Two circuits for cooling?

Featured Replies

On 10/08/2025 at 08:56, -rick- said:

 

Oh now I'm confused. Am I thinking of someone else?

 

I thought you had a heat gain problem in the bedrooms even during heating season so wanted the ability to cool the bedroom while the downstairs wanted heat. After I read that I looked back at some old threads and thought I read about how to do that you had to install a second zone with a big buffer tank to give the zone enough volume to avoid cycling. Have I misunderstood something?

Haha well remembered - yes that is a problem we have in our house, but not one I've tried to solve through simultaneous ASHP heating and cooling. (Although a w2w heatpump would indeed allow pumping excess heat from the FCUs upstairs back down to the UFH downstairs)

My solution is during the heating season, the ASHP is in heating mode only (for the UFH) and the bedrooms have additional fan bringing in cool air from outdoors as needed (essentially an MVHR mega-boost mode). This air intake fan shares duct work and electronic dampers with the FCU network.

 

  • 4 weeks later...
  • Replies 79
  • Views 7.7k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Thing often missed in oversizing ASHP and then adding buffers is the huge impact on running cost. You have additional pump(s) to run, but more importantly is the ASHP cycling because just too big. If

  • Thanks Nick - that post was from 2022 and our current build - we're going again, so different house.

  • Both My opinion and will be on the threads I answer.   Is size for heating and DHW.   An over sized takes a lot to get your head round and plenty of fiddling to get it to ef

Posted Images

On 07/08/2025 at 23:25, JohnMo said:

So including DHW if 9kW is correct you need a 10kW Vaillant, but if 9kW is rounded up you could use a 7kW. Your flow temp shouldn't exceed 35, possibly lower and a 7kW puts out 8.8kW.

Screenshot_2025-08-07-22-18-00-90_40deb401b9ffe8e1df2f1cc5ba480b12.thumb.jpg.7ab5cc3f9cbe8031100db92ffab491da.jpg

 

 


We need to stop quoting/using Vaillant datasheet numbers in relation to sizing; they are peak output figures which cannot be achieved over any length of time in UK winters with frequent defrosting. 
 

There’s a reason the units are named ‘7kW’, ‘10kW’; these are roughly the sustained outputs they’re capable of under prolonged defrost conditions (providing there’s enough water volume to facilitate the defrosts). 

 

4 minutes ago, ectoplasmosis said:

There’s a reason the units are named ‘7kW’, ‘10kW’; these are roughly the sustained outputs

What is your source for said information? So we can use that instead, and what do we use for other manufacturers data?

16 minutes ago, ectoplasmosis said:

At least that is some good testing to show where Vaillant get the name plate data from, which has always been unclear. 

 

So a general in the round assumption for heat pumps - not just Vaillant.

 

ASHP are tested to European standards. Europe (not UK) is less coastal than the UK, so has a lower humidity in winter than the UK. As a result, the ASHP has less need to complete defrosts. 

 

To compensate for the difference in humidity levels at or close to design point, an ASHP designed to be installed in the UK, should be over sized by 20% (above datasheet) at design point conditions, to allow a clear margin for defrosting. This is especially important in coastal and near coastal locations.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.