Because of my kitchen design I've been looking for a kitchen extractor/cooker hood design that is similar to commercial designs in that I've got a canopy with grease/carbon filters and then ducting (29mm that goes in my service void) to a remote fan unit, that I can box in and isolate acoustically (I've even got a dedicated space available for this in my kitchen). Other than to have a commercial canopy company make a bespoke one, I've been unable to find anything like what I'm looking for.

 

Otherwise, every other extractor seems incredibly noisy (all our previous ones have been too), and unfortunately most, if not all, are imposing on my attempted clean space and drawer/cabinet design. Even the downdraft ones seem to have fundamental flaws, like I've got to reach over my cooker to operate the controls and the motor unit ends up taking up all my under counttertop space which is designed for drawers to store all my pots and pans.

 

If I can't find what I'm looking for above, at a push I'm thinking of a subtle cantilevered recirculating unit (that provides a low profile) - we're not having any wall hung cabinets in our kitchen. My other desperate thought is not to have a hood at all and maybe just install a single room mvhr that has a boost function for local ventilation for the kitchen. Or maybe I can gut a hood by just removing the motor & fan assembly?

 

I've been looking for months on and off and feeling rather downheartened that I haven't found an adequate solution yet. I've left it a bit late because I'm making the kitchen right now and cutting the plywood for my drawers as I start this thread. Can any one help with some creativity here please as mine's deplete? Desperate for some ideas.

Posted

29mm ducting ???? That is not going to be worth having. When i did kitchens for a living, all of the external extractors i fitted required ducting of 250mm, and sometimes 300mm. If you have only got 29mm for ducting you need to have a serious think about alternatives.

Posted

We did a design for something similar on my wall in marker pen, spent a good couple of hours on it, it might still happen. 

Basically it was two 225x25 ducts hidden in the wall, turning 90degrees to project outwards.

The outer opening would line up with a decor panel that was on the underside of the upper cupboards

these ducts would have a 3D printed grill over them.

Ducting then went back to an in-line unit with Greece filter on the loft above kitchen.  

Posted
2 minutes ago, Big Jimbo said:

29mm ducting ???? That is not going to be worth having. When i did kitchens for a living, all of the external extractors i fitted required ducting of 250mm, and sometimes 300mm. If you have only got 29mm for ducting you need to have a serious think about alternatives.

Isn’t it 29x225. 

Posted
18 minutes ago, Big Jimbo said:

29mm ducting ????

 

16 minutes ago, Russell griffiths said:

Isn’t it 29x225. 

 Yes, it's 29mm deep. I've also found some that's 308mm wide https://www.nationalventilation.co.uk/wp-content/uploads/2020/11/Monsoon-Rectangular-Ducting-308mm-x-29mm-Duct-Accessories.pdf

 

18 minutes ago, Russell griffiths said:

We did a design for something similar on my wall in marker pen, spent a good couple of hours on it, it might still happen. 

Basically it was two 225x25 ducts hidden in the wall, turning 90degrees to project outwards.

The outer opening would line up with a decor panel that was on the underside of the upper cupboards

these ducts would have a 3D printed grill over them.

Ducting then went back to an in-line unit with Greece filter on the loft above kitchen.  

 

Okay so I haven't completely lost it. That sounds very similar where I'd planned on using the corner in the kitchen base units to house the fan as I've ditched the idea of a corner cabinet to have some services in there instead.

Posted

I have a canopy extractor and have removed the motor but left the lights and the grease filters.  I have a 200mm TD Silent inline fan mounted in a service room above the kitchen connected up with 150mm round ducting and spigots.  Operated by a switch on the wall.  It is very nice and quiet and very good at extracting.

  • Like 3
Posted
51 minutes ago, Mr Punter said:

I have a canopy extractor and have removed the motor but left the lights and the grease filters.  I have a 200mm TD Silent inline fan mounted in a service room above the kitchen connected up with 150mm round ducting and spigots.  Operated by a switch on the wall.  It is very nice and quiet and very good at extracting.

Good to know. Thanks for the heads up on the TD Silent. I have a Vent Axia unit going spare I thought I'd used so I'll check to compare extract data.

Posted (edited)

That looks great @Mr Punter. Neat profile on the hood and simple which is what I'm looking for. Did you have any issues with the internals when you removed the motor, like losing the spigot or other necessary ducting that needed to be fixed?

Edited by SimonD
Posted
34 minutes ago, SimonD said:

That looks great @Mr Punter. Neat profile on the hood and simple which is what I'm looking for. Did you have any issues with the internals when you removed the motor, like losing the spigot or other necessary ducting that needed to be fixed?

 

No it was fairly straightforward.  Here is how it looks now with a couple of the grease filters removed:

 

bcxDUEjxfrgbcse99GK_mf-4KyLWmCckmkU752u99URuJW1fV3lt-l1Jjf741UeEo7fG661zOExXEp1MoKdieebTdI8iM9ON3Hpj2LyKwHcqVCoMwmixeIVooR-LpQnqChsNOLtfBbc2Wa0M72WQ0Xys4EbWn3xAPAC1PSQ2PxdmztT9qeoH1aBvIsPRFQ2NTPmWSM1qcyiXcxCH4tTV3Tz3hN8gmzh0bgvOCR4ZrY3RVxgfkltyScBP6kEn-6N1uS51mE-gRBvCcgJEF9mvvYHxedtuLnweIVGZXExQqq1RlRjEdLmaRDCzkE18JLaEYj6yBd3nb-tWaIPe46ruOSLvOMi7pztmEmuqVrAZqXt8CitVOzI5dKDfJUw4STOXlcqghtefTbxeGrZp30WYwm5_C-3VrV9qGi4DeAu-_DvNeKObTGrRKnuYhRYQLBfKSGSzfTgMZ-gYX7RziCoXO4CMw1lx6EB0jJPt6kLVzrFaa-eVGU0mu36Xl5Y3JcF-oG90pug5_WXyWTV_4Sqjaaxd_VOJ5MXJa3hXt9qcfmCB4qlgJsdLU7svd2flCz8ziMQfKNgm-Wih4YUVTzHwjMeDel-9JL0yUOqfsmDdg5yQwM5Vq2-ap1VXFBc_4NFFaPo7iRjHmqloydg31CzXFYQDx2wzwJWFnGiKxbQTZQhOSYU6LwDphrWbPW5fPuZJsVNhSIGOFteBV9LPYGs266F9iBM3FfxNlk2lRemJrgwCpOu9vQF5EWz7cOU=w1250-h937-no?authuser=0

  • Thanks 1
Posted
1 hour ago, Mr Punter said:

I have a canopy extractor and have removed the motor but left the lights and the grease filters.  I have a 200mm TD Silent inline fan mounted in a service room above the kitchen connected up with 150mm round ducting and spigots.  Operated by a switch on the wall.  It is very nice and quiet and very good at extracting.

 

Basically that's what I did in our last house but used a monsoon external centrifugal fan. Almost silent and great airflow. Used a dimmer switch to control fan speed.

  • Like 1
Posted

Before we rebuilt and now have a new kitchen I fitted an external motor for an existing hood. It was Weston in West Yorkshire that supplied the exterior motor complete with remote control. I was going to add a humidistat in the hood to trigger the motor but never got round to it. They also do custom hoods

  • Like 1
Posted
On 01/04/2022 at 14:45, Mr Punter said:

 

No it was fairly straightforward.  Here is how it looks now with a couple of the grease filters removed:

 

bcxDUEjxfrgbcse99GK_mf-4KyLWmCckmkU752u99URuJW1fV3lt-l1Jjf741UeEo7fG661zOExXEp1MoKdieebTdI8iM9ON3Hpj2LyKwHcqVCoMwmixeIVooR-LpQnqChsNOLtfBbc2Wa0M72WQ0Xys4EbWn3xAPAC1PSQ2PxdmztT9qeoH1aBvIsPRFQ2NTPmWSM1qcyiXcxCH4tTV3Tz3hN8gmzh0bgvOCR4ZrY3RVxgfkltyScBP6kEn-6N1uS51mE-gRBvCcgJEF9mvvYHxedtuLnweIVGZXExQqq1RlRjEdLmaRDCzkE18JLaEYj6yBd3nb-tWaIPe46ruOSLvOMi7pztmEmuqVrAZqXt8CitVOzI5dKDfJUw4STOXlcqghtefTbxeGrZp30WYwm5_C-3VrV9qGi4DeAu-_DvNeKObTGrRKnuYhRYQLBfKSGSzfTgMZ-gYX7RziCoXO4CMw1lx6EB0jJPt6kLVzrFaa-eVGU0mu36Xl5Y3JcF-oG90pug5_WXyWTV_4Sqjaaxd_VOJ5MXJa3hXt9qcfmCB4qlgJsdLU7svd2flCz8ziMQfKNgm-Wih4YUVTzHwjMeDel-9JL0yUOqfsmDdg5yQwM5Vq2-ap1VXFBc_4NFFaPo7iRjHmqloydg31CzXFYQDx2wzwJWFnGiKxbQTZQhOSYU6LwDphrWbPW5fPuZJsVNhSIGOFteBV9LPYGs266F9iBM3FfxNlk2lRemJrgwCpOu9vQF5EWz7cOU=w1250-h937-no?authuser=0

 

That's really helpful, thanks for that.

  • 3 years later...
Posted
On 01/04/2022 at 14:53, Conor said:

 

Basically that's what I did in our last house but used a monsoon external centrifugal fan. Almost silent and great airflow. Used a dimmer switch to control fan speed.

Do you remember how dimmer switch was connected? Ive just got my fan delivered and there is very little in the manual. I think there are two ways of connecting dimmer, one is adding dimmer separately (2 additional connectors inside the fan and probably work with capacitor) or just replace fan switch with a dimmer.

Posted

I fitted the dimmer along the supply to the unit. I ripped everything out of the hood and dumped it, everything except the lighting went to the Monsoon unit outside. So two power supplies, one to the Monsoon via a dimmer, and another to the hood just to power the lights.

  • Like 1
Posted
13 hours ago, Conor said:

I fitted the dimmer along the supply to the unit. I ripped everything out of the hood and dumped it, everything except the lighting went to the Monsoon unit outside. So two power supplies, one to the Monsoon via a dimmer, and another to the hood just to power the lights.

At what speed do you normally run it? It's quite noisy at max speed so a bit worried about neighbours.

What was your solution for the hood? Custom or just ripped apart a kitchen extractor fan with hood?

Posted
4 hours ago, gambo said:

At what speed do you normally run it? It's quite noisy at max speed so a bit worried about neighbours.

What was your solution for the hood? Custom or just ripped apart a kitchen extractor fan with hood?

Yeah, pretty loud on the outside. Rarely ran mine full tilt.

 

Yes, just ripped all the fan stuff out of the cheap hood I got from Currys.

 

 

  • Thanks 1
Posted

The external motors from "Best or Westin" that i used to use were expensive at the time.  What ever you do, make sure you have a grease filter at the start, source. Try and keep bends to a minimum. Every bend with have a big effect on the airflow. If you can try and keep your pipework round. Again for the benefit of airflow. If using round pipe, try and get One that has a smooth inside. Again air does noy like going passed loads of ripples. Best of luck with the project.

  • Thanks 1
Posted
2 hours ago, Big Jimbo said:

The external motors from "Best or Westin" that i used to use were expensive at the time.  What ever you do, make sure you have a grease filter at the start, source. Try and keep bends to a minimum. Every bend with have a big effect on the airflow. If you can try and keep your pipework round. Again for the benefit of airflow. If using round pipe, try and get One that has a smooth inside. Again air does noy like going passed loads of ripples. Best of luck with the project.

I was lucky to prepare it during renovation so there is a duct with only one 90degree bend. The total run to outside is less than 1.5m. the bad stuff is that we could only easily fit 100mm pipe due to limited space and the wiring is hanging from the ceiling in the kitchen so I would need to either keep the wire inside the pipe to the fan or find a way to run it outside the pipe but without ripping too much of the ceiling.

 

Any recommendations for grease filter solutions? I want to add one as it will also add a bit of sound and heat insulation between the outside air and kitchen.