timhowes Posted 4 hours ago Posted 4 hours ago Thanks to all those who have already assisted me on these topics. We are embarking on a major renovation of an 1949 bungalow, extended through the late 1900s to dormer bedrooms. Building a new first floor with timber construction, extending ground floor a little, adding external insulation to any existing walls, new DG windows and doors throughout. South-westerly aspect without shade. Will have PV and battery storage (not got to work on planning this yet). GF heated area 148m2 FF heated area 85m2 Total vol approx 600m3 Location N Somerset, just west of Bristol I have run Jeremy's heat loss calcs as best as I can, yielding the following (with soil temp 6C, ACH 0.5, no heat recovery) Looking at UFH throughout ground floor - mainly suspended timber and will be able to add plenty of insulation, but small area (kitchen/dining) of existing concrete floor to be extended slightly. Probably FCUs upstairs, although not decided yet, with the intention of some heating if necessary (maybe not needed?) but definitely active cooling, Family of 5 with 3 kids who will be teenagers soon - I am firmly against long showers but their mother is harder to persuade. Envisaging 300L UVC emptying rather fast so considering a larger one. Have been offered plenty of high output heat pumps through MCS-certified installers, with the accompanying eyewatering costs. Trying to get my house in order to challenge them, but also want to know I'm not going to regret going smaller! Questions: I am looking at ASHPs with max ouput 8-9kW based on previous advice from this forum. However my interpretation of the above calcs is that I need to be able to modulate down towards 3kW for efficient running in the less cold months. Is this correct? I've earmarked the Vaillant aroTherm + 10kW model as one option but finding it hard to identify other models with enough modulation (mainly due to poor documentation by the manufacturers - is there an "uber sheet" with these data anywhere?!) Wunda have offered me a 2-zone UFH system for the GF for £4.4k inc VAT - 2 zones needed as, whilst most is suitable for a between-joist system, the concrete floor area needs their "rapid response" to give similar performance. I had asked them for a screed system throughout the GF and need to ascertain why they think their proposal is better. Also sounds like a lot of £ compared to what others have posted. Thoughts? System volume is 148m3 As will be evident, I've never done anything like this before and am doing as much reading as I can to defend myself against blowing a big chunk of the budget on an inappropriate heating system! Floor plans attached. Location https://maps.app.goo.gl/acCH67SJ65B4fWmJ8 TIA GAP000 - Level 0 General Arrangement Plan.pdf GAP001 - Level 1 General Arrangement Plan.pdf
JohnMo Posted 4 hours ago Posted 4 hours ago I would look at Hitachi and HiSense also for their heat pumps. Hitachi and Hisense have a sharing agreement, looking at the datasheet outputs are idenical for each model. But Hisense comes with cooling out the box, Hitachi is an additional cost. But modulation is great. Neither are that expensive either. 13 minutes ago, timhowes said: 2-zone UFH system for the GF for £4.4k inc VAT Sounds a lot. What is included in that cost
timhowes Posted 4 hours ago Author Posted 4 hours ago 130m2 heated area - mixture of their between-joist system and the "rapid response" overlay for the concrete area, with 150mm pipe centres Designed and supplied as follows: Isolation Vales with temperature gauges - pair 12 Port Manifold 16mm Pipe Actuator Valve Smart Hub V4 & Boiler Switch - 48 Zones Smart Connection Box V4 - 12 Zones V1 - Wunda Thermostat Sensor (Slim) Perimeter Strip Insulation - Overfloor (25m Roll) 20mm Overfloor EPS 400 Transitional Panel 20mm Overfloor EPS 400 Plain Panel 20mm Premium Rapid Response Main Panel 20mm Premium Rapid Response End Panel (x2) Wunda Panel Spray Adhesive Joist Insulation Main Panel (200 Micron Aluminium Coating) 16mm Wundapipe (80 metre Coil) 16mm Wundapipe (100 metre Coil) 16mm Wundapipe (120 metre Coil)
sharpener Posted 4 hours ago Posted 4 hours ago 33 minutes ago, timhowes said: I've earmarked the Vaillant aroTherm + 10kW model as one option but finding it hard to identify other models with enough modulation Vaillant FB forum has the famous "Czech" performance charts in the Files tab, shows turndown of all models (which is pretty good). The 10kW is a software limited 12, you might as well have the latter as the min o/p is the same but it would give you faster HW warmup if that is a concern.
timhowes Posted 4 hours ago Author Posted 4 hours ago 3 minutes ago, sharpener said: The 10kW is a software limited 12, you might as well have the latter as the min o/p is the same but it would give you faster HW warmup if that is a concern. Good to know - thanks for this. 4 minutes ago, sharpener said: famous "Czech" performance charts This was what led me to the aroTherm - the best data representation of any manufacturer I've seen so far. Why can't they all do this?!
SimonD Posted 3 hours ago Posted 3 hours ago 47 minutes ago, timhowes said: Have been offered plenty of high output heat pumps through MCS-certified installers, Who have you gone to? Please feel welcome to dm me if you don't want to publish the list in public - that way I can check if you've been to the sensible ones in your area. I can also point you in the direction of an organisation that can assist you in the design process who are also local but not tied to any particular installer.
SimonD Posted 3 hours ago Posted 3 hours ago 18 minutes ago, timhowes said: 130m2 heated area - mixture of their between-joist system and the "rapid response" overlay for the concrete area, with 150mm pipe centres Designed and supplied as follows: Isolation Vales with temperature gauges - pair 12 Port Manifold 16mm Pipe Actuator Valve Smart Hub V4 & Boiler Switch - 48 Zones Smart Connection Box V4 - 12 Zones V1 - Wunda Thermostat Sensor (Slim) Perimeter Strip Insulation - Overfloor (25m Roll) 20mm Overfloor EPS 400 Transitional Panel 20mm Overfloor EPS 400 Plain Panel 20mm Premium Rapid Response Main Panel 20mm Premium Rapid Response End Panel (x2) Wunda Panel Spray Adhesive Joist Insulation Main Panel (200 Micron Aluminium Coating) 16mm Wundapipe (80 metre Coil) 16mm Wundapipe (100 metre Coil) 16mm Wundapipe (120 metre Coil) Best thing to do is step back and look at the heating system as a whole which could allow you to run the system open-loop and allow the heat pump controls to modulate output as opposed to installing a load of control gumpf from the ufh people - a sensible installer would have made this point. Also, if you're thinking about engaging someone to design and install, don't hive off the ufh design to diy and then ask the installer to tack on the heat pump. You need a holistic approach here.
timhowes Posted 3 hours ago Author Posted 3 hours ago @SimonD this is all very helpful, thanks. DMing you a list now
ectoplasmosis Posted 3 hours ago Posted 3 hours ago 48 minutes ago, JohnMo said: I would look at Hitachi and HiSense also for their heat pumps. Apparently Hitachi's parts, warranty and engineer support is almost non-existent in the UK. This would make it a complete non-starter for me.
JohnMo Posted 3 hours ago Posted 3 hours ago 43 minutes ago, timhowes said: Why can't they all do this They nearly all do, you just need to search hard as they all call the files different names. Mitsubishi have a excellent data set, for actual UK models, how actuate a Czech data set is for the UK market is questionable. Especially as the data set has models not available in the UK.
timhowes Posted 3 hours ago Author Posted 3 hours ago 1 hour ago, JohnMo said: modulation is great Struggling to find a Hisense datasheet which shows modulation capabilities... Trying quite hard!
JohnMo Posted 2 hours ago Posted 2 hours ago 12 minutes ago, timhowes said: Struggling to find a Hisense datasheet which shows modulation capabilities... Trying quite hard! Its in the brochure, they state the 7 degs min out put for each model 4.4kW is 1.85kW 8kW is 2.1kW 10kW is 3.3kW etc They all do just about nameplate rating at -7 outside There is a huge technical book tha has all the details as well but I have deleted it https://solartradinguk.co.uk/wp-content/uploads/2025/01/Hi-Therma-Monobloc-brochure-2024-1.pdf
timhowes Posted 2 hours ago Author Posted 2 hours ago @JohnMo so it is... min/nom/max in top row. Thanks. It is presented differently in every brochure which I find challenging!
sharpener Posted 2 hours ago Posted 2 hours ago 1 hour ago, timhowes said: This was what led me to the aroTherm - the best data representation of any manufacturer I've seen so far. Why can't they all do this?! Glad you found them. Even Vaillant SW Field Sales Manager did not know they exist. Have no idea why they do not seem to be available in English - or even German. For others here they are https://www.facebook.com/download/367541079323119/kl-06-e2-verze-01-18012023-2564719.pdf BTW I can confirm the 12kW is extremely quiet at less than about 80% output and not exactly noisy above that. 39 minutes ago, JohnMo said: how actuate a Czech data set is for the UK market is questionable. Especially as the data set has models not available in the UK. Data seem to be accepted as accurate for the models sold in UK.
SimonD Posted 2 hours ago Posted 2 hours ago I'm not sure that the way the losses are displayed from Jeremy's heat loss sheet is the most user friendly and helpful. Personally, I always derive a W/K heat loss value from the heat loss calc which I then use to understand a what outdoor temperature the heat pump reaches minimum output. For example, if it reaches this at 13C, it may be much less of a problem than if it reaches it at 8C. Some manufacturers, like Nibe provide max and min outputs in charts (not including defrost) for all relevant outdoor temperatures whereas so many just give a figure at a defined outside air temperature and you then have to learn what it really does. 4 minutes ago, sharpener said: Data seem to be accepted as accurate for the models sold in UK. By whom? I've tried to extract the info from UK tech to no avail and won't publish some of the opinions I've heard about how to UK market is viewed from some in head office across the pond (only from people who have left to organisation so don't know how biased that is)!
JohnMo Posted 2 hours ago Posted 2 hours ago 6 minutes ago, SimonD said: By whom? By people that want it to be true? 1 1
Nickfromwales Posted 1 hour ago Posted 1 hour ago Why not Panasonic? Cools out of the box, very good units and quiet too. Done a few of them (and some Stiebel Eltron units too) and I’m very impressed for the money tbh.
SimonD Posted 1 hour ago Posted 1 hour ago 16 minutes ago, Nickfromwales said: Why not Panasonic? I was really keen on Panasonic until I saw this https://www.aircon.panasonic.eu/GB_en/happening/aquarea-hp-and-smart-control-with-tado/ I have developed an allergy to Tado 😉 Joking aside I do plan to add these to my offerings at some point soon.
timhowes Posted 1 hour ago Author Posted 1 hour ago @Nickfromwales I tried to identify a suitable Panny, say 9kW down to 3kW, but got lost with their various ranges (T-CAP etc). I would welcome any suggestions if you have a moment...
sharpener Posted 44 minutes ago Posted 44 minutes ago (edited) 1 hour ago, SimonD said: By whom? I've tried to extract the info from UK tech to no avail and won't publish some of the opinions I've heard about how to UK market is viewed from some in head office across the pond (only from people who have left to organisation so don't know how biased that is)! Well there are ppl on the FB forum who are heavily into numerical performance stuff and HA (notably Mick Wall who has published many helpful articles e.g. this) and they don't seem to have raised any big issues about the Czech tables. And many others e.g. @Dan F who is active on this forum (and the Victron forum as well) who is technically qualified and talks good sense. Of course there are also the usual contributors of misinformation and general nonsense but hopefully I have got to learn the difference for the most part. I would be interested in further detail of how the UK market is viewed by Vaillant. I can see it must be a bit odd viewed from Germany particularly the shambolic regulatory setup involving the MCS. I have also to say as an experienced electronics designer they do not help themselves. Example: the internet gateway is mostly sold in the UK with a power supply card intended to plug into a boiler not an HP, rather than the one with a 13A power brick which is more expensive and needs a power point. Since the main controller can be and is powered off the low voltage ebus it would seem obvious to do the same with the gateway, which would remove the whole compatibility problem. Also the current generation of HP products has no way of receiving s/w upgrades in the field short of swapping out the main pcb, it is now 2025 fgs. Will be interesting to see if the new range has this. Edited 29 minutes ago by sharpener Changed link to a more relevant article by Mick Wall