Gballam Posted March 15 Posted March 15 Has anyone built a wall build up like this? Any thoughts? Walls – U-value 0.12 W/m²K Internal Finish: 12.5 mm Plasterboard Service Cavity: 50 mm battened void (filled with extra mineral wool?) Airtight & VCL Layer: Pro Clima Intello with joints taped using Pro Clima Tescon Vana. Structural Frame: 140 mm timber studs. Insulation: 140 mm full-fill mineral wool cavity insulation (e.g., Knauf RS45 or Rockwool RWA45). External Sheathing: 9 mm OSB3. Breather Membrane (Frame): Protect TF200. EWI: 160 mm high-density mineral wool (e.g., Rockwool Frontrock or density-equivalent RWA45 slabs). Weather Seal: High-performance W1-rated breather membrane (e.g., Tyvek Housewrap) installed over EWI. Cavity Fixings: Thermally broken structural insulation screws (e.g., HECO Topix-Plus Therm) installed at a 60–67° angle. Screws must achieve a minimum 50 mm embedment into structural timber studs. Ventilation: Horizontal structural battens (min. 38x89 mm) + vertical counter-battens Fire Safety: Euroclass A1 non-combustible cavity barriers. External Finish: Cedral Click vertical cladding + starter/top profiles + vermin mesh.
Russell griffiths Posted March 15 Posted March 15 Why. just build a wider wall and put the insulation in that, your Ewi sounds a nightmare to install and detail. just sounds all over complicated and not needed. 2
Gballam Posted March 15 Author Posted March 15 The why is trying to avoid thermal bridging without a twin frame. The issue is the complexity!
saveasteading Posted March 15 Posted March 15 A service cavity filled with mineral wool isn't accessible any longer. Just partially fill? Your thermal bridging is through the studs but this will be calculated... it is normal. Have you a target for insulation or throwing all you can at it?
JohnMo Posted March 15 Posted March 15 Do you need the internal breather membrane? Cannot see what that does. Between studs knauf Frametherm 32, easier to install and better U value. I would do a simple twin stud, fill with frametherm 32, or blown in insulation. OSB board outside with membrane. Or 140mm structural, OSB outside with membrane, internally PIR skin over studs to achieve u value
Redbeard Posted March 15 Posted March 15 (edited) I have done something vaguely similar, but with wood fibre. Just stagger the outside and inside verticals and make it as 'fat' as you need to get your desired U value net of the timber fraction. In my case the external members were structural and the internals not so, but it can be either way round, or indeed the load can be shared. Edited March 15 by Redbeard
Gballam Posted March 15 Author Posted March 15 Thanks all, very helpful thoughts. Yes I have been wondering whether a hybrid wall of 60mm woodfibre outside studs plus the mineral wool and then pir inside studs is more achievable
JohnMo Posted March 15 Posted March 15 27 minutes ago, Gballam said: Thanks all, very helpful thoughts. Yes I have been wondering whether a hybrid wall of 60mm woodfibre outside studs plus the mineral wool and then pir inside studs is more achievable Think that 33% more complex than you need. Stud plus internal OR external, NOT both
Gballam Posted March 15 Author Posted March 15 Aiming for near-passive (and hoping to have walls around 0.13) so will need both internal and external the hybrid design
Nickfromwales Posted March 15 Posted March 15 1 hour ago, Gballam said: Thanks all, very helpful thoughts. Yes I have been wondering whether a hybrid wall of 60mm woodfibre outside studs plus the mineral wool and then pir inside studs is more achievable Go for a twin wall Larsen truss or I-beam, and lose all this unnecessary complication. PIR is a complete and total PITA to cut and fit (properly) so just go for blowing cellulose and gain the benefits of a one man insulation process (roof and walls) and also the hugely improved sound-deadening that you lose with PIR. Your initial proposal is hugely over complicated, sorry. KISS wins every time, and will get you to PH targets quickly and simply, with far less to go wrong. The biggest issue will be getting all these layers, materials, installers to do their work meticulously, which most either can’t or don’t.
Redbeard Posted March 15 Posted March 15 1 hour ago, Gballam said: Thanks all, very helpful thoughts. Yes I have been wondering whether a hybrid wall of 60mm woodfibre outside studs plus the mineral wool and then pir inside studs is more achievable If I were doing something like that I would use Pro Clima's Intello (which is vapour-closed in low temperatures but becomes slightly vapour-open as te weather warms up, allowing 'dumping' of any accumulated moisture) as VCL, not the foil on PIR, so just make the wall as thick as you need to get the U value you want without the PIR, then it could 'breathe' (a bit) both ways instead of being 'blocked off' on the inside.
JohnMo Posted March 15 Posted March 15 (edited) 30 minutes ago, Gballam said: 0.13 Or just do an ICF, stack the blocks fill with concrete, U value 0.14 with service void. Parge coat for airtight if woodcrete, no need with polystyrene blocks. Our house, 4 weeks (end Nov to Christmas, bloody freezing) 70m perimeter and average 3m tall, two of us never done it before. 2 days to parge coat internal wall. Edited March 15 by JohnMo
Russell griffiths Posted March 15 Posted March 15 (edited) 4 hours ago, Gballam said: The why is trying to avoid thermal bridging without a twin frame. The issue is the complexity! Single wall with horizontal studs on the inside lined with more insulation. or go icf, or buy the frame all done depending how much you want to do. Edited March 15 by Russell griffiths
TimberFraze Posted 6 hours ago Posted 6 hours ago Hi Gballam, Just reading this and the comments and want to put in my 2 cents. Outside to in: Breather Membrane - W1 or W2 depending on where you are 9mm OSB 140mm timber frame with 140mm 0.035R between studs 90mm PIR insulation to face = No thermal bridging, and keeps it thermally broken down to the foundation. Reflective vapour control layer Standard Service Battens OR theoretically can use a partition to save making any penetrations through the VCL but may affect sequencing! Plasterboard Gets you 0.12, keeps it simple and follows passivehouse principles. I think it would be more cost effective than going down bigger stud or other forms of timber frame construction but open to debate! Obviously will come with it's own problems. I also saw a comment about Frametherm 32 insulation, I just want to put a note on it I think it's mega expensive for the performance gain it gives. Fraze
stu w Posted 5 hours ago Posted 5 hours ago On 15/03/2026 at 08:28, Gballam said: Has anyone built a wall build up like this? Any thoughts? Walls – U-value 0.12 W/m²K Internal Finish: 12.5 mm Plasterboard Service Cavity: 50 mm battened void (filled with extra mineral wool?) Airtight & VCL Layer: Pro Clima Intello with joints taped using Pro Clima Tescon Vana. Structural Frame: 140 mm timber studs. Insulation: 140 mm full-fill mineral wool cavity insulation (e.g., Knauf RS45 or Rockwool RWA45). External Sheathing: 9 mm OSB3. Breather Membrane (Frame): Protect TF200. EWI: 160 mm high-density mineral wool (e.g., Rockwool Frontrock or density-equivalent RWA45 slabs). Weather Seal: High-performance W1-rated breather membrane (e.g., Tyvek Housewrap) installed over EWI. Cavity Fixings: Thermally broken structural insulation screws (e.g., HECO Topix-Plus Therm) installed at a 60–67° angle. Screws must achieve a minimum 50 mm embedment into structural timber studs. Ventilation: Horizontal structural battens (min. 38x89 mm) + vertical counter-battens Fire Safety: Euroclass A1 non-combustible cavity barriers. External Finish: Cedral Click vertical cladding + starter/top profiles + vermin mesh. I completed my own house in December 2025, using a very similar system to yours. For insulation, I selected Rockwool NyRock Frame Slab, combined with a thicker OSB layer to enhance structural performance. The majority of the building is finished with Hardie VL cladding so no external (EWI) system. I used the same construction approach on a house I built three years ago, which has performed faultlessly. Based on that experience, I chose to adopt the same system again for my own home. I stick build this project using kiln dried treated timber, at the point of the build the timber was at 12.8% to minimise movement