10 hours ago, Nickfromwales said:

 

 

I prefer products like Beam-shield, where the sections tuck under the beam and contact the preceding block. So when you look at the underside, you cannot see anything other than EPS.

Thanks, I had not come across this option before. I can see that it potentially lets you use the beams and the screed layer as thermal mass as they can effectively be "warm" inside the insulation envelope.

 

Do you have any experience of how it ends up comparing cost-wise with a conventional b&b buildup?

Link to comment
Share on other sites

15 hours ago, lineweight said:

What makes it more costly - the bits you buy from Jetfloor?

 

The bits you buy from Jetfloor are more expensive. A shaped section of eps is always going to be more than standard 8x4 sheets.

Also, you can't shop around so much for the concrete beams as you have to buy the whole Jetfloor system.

Also Agilia concrete is more expensive than standard concrete and needed a pump.

 

No issues with cracking. Went in the next day after pouring and cut breaks in natural places,e.g. across doorways etc.

Link to comment
Share on other sites

i looked at these last build, the problem with them is it makes you screed the floor before the walls go up as they are not a workable surface for loading out. So you have to get underfloor etc all in before the roofs on which doesnt work.

 

maybe a shed build where roof goes on quick they could work.

Link to comment
Share on other sites

4 hours ago, Dave Jones said:

i looked at these last build, the problem with them is it makes you screed the floor before the walls go up as they are not a workable surface for loading out. So you have to get underfloor etc all in before the roofs on which doesnt work.

 

maybe a shed build where roof goes on quick they could work.

No screed, just a single layer of structural concrete.

Leave to set for a few days then put a few sheets of plywood on for extra protection, but yes it does mean ufh pipes need to be in at an earlier stage than otherwise would be the case

Link to comment
Share on other sites

23 hours ago, saveasteading said:

Beam and block comfortably spans 4m.

Polishing the slab is ok, but a bit specialist for domestic. I prefer concrete screed, pir, screed with ufh. Control.

 

Or b and b, then pir and screed.

 

150 slab with 1 bottom layer of mesh is a surprise as a suspended slab. That will require great precision. 

 

 Crack control is simple enough. For later discussion.

The 4m span is the reduced span due to adding a dwarfwall/footing to help with either b&b or suspended slab. I poured a raft for my double garage on the same site and polished the slab as a test run. It worked well and so far no issues. My plan was to polish the main house floor with the aim to reduce the need for both a slab and a screed. I see this may be harder to achieve now but hopefully not impossible. I’m now looking at the Golcar ph slab design, only difference being the void formers in my case. My engineer spec’d the slab reinforcement so I don’t have too much concern regarding the mesh detail, however this isn’t my specialism and I trust he would be confident in his own design. Which details do you think would require great precision? If it’s just one layer of mesh to the base I think the mesh would be a lot easier than jobs I’ve done with several layers/hystools /overlap build ups. 
 

Aiming for ph levels of insulation with mvhr, 3G ect. Wouldn’t  a 150mm slab with underfloor heating be better suited than a screed for storing more heat? Happy to change design if I foresee the slab finish not being achievable. 
 

22 hours ago, lineweight said:

Presumably it depends whether the void formers are the type that are designed to disintegrate? If they are to deal with ground heave then presumably they are - in which case wouldn't you end up with an airspace of some kind under the slab?

I have been looking at the jablite void formers which look to simply compress when the ground does heave. I don’t like the look of the ‘just add water’ ones to create a void. I see the Jablite ones as ground baring up until the ground moves, if it moves. Once the soil heaves, does it retract at all? 
 

Although we have ‘medium’ shrinkage clay, the void formers are being used to overcome being close to where we had an old, now removed pear tree. All spec being followed directly from nhbc guidelines. 
 

Edited by Rishard
Link to comment
Share on other sites

14 minutes ago, Rishard said:

I have been looking at the jablite void formers which look to simply compress when the ground does heave. I don’t like the look of the ‘just add water’ ones to create a void. I see the Jablite ones as ground baring up until the ground moves, if it moves. Once the soil heaves, does it retract at all? 
 

Although we have ‘medium’ shrinkage clay, the void formers are being used to overcome being close to where we had an old, now removed pear tree. All spec being followed directly from nhbc guidelines. 

I'm not a particular expert on this but I think you would have to allow for the possibility that it could shrink again. I think the process can occur to some extent on a seasonal cycle as the amount of water in the ground increases and decreases.

 

With a suspended slab are you still obliged to provide ventilation to the cavity underneath?

Link to comment
Share on other sites

15 hours ago, Dave Jones said:

i looked at these last build, the problem with them is it makes you screed the floor before the walls go up as they are not a workable surface for loading out. So you have to get underfloor etc all in before the roofs on which doesnt work.

 

maybe a shed build where roof goes on quick they could work.

 

You mean internal partitions I guess? You can carry on building up external walls and loadbearing internal walls, can't you, before the screed goes in?

Link to comment
Share on other sites

5 minutes ago, lineweight said:

I'm not a particular expert on this but I think you would have to allow for the possibility that it could shrink again. I think the process can occur to some extent on a seasonal cycle as the amount of water in the ground increases and decreases.

 

With a suspended slab are you still obliged to provide ventilation to the cavity underneath?

I’m not sure about the air space below a void formed suspended slab. Hopefully someone on here knows… I’m about to crunch some numbers on supply only for both b&b vs void formed slab so will post my results. 

Link to comment
Share on other sites

1 hour ago, Rishard said:

great precision? 

Assuming this slab is designed as structural, ie self supporting, then the reinforcement must be positioned precisely as instructed, ie distance off the bottom. Then concrete quality and compaction. This is not stuff that most groundworkers do, or even know about.

 

And one layer of bottom mesh is unusual in a structural slab. I'd expect some top as well.

 

It all seems strange and I feel this is not the whole story. Drawings?

Edited by saveasteading
Link to comment
Share on other sites

8 hours ago, saveasteading said:

Assuming this slab is designed as structural, ie self supporting, then the reinforcement must be positioned precisely as instructed, ie distance off the bottom. Then concrete quality and compaction. This is not stuff that most groundworkers do, or even know about.

 

And one layer of bottom mesh is unusual in a structural slab. I'd expect some top as well.

 

It all seems strange and I feel this is not the whole story. Drawings?

I can send you my engineers annotated plans which he put together for me for the sake of a costing exercise. His final calculations are on going with some of the other calculations for the house. He did recommend some mesh to the top of the slab but like I said previously, only in a few places where there would be hogging moments (I believe he called them) 

Link to comment
Share on other sites

Up to you. I don't expect any errors in the calculations. It's more about understanding the whole scenario. Anything from your consultants should anonymise who they are.

 

I was thinking about quality. Having worked on major structural concrete projects, then come across the typical groundworker, they are not remotely the same.

With my own money I use the normal groundworker but have to supervise.

I have seen them variuosly leave drink tins on the bottom about to be concreted in, add masses of water to concrete, stamp mesh down to the bottom,  not lap the mesh, bodge drains with silicon, refill overdug excavations......

Some of them don't take instruction willingly.

I am seeing on BH why an SE might overdesign a bit....knowing it is likely to be badly built

Link to comment
Share on other sites

  • 4 months later...

I had two identical floors poured on Thursday. Both with Agila 75 mm thick with fibres. The first was fine but the lads struggled with the second due to the heat and the concrete going off very quickly. It was a separate load of concrete for each floor. The second floor is riddled with cracks. I’m not a happy bunny. 

  • Sad 1
Link to comment
Share on other sites

On 25/08/2023 at 20:20, Canski said:

I had two identical floors poured on Thursday. Both with Agila 75 mm thick with fibres. The first was fine but the lads struggled with the second due to the heat and the concrete going off very quickly. It was a separate load of concrete for each floor. The second floor is riddled with cracks. I’m not a happy bunny. 

 

traditional screed for me every time.

Link to comment
Share on other sites

On 25/08/2023 at 20:20, Canski said:

second floor is riddled with cracks. 

They probably added water to keep it fluid. That then evaporates leaving the equivalent amount of aero type voids and weakness.

I don't know the product. But ready-mixed suppliers will require a signature on the ticket before adding water. ...because it is a bad thing.

Did you buy it or your contractor? Either way, the delivery ticket will say.

 

It isn't disastrous. This happens with all concrete in hot climates.

 

Photo?

 

 

  • Like 1
Link to comment
Share on other sites

45 minutes ago, saveasteading said:

They probably added water to keep it fluid. That then evaporates leaving the equivalent amount of aero type voids and weakness.

I don't know the product. But ready-mixed suppliers will require a signature on the ticket before adding water. ...because it is a bad thing.

Did you buy it or your contractor? Either way, the delivery ticket will say.

 

It isn't disastrous. This happens with all concrete in hot climates.

 

Photo?

 

image.jpeg.aa1e04e8b437aea890196c7f32fbca7c.jpeg

IMG_3873.jpeg

IMG_3875.jpeg

Link to comment
Share on other sites

14 minutes ago, saveasteading said:

First I'd ask the contactor what they think about it. Prediction....its normal.

Then see thd delivery tickets.

 

What's underneath determines whether this is a problem or inconvenience.

Thanks. Yes I have asked for the delivery receipts and asked them to pop out and take a look.

 

Underneath is a beam and insulated block floor. Litecast GT12

Link to comment
Share on other sites

15 hours ago, Canski said:

and it still wouldn't work on an insulated beam and block floor

 

sure it would, sleeper walls etc. still wouldn't bother with them with the massive built in thermal bridging, double/treble the price of a standard floor and only benefit is saving a couple muck always.