JohnMo Posted August 9 Posted August 9 A PHE need approx 1/3 to 1/2 the area of a normal cylinder coil to do the same job. Mainly due to the turbulent floe within the phe compared to almost static flow in the cylinder. When I was doing hybrid heating against a 3m² coil I was heating cylinder to 50, it would overshoot to 52. But boiler flow temp never went above 55. 1
marshian Posted August 9 Author Posted August 9 54 minutes ago, JohnMo said: A PHE need approx 1/3 to 1/2 the area of a normal cylinder coil to do the same job. Mainly due to the turbulent floe within the phe compared to almost static flow in the cylinder. When I was doing hybrid heating against a 3m² coil I was heating cylinder to 50, it would overshoot to 52. But boiler flow temp never went above 55. This is exactly my aim - minimal overshoot at the top of the tank - whole cyl heated to almost same temp at as low a flow temp as I can get away with in one burn cycle within the shortest time frame (ideally under 30 mins) If I can achieve that with current 13 year old copper tank (where I know my losses are still higher than a modern tank) then subsequent replacement of the tank for a more modern jacketed tank is hopefully only going to reduce the static losses and the efficiency of the HW heating isn’t going to change for the worse.
JohnMo Posted August 9 Posted August 9 5 minutes ago, marshian said: under 30 mins I was doing 210L in that time frame
marshian Posted August 9 Author Posted August 9 6 minutes ago, JohnMo said: I was doing 210L in that time frame Blimey!!!
marshian Posted August 9 Author Posted August 9 In other news Boiler had it's first service Gas turned off and disconnected from burner All electrical connections to burner and ignition removed Burner came out and it and the ignition electrode were cleaned Heating coil scrubbed with plastic spinny brush on a drill Burner re-fitted Condensate trap removed - emptied - cleaned and replaced (refilled with water) All removed connections checked - he found a loose/poor connection on the outside temp sensor so he cut back and re-did it. Boiler fired up and he repeated all the commissioning gas checks (hi and low flue gases) Boiler wasn't quite 1 year old and from arrival to leaving it was about 75 mins and £72 with the vat (he did say his service work is normally busiest in Sept and Oct and right now it’s fairly quiet for anything except new installs, mainly ASHP because of BUS grants) but I had the boiler purchased & fitted in July for the same reason I want any servicing to be outside the busy period. Scores on the doors from the boiler stats for one year Heating Demand Hours 4117 (171 days - I was initially heating to schedule and only moved to 24/7 in Dec 2024) Burner Hours 1917 Burner Starts 3965 Hours on CH 1683 Hours on HW 234 Average Cycles per day 11 (Summer HW process has driven down the average) Average Boiler Cycles per day in winter heating period 22
JohnMo Posted August 9 Posted August 9 Just found a trend I posted on another thread For clarity the boiler and heat pump were running, the boiler sat behind a plate exchanger and added heat to the ASHP flow. ASHP on its own takes nearly twice as long to heat cylinder. 1
John Carroll Posted August 9 Posted August 9 (edited) 5 hours ago, marshian said: Ideal world I’d like to achieve flow temp of less than 55 deg C and a target tank temp of 50 deg C with 115 litres of water at 25 deg C heated in a maximum of 30 mins max with one boiler cycle (ie it fires once and runs till stat satisfied - not cycle several times to achieve the target) In that case above, then a B8X20, almost 0.5m2, will output a minimum of 15kW with boiler flow/return temps of 55C/40C at a boiler flowrate of only 14.5LPM/0.87M3/hr & secondary side inlet/outlet temps of 25C/50C at a flowrate of 8.7LPM/0.52M3/hr, to heat 115L from 25C to 50C in 25 minutes assuming the cylinder stat is located just above the cylinder outlet to the PHEX inlet. Edited August 9 by John Carroll
marshian Posted September 18 Author Posted September 18 Last year at the start of the heating season I was running scheduled heating and manually setting flow temps. I transitioned to full WC flow temps during Dec moving to 23.5/7 heating (0.5 is HW recharge) and refined the curve in Jan, Feb and Mar with a really small tweak in Apr to fix overheats on warmer days (so bottom of the curve stuff). This year I used the same WC setting I was using at the end of the heating season Comparison of kWh/HDD (based on 16.5 Deg C base line) for first 6 days of this house heating season Day Last year This year Day 1 2.3 0.6 Day 2 4.9 1.8 Day 3 3.5 4.1 Day 4 2.7 2.0 Day 5 5.5 2.4 Day 6 7.6 2.3 Avg 4.4 2.2
marshian Posted October 13 Author Posted October 13 All of this post is related to CH only - not HW OK since I've had this boiler installed it's always had a little niggle where even range rated down to min (19 out of 100 so should be 3.2 kW but is actually realistically 4.0 kW due to low flow temps I'm running) it occasionally ramps up to 20% to 30% just before shutting down or even sometimes in the middle of a burn cycle resulting in an early shut down for over temp.... It's definitely worse on warmer days. If I'm in the kitchen and the boiler is on a burn cycle I can hear the tone change as it ramps up. Viessmann replaced both Main Board and WC Temp Sensor in March this year to eliminate those as a reason for the behaviour even though I wasn't convinced by this action. It improved it enough that I didn't notice it happening so much but it definitely still happened. I've tried to understand what is driving this issue but not been able to (so I've actually put it down to a "characteristic" and recently I increased the range rating to 30 out of 100 (roughly 6 kW) - logic being the boiler is ignoring it anyway so might as well give a bit more head room back Strangely and I hadn't heard it do it since - then on Sat it did it again and then again on the next cycle. I went and checked the circulation pump - I'm running it at 0.5m3/hr on CH and 0.6m3/hr on HW and the pump was 0.4m3/hr flashing with 0.5m3/hr a little lower than normal but all 4 of the rads where TRV's can and do intervene were closed. (Difference in flow rate is accounted by the lack of resistance thro the coil as opposed to 13 rads with flow controls/restrictors fitted to all of them) I bumped the pump speed from 1 to 2 and it was rock solid on 0.6m3/hr It didn't do it for the next two cycles I put the pump back down to 1 and it did it on the next cycle. I went back to the manual - I'd made the assumption that the boiler flow rate requirement would be at peak output and running a 16kW boiler range rated to 6 kW I could comfortably run at 0.4 to 0.5 m3/Hr I dislike system noise so really want to run the pump on the slowest speed but it looks like the boiler likes a little more flow. Early days but I really hope that's resolved the niggle - I might range rate it back to minimum and see if the issue comes back
marshian Posted October 24 Author Posted October 24 (edited) On 13/10/2025 at 15:37, marshian said: Early days but I really hope that's resolved the niggle - I might range rate it back to minimum and see if the issue comes back Well it hasn't 😞 so I'm going to put my thoughts down and maybe a proposal for consideration from the great minds of Build Hub The "niggle" now only occurs between 6 deg OAT and 12 Deg OAT So lets cover the data I can provide Pump Pump Speed 0.5 to 0.6 m3/hr set on Constant Curve Watts 15 Head 3.1 m Rads I have 13 Rads all with TRV's in the house table below explains what they are room sizes Heat loss at -2.5 Deg C OAT and how they are set up (Because there are issues with getting the flow rate low enough for some rads and solar gain with some rooms) I regard the circuit as well balanced both upstairs and downstairs I have a pressure relief by-pass but it's fully closed as the circuit never shrinks enough to need it. Boiler Viessmann 100-W "Heat Only" 16kW set up with Weather compensation and DHWP (Using an outside temp sensor and HWD box) It's piped up as X Plan It's running a delta between flow and return at the boiler of 6 to 7 deg C at Weather compensated flow temps Weather Compensation Curve When it's not in the OAT temp range where I see the niggle this is how the boiler behaves Good Days On CH the boiler fires up when the flow temp drops "X" deg below WC Target (Gut feel is X = -7 Deg C below target temp) It will do an initial start at 58% modulation and then over 90 secs drop down to the lowest modulation level that enables the boiler to maintain the target flow temp typically 10.8% It will then run happily at that level until the flow temp exceeds the target by "Y" Deg (Pretty sure "Y" is 5 Deg C above the target temp) Bad Days When it's in the "Niggle" window its behaviour is different during the burn Even if the Boiler is range rated to min (19 out of 100 in the menu = 10.8% or ~4.0 kWh) the boiler ignores the range rating Initial start up is identical to above but very quickly into the period after the start it starts to miss-behave - modulation swings between 10.8% and 30% This frequently results in the Target temp + "Y" being reached during the higher modulation and the boiler shutting down before it's fully refreshed the water in all the rads that were open for heat. My thoughts are that the return temp is changing as some rads have quite a large flow and a decent delta between flow and return and some other rads have much smaller deltas and the boiler is trying to maintain the target flow temp so modulating up and down to provide a stable output. If you read all that - thank you. Proposal So I had a thought what would happen if I set all the rads to an elevated flow rate said sod the balancing control - leave the TRV's to manage the room temps and flows and bring back into play the by-pass (just in case all the rooms hit target temp and TRV's shut down the flow). Part of me says I should just try it and see what happens Part of me says the TRV's will end up managing the flows as they close and the flow rate in the system and the return temps will be the same so it won't change a damn thing. Anyone think anything else will happen? Edited October 24 by marshian Spelling
marshian Posted October 26 Author Posted October 26 It didn't change a thing (well all that did happen is the room that needed the highest flow lost temp because it was being shared out to other rooms and it's the last in the circuit) So I reverted it to a dumb boiler and manually set the flow temp - still did the same thing ramping up randomly mid burn cycle - often causing + 5 deg trip. Then I needed to do HW cycle so manually increased the flow temp First thing boiler was only slowly increasing temp (because range rated to 4 kWh - ahh bugger need to undo that setting - Increased range rating to Max because it's one button press in the menu. Then boiler reached my previously set max flow temp cap of 45 deg. So that got changed for 70 Deg and then the boiler froze as I was trying to exit the menu - it was doing HW so I just walked away and left it to heating water (it's happened once before and the solution was to turn the boiler off at the main switch) So when it finished the HW I powered down the boiler (made a cuppa and then switched it back on) house needed a top up heat wise so I range rated it back to Min and waited for it to fire. Guess what happened next? It fired - ramped up to 58% and over the course of 2 mins modulated down to min 10.6% and sat there at min for 17 mins and 30 secs - used 0.103 m3 of gas which by my calcs is 3.98 kWh....... It didn't miss a beat for the rest of the day. This morning however it was back to it's old tricks - starting to really get on my wick now So I switched off the boiler waited 5 mins and then waited for it to fire for the next cycle and it respected the min range rating again. So now every time it starts to play up I have a solution to the issue - it's not pretty and I don't believe it's acceptable but I have some information now to go back to Viessmann with to point out that it still has the same problem it had before (and crucially what resets it back to how it should operate) It doesn't seem to matter what pump speed I use Constant Curve 1 or Constant Curve 2 the only difference that makes is the DeltaT at the boiler is 9 deg C with CC1 and 5 Deg C with CC2 Pump in CC1 5.5 w 1.1 m head 0.4 m3/hr Pump in CC2 16 w 3.1 m head 0.6 m3/hr
marshian Posted November 23 Author Posted November 23 Ignoring the unusual behaviour the boiler occasionally has........ I've done some changes to the system configuration it was covered elsewhere but I though it would be handy to document it here as well I've replaced all the Drayton EB4 TRV Bodies (6 position variable orifice) with Danfoss RAS-B2 TRV bodies - these are "Pressure Independant" flow regulators with flow rate settings of between 10 L/Hr and 135 L/Hr (max flow rate) The aim of the changes was to convert to fully open system and stop the Wiser TRV's from intervening on the 4 rads where I couldn't reduce the flow enough with the EB4 bodies (even on the smallest orifice setting) Once I've got stable room temps as a result of the correct flow rates for the WC flow temp the Wiser "Smart" TRV's are being removed and replaced with std Danfoss ones - Hopefully I can recover some on the cost with selling on a well known auction site. I also took the opportunity to re-configure the "Plant Room" (OK Airing Cupboard - picture below) 1. London loop on the HW outlet of the tank (early days but it already seems to have reduced standing tank losses) 2. Re-pipe the bypass so it's after the CH zone valve (it was before so when I restricted the flow thro the HW tank coil it opened the damn bypass and defeated my efforts to slow down the flow thro the coil!!!) 3. Combined 22mm Feed and vent for CH (removing the old 15mm feed) - it's solved all the issues with air ingress and got rid of another pipe in the cold loft 4. Generally remove a load of joints (from previous versions being adjusted) and clean up the lagging 5. Replaced a compression fitting with press fit that was used as an emergency fix years ago!! Outside the Plant room 1. Convert all the panel rads to TBOE from BBOE with Danfoss RAS-B2 flow control TRV bodies 2. Covert the vertical rads and towel rails to Danfoss RAS-B2 flow control TRV bodies and reconfigure the pipework
marshian Posted November 29 Author Posted November 29 I've now removed all the "smart" TRV's from the rads and replaced with std Danfoss ones but they are all currently set to max as now we are in winter with a low sun I don't really get any solar gain on the south side of the house anyway. Hopefully I can recover a little back by selling them on a well know auction site. The schedule for heating is 24/7 (no setbacks) In fitting the Danfoss RAS-B2 TRV bodies I've got flow control over all the rads even the ones that needed TRV control to limit the temps Pump is on CP2 - rock steady at 16w 3.1 m head and 0.5 m3/hr System noise is absent and I've been able to make a small tweak to the WC curve (slope and level) now running a slope of 0.6 and a level of -2.0 So 20 at 20 Deg OAT 25 at 10 Deg OAT 31 at 0 Deg OAT 37 at -10 Deg OAT The niggle with the boiler remains but I've removed the range rating and I'm letting the boiler do what it wants.
JohnMo Posted November 29 Posted November 29 34 minutes ago, marshian said: Hopefully I can recover a little back by selling them on a well know auction site. I need to get into my "heating system - useless tatt" box and get some money back. 1
marshian Posted Thursday at 23:50 Author Posted Thursday at 23:50 Just an update on the RAS-B2 TRV bodies I used the Danfoss installer app to get the base line settings but over the first week I tweaked them from the suggested to get the rooms to where I want then to be. Vertical rads need more flow than suggested (no convector fins I think is the main reason). I've not had to adjust them since and room temps are rock solid and the DT on the rads are all between 5 and 7 deg. Pump output is also rock solid at 0.6 m3/hr Absolute game changer I reckon - the Wiser EB4 bodies were good and I've been happy with then for a few years but the adjustment range was too coarse from 1-3 (I ended up using a setting along side a tweak on the lockshield to get the flow rate right and this caused a little system noise and I really dislike system noise - it's me I know but I want a quiet heating system) Next thing on the list is the HW side and options are 1. Replace the tank with another vented tank but with a 2m2 coil 2. Keep the current tank but use a PHEX and reconfigure the pipework to suit that 3. Replace the tank with ASHP compatible tank 3m2 coil (and stay vented) 4. Replace the tank with direct tank but use PHEX and reconfigure pipework to suit (Vented) 5. Replace the tank with ASHP compatible tank (3m2 coil) and convert to unvented (upside is I get to ditch 2 shower pumps - downside is risk of leaks in old circuit)
-rick- Posted Friday at 11:35 Posted Friday at 11:35 (edited) 11 hours ago, marshian said: 5. Replace the tank with ASHP compatible tank (3m2 coil) and convert to unvented (upside is I get to ditch 2 shower pumps - downside is risk of leaks in old circuit) Without knowing about the extent of the pipework you are worried about leaking this would be my strong preference. Getting rid of shower pumps, cold water tank, etc, and if the pipework is fragile enough to break under mains pressure then chances it fails anyway at some point? (replace with point to point plastic with no joins if access isn't too bad?) Obviously, need to worry about the G3 stuff so you have less scope for DIY but overall I think you end up with less to go wrong in future. Edited Friday at 11:36 by -rick-
marshian Posted Friday at 11:50 Author Posted Friday at 11:50 1 minute ago, -rick- said: Without knowing about the extent of the pipework you are worried about leaking this would be my strong preference. Getting rid of shower pumps, cold water tank, etc, and if the pipework is fragile enough to break under mains pressure then chances it fails anyway at some point? (replace with point to point plastic with no joins?) Obviously, need to worry about the G3 stuff so you have less scope for DIY but overall I think you end up with less to go wrong in future. First point is no plastic in the house - it's all copper and it's going to stay that way but the 22mm that are tee'd to 15mm to feed the rads circuits under the first floor I've already found 2 x 15mm joints that had no soldering from build in mid 1980's (On CH return rather than flow) - sealed up with limescale rather than solder. This makes me mistrust the plumbing - 4 beds and 2 baths and 3 rooms have had floor lifts over the last 34 years but to lift all the remaining 3 room's floors to check/replace is a nightmare. (it would be just three rooms but still not keen to do that) Second point that makes me lean away from unvented is we often get water interruptions with the water company fixes leaks elsewhere in the area - it's handy having a decent sized tank in the loft as we don't have an issue unless we run the tank out which will last a couple of days of "reduced" usage.
-rick- Posted Friday at 12:00 Posted Friday at 12:00 2 minutes ago, marshian said: First point is no plastic in the house - it's all copper and it's going to stay that way but the 22mm that are tee'd to 15mm to feed the rads circuits under the first floor I've already found 2 x 15mm joints that had no soldering from build in mid 1980's (On CH return rather than flow) - sealed up with limescale rather than solder. 🫣 2 minutes ago, marshian said: This makes me mistrust the plumbing - 4 beds and 2 baths and 3 rooms have had floor lifts over the last 34 years but to lift all the remaining 3 room's floors to check/replace is a nightmare. (it would be just three rooms but still not keen to do that) Assume the HW pipes flow through these rooms to the kitchen/bathroom? Changing the HW tank shouldn't affect CH pressure unless I've misunderstood something. 2 minutes ago, marshian said: Second point that makes me lean away from unvented is we often get water interruptions with the water company fixes leaks elsewhere in the area - it's handy having a decent sized tank in the loft as we don't have an issue unless we run the tank out which will last a couple of days of "reduced" usage. That is an advantage. My experience of cold water tanks in lofts is they end up with unpleasant things in them and are located in a diffcult spot for maintenance. Having said that you are not my relatives and are likely taking much more care of the system than the average person.
marshian Posted Friday at 12:59 Author Posted Friday at 12:59 47 minutes ago, -rick- said: 🫣 My feelings exactly - I was less than impressed........... 47 minutes ago, -rick- said: Assume the HW pipes flow through these rooms to the kitchen/bathroom? Changing the HW tank shouldn't affect CH pressure unless I've misunderstood something. Ahhh I had miss-understood you are proposing leaving vented for CH but unvented for HW/CW - that actually wouldn't be too bad as I've never found an issue with HW or CW pipework - it would leave just a F&E tank in the loft so just two pipes (CW Feed for top up and a combined 22mm Vent and circuit make up pipe). 47 minutes ago, -rick- said: That is an advantage. My experience of cold water tanks in lofts is they end up with unpleasant things in them and are located in a diffcult spot for maintenance. Having said that you are not my relatives and are likely taking much more care of the system than the average person. It gets cleaned out once a year - it's easily accessible, has a good fitting lid, reasonably well lagged, in a loft where 80% is boarded, access is excellent and it's well lit, All the pipes to and from are lagged (Plus I did the plumbing when I relocated the tank from a stupid place right by the loft hatch so I'm very confident in the std of joints)
-rick- Posted Friday at 13:33 Posted Friday at 13:33 24 minutes ago, marshian said: Ahhh I had miss-understood you are proposing leaving vented for CH but unvented for HW/CW - that actually wouldn't be too bad as I've never found an issue with HW or CW pipework - it would leave just a F&E tank in the loft so just two pipes (CW Feed for top up and a combined 22mm Vent and circuit make up pipe). I wasn't thinking about CH at all. Now I remember you previously talking about it being unvented. No matter, the HW cylinder/system can be dealt with independently AFAIK so no need to link the two in a single job. 24 minutes ago, marshian said: It gets cleaned out once a year - it's easily accessible, has a good fitting lid, reasonably well lagged, in a loft where 80% is boarded, access is excellent and it's well lit, All the pipes to and from are lagged (Plus I did the plumbing when I relocated the tank from a stupid place right by the loft hatch so I'm very confident in the std of joints) So no real reason to change it from a delapidations point of view. As far as maintenance goes, I remember you saying you were aiming to get as much done as possible before retirement so that you kept your costs low in future. Retirement also brings the future potential of not being as able to DIY as much. I tend to think that both of these lean more towards the unvented solution as it's simpler* but maybe not by a lot. But the backup water during outages is a big positive of the vented option. *Yes you have the PRVs and the associated maintenance. But these are all contained in an accessible heated/controlled space, no ladders involved, no float valves or pumps to play up. 1