Hi everyone.
My query involves a ring final circuit in our lower ground floor.
The house was built in 2003 so is 16th Edition regs. The CU is a Hager split unit with six 32A MCBs with a 30mA RCD, and six 6A MCBs with the isolator switch to the far right of the box. The room has six twin sockets and as far as I am aware none are spurs; they all run around the perimeter of the room and I can identify where the ring enters/leaves the room. There have been no alterations to any sockets in the room since new.
Last week the RCD tripped the whole house and by elimination I isolated the lower ring final as the issue.The fault occurred after heavy rain here, and after exposing the socket tops I observed that box 6 was very damp with badly corroded conductors and switch connectors. I replaced the socket with new after treating the corroded cables, but still the RCD trips when the phase is energised.
From the CU I have continuity and resistence as follows... L=0.43 N=0.43 CPC=0.7; the ring length I estimate at 45 meters in 2.5/1.5mm twin and earth. On my clamp meter I show 4mA leaking through the main earth bonding leaving the board. I did not do a figure of eight test as I only wanted to establish there was no break in the cable, as we do get mice here quite regularly.
I am totally perplexed that I have continuity with correct resistence, but still the RCD trips.
Here in South Devon we can't get electricians out for love nor money, so I'm hoping someone on the forum can point me in the right direction. Once this issue is resolved I plan to upgrade the CU to RCBOs for all the power MCBs. In case anyone is wondering, I am not an electrician but do have a background in automotive electronics so feel competent enough to tackle this stuff.
Many thanks in advance.
Could you explain what you mean by 'treated the corroded cables'?
Have you double checked the terminations in the socket you replaced? They are not always in the same places for different brands.
The next step would be to split the circuit at other sockets (isolating different legs of the cables) and see if it holds.
The first thing to do with a fault like this is always always always insulation resistance testing. It solves 90% of these faults or more.
If you haven’t got a tester or don’t know how to use it properly then your going to be flailing around in the dark… possibly literally!
You can do the very slow and boring resistance testing.... Disconnect at CU completely, then test resistance between cables pairs at every socket and see where resistance is lowest. Might tell you when you are closet to problem.
As @Mattg4321 says you really need to test the resistance between cores.
Your continuity tests have proved that the copper is not broken/damaged.
However that doesn't tell you anything about whether there's a section of insulation either damaged (e.g. by rodents) or bridged (e.g. by water).
If you're only testing continuity of each core separately then the other cores are not connected to the test circuit, so even if there was a dead short somewhere the test current will flow entirely within the core you're testing and give you the continuity result you expect.
As above, insulation resistance testing is needed Live to earth and neutral to earth.  If you don't have one, buy one, or get an electrician.
Clearly there is damp where the wet socket is. It sounds likely there is a lot of damp in the cable as well as just in the socket.
That works if you have a low resistance fault. A lot, maybe even most, are not. It might be outside the scope of a low reading ohm meter/continuity meter and require an insulation resistance tester. No need to disconnect all the legs at this stage yet either.
That’s a good test, but is that with all the other MCBs off? Check that reading on each circuit by switching the MCBs on one-by-one to double check which circuit(s) the leakage is on?
Similarly, take your suspect box out of circuit temporarily by taking it out of circuit? That is, binary search until you prove to yourself exactly what circuit / box / connection / device is causing the majority of the leakage.
Edited by Alan Ambrose
Personally I wouldn't spend too long chasing that - unless you confirm that it's entirely from the suspect circuit and there are no appliances of any kind connected (including sockets with built-in usb chargers etc).
That sort of leakage would be quite normal once you have a few electronic circuits connected as they often intentionally leak to earth as part of electromagnetic interference protection circuits etc. It's nowhere near the 30mA that would be required to trip the RCD and well within the 30%-of-tripping-current safe limit whhich would be 9mA.
22 minutes ago, Nickfromwales said:
If one link wire is dead in the ring you can omit it and reduce the 32a breaker to 20a and run it as a radial.
But you are not going to find which one without an insulation tester.  Unless you have the patience of a saint and try the "disconnect one and see if it still trips" method.
That one is DIY friendly and at a price even you’d like ;)
Thanks ever so much everyone; really helpful response.
  • I cleaned the corroded cable ends (that is the end outside the plastic) back to copper using dilute hydrochloric acid and rinsing/drying. It looks like corrosion has crept up the CPC right into the flat sheathing. Assuming that's the same for the phase and neutral (and that it's very damp as well), will that be enough to allow current to leak past the plastic insulation surrounding the copper core? I have blown through the conduit between box 5 and the suspect box 6, and there is no water pooling inside.
  • The earth leakage clamp test was done with all the board energised; I thought that would indicate if there was any significant loss elsewhere.
The maximum load likely to be taken from any appliance in this particular room will never exceed 7 amps, so a 20A RCBO/MCB will be fine if I decide to convert to a radial as suggested by #FuerteStu. I'll start by isolating the run between the suspect socket 6 and socket 5; if it holds then I guess I'll be ordering a 20A MCB.
(Just as an aside, I did put 12v DC down the ring and got no voltage drop whatsoever, but I'm guessing this would not be enough voltage to expose any fault. I think a Megger uses 500v DC or something?)
Anyway, thanks again for the very positive and constructive suggestions; I'll post the progress (or not, as the case might be).
I wouldn't necessarily expect corrosion/damp within the cable sheath to cause an issue of itself - the sleeving on the phase and neutral cores should in theory be enough to insulate them from the CPC and any contamination around it. However it's possible in practice that the inner insulation is degraded or cracked (especially if the cable has tight bends and/or is old) which has allowed liquid or salts to migrate into the gap and reduce the resistance. It's also possible the hydrochloric acid has damaged it - in theory I think that's compatible with pvc but I think it depends on the exact makeup of the plastic.
I'd certainly agree that I'd start by suspecting this cable if I was fault-finding, unless I could prove it was fine.
Yeah in that case I'd ignore that, it's a very acceptable result for a complete energised installation.
Yep - faults like this will generally require a higher voltage to overcome the initial resistance of the fault. An insulation resistance test needs to be done at 250/500/1000V to give meaningful results (voltage depending on the characteristics of the circuit and whether any sensitive devices are connected).
The elephant in the room is that this is terminally ill though?
If water / moisture are a constant then this’ll keep recurring. The only cure would be to replace the twin and earth with HO5 or 7, for a long term solution, and swap the metal boxes for PVC ones.
You can buy an old style, not calibrated insulation tester second hand on the likes of ebay for not much money that would solve this quickly if intent on doing it DIY.
This is a very good point. I'd assumed as this is indoors then the source of the leak has been identified & fixed but you're right OP doesn't specifically say so.
You are right. The part of the lower ground floor where the issue lies used to be the underground garage of the old house, now converted to a habitable room. We don't have water running down the walls or anything, but the pier where the socket is set has always been damp. I am looking into fixing this once and for all with a local damp-proofing outfit.
As above. You need an insulation resistance tester or you’re just guessing really. Then having to ‘bang test’ it.
Clamping the earth is the wrong way to use an earth leakage clamp meter (assuming you have one designed for this and not just a standard clamp meter, where the resolution won’t be high enough at low currents to be useful). You need to clamp line and neutral together, mirroring what the RCD is testing.
So to conclude, the fault lay with the incoming leg of the ring that descends down the damp pier into socket 6. As #AndyScotland hinted, the cable is bent at a 90 degree angle as it enters the wall so somewhere in the two metre drop to the socket, the twin and earth has degraded over the years. I'm going to cut and terminate that leg of the ring into a safe socket until it can be disconnected at the MCB. The other leg of the ring will now be a radial protected by a 20a MCB retaining the original six sockets.
Before finishing, I just wanted member's views on regulatory compliance. I am perfectly capable of replacing the existing MCBs and single RCD with six RCBOs, but believe this is what is regarded as 'notifiable' work. As I am not a registered sparky will I need to get one to test the residual current of each RCBO and sign off the mods? Is this correct, as BS7671:2018 is not statute law, just guidelines for safe systems of design and working? An electrician has been in touch at last and I'm tempted to just give hime the job and have done with it.
Anyway, thanks again to everyone who has commented and contributed; it's been a big help.
Glad you have a way forward. The 20a option is a perfectly good ‘way out’.
If you’re the only person living there then it’s fine to deem yourself competent, but if you’ve family to consider then get a sparky in and enjoy the safety of knowing that the jobs been done to the current standard and tested accordingly.
Better safe than brown bread. It’s not much money in the grand scheme.
Glad you've found the cause and got a solution. Assuming it's 2.5mmcable a 20A radial is fine unless it's covered by insulation for any significant length?
There's a little confusion here. You're right that BS7671 is non-statutory and only represents one way of achieving compliance with the legal requirements for electrical safety.
However the requirement to notify Building Control of certain electrical work in England & Wales is statutory - it comes from regulation 12(6A) of the Building Standards Regulations 2010. BS7671 doesn't include any requirements for notifying, or any specific definition of competence.
There is however a bit of a grey area in your case : the only notifiable work defined in law is installing a new circuit, replacing a consumer unit, or circuits in a special location (bath/shower room etc). Other repairs, alterations & replacements are outside the scope of that regulation.
I'm not sure whether replacing the existing protective devices on the existing circuits without replacing the consumer unit itself would trigger that requirement (though it probably falls at least within the spirit of the law, if not the letter of it).
As @Nickfromwales says, if you're the only person there, and you are confident you have the skills to do a good job, then I suspect it's fairly unlikely you'd get caught.
Equally there are some things that can go wrong.
For starters, you will need a proper torque screwdriver to ensure that the terminations are at the right torque to avoid fire risk from damaging the cable by crimping it too tight, or arching by having it too loose.
You'll also need to ensure the new protective devices are suitable for the board (mechanically , heat dissipation between devices , etc) - e.g. from same manufacturer and same generation.
Moving from MCBS to RCBOs can also throw up various faults - e.g. from incorrect connections between neutrals from different circuits - that can be time consuming & faffy to trace especially if you don't have proper test equipment.
So depending how much the spark wants to charge, you may find there's a benefit to getting a spark to take that all on for you, in which case you will also have the right paperwork if the council ever do get involved.