfromwales said: Length of pipe feeding the house? comes from a bore hole 30m up the hill behind --120m deep in solid rock all the way
Nickfromwales Posted Friday at 11:25 Posted Friday at 11:25 31 minutes ago, scottishjohn said: comes from a bore hole 30m up the hill behind --120m deep in solid rock all the way Ok. Plenty cold enough from source then. Where does this pipe first appear above ground?
scottishjohn Posted Friday at 11:38 Author Posted Friday at 11:38 10 minutes ago, Nickfromwales said: Ok. Plenty cold enough from source then. Where does this pipe first appear above ground? in the plant room picture attached
Nickfromwales Posted Friday at 11:51 Posted Friday at 11:51 All that should be heavily insulated. It’s basically stagnating and then warming up to ambient.
scottishjohn Posted Friday at 13:58 Author Posted Friday at 13:58 (edited) 2 hours ago, Nickfromwales said: All that should be heavily insulated. It’s basically stagnating and then warming up to ambient. I agree -- but i think there is another problem in the ceiling other wise why would water start at 24 00then go to 30 and then back down must be heating of uninsulated pipes in the ceiling void I think well told the builder and the only way to get at them is to drop ceiling as upstairs has stuck down floor +ufh heating as well If he won,t do it then I go to building control --as he should not have fitted all those pipes in same void with no insulation or HSE as it clearly sates cold water should be less than 20c I really did not want to do this --but needs must so insulate pipes in plant room fit 2 vents one at ceiling level one at floor and get some convection of the warm air happening in the plant room and out outside unless you have a better suggestion just shows houses built to new insulation stds can have other problems you don,t initally think of certainly if it was mains coming up through the concrete slab in kitchen --as normal and not shifting it across the ceiling space maybe 8ms from plant room with an accumulator storing it Edited Friday at 14:00 by scottishjohn
Oz07 Posted Friday at 15:36 Posted Friday at 15:36 5 hours ago, scottishjohn said: neither of you addressed the question I take it from that there are no regulations about insulation of pipes inside house I don't think there are any regs for insulating cold water pipes in domestic dwelling. I've certainly seen plenty of un insulated pipes in my time. Are you looking to claim from the plumber? I don't think they problem is avoidable if you have a tank in the house at room temperature regardless what you do with the pipes.
Oz07 Posted Friday at 15:37 Posted Friday at 15:37 4 hours ago, scottishjohn said: I think insulation is part of my problem --too much and the batteries +invertor for the solar are in there == plus washing machine and condensing dryer may be i need some positive ventilation in there? vent at bottom of wall and one at ceiling level but that would not stop it getting hot in the space between floors I suspect they did not insulate the SHP pipes to the controller and tank which is upstairs in center of house house is 22m long granite with TF built inside it Would it be possible to cool the accumulator in any way?
-rick- Posted Friday at 15:38 Posted Friday at 15:38 Not a plumber but I suspect there are water quality/plumbing standards that require water to be kept below a certain temperature. Not necessarily specifying how that is achieved.
JohnMo Posted Friday at 17:10 Posted Friday at 17:10 On 31/07/2026 at 14:58, scottishjohn said: upstairs has stuck down floor +ufh heating as well The second floor UFH will ensure the incoming water will get warm in winter also
Alan Ambrose Posted Saturday at 11:46 Posted Saturday at 11:46 (edited) I think it would be easier to concentrate on the physical problem and seeing if it could be solved easily. For reference, we have ‘temporary’ taps around the site and atm the water feels surprisingly hot for a few seconds when turned on. It’s just a few metres of pipe getting heated up by the sun. Plant rooms often get quite hot because of all the gear in there. Suggest buy yourself a few metres of the grey snap on insulation for a couple of quid, fit it neatly to all the cold supply pipes you can see and see if that helps. Does this happen all the year round or only in the summer? Edited Saturday at 11:50 by Alan Ambrose 1
Nickfromwales Posted Sunday at 21:42 Posted Sunday at 21:42 On 01/08/2026 at 12:46, Alan Ambrose said: I think it would be easier to concentrate on the physical problem and seeing if it could be solved easily. For reference, we have ‘temporary’ taps around the site and atm the water feels surprisingly hot for a few seconds when turned on. It’s just a few metres of pipe getting heated up by the sun. Plant rooms often get quite hot because of all the gear in there. Suggest buy yourself a few metres of the grey snap on insulation for a couple of quid, fit it neatly to all the cold supply pipes you can see and see if that helps. Does this happen all the year round or only in the summer? The pipe run between plant and outlet is defo getting heated by other influences, as at worst it should be tepid then cool then cold. 24° to 30° and then downwards means this is more of an instance of negligence methinks. @scottishjohn, you need to approach the builder with your concerns and intended path of HSE, and simply say you’ll accept him (re)doing the work as cost effectively as is practicable, under your immediate supervision, or he can pay for someone else to be appointed. Legally you MUST offer him the opportunity to rectify, do NOT touch a thing until you have your ducks in a row.
scottishjohn Posted Monday at 07:32 Author Posted Monday at 07:32 (edited) 9 hours ago, Nickfromwales said: The pipe run between plant and outlet is defo getting heated by other influences, as at worst it should be tepid then cool then cold. 24° to 30° and then downwards means this is more of an instance of negligence methinks. @scottishjohn, you need to approach the builder with your concerns and intended path of HSE, and simply say you’ll accept him (re)doing the work as cost effectively as is practicable, under your immediate supervision, or he can pay for someone else to be appointed. Legally you MUST offer him the opportunity to rectify, do NOT touch a thing until you have your ducks in a row. I have already emailed him and awaiting his reply I will be attending to the plant room and I will continue with this and insulate everything in there but we know that will not stop the problem till pipes are insulated in the ceiling void-both ASHP feed pipes and cold water Edited Monday at 07:36 by scottishjohn
Nickfromwales Posted Monday at 08:16 Posted Monday at 08:16 44 minutes ago, scottishjohn said: I have already emailed him and awaiting his reply I will be attending to the plant room and I will continue with this and insulate everything in there but we know that will not stop the problem till pipes are insulated in the ceiling void-both ASHP feed pipes and cold water ASHP flow and return travel with the cold mains? All uninsulated??
-rick- Posted Monday at 09:21 Posted Monday at 09:21 1 hour ago, scottishjohn said: I will be attending to the plant room and I will continue with this and insulate everything in there but we know that will not stop the problem till pipes are insulated in the ceiling void-both ASHP feed pipes and cold water Obviously it should be your builders problem to resolve. But in the interests of making it as easy as possible, have you thought about whether there is an alternative route to run a new cold water pipe? Obviously not ideal but if there is a way to run a new (insulated pipe) without as much disruption it may be worth considering.
scottishjohn Posted 7 hours ago Author Posted 7 hours ago On 03/08/2026 at 10:21, -rick- said: Obviously it should be your builders problem to resolve. But in the interests of making it as easy as possible, have you thought about whether there is an alternative route to run a new cold water pipe? Obviously not ideal but if there is a way to run a new (insulated pipe) without as much disruption it may be worth considering. not possible
scottishjohn Posted 7 hours ago Author Posted 7 hours ago (edited) On 03/08/2026 at 09:16, Nickfromwales said: ASHP flow and return travel with the cold mains? All uninsulated?? that is my guess certainly ASHP pipes not --so pretty sure no insulation on nay internal piping using a thermal camera a while ago -- i could see heat bloom from ASHP pipes in the ceiling space where they go to the hot water tank and controller upstairs i am guessing the dipshit plumbers -thought that heat lost in the house is ok and too much trouble to insulate all the pipes --which it is not no point in having individual individual thermostats on each room with programmers etc and in a big house most of the time you do not want to heat all the rooms Edited 7 hours ago by scottishjohn
Nickfromwales Posted 6 hours ago Posted 6 hours ago 1 hour ago, scottishjohn said: that is my guess certainly ASHP pipes not --so pretty sure no insulation on nay internal piping using a thermal camera a while ago -- i could see heat bloom from ASHP pipes in the ceiling space where they go to the hot water tank and controller upstairs i am guessing the dipshit plumbers -thought that heat lost in the house is ok and too much trouble to insulate all the pipes --which it is not no point in having individual individual thermostats on each room with programmers etc and in a big house most of the time you do not want to heat all the rooms Worse if you go to use cooling as they’ll condense. B Regs will mandate insulation so they defo need to come back and rectify, even more so if it’s the feeds that run very hot for heating the DHW cylinder….
scottishjohn Posted 3 hours ago Author Posted 3 hours ago 2 hours ago, Nickfromwales said: Worse if you go to use cooling as they’ll condense. B Regs will mandate insulation so they defo need to come back and rectify, even more so if it’s the feeds that run very hot for heating the DHW cylinder…. thank you -which was what i was trying to get at --they have to be insulted no reply from builder yet will give him a few more days then email him again