James of the North Posted Thursday at 18:49 Posted Thursday at 18:49 Yo! Accoring to LoopCAD we are struggling in a couple of rooms to achieve required load with our params (flow temp, heat loss, floor covering etc.). For example, a side extension with 3 out of 4 rooms glazed floor to ceiling, and kitchen with a smaller floor area due to cabinets and penisular on 3.5 walls. I've not been able to find out much about running at 50mm pipe spacings, and I would only do it in these very limited situations (trying to avoid supplemental heating), and use regular pipe spacings in the rest of the rooms. Are there any bad effects of doing this, other than the extra cost of an extra circuit (pipe and more manifold ports)? For example heat short circuiting from the flow to the return due to the closer proximity? Floor not taking the heat as easily or quickly when so much heat presented to it? I've seen photos of UFH pipework where for limited distances, like transition runs, or around the outsides of rooms, people run pipes almost touching (just the pipe staples preventing them from touching), and not sleeved, or, at 50mm pipe spacings when using the egg crate type panels, so this suggests there aren't any 'bad effects' for the heated floor area of floor covering above? More heat in the floor due to closer spacings = more heat output into the room? Anyone any experience of 50mm pipe spacings in limited situations (even just on lenghty transition runs - can you notice a difference compare to standard pipe spacings)? Retrofit, not PH & gas boiler not HP. James the Red Engine
JohnMo Posted Thursday at 19:21 Posted Thursday at 19:21 If you need 50mm spacing I would go back to basics and see what you have done wrong. Increase flow temp, change floor coving. Are you sure you have insulation values correct?
James of the North Posted Thursday at 19:25 Author Posted Thursday at 19:25 I'm genuninely curious to know if there are any negatives other than those I outlined (cost, etc.) for 50mm spacings. Thanks
BotusBuild Posted Thursday at 19:45 Posted Thursday at 19:45 James, John's suggestion to double/triple check your workings is a sound one. How big is this room? Do you know what the heat loss is for the room? What solar gain are you going to get if three sides are glazed floor to ceiling?
Conor Posted Thursday at 19:51 Posted Thursday at 19:51 At 50mm spacing your bend radius will be really tight and tough to achieve in some places. You'll need to increase spacing to 100mm at room edges / corners to make it doable. But as above, something fundamentally wrong if you need 50mm pipe spacing. To modern standards, 200mm, or worst case 100mm, would be standard. 1
JohnMo Posted Thursday at 19:51 Posted Thursday at 19:51 You just need to look at the practicality of installing. It's been done, but by overlapping various loops, so more like a 100mm or something spacing then a second loop straddling the first. Little bit of a pain to do, but doable. But why, are you trying to flow stupid low flow temperature, that may not even be practical to run? If sounds wrong it normally is What depth of screed are you using? Our room with the most loops is fully glazed one end, 6m tall fully vaulted and we can manage on 300mm centres and we have to heat down to -9 on a regular basis.
marshian Posted Thursday at 20:12 Posted Thursday at 20:12 1 hour ago, James of the North said: Retrofit, not PH & gas boiler not HP. simple questions from me what gas boiler, what’s it min modulation rate and what flow temp are you targeting from the boiler? why am I asking this? I’m using a gas boiler on weather comp with only rads (13 with 135 litres of circuit volume) no UFH. House has a heat loss of 4kW at -2.5 deg C At 10 Deg OAT the boiler target is 23 Deg C and at -5 Deg OAT the boiler target flow temp is 36 Deg C (we don’t see that OAT very often) For all the Viessmann boilers good points it struggles to not overshoot at the 10 Deg OAT flow rate and I think a practical min is probably closer to 28 Deg C but it has a neat party trick that helps to reduce cycling so I’m comfortable with the level of cycling in the shoulder season. Boiler is a Viessmann “Heat Only” 16 kW range rated to 4.0 kW however has been set up with DHWP so RR is ignored for HW My previous boiler practical min flow temp was 45 Deg C with a 10 kW min output
James of the North Posted yesterday at 09:23 Author Posted yesterday at 09:23 13 hours ago, Conor said: At 50mm spacing your bend radius will be really tight and tough to achieve in some places. You'll need to increase spacing to 100mm at room edges / corners to make it doable. But as above, something fundamentally wrong if you need 50mm pipe spacing. To modern standards, 200mm, or worst case 100mm, would be standard. The bend radius is the same for 50mm pipe spacings on 90 degree corners, as it is for any other pipe spacing, which is the bulk of a sprial counterflow circuit. It's only in the middle you have to revert to 150mm spacing to create one or two 180 degree returns.
JohnMo Posted yesterday at 10:41 Posted yesterday at 10:41 What flow temp are you trying to achieve that needs 50mm centres?
James of the North Posted yesterday at 17:23 Author Posted yesterday at 17:23 (edited) Here's some examples of masses of transition pipes at 50mm spacings, NOT sleeved. Must result in over heated areas above 27 to 29 degrees if the flow temps are set to achieve 27 to 29 in the rooms they are going to? Is my assumption correct, that if a flow temp and flow rate for a particular circuit to achieve a floor surface temp (top of screed) of N degrees (27, 29 etc.), then bunching up a load of transition pipes together with closer spacing, will result in a higher floor surface temperature? LoopCAD doesn't seem to model this; looks like it creates an 'average' floor temp (can't see an analysis view for hot spots 🥵) What about short-circuiting from flow to returns, at what is the extremeity of the circuit (hottest part of the flow, coolest part of the return)? I can't see how the floor temperature can be controlled in these areas 🥵. Surely will lead to much higher floor surface temperature, for whatever floor covering is going above (tile or brick slips would be fine, but carpet, wood etc. Edited yesterday at 17:31 by James of the North
Mike Posted yesterday at 20:25 Posted yesterday at 20:25 2 hours ago, James of the North said: Surely will lead to much higher floor surface temperature The temperature will be limited by the water temperature supplied, so it will just reach the maximum temperature of 27 to 29 quicker - it can't go higher than that. 2 hours ago, James of the North said: What about short-circuiting from flow to returns No problem; the hot water is still being pushed through the pipes, so the floor will warm up.
JohnMo Posted yesterday at 21:20 Posted yesterday at 21:20 Depends on a number of factors, screed thickness being one. Wide pipe spacings give a ripple temperature across the floor, the closer the spacing the smaller this ripple becomes. The floor loop pipes emit heat radially, the wider the spacing the more the heat is diluted before getting to the surface where it is used to heat the room. But reducing that ripple is in the form of diminishing returns. And when running low temperature UFH cannot be felt. Examples 100mm screed, with 18mm oak floor covering for 20W/m2, on 300mm spacing you need a flow temp of 30 degs For 23W/m2 on 300mm spacing you need a flow temp of 31 degs Same conditions but 50mm centres, you drop the flow temp by about 2 degs, so 28 and 29 for the above outputs. For every m2 300mm centres has about 3.3m of pipe, while 50mm has circa 20m. Our 192m house has a loose 300mm spacing and 7 loops in total. Moving to 50mm centres would increase the number of loops to about 40, so 4 or more manifold instead of one. ASHP circulation pump would require several other pumps to supplement it. The gain in efficiency from boiler or heat pump would be spent on stupid amounts of pipe, pumps to buy and run for ever more. LoopCad does analyse the bunched pipes, our utility showed a huge overheat just by transiting pipes, I added insulation to the flow pipes the overheat went away. If you can't do the floor at 150mm centres your target parameters are wrong - increase flow temp, sort the design for your worst room first, then it is easy to sort the balance of the house, with wider spacings if needed, to get a balance output in all areas.