JohnMo Posted December 21, 2025 Posted December 21, 2025 5 minutes ago, marshian said: see no benefit to a higher DT at the expense of increase cycling but I maybe missing something Me neither, every start equals wasted heat out the flue and stabilising metal work temperature, instead of real work heating the house. Long runs equal efficient use of gas.
Gus Potter Posted December 22, 2025 Posted December 22, 2025 5 hours ago, marshian said: The house didn't overheat but I can't see the point of increasing the level of cycling for a higher DT Did anyone open doors in the house, go out and get mucky and need a shower, was it a windy day or not, have you moved the furniture about or got a new sofa. Nice idea but at my end it's just like a theoretical, like structural design model, it's there to inform, and only that.
SimonD Posted December 22, 2025 Posted December 22, 2025 14 hours ago, marshian said: I'd probably agree based on his content However today I've tried to get a wider DT (I manged to get it to just over 10 by reducing pump speed and lowering the flow rates thro the rads) and whilst the boiler managed the situation it did it by increasing the cycling and shortening the burn times (Flow temp 36 - return temp 26) The house didn't overheat but I can't see the point of increasing the level of cycling for a higher DT I suppose the fundamental question is whether the DT in a heating system actually matters if the system is running efficiently, producing and distributing the required heat and not causing excess wear and tear, or noise in the system. I'm actually trying to find the engineering origins of delta T 20 in the first place, or even Delta T 11 and I don't seem to be able to find a specific engineering reason why this has to be. It seems more like a hereditary thing that has been passed down from boilers of old. In the imperial view the maths was simplified to using calcs based on 10,000 btu factor - divide the btu by 10,000 give you the flow rate in gallons per minute at delta T of 20 degrees F which is 11C. There are some boilers, like the Ideal Logic that specifically ask for DT 11 in commissioning. Cycling in an of itself is not necessarily a bad thing - short cycling yes. I read a paper a while ago that showed that 6 cycles per hour was not detrimental to the efficiency of the test system, but obviously systems vary greatly. There was a minimum burn time given where I recall something like 7 minutes but I could be wrong here as just like you I think it;s sensible to just aim for a long burn time as you can achieve. And as you'll already know the overall efficiency of the system isn't just down to the cycles, but also pressure drop, flow rates etc. so it's all just a balance of these. Like on my system, I generally have a DT of about 2-3C, even though emitters are all balanced to about 5. My system is currently showing a SCOP of 6.6 for the last 2 months including DHW - seems implausible and surprising so I need to dig deeper to confirm. I'm interested in whether you did a gas rate to compare gas usage between the two set up?
marshian Posted December 22, 2025 Author Posted December 22, 2025 7 minutes ago, SimonD said: I'm interested in whether you did a gas rate to compare gas usage between the two set up? At a DT of 6 Deg at the boiler for the period before the change usage was 2.0 kWh (OAT was 10 Deg) Boiler burning once per hour - Boiler at start fires at 58% and then over the the 90 secs it slowly modulates down before settling on the min output of 10.8% for the rest of the cycle. At a DT of 11 Deg at the boiler for the period after the change usage was the 2.2 kWh (OAT was still 10 Deg) But the boiler was cycling 3 times in an hour (I think the additional gas used was as a result of the more frequent initial fires when for the first 90 sec it fires at 58% and then over the the 90 secs it slowly modulates down with the higher target temp the modulation stayed at a slightly higher rate for longer before settling on the min output of 10.8% for the rest of the cycle. I actually learnt something from the exercise (or rather remembered previous boiler behaviour) sometimes it helps to write down my thoughts. So my heating circuit is pretty close to 130 Litres with all rads open with a flow rate of 9 litres per min it takes 15 mins for the return water to start to rise and the boiler flow temp starts to increase until the over temp point is reached At WC Flow temps the boiler allows an overshoot of the target temp of 4 Deg C Target flow temp is 27 Deg C but the boiler runs until the flow temp hits 31 deg C (Basically extending the burn length) When the burn is finished the circuit cools down to around 4 deg below the target so 23 Deg C (this takes around 20 mins ish) With a higher flow temp and the same return (so a wider DT) and a slower flow rate 3 lires/min the return water stays fairly low and as the boiler is targeting a higher flow temp it runs a little harder for longer. The time it takes for the return temp to drop to the restart point is much quicker - I think possibly because the warmer water never gets back to the boiler during the burn period (Typically the restart temp point was reached in 10 mins) I wouldn't call it short cycling and at 3 cycles per hour it's still much lower than 6 cycles per hour limit
marshian Posted December 22, 2025 Author Posted December 22, 2025 15 hours ago, JohnMo said: Me neither, every start equals wasted heat out the flue and stabilising metal work temperature, instead of real work heating the house. Long runs equal efficient use of gas. My thoughts exactly - with an open system every rad getting the correct flow rate to meet the heat loss of the rooms I wasn't sure why a higher DT was going to drive any more efficiency.
SimonD Posted December 22, 2025 Posted December 22, 2025 1 hour ago, marshian said: At a DT of 6 Deg at the boiler for the period before the change usage was 2.0 kWh (OAT was 10 Deg) Boiler burning once per hour - Boiler at start fires at 58% and then over the the 90 secs it slowly modulates down before settling on the min output of 10.8% for the rest of the cycle. At a DT of 11 Deg at the boiler for the period after the change usage was the 2.2 kWh (OAT was still 10 Deg) But the boiler was cycling 3 times in an hour (I think the additional gas used was as a result of the more frequent initial fires when for the first 90 sec it fires at 58% and then over the the 90 secs it slowly modulates down with the higher target temp the modulation stayed at a slightly higher rate for longer before settling on the min output of 10.8% for the rest of the cycle. I actually learnt something from the exercise (or rather remembered previous boiler behaviour) sometimes it helps to write down my thoughts. So my heating circuit is pretty close to 130 Litres with all rads open with a flow rate of 9 litres per min it takes 15 mins for the return water to start to rise and the boiler flow temp starts to increase until the over temp point is reached At WC Flow temps the boiler allows an overshoot of the target temp of 4 Deg C Target flow temp is 27 Deg C but the boiler runs until the flow temp hits 31 deg C (Basically extending the burn length) When the burn is finished the circuit cools down to around 4 deg below the target so 23 Deg C (this takes around 20 mins ish) With a higher flow temp and the same return (so a wider DT) and a slower flow rate 3 lires/min the return water stays fairly low and as the boiler is targeting a higher flow temp it runs a little harder for longer. The time it takes for the return temp to drop to the restart point is much quicker - I think possibly because the warmer water never gets back to the boiler during the burn period (Typically the restart temp point was reached in 10 mins) I wouldn't call it short cycling and at 3 cycles per hour it's still much lower than 6 cycles per hour limit It would be interesting to see any difference in colder temperatures with greater load on the system, but extrapolationg that 10% over a heating system would be significant. What was the rationale for suggesting a higher DT to begin with?
marshian Posted December 22, 2025 Author Posted December 22, 2025 9 minutes ago, SimonD said: It would be interesting to see any difference in colder temperatures with greater load on the system, but extrapolationg that 10% over a heating system would be significant. I think at colder temps it would have been less of an issue but with current set up this isn't an issue either. Fundamentally the boiler "burn" time just increases as it gets colder outside and the "coast" period gets shorter - it still pretty much cycles once per hour - length of the burn and coast periods just change. 9 minutes ago, SimonD said: What was the rationale for suggesting a higher DT to begin with? He'd read some research by Viessmann indicating that a higher DT was better for condensing efficiency. He worked out my flow rate was 3 times what the house needed!!
JohnMo Posted December 22, 2025 Posted December 22, 2025 22 minutes ago, marshian said: higher DT was better for condensing efficiency. That really depends on your starting point. There gets a point where return temp doesn't really get much lower, especially with WC when heating at 10 degs outside. Return temp can never drop below room ambient, even if it got to ambient, rads would be huge. 1 hour ago, marshian said: When the burn is finished the circuit cools down to around 4 deg below the target so 23 Deg C (this takes around 20 mins ish) So practically you are at min return temp already. Getting a bigger dT is just increasing flow temp for no reason. If you lowered your return temp any more, your 4 degrees delta for restart would never be reached or take too long.
marshian Posted December 22, 2025 Author Posted December 22, 2025 Just did some quick an dirty calculations on burn time v HDD ranges At HDD between 0 and 4.9 Boiler runs for 19% of the time so 11 mins in every hour (Sample 10 Days) (in reality it runs for 20 mins in two hours) Between 5 and 9.9 Boiler runs for 35% of the time so 21 mins in every hour (Sample 24 Days) Between 10 and 14.9 Boiler runs for 56% of the time so 33 mins in every hour (Sample 14 Days) Between 15 to 20 Boiler runs for 69% of the time so 40 mins in every hour (Sample 2 Days)
marshian Posted December 22, 2025 Author Posted December 22, 2025 14 minutes ago, JohnMo said: That really depends on your starting point. There gets a point where return temp doesn't really get much lower, especially with WC when heating at 10 degs outside. Return temp can never drop below room ambient, even if it got to ambient, rads would be huge. Exactly my starting point is pretty low already - my flow temps are only good when I'm heating 24/7 - I can get away with a very small set back but the house does need a little solar gain to recover 14 minutes ago, JohnMo said: So practically you are at min return temp already. Getting a bigger dT is just increasing flow temp for no reason. If you lowered your return temp any more, your 4 degrees delta for restart would never be reached or take too long. I think it might heat for longer if the boiler responded correctly to being range rated but as it seems to hate being range rated I'm not going to try any more to work with a higher DT at the boiler. House is a comfortable temp all the time so it works as it is System Noise since I fitted the pressure independant TRV bodies is super quiet Boiler doesn't seem to be unhappy with a higher flow rate and a 6 deg DT
marshian Posted December 26, 2025 Author Posted December 26, 2025 Well for the last three days the boiler has been a very naughty little pixie (Note - It is not range rated at all) Despite falling outside temps the cycles per day have steadily increased - the cycle lengths have shortened Date - No' Cycles - Avg Cycle Length 23/12 - 27 - 21.9 mins 24/12 - 32 - 34 mins 25/12 - 34 - 22.7 mins Boiler behaviour is basically intitial purge and burn up to 58% and then modulate down to 10.8% - it'll sit there for a while before starting to ramp up to 25 -35% even tho the flow temp is already at the WC setting - it'll hit temps of 4 or 5 deg higher than the target temp before shutting down - the return temp would then drive a restart 10 mins later. Once the boiler gets into this spiral of increased cycles with shorter burns it's always defeated my efforts to get it back in line but I don't always have the time to try different things. Normally it goes away with a sudden change in outside temps - either a warmer day or a cooler day. Yesterday I took the boiler off weather compensation mode and set it to a fixed temp setting - boiler did the same thing, I range rated it to minimum - boiler ignored the RR'ing and continued to randomly ramp up. I've powered the boiler down - several times - made no difference I set it back to Weather Compensated flow temps - still the same In the end I turned the whole system off for an hour and then restarted it late yesterday evening. Overnight normal behavior is resumed...... It hasn't missed a beat all day As of 16:30 today Date - No' Cycles - Avg Cycle Length 26/12 - 15 - 40 mins Should end the day at 22 or 23 cycles (one of those would have been HW) Which is exactly as it should be. So I think it's time to schedule some stops into it's activities as opposed to an overnight setback temp My Wiser controller isn't currently linked to the boiler (it has a link wire providing power to both perm live and switched live but a single core cable from the Wiser Hub will fix that and then I'll schedule two hours of downtime for the boiler 1 hour overnight and 1 hour in the daytime I appreciate that the above sounds a bit mental for a WC system but I'm not always at home to see and hear it ramp up but as the Boiler App provides me the total number of hours run and the number of boiler starts I've been noting down the readings every day at the same time so I can see when it's either cycling more than normal or cycle length is shorter than normal
John Carroll Posted December 26, 2025 Posted December 26, 2025 (edited) From some horse's mouth re cycling and boiler efficiency degradation. Edited December 26, 2025 by John Carroll
marshian Posted December 26, 2025 Author Posted December 26, 2025 14 minutes ago, John Carroll said: From some horse's mouth re cycling and boiler efficiency degradation. Seen that before - my take away is that above 60 mins cycle time there is no efficency degradation - anything below that there is and the shorter the cycle the greater the eff loss
JohnMo Posted December 26, 2025 Posted December 26, 2025 Just now, marshian said: Seen that before - my take away is that above 60 mins cycle time there is no efficency degradation - anything below that there is and the shorter the cycle the greater the eff loss Definitely found that with mine, certainly once you get cycle times below about 10 mins, you may as well give up.
marshian Posted Monday at 22:35 Author Posted Monday at 22:35 OAT overnight -4.4 Deg C highest temp in the day -0.2 Deg C but it wasn't there for long All internal room temps held nice and stable Boiler ran from Midnight to just before 10am with one burn (it finished that burn just before the HW cycle was scheduled probably due to OAT warming up or the modulation blips threw the flow temp over target. Avg energy usage for that period 3.81 kWh That's quite impressive considering the modulation hiccups it has on a regular basis Looking like my heat loss calcs are a little more than actual ~4.25 kWh @ -2.5 OAT From my Octopus account Gas usage over the 24 hr period Overall the whole day saw the boiler do 7 cycles (normal is 20 to 24) Bloody modulation blips annoy me still..............
John Carroll Posted Monday at 23:14 Posted Monday at 23:14 31 minutes ago, marshian said: OAT overnight -4.4 Deg C highest temp in the day -0.2 Deg C but it wasn't there for long All internal room temps held nice and stable Boiler ran from Midnight to just before 10am with one burn (it finished that burn just before the HW cycle was scheduled probably due to OAT warming up or the modulation blips threw the flow temp over target. Avg energy usage for that period 3.81 kWh That's quite impressive considering the modulation hiccups it has on a regular basis Looking like my heat loss calcs are a little more than actual ~4.25 kWh @ -2.5 OAT From my Octopus account Gas usage over the 24 hr period Overall the whole day saw the boiler do 7 cycles (normal is 20 to 24) Bloody modulation blips annoy me still.............. If you ran from midnight to 10 AM, 10hrs, with a energy consumption of 3.81kWh then the average heat demand/boiler output was only 0.381kW, if the average power consumption was 3.81kW then the 10hr energy consumption was 38.1kWh.
marshian Posted Monday at 23:29 Author Posted Monday at 23:29 13 minutes ago, John Carroll said: If you ran from midnight to 10 AM, 10hrs, with a energy consumption of 3.81kWh then the average heat demand/boiler output was only 0.381kW, if the average power consumption was 3.81kW then the 10hr energy consumption was 38.1kWh. Avg energy consumption was 3.81 kWh Total Consumption was 38.1 kWh (38.1 divided by 10 hrs) 1
marshian Posted Tuesday at 22:08 Author Posted Tuesday at 22:08 I'm debating upgrading the two bathroom rads They are verticals - I purchased them in 2023 when I was still using the previous glow worm boiler that couldn't cope with a flow temp below 45 and I had to fit aftermarket diverters to make them work properly (picture below was from a thread on rubbish quality rads) Last winter I was transitioning from scheduled heating at higher temps to 24/7 with weather compensation so the bathroom temps were a lot warmer Now I've been running flow temps in the winter of low to mid 30's the bathrooms only reach 21 deg C - personally I find that OK but Mrs Alien feels that they need to be warmer (she does however like a long bath. They are rated at 0.89 kW at T50 - heat loss of the bathrooms is pretty much identical at 220 w What I'm trying to get my head round is how much larger a rad I need to get to a target of 23 Deg C with my current flow temps (I know I can get a double version of the on I have and Mrs Alien is happy with the asthetics.............. The current rads wouldn't go to waste as one could replace a towel rail rad in downstairs toilet and another in the utility room (both the towel rails used to be in the bathrooms but couldn't get the rooms to temp at 45 deg flow temps so were relocated to replace 1980's single panel single convectors rads rather than wasted) The utility room in particular has additional heat sources, tumble drier, Freezer, Fridge and washing machine so needs very little additional heat I might ask ChatGPT to see if it can work out what wattage I need to hit 23 seeing as that's the current trend for everything PS No the rooms wouldn't be continually heated to 23 - I'd manage the rooms temps with a setback when not bathing!!!
SimonD Posted Tuesday at 22:32 Posted Tuesday at 22:32 (edited) 25 minutes ago, marshian said: What I'm trying to get my head round is how much larger a rad I need to get to a target of 23 Deg C with my current flow temps (I know I can get a double version of the on I have and Mrs Alien is happy with the asthetics.............. With a flow return 35/30 something like DT50 output of 1985. Have a look and play with the attached spreadsheet. What I've generally found with radiators is that as soon as you get into the 35 and below flow temp and DT5 the sizes start to get quite ridiculous, especially with warmer rooms - e.g. with this one the conversion factor is 0.115 bathroom rad size estimate.ods Edited Tuesday at 22:35 by SimonD
marshian Posted Tuesday at 23:07 Author Posted Tuesday at 23:07 11 minutes ago, SimonD said: With a flow return 35/30 something like DT50 output of 1985. Have a look and play with the attached spreadsheet. What I've generally found with radiators is that as soon as you get into the 35 and below flow temp and DT5 the sizes start to get quite ridiculous, especially with warmer rooms - e.g. with this one the conversion factor is 0.115 bathroom rad size estimate.ods 17.46 kB · 1 download Hmm that's interesting - Thank you A double version of what I currently have 1600 x 472 has an claimed output of 1579 w I could easily increase the height to 1800 x 472 and that has a claimed output of 1750 w It seems neither will get me to target (closer but no cigar as they say)
JohnMo Posted 23 hours ago Posted 23 hours ago One of these? https://coolenergyshop.com/products/cool-energy-reverso-towel-rail-water-fan-coil-ce-bt400?srsltid=AfmBOooq7706CGmIshZFQdCuvbdMxRj_pSnjyrd_Yw3GQiz-wMRnHEQj