Hi,
Been reading a few posts on IWI in the forum, and want to check some thoughts....
We are building an extension, and renovating the existing structure.  We are planning on adding IWI during the renovations to the ground floor (upper floor to be done in a couple of years time).
Current existing wall build up is:
  • 100 mm brick
  • 100mm filled cavity with EPS
  • 100mm concrete block, partially filled with EPS.
From reading others posts it appears that I would be better off insulating with something like mineral wool / wood fibre,  rather than using insulated plasterboard. I have modelled both quickly in Ubakus, and whilst the insulated plasterboard shows much lower moisture levels, I assume this is based off perfect fitting of it. Obviously it wont be fitted perfectly, with potential moisture entering at the top and bottom (particularly the top as upper floor not insulated for a couple of years), as well as sockets etc.
So, my proposed build up for the renovation is this below.
The thickest mineral wool build up ubaqus suggests is 50mm of wool without adding a vapor barrier. If I add a vapor barrier then I think I could increase the thickness of the insulation, as shown below. However, my gut feel is I wont be able to do the barrier well due to brining through existing socket cables etc.
To note I am removing all existing plaster from the walls and parge coating with lime as part of the renovation, so I suppose I could re-route electrics then to the service void.
Finally, I suppose this is my other option using PIR board between studs, then a service void....
Grateful for thoughts. I am sure I have misunderstood something...
Toby
Have you thought of EWI? You could consider building the extension solid and EWI-ing it, carrying the EWI round, at the same or lesser thickness, to the main house. Given the choice between EWI and IWI I would usually choose EWI.
Be cautious of Ubakus. It's imperfect and shows a snapshot, typically of -5 outside. Unless you live in Greenland that isn't a fair representation of the lightly seasonal behaviour of the wall. Lightly in the UK the weather will be warmer 360 days of the year.
No need to remove the existing plaster. Just patch up the holes and make sure anything at a penetration is sealed in a manor that won't crach with slight movement, tapes airtight paints and silicone are all fine.
There's so much nonsence talked about vapour barriers. It really is almost nothing compared to leaks casued by airtightness.
Concentrate on great airtightness, add mechanical ventialtion and you can get away with as much internal insulation as you like proviced it's not vapour impermeable like PIR.
Don't do this. Moisture will get stuck behind the boards.
Cool. Assumed as much. Assume that having the boards run continuously, then studding in front is slightly better, but still not great.
Thanks. I'll look properly with WUFI at some point. Good to know the limitations.
26 minutes ago, Iceverge said:
Concentrate on great airtightness, add mechanical ventilation and you can get away with as much internal insulation as you like provided it's not vapour impermeable like PIR.
Super. That's basically my plan. MVHR is planned, just playing with CFD to work out flow etc.
Computational flow dynamics?!
Yup. Complete overkill, but interesting. Takes about an hour to model a house, and then 20 min per run.
Been playing with either optimising age of air in the house (low), or creating longest flows through house. Obviously whilst ensuring coverage. Not sure what's best. But, not really needed to just a play thing.
Post is here on it:
Yeah it's interesting alright.
Out of interest can you accurately model an air leak?
For instance a badly sealing patio door with a 1mm gap over the height and a corresponding rattled sliding sash window on the opposite face of a building in say 10m/s or wind?
I'm sure you could. 2 different approaches:
Estimate and simplify: just add a new source and exhaust on opposite sides of the building, and add estimated flow in and out at each point.
External model: model the outside of the building, and see how much air travels through. Bit harder as you have to do temperature as well. However simscale (the platform) I have been using does do thermal modelling with airflow so I'm sure it's possible.
Maybe I’m just a renegade, but when it comes to IWI - I’m usually of the opinion of don’t bother. Just make the sure the emitters are sized for 40c or less (ideally 35c) flow temperature on an ASHP and get the benefits there rather than potentially causing interstitial condensation issues with IWI. Much less risk and still high comfort with low energy inputs.
Hmmm, controversial.
I like the idea though as it solves so many problems. But, going to cost a ton in energy, depending on the exact construction.
I have to say, id not actually considered that option on my house. 🤔
I'm not so sure it's going to cost a ton in energy and can in fact be less. This is the Valliant Arotherm Plus table, which is probably there or there abouts a good approximation for most heat pumps.
 How to Measure Vaillant Arotherm COP
If say, I've got a property thats got a annual usage of say 10,000kWh of heating requirements which roughly approximates to a heat loss of 4kW at design outdoor temp (10,000 / 2500 degree days) and I run it at a 'bog standard' 55c flow , it gives a SCOP of 3.06, which would use approx 3268kWh/year elec.
If I insulated the same property, and knocked of 1kW of heat loss of design temp (so now it's 3kW, 25% reduction of overall heat loss) by using IWI - that would be approx 7500kWh annually heat demand, and at the 55c flow temp would mean an annual use of approx 2,450 kWh / year.
However, if i did nothing to the fabric, but instead upgraded the heating system to run at 35c flow at the outdoor design temp, that would give me a SCOP of 4.48, which would mean an annual electricity use of (10000/4.48) = 2,232 kWh / year.
Yeah, at same time I'm installing UFH with lots of insulation below. Flow temp at -2 would be 30degrees (ISH). Emitters are too small upstairs for open flow system, so planning on replacing them in 2-3 years then and putting in a heat pump then. For now will mix down the flow for the UFH.
Well, i was actually planning on retaining the oil boiler, but, i know how much that costs, Exactly. 1700 litres per year. (thats heating and hot water) So if we assume 70% efficiency, that circa 2428kWh / year.
Having just filled my tank this week at 56p, lets use 60p. 60p +5% vat is 63p. 1700 x 63p is £1071 PA.
Ive turned the flow temps down, but ive concluded after the cold spell, i can turn it down further.
Its clear that NO insulation project beyond the roof (already done) is remotely financially viable, especially if one uses the 15 year payback rule as per building regs.
Im currently leaning towards your idea. Especially as doing it properly, and involving building control brings a number of additional costs down on me, further excarbating its unviability.
I will, however, fit triple glazed windows for comfort and weather proofing reasons, and install UFH in the existing uninsulated floor. The windows in particular should yield a useful improvement as theres quite a lot of them.
Adding an ASHP, even if the running costs were similar, still costs me the capex for no tangible improvment of any sort. Yes, oil prices can go up as well as down, but electricity is a one way bet, up.
I'm not so sure on electricity being a one-way bet, unless all you're thinking about its price cap/fixed tariffs. Taking Octopus agile as the most extreme example of the smart tariffs, it's clear that the average price is in the 15-18 p/kWh range if you can avoid lots of consumption between 4-7pm. Given that a HP would run low and slow all day, the vast majority would be at these averages (you could also do a setback during the 4-7pm peak).
There are numerous other smart tariffs, each with their own pros and cons but they usually mean there are bargains to be had if you want to take them.
Im sufficently comvinced electricity prices can only go up, that everything i do and plan is based around that.
The politics and ideolgy in play virtually gurantees it. Accept of course, that things can change.
  • 1 month later...
Circling back to this. One final thing I am confused / not sure about:
My current plan after advice is to keep the existing plaster for airtightness, adding airtight paint at top and bottom where it is missing / between floors, and tape round windows. Then add mineral wool with no vapour barrier. Material profile below (not airgap size / service cavity size TBC).
However, from reading others posts this may have air convection losses with air travelling up in front of the mineral wool as I am not planning to install a vapour barrier / membrane in front of the insulation. Are the losses going to be significant? Or is this not really an issue.
This resource suggests I should avoid doing what I am doing: https://www.eurima.org/uploads/files/modules/articles/1607345579_DEF_2020_eurima_howtoinstall.pdf
My easy alternative is just to remove the air gap as shown below. But that means electricians have more of a pain running cables / boxes etc, and likely require thicker cables.
Thoughts appreciated!
Not an issue. It's airtightness to the outside that is important to avoid.
That timber frame is going to be rather spindly. You'd do better to use metal studs. See my comments in this interesting (but meandering) thread:
Agreed - actual plan is either 63mm CLS or metal c / I stud. Just drew it badly as 2 bits on the air gap drawing, and didn't correct the non air gap one.
For awareness: Done some quick u-value calcs. Using metal studs looks to be worse than wood studs due to thermal bridging.
0.2 vs 0.19
True, but only by a very small amount
For example, with a room 2.4m high, vertical studs at an average of 400mm centres, plus sole and head plates and (for the timber only) one central noggin, then
- for timber we have 5.5 linear metres of timber / 2.4m high x 50mm thick = 0.115m² timber / m² wall (a 11.5% timber thermal bridge)
- for steel we have 4.5 linear metres of steel / 2.4m high x 0.5mm thick = 0.001m² steel / m2 wall (a 0.1% steel thermal bridge)
Sticking those figures into my u-Value calculator for IWI on a solid wall, assuming 100mm Rockwool and that those timbers are 50x75mm, we get (timber on the left with λ 0.130 W/mK, steel on the right with λ 50 W/mK )
i.e. the difference in U-values is in favour of timber, but only in the 3rd decimal place. You could improve on that by using 38 x 75 timber studs, but the difference is still small (U-value 0.338).
BTW, I wouldn't advise putting metal studs anywhere close to the face of the wall due to the higher condensation risk, whereas with timber you could, if you're short of space.
The much bigger thermal bridge will be any internal walls that join the external wall. Ideally you'd insulate them for the first metre to reduce that, though that isn't always practicable or visually attractive.
Edited by Mike
Here's my Ubaqus calcs, including a batten (wrongly sized) for metal.
Metal first
Then wood. Sizes based around 40*63 CLS.
Also annoyingly discovered my existing cavity is 50mm, not 100mm, and the existing insulation in there isn't in great shape.
I guess they're making some different assumptions - or maybe not taking into room height, sole plates and the like - difficult to know.
Anyway here's the same (excepting some small difference in material densities and the like) based on my assumptions above and using the BRE U-value calculator. As you can see, there's very little difference between them: