I am looking for some design critique on a IWI design which I am planning to install in my Victorian semi-d renovation project.

The existing walls are 9" solid brick with original lime mortar jointing and the house is sited in a relatively sheltered urban location in Kent.

 

Following weeks of reading the wide array of opinions regarding installation of IWI to a solid walled house I have arrived at the buildup below with two different insulation options:

  • Internal to external 
    • Breathable paint finish
    • Gypsum skimcoat
    • Gypsum Wallboard 12.5mm
    • Service cavity 38mm x 50mm battens @ 400mm c/c
      • Intello plus VCL
      • 60mm Breathable Insulation layer
    • OR
      • 60mm PIR foil backed Insulation/VB layer 
    • 225 solid brick wall *Existing 

 

The design follows the "warm batten" arrangement.

Preference is for a vapour open design and use breathable insulation, however I am unsure what specific type product could be used in that instance.

I imagine the insulation would need to somewhat resist compression from the battens so perhaps batt type format.

HAs anyone used a glass or mineral wool slab in a similar situation? Wood fibre is a candidate but it is pricey.  

 

I believe a vapour closed design has more risk in terms of trapping moisture within the buildup, however PIR insulation with its relatively high compressive strength lends its well to the warm batten design so this option is easier to spec material wise.

 

After much reading I am satisfied that a gypsum plasterboard and finishing coat can provide a satisfactory degree of vapour permeability, hence their inclusion.  

Some will disagree (some who worship at the Lime Alter will be horrified) however there are studies that suggest that gypsum is more "breathable" than lime.

I actually spoke to a tech/sales member of staff of a well known eco & natural BM and he (of his own accord) said he regards gypsum as entirely suitable in some IWI system build up, in fact they have it specified in some of their IWI solution on their website.

 

Posted

The problem with gypsum isn't its breathability, but the fact it's hygroscopic. With a permeable construction you're allowing water vapour to travel as it pleases, but if that condenses, your skim and plasterboard is knackerd.

Either go with a IWI solution recommended by the likes of Mike Wye/Ty-Mawr which will include a breathable insulation layer (wood fibre, sheep wool etc) and a lime plaster, which requires a lime wash/clay paint, or go with a impermeable build up, like PIR and warm batten and plasterboard. Don't mix the two. 

 

There isn't enough data out to make informed recommendations either way. I've done sections of my house using both; vapour permeable in the cellar, PIR elsewhere, and I'm not seeing any ill affects, however someone else could quite easily come along and show you images of damp/rot/mould caused by the same, or similar, build ups. There are clearly a number of variables to consider before making your choice. 

Posted

Thanks for the response.

I know you have posted a lot on the subject and believe me I have read reams of material on the subject and still can't confirm my spec!

 

Agreed that hygroscopy may be an issue with gypsum and my initial thought was that gypsum could not be used in vapour open system but as my original post it is a recommended detail from Back to Earth.

 

Surely given where the PB and skim layers are located in the build up condensation should not be an issue.

Modelling shows the Dewpoint within the insulation albeit it is towards the warmside; perhaps you saying the concern is if the Intello membrane allows vapour to travel outsode to inside should relative conditions drive it so?

img_wall_v3.70.php?Height=800&Width=800&Thickness=321.5&R1type=Coatings&R1size=3&R1desc=Gypsum%20medium&R1perc=100&R1stemp=23.82&R1etemp=23.65&R2type=Boards&R2size=12.5&R2desc=Gyproc%20Wallboard&R2perc=100&R2stemp=23.65&R2etemp=22.55&R3type=Cavity&R3size=25&R3desc=Unventilated%20airspace,%20normal%20(high)%20emissivity&R3perc=100&R3stemp=22.55&R3etemp=19.54&R4type=Membrane&R4size=1.00&R4desc=Vapour%20Control%20Layer&R4perc=100&R4stemp=19.54&R4etemp=19.52&R5type=Insulation&R5size=50&R5desc=Rockwool%20Cavity%20wall%20Slab&R5perc=100&R5stemp=19.52&R5etemp=-4.35&R6type=Bricks&R6size=230&R6desc=Bricks%20medium&R6perc=100&R6stemp=-4.34&R6etemp=-9.34&DPShow=true&Dewpoint=14.8&IntTemp=26&ExtTemp=-10&IZgf7RJhbA2t4HBLyeQMxGDz  

 

 

 

 

 

Posted

What standard of workmanship are you intending to employ?!

 

Anything can work. You just need more "drying" than "wetting"

 

The big one with internal insulation is airtighess, most moisture gets into a structure via airpaths from inside. Not diffusion through materials. 

 

You can do PIR internally and expertly isolated any part of the cold external structure from the moist warm internal air and you'll be fine. 

 

However do a slapdash job with insulated plasterboard and you're asking for trouble.

 

 

 

 

  • Like 1
Posted
  On 20/04/2024 at 00:12, Iceverge said:

What standard of workmanship are you intending to employ?!

 

Anything can work. You just need more "drying" than "wetting"

 

The big one with internal insulation is airtighess, most moisture gets into a structure via airpaths from inside. Not diffusion through materials. 

 

You can do PIR internally and expertly isolated any part of the cold external structure from the moist warm internal air and you'll be fine. 

 

However do a slapdash job with insulated plasterboard and you're asking for trouble.

 

 

 

 

Expand  

Thanks for the response @Iceverge

I am fortunate with regard workmanship/QC as I am a carpenter by trade (consider myself to have an eye for detail) and I will be doing the work with my own team. 

And I also have an appreciation for the level of attention that correct installation of an airtightness membrane requires. 

 

As my original post I have endlessly read every facebook group posts, forums, etc in researching IWI options.

PIR got eliminated for consideration early on, almost entirely due to the absolute contempt the heritage/lime community have for it. Obviously they have a bias but it can be hard to ignore. 

 

That led me down the path of vapour open/breathable system, however not being a die hard conversationalist I still wanted to integrate the buildability of modern solutions into the mix.

I also follow a house renovation channel on youtube which recently uploaded a video of a hybrid system called SWIP, and that in short is how I ended up with the bastard solution above with a foot in each camp if that makes sense.

 

There is so much conflicting opinion regarding IWI that I'm ready to pull my hair out with analysis paralysis!  .

I personally have not had, or seen a PIR IWI cause damp/mould, and it is a system I would prefer. 

I feel there is too much broad strokes when discussion the various systems. The only differences debated are of the systems themselves; relevance of where (location, orientation, aspect) and how (workmanship) is ignored.  

So I must say its a relief to hear some experienced hands form this forum give a vote for PIR!

 

I have modelled the PIR solution on Ubakus, and to me it looks ok. 

Humidity doesn't approach saturation point which I imagine is the most important thing.

 

image.png.2287e765ca5fd8f9a1ae91e3205473d3.png

 

 

 

 

 

 

Posted
  On 19/04/2024 at 12:14, Annker said:

Preference is for a vapour open design and use breathable insulation, however I am unsure what specific type product could be used in that instance.

I imagine the insulation would need to somewhat resist compression from the battens so perhaps batt type format.

HAs anyone used a glass or mineral wool slab in a similar situation? Wood fibre is a candidate but it is pricey. 

Expand  

On my French renovation, I'm using hemp batts. There's at least one UK company producing an equivalent - Hemspan Bio Wall.

 

A key advantage of natural fibres is that (unlike other products) they are usually good at the adsorption / desorption of water vapour - that is taking water vapour from the air into the fibre's cell walls (often a considerable quantity) and releasing it again. There are several technical benefits to that, provided you have a construction that's vapour-open ('breathable') to take advantage of those properties:

  •     it reduces the risk of condensation
  •     improves thermal comfort by keeping the air within a comfortable relative humidity range for longer
  •     improves air quality by keeping the air within a healthy relative humidity range for longer (at <40% RH respiratory infections are more likely; at >60% bacteria and mould thrive)
  •     tends to reduce heating and cooling requirements (adsorption of moisture releases heat, desorption takes heat, though research into quantifying this in buildings is limited)

There are also non-technical benefits - they use renewable materials, have low carbon emissions, support (potentially local) agriculture, and tend to be pleasant products to work with.

 

On the other hand they take up more space than PU foam or the like for the equivalent u-value. My IWI is 100mm / 145mm thick depending on elevation & space available.

Posted
  On 19/04/2024 at 12:32, jayc89 said:

The problem with gypsum isn't its breathability, but the fact it's hygroscopic. With a permeable construction you're allowing water vapour to travel as it pleases, but if that condenses, your skim and plasterboard is knackerd.

Expand  

It's correct that condensation can cause problems with gypsum & plasterboard, but there's no need to worry at the exposed wall surface. What you don't want though is gypsum left on the original wall that you're insulating, as that's where condensation is most likely.

  • Like 1
Posted (edited)
  On 20/04/2024 at 10:06, Annker said:

I have modelled the PIR solution on Ubakus, and to me it looks ok. 

Humidity doesn't approach saturation point which I imagine is the most important thing.

Expand  

Ubakus uses the Glaser modelling technique which, unfortunately, is too simplistic. The gold standard is dynamic modelling (WUFI being the main software used), which takes into account multiple factors - like those you mention (location, orientation, aspect) as well as climate data - and models the element over the course of several years. However if you're not going too low with the U-value then that's normally not necessary. Wall U-values down to 0.5 W/m²K are normally 'safe', while research in Scotland suggest that values down to 0.35 are likely safe too.

 

FWIW I have a very peculiar non-ventilated ceiling that I'd like to insulate to the max (with hemp insulation batts), so I have just commissioned someone to model that in WUFI to determine how low I can go.

 

Edited by Mike
Posted

@Mike Yes I agree that a vapour open system put together with natural fibres fairs better should significant amounts of moisture penetrate the external brickwork.

 

My hope is that that favourable site conditions (well sheltered semi-d, lime pointed brickwork, floor levels ~300mm to 900mm above external GL) and a conscientious install of the VB should eliminate or at least minimise moisture levels within the wall being raised to a level that will cause issues.

 

I have read elsewhere alright that Ubakus is not that comprehensive.

I played around with the outside temp & humidity values to somewhat compensate for that.

 

It was interesting to see that with the outside temp set to -10 degrees the model with 60mm PIR remined condensate free.

However condensation was indicated in the model with 60mm wood fibre (screen grab below)

Not sure if that observation has any validity/relevance.

 image.thumb.png.2a2ef594b310dd341ccff37185de9e41.png   

 

  

Posted
  On 20/04/2024 at 20:24, Mike said:

It's correct that condensation can cause problems with gypsum & plasterboard, but there's no need to worry at the exposed wall surface. What you don't want though is gypsum left on the original wall that you're insulating, as that's where condensation is most likely.

Expand  

The existing internal wall lining on the externals wall is lath & plaster, all of that will be removed so the proposed IWI will be on to barefaced brick. 

Posted (edited)
  On 21/04/2024 at 08:25, Annker said:

The existing internal wall lining on the externals wall is lath & plaster, all of that will be removed so the proposed IWI will be on to barefaced brick. 

Expand  

Sounds good! You'll probably need to apply a parge coat over the brickwork to ensure all the joints are airtight.

 

  On 21/04/2024 at 08:22, Annker said:

Yes I agree that a vapour open system put together with natural fibres fairs better should significant amounts of moisture penetrate the external brickwork.

Expand  

You really don't want moisture (in the form or rain or the like) penetrating the external brickwork to any great extent. It's moisture vapour, coming (mostly) from within the house, that natural fibres are good at buffering (adsorption). You don't want them soaking up liquid (absorption). The U-values of 0.5 & 0.35 that I mentioned are only 'safe' if the wall is protected from rain penetration or ground moisture, which yours seems to be.

 

  On 21/04/2024 at 08:22, Annker said:

I have read elsewhere alright that Ubakus is not that comprehensive.

I played around with the outside temp & humidity values to somewhat compensate for that

Expand  

The Glaser method that Ubakus uses just isn't up to predicting problems with internal wall insulation.

 

  On 21/04/2024 at 08:22, Annker said:

It was interesting to see that with the outside temp set to -10 degrees the model with 60mm PIR remined condensate free.

However condensation was indicated in the model with 60mm wood fibre (screen grab below)

Not sure if that observation has any validity/relevance.

Expand  

None at all - the results aren't valid for the purpose. There are many factors it fails to take into account.

 

Edited by Mike
Posted
  On 21/04/2024 at 14:37, Mike said:

Sounds good! You'll probably need to apply a parge coat over the brickwork to ensure all the joints are airtight.

Expand  

I have considered a parge coat. Given I've ~130 sqm of walling to cover, it would be a significant addition cost so I am debating if it is required

 

Firstly, the internal face of the walls are plumb floor to ceiling but there are discrepancies in flatness. 

So a parge coat would fill out those discrepancies and hollows that otherwise may exist and I imagine could provide space for moisture to gather.

 

Secondly, as you say a parge coat would fill any brickwork joints, and there are a few joints that aren't fully filled.

However is the parge coat required to provide an airtight barrier?

Going down the vapour closed route the PIR layers, and their perimeter, will need to be meticulously sealed, that is critical for the system to work. I need to ensure that provides an airtight layer.

I wonder if I can consider a parge coat would optional second line of airtightness defence that I dont need to spend money on, or perhaps I should consider it as a critical component.      

 

Posted
  On 21/04/2024 at 17:45, Annker said:

However is the parge coat required to provide an airtight barrier?

Going down the vapour closed route the PIR layers, and their perimeter, will need to be meticulously sealed, that is critical for the system to work. I need to ensure that provides an airtight layer.

Expand  

One or the other is enough - it just needs to be very airtight.

 

  On 21/04/2024 at 17:45, Annker said:

I have considered a parge coat. Given I've ~130 sqm of walling to cover, it would be a significant addition cost

Expand  

Not that much of a cost - you only need to brush or trowel on a couple of mm thick - the cost is mainly labour. You have a cost whether you choose parge or PIR joint-sealing; probably not much difference.

  • Like 1
  • 5 months later...
Posted
  On 20/04/2024 at 20:13, Mike said:

On my French renovation, I'm using hemp batts. There's at least one UK company producing an equivalent - Hemspan Bio Wall.

 

Expand  

Hi Mike

I wonder of you can share how you tackled your project with respect to method of insulating your property internally. Particularly interested in the thicknesses of material use and how it was applied to the walls.

I need to go down the breathable insulation route but unsure whether to go down the batten route and installing hemp batts or equivalent product between the products or 'glueing' wood fibre boards to the walls with lime plaster.

Thanks

Posted

so 

 

being a victorian house 

did it have direct plaster on solid walls or was thier wooden battons and lathe  +plaster giving an air gap from below floor up into the cold roof space 

as this is the simple way to get drying out  and is time proved method 

If you have big rooms could you except loosing 100-150 mm on inside of outer walls 

if so just build a stud wall betwwen exsisting floors and ceilings and makke sure thier is an air gap all the way  from below floor to eaves 

 

insulate walls with what ever and fit a vapour barrier

 it would also give you space for running new electrics or plumbing etc 

without touching exsisting walls   

so technically you could do it  phases   ,one outside wall at a time 

 just a suggestion 

Posted
  On 17/10/2024 at 15:37, ab12 said:

Hi Mike

I wonder of you can share how you tackled your project with respect to method of insulating your property internally. Particularly interested in the thicknesses of material use and how it was applied to the walls.

Expand  

I've mostly constructed single-sided metal stud partitions to create a void that's filled with either 100mm or 145mm of hemp-based insulation (100mm wedged behind the studwork everywhere, plus 45mm within the depth of the metal stud itself where external rain penetration is unlikely or impossible). In case you're wondering, the use of timber for studs in virtually unknown here in France.

 

In a few places where space is tight - reveals, for example - I'll be applying 20mm of cork insulation direct to the existing wall, probably bedded in a thin coat of plasterboard adhesive (scheduled for late November).

 

In preparation, the plaster on brick/stone walls was hacked off and replastered in sand - hydraulic lime to even it up and improve airtightness.

  • Like 1
Posted
  On 17/10/2024 at 19:41, scottishjohn said:

so 

 

being a victorian house 

did it have direct plaster on solid walls or was thier wooden battons and lathe  +plaster giving an air gap from below floor up into the cold roof space 

as this is the simple way to get drying out  and is time proved method 

If you have big rooms could you except loosing 100-150 mm on inside of outer walls 

if so just build a stud wall betwwen exsisting floors and ceilings and makke sure thier is an air gap all the way  from below floor to eaves 

 

insulate walls with what ever and fit a vapour barrier

 it would also give you space for running new electrics or plumbing etc 

without touching exsisting walls   

so technically you could do it  phases   ,one outside wall at a time 

 just a suggestion 

Expand  

Hi John

I wasn't getting notification to the thread or your response.

 

Walls were lined with battens, lathe and plasters and the effectiveness of this arrangement is one I've given thought on.

I've concluded that doesn't provide any ventilation as in all instances the bottom foot or so of the air gap is packed with plaster resulting in no air gap at all.

Yes the plaster is lime based and breathable, but how breathable is a foot of it and it's certainly was not providing any ventilation route. 

Well that was the observation in my experience other houses may differ of course.

Posted (edited)

so you need to make a clear passage way for air to go from under floor behind the lathes and right up to the loft 

if you want somewhere for the moisture to evaporate out 

on well built houses the floor boards stop short of the walls to allow a gap and the plaster to fall into the space under the floor 

 

If you intend to remove all the old lathes ect and build a stud wall  instead then it it easy to fit a vaour barrier onto the studs  after the pir  infill ,

 just make sure you have this air gap top to bottom of the house  and through the first floor into the eaves or cold roof space

 

 my old house was TF with brick outer venitng into cold roof  

 

 being clever ,as i thought i blocked up the gap at top of wall into roof space 

 

 the roof is sheeted plywood 

 

to my suprise  when i checked it after one winter i found the north side of the roof was showing black mould on inside of ply wood 

 unblocked the gap i had filled and it stopped 

so that is where my understanding of need for ventilation  in the cavity comes from 

 

 are you sure you cannot accept loosing al ittlem ore space on outer walls ,  and use 100mm studs 

 

 and then use insulated plasterboard to bump up the insulation  

 smae goes for ceiling into roof space  vapour barrier with insulation above and get it much more air tight

 will you really notice a loss of another 100mm for all the beneifts it will bring 

 very easy job to construction stud walls insdie and between the exsisting ceiling and floors,rembering to cut gaps out of floor boards behind the stud walls if there is not sufficent gap 

 

 

 

Edited by scottishjohn
Posted (edited)

Free-standing stud wall with insulation and adequate x-vent behind is great, and ventilation may be adequate for a whole elevation with say 4 air-bricks per storey. If you have studs against the wall then you need an 'in' and an 'out' (say 225 x 150 each) between *each pair of studs'. That's a hell of a lot of air-bricks, ranging from 'not aesthetically pleasing' on, say, brick walls to virtually impossible of rubble-filled stone with a loose core. https://assets.publishing.service.gov.uk/media/614b30aad3bf7f718a54c0be/iwi-guidance.pdf 

 

Edited by Redbeard
BEIS Best practice link
Posted

Don’t like the idea of ventilating any cavity in a wall straight into the loft space due to the risk of fire spread

  • Like 1
Posted
  On 29/10/2024 at 08:59, Redbeard said:

Free-standing stud wall with insulation and adequate x-vent behind is great, and ventilation may be adequate for a whole elevation with say 4 air-bricks per storey. If you have studs against the wall then you need an 'in' and an 'out' (say 225 x 150 each) between *each pair of studs'. That's a hell of a lot of air-bricks, ranging from 'not aesthetically pleasing' on, say, brick walls to virtually impossible of rubble-filled stone with a loose core. https://assets.publishing.service.gov.uk/media/614b30aad3bf7f718a54c0be/iwi-guidance.pdf 

 

Expand  

This is very similar to a TF with brick outer leaf, however their is no requirement to ventilate the cavity in that particular construction.

Am I correct to assume the reason to ventilate in the retro-fit version is due to the difficulty in ensuring the continuity of the VCL?

Posted
  On 29/10/2024 at 09:29, Annker said:

This is very similar to a TF with brick outer leaf, however their is no requirement to ventilate the cavity in that particular construction.

Expand  

 

I think there is. I had always believed so and a quick search suggests that my mind is not addled in that view!

  On 29/10/2024 at 09:29, Annker said:

Am I correct to assume the reason to ventilate in the retro-fit version is due to the difficulty in ensuring the continuity of the VCL?

Expand  

Ye-e-e-e-s. My preference for retrofit is to choose methods which do not rely on a VCL (which in the methods I use limits how low you can get the U value). Theoretically if you use moisture-buffering materials and have a guaranteed excellent air-flow then you can go for lower U values and deficiencies in the VCL are less of an issue (though you still want an air barrier).

  • Like 1
Posted
  On 29/10/2024 at 10:44, Redbeard said:

 

I think there is. I had always believed so and a quick search suggests that my mind is not addled in that view!

Ye-e-e-e-s. My preference for retrofit is to choose methods which do not rely on a VCL (which in the methods I use limits how low you can get the U value). Theoretically if you use moisture-buffering materials and have a guaranteed excellent air-flow then you can go for lower U values and deficiencies in the VCL are less of an issue (though you still want an air barrier).

Expand  

Good job I mentioned the ventilation WRT TF and brick facade as that is the arrangement in my extension. Another topic I'll have to research!

 

Posted
  On 29/10/2024 at 09:29, Annker said:

This is very similar to a TF with brick outer leaf, however their is no requirement to ventilate the cavity in that particular construction.

Expand  

@Redbeard is correct - there is a requirement to ventilate a timber frame cavity.

 

  On 29/10/2024 at 09:29, Annker said:

Am I correct to assume the reason to ventilate in the retro-fit version is due to the difficulty in ensuring the continuity of the VCL?

Expand  

No - air contains moisture, and if you lower the temperature enough it will condense, with or without a VCL (although it's sustained high relative humidity that's the problem, rather than the incidence of condensation). The presence / absence / continuity of a vapour control layer will however affect the flow of moisture vapour passing into (and out of) the insulation from / to the room, as will the presence / absence of good controlled ventilation within the room. You also have moisture tracking through the wall from outside, which no VCL will control - from rain, for example - which can be a bigger factor than moisture from internal sources.

 

A ventilated gap behind the insulation can be essential or useful in some specific circumstances - for example if the wall is so irregular that a gap between the wall and the insulation in unavoidable in places (unventilated gaps are always to be avoided), or if the wall is subject to driving rain and it's not feasible to render it / apply a vapour-permiable sealant, or when wanting to achieve very low U-values.

Posted
  On 29/10/2024 at 15:40, Mike said:

@Redbeard is correct - there is a requirement to ventilate a timber frame cavity.

 

No - air contains moisture, and if you lower the temperature enough it will condense, with or without a VCL (although it's sustained high relative humidity that's the problem, rather than the incidence of condensation). The presence / absence / continuity of a vapour control layer will however affect the flow of moisture vapour passing into (and out of) the insulation from / to the room, as will the presence / absence of good controlled ventilation within the room. You also have moisture tracking through the wall from outside, which no VCL will control - from rain, for example - which can be a bigger factor than moisture from internal sources.

 

A ventilated gap behind the insulation can be essential or useful in some specific circumstances - for example if the wall is so irregular that a gap between the wall and the insulation in unavoidable in places (unventilated gaps are always to be avoided), or if the wall is subject to driving rain and it's not feasible to render it / apply a vapour-permiable sealant, or when wanting to achieve very low U-values.

Expand  

One issue I dont have is moisture passing through the walls from outside. 

The brickwork is the house bone dry, you cannot imagine how dry.

If I handle the bricks (I've knocked through many openings) for a day the skin on my hands opens up, the bricks literally pull the oil from them and we're not talking office boy hands here either 😂

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...