ASHP - how noisy are they in reality
John Carroll replied to Walshie's topic in Air Source Heat Pumps (ASHP)
The closer the evaporating and condensing temperatures are, the less compressor power required, a very quick look at 410A refrigerant tables shows, purely based on the table pressures, ~ a pressure ratio of 3.148 in compressing from -5C to 35C and 3.727 in compressing from -10C to 35C so ~ 18/19% more power required maybe? -
ASHP - how noisy are they in reality
John Carroll replied to Walshie's topic in Air Source Heat Pumps (ASHP)
One might think that, assuming a modulating as against a on/off ASHP, that the pump should be automatically controlled to give maybe a fixed dP of say 5C, the flowrates above of max/min of 540/1205 LPH would then give a ASHP output of 3.14/7.0 kW. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
You shouldn't have to drain down the UVC, just shut the mains supply to it, open a hot tap and any cold tap off the bananced cold, the water should then stop fairly quickly as there is/should be a check valve in the combination valve set. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
Friction loss tables would indicate that the dP through that pipework should be well < than 0.25bar at 11.6LPM, (one table shows a loss of < 0.1bar), add the elevation loss of 0.15bar gives a total (max) loss of 0.4bar, a 1M dP should give a flow of 18.34LPM and still leave ~ 1.8bar after the PRV. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
That makes sense allright as there is/should be no flow in that balanced cold with any hot flow only, so what is your next step as it points to a restriction upstream from or at the PRV. You have 6M of 25mm MLCP + ??M of what type/size of remaining piping to the PRV? -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
No idea but I think you will just have to methodically plod through logical checks, one could also say that the chances of two PRVs being faulty are tiny, one strainer might get full of debris but hardly the second one. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
Exactly, I'm happy now. There is one "foolproof" method of checking if the problem is with the PRV and that, as you suggested, is to remove the PRV and install a spool piece but this ia a bit messy as the balanced and EV connections must be removed and the spool piece made up, easier IMO to remove the balanced cold at the PRV, make up a connection and install the PG here, then check this pressure with shower on (HW) only and/or other HW users, this will also show, if the PG reads say 2.6/2.8bar, that the problem is downstream of the PRV. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
What does the Utility tap PG read when drawing 37LPM ONLY from the outside tap? -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
Agree, but IMO, the "1.4" bar PG should read exactly the same as the cistern PG which reads 2.6bar with a flowrate of 37LPM as long as there is no demand from the PRV, and allowing for any elevation difference between the two PGs. IF it does and it would have to IMO (static measurement) then the problem might appear to be somewhere between the tee off to the water softner (including its now bypass valve) and the 25mm MLCP etc + and including the PRV. Also if the shower is flowing 11.6LPM @ 1.4bar then assuming a "normal" minimum of 2.7bar should give a shower flowrate of 11.6*sqroot(2.7/1.4), 15.8LPM. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
Well then that PG should show (with the shower off) the dynamic pressure when the outside tap is flowing 37LPM or whatever, is that the 2.6bar you mentioned above?. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
OK getting there slowly I think. IMO, if you take a pressure reading off any tap fed from the balanced cold then that will tell a lot as its downstream of the PRV, that pressure should be showing ~ > 2.8bar ish if the PRV is set to 3.0bar and working properly and with no debris in its strainer while supplying only 11.6LPM to the shower. Can you (again?) say where exactly that "1.4bar" pressure is taken from? -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
Where is the "1.4bar" measurement been taken?, is it directly off the UVC?. If a balanced cold is taken off where shown, try and install a PG on any tap that its supplying and note the pressure with the shower flowing 11.6LPM, that should show the PRV downstream pressure. If the balanced cold is unused and capped off then shutting the mains supply to the UVC should allow the removal of the cap nut without draining down the UVC as there is/should be a check valve, take care when slackening off the cap nut to ensure pressure falls off after shutting the mains. -
Questions/Issues with new UVC System
John Carroll replied to Spinny's topic in Boilers & Hot Water Tanks
Are you saying that you are only getting 1.4bar (static) pressure where indicated at a shower flowrate of 11.6LPM?? Can you take the pressures where indicated with the shower only in service on its hottest setting, the dP (pressure drop) through the 23m of 32mm MDPE should only be ~ 0.04bar at 19LPM and practically nil, 0.02bar, at the shower flowrate of 11.6LPM, trying to see if there is a problem with the UVC PRV (pressure reducing valve), maybe the strainer is full of crap after commissioning the system or something simple like that. I don't think you said if a balanced cold is taken off just after the UVC PRV, if so, open and measure the flow from a (balanced) cold only and take pressures. What is the height of the shower (head) above the top of the UVC roughly. -
Maybe look at it from two opposite ends. One is to assume no anticycle time and a very small HEX of say 5L and a dT of 5C between firing on/off, a 1 kw "rad" would, more or less output this under these conditions. The other extreme is (by using anticycle logic) is to allow the whole system contents of 130L to fall to 25C, the dT through the HEX when firing is almost 7.02C, 4*860/60/0.5/16.66, (6.88), so when the rads/HEX return rises to 25C then the HEX will shut down as its discharge temp will be 32C, by allowing the system contents to fall to almost "cold" conditions of 20/20.5C will give a system buffer of 130*5/860, 0.756kWH and a OFF time of ~ 45 mins to give a cycle time of 1 per hour!!, of course the rad output would require to be doubled as the average output will only be ~ 50% with the flow temperature rising and falling, bif effect at very low flow temperatures. Anyway have a look at this. Buffer mars Rev0.xlsx
-
Expansion Vessels Positions
John Carroll replied to John Carroll's topic in Boilers & Hot Water Tanks
Of course, easy to install it correctly on a heat only boiler, or a system/combi boiler where one would expect the internal EV to be teed in allso (and allways?) to the pump inlet but I seem to recall someone who installed a external EV on a combi and had some problems but found subsequently that the internal EV was installed on the pump outlet by design if i'm remembering this properly. -
I thought I had this figured out but can't do it now, someone else might. Its generally recommended that a EV is installed on the pump inlet, the system pressure then runs at a higer level than if it is installed on the pump discharge, if a second EV is required for system expansion etc then it might be teed into the existing EV but certainly on the same side of the pump if not. Query is, what happens if one EV is teed in before the pump and one after it Expansion Vessels Positions Rev0.xlsxExpansion Vessels Positions Rev0.xlsxExpansion Vessels Positions Rev0.xlsx since the point of no pressure change is where the EVs are teed in. Expansion (2) Vessels Positions Rev0.xlsx
-
The above gives different precharge pressures but no charging pressures which makes a big difference to the system volumes that can be accomodated by a (the) 10L EV. For example they indicate that at a system mean temp of 65C that the EV wiil be sufficient for 180/185L, it will, (my calcs) but just about with precharge/filling pressures of 0.75/1.25bar, I would allways calculate for a final pressure of 2.5bar so the 10L EV will comfortably accomodate 150L with precharge/filling pressures of 0.75bar/1.25bar with a final pressure of 2.5bar. Commonly used precharge/filling pressures of 1.0bar/1.5bar should give a final pressure of 3.0bar with a system vol of 163L but only 125L at a final pressure of 2.5bar. A "trick" thats sometimes used is to have the precharge and filling pressures the same which gives a huge increase in system volume, for example the 125L above at precharge/filling pressures of 1.0/1.5bar can be increased to over 230L with precharge/filling pressures of 1.0bar/1.0bar and still not exceed a final pressure of 2.5bar, of course no reserve vol then to make up for tiny leakages/microbubbles which can lead to frequent top ups, or, far worse, the installation of a auto top up (PRV) valve set to 1.0bar. EV Rev 0.xlsx
-
This Graph is based on what may be the 6 PP settings, just change the values to see the effect on the head/flow. Dab Evosta3 PP Various Rev 0.xlsx
-
I think I know exactly how PP control is supposed to work. If you look at the attachments, it will become pretty clear. On the graphs, the red line shows what the actual flow&head is as the pump ramps up in speed, the blue line is the PP setting, on PP2, zero flow is 1.6M & 3.2M is 1.85m3/hr, as the pump speed ramps up the actual flow and calculated PP flow become exactly the same at only one head, where the red&blue lines intersect, you can see more definition in the calculations. On CP2 you got a flow 0.5m3/hr at @ 3M head & 15W, these all correspond to exactly the very accurate Wilo data for my 6M wilo Yonos Pico so that flow and head are quite correct IMO. On PP2, using that flow&head, 0.5m3/hr@3.0M, results in a flow/head of 0.403m3/hr@1.95M and on PP3, 0.535m3/hr@3.44M. IF the flow&head are steady in CP mode then the should also, too, be steady in any PP mode, (a gradual change will take place if say TRVs are closing in etc.) Note though that the PP2 & PP3 settings are taken from the 3 standard settings shown in the screenshot but doesn't really matter as there shouldnt be any fluctuating PP settings. Dab Evosta3 PP2 Rev 0.xlsx Dab Evosta3 PP3 Rev 0.xlsx
-
Will get back re rad outputs later. Re the pump, Are you saying that PP3 gives a flowrate of 0.3m3/hr and PP6 gives a flowrate of 0.6m3/hr? or, is the flowrate fluctuating while the setting is set on any one of the PP3 to PP6 settings?
-
Assuming it fully anticlockwise now, can you remove that plastic quadrant and reposition it a (good) bit to the right to see can you then turn the adjustment more anticlockwise.
-
Immersion thermostat keeps tripping
John Carroll replied to Little Clanger's topic in General Plumbing
I 've used a a vey simple few for decades. Energy, kWh = litres x (T2-T1) / 860. Time, hrs = kWh/heating power in kW. And. To calculate power required to instantenously heat water..... Power. kW = LPM x 60 x (T2-T1) / 860 or any variation of this. -
Immersion thermostat keeps tripping
John Carroll replied to Little Clanger's topic in General Plumbing
You might save a few bob due to the tiny bit extra of cylinder losses but it won't fix your current problem. Assuming the top 40L or so still at 60C when the night heating cuts in then you will have to heat 120L of mains water at (my) 12C to 60C, requiring, 120*(60-12)/860, 6.7kWh, add say another kWh for cylinder losses, 6.7+1.0, 7.7kWh, requiring 7.7/2.519, 3.06hrs, say 3hrs 15 minutes and a very worst case of, assuming a whole cylinder reheat, of 160*(60-12)/860/2.519, 3.55hrs, say 4hrs, you will be well covered to programme it on for 4hrs before the end of the night rate as this will cover cold mains at 5/6C in the debths of winter.