  On 22/11/2018 at 14:04, PeterW said:

And then what on top..?? How are they detailing around the rooflights..??

Expand  

 

Usually a 45deg fillet at the base of the upstand then an inch thick or more up the sides with a wrap of expanding mesh to support if you feel the need (not essential but do so on a steel post). Needs to return into some form of rebate / tuck in the top. Sides sometimes straight not tapered. Nice lead cap to finish off.

 

...imho

 

Done a good few plinths like this over the years but always subbed out the asphalting. Top of lead cap usually 6" off of main roof.

 

As the Welshman says, never lost a patient yet!

 

Only got a Sharpie on me...

 

20181122_145839.thumb.jpg.72b416c80e1b683bace7914e24ab5e49.jpg

 

 

 

 

  • Thanks 1
Posted
  On 22/11/2018 at 15:07, Onoff said:

 

Usually a 45deg fillet at the base of the upstand then an inch thick or more up the sides with a wrap of expanding mesh to support if you feel the need (not essential but do so on a steel post). Needs to return into some form of rebate / tuck in the top. Sides sometimes straight not tapered. Nice lead cap to finish off.

 

...imho

 

Done a good few plinths like this over the years but always subbed out the asphalting. Top of lead cap usually 6" off of main roof.

 

As the Welshman says, never lost a patient yet!

 

Only got a Sharpie on me...

 

20181122_145839.thumb.jpg.72b416c80e1b683bace7914e24ab5e49.jpg

 

 

 

 

Expand  

Now you mention it - that’s almost exactly what he stated !!!! ?

Only difference would be the upstand ( still  have the fillet ) would be thinner otherwise walk on glass frames won’t fit . That was his suggestion.

Posted (edited)

Also , which I didn’t realise the hot bitumen isn’t bonded to the concrete ! ?

This was to allow for any movement and prevent cracking . As for the parking area he said cover in polythene and just cement pavers ontop . He did indicate UV was the biggest problem ; but as mine is entirely covered not an issue .

Edited by pocster
Posted
  On 22/11/2018 at 15:21, pocster said:

Also , which I didn’t realise the hot bitumen isn’t bonded to the concrete ! ?

This was to allow for any movement and prevent cracking . As for the parking area he said cover in polythene and just cement pavers ontop . He did indicate UV was the biggest problem ; but as mine is entirely covered not an issue .

Expand  

 

Sounds my kinda guy! How old?

 

(Not in THAT sense...unless he's minted! :) )

 

You can mitigate UV damage by painting on solar reflective paint direct to the asphalt. I'll take a pic of a can if I have one.

  • Thanks 1
Posted
  On 22/11/2018 at 15:36, Onoff said:

 

Sounds my kinda guy! How old?

 

(Not in THAT sense...unless he's minted! :) )

 

You can mitigate UV damage by painting on solar reflective paint direct to the asphalt. I'll take a pic of a can if I have one.

Expand  

Don’t know . Didn’t really chat him up ; mid 40’s I guess . I’ve got his phone number if you want to sweet talk him ? 

Posted
  On 22/11/2018 at 16:18, pocster said:

Don’t know . Didn’t really chat him up ; mid 40’s I guess . I’ve got his phone number if you want to sweet talk him ? 

Expand  

 

Did you get felt up?

 

Cromasol White btw sold in Asphaltic branches. Also "Solaflex" but that's twice the price.

  • Haha 1
Posted
  On 22/11/2018 at 16:48, Onoff said:

 

Did you get felt up?

 

Cromasol White btw sold in Asphaltic branches. Also "Solaflex" but that's twice the price.

Expand  

Think he said some mastic perma iko 

Apparently you can create a fall with it also !

Posted
  On 22/11/2018 at 17:10, pocster said:

Think he said some mastic perma iko 

Apparently you can create a fall with it also !

Expand  

 

Iko Permatec?

 

Massive company, do roof rain water outlets and all sorts.

Posted
  On 22/11/2018 at 17:16, Onoff said:

 

Iko Permatec?

 

Massive company, do roof rain water outlets and all sorts.

Expand  

Yeah I think that was it

Said it was the best ( presumably expensive also ! )

  • 4 weeks later...
Posted (edited)

Right !

SIG guy recommended roofer .

Roofer guy recommended guy to screed a fall .

The screed has been done ; I can’t walk on it but looks to be a proper job .

Problem is 1 up stand in particular is low - real low .

Maybe just 20mm above the screed .

Bearing in mind hot bitumen has to go ontop the screed so the upstand will be even lower .

I know upstands are meant to be a min of 150mm but that was always impossible in this situation .

I could timber across all the upstands to raise them before the bitumen .

But then I’ll be much higher than the house damp course and much higher than the street entrance way . ?

Trying to think how to make a ‘feature ‘ out of a raised corner ( stilted tiles sitting around glazing ) . Or just not worry - see what happens .

The screed does look spot on fall wise so perhaps it’s less of an issue than I imagine .

Just when it’s meant to be 150mm and I will struggle to get 15mm I worry .

Edited by pocster
Posted (edited)

Hey @Onoff !

 

Suppose I fitted this 1 walk on glass frame before the bitumen .

Could he bitumen too it ? Essentially embed it in the bitumen ? . Then he could fillet away from it on each side .

Hope that makes sense !?

Edited by pocster
Posted

Actually that might be a dumb idea and cause other issues .

i did consider raising all the up stands but then the gates would also need a rising hinge or something to clear the driveway !! ?

Posted

I'm lost...aren't you having block paving atop the asphalt? With the top of the glass level with top of the blocks?

 

Need a section view to remind myself.

Posted
  On 16/12/2018 at 12:51, Onoff said:

I'm lost...aren't you having block paving atop the asphalt? With the top of the glass level with top of the blocks?

 

Need a section view to remind myself.

Expand  

Yes . But only on the centre section where you park . Stilted tiles everywhere else I.e around walk on glass 

Posted

Here we are

 

You can see the lowest upstand with and without the frame . Too be fair his screeding is like perfect !!

 

 

0C09502F-3A7C-42CB-AAD8-B1AFC8CF1283.jpeg

92338557-24D6-4B5B-8CB6-44D6A7D7A1C5.jpeg

Posted
  On 17/12/2018 at 09:52, pocster said:

Here we are

 

You can see the lowest upstand with and without the frame . Too be fair his screeding is like perfect !!

 

 

0C09502F-3A7C-42CB-AAD8-B1AFC8CF1283.jpeg

92338557-24D6-4B5B-8CB6-44D6A7D7A1C5.jpeg

Expand  

 

Can't help feeling that should have  "tuck" on all 4 sides of the upstand. As if you'd put say a 20x20 batten around the shuttering before you cast it. Something for the asphalt to key into. Like my little hand sketch a while back. Then you bed the skylight on whatever goop you're using.

Posted (edited)
  On 17/12/2018 at 09:57, Onoff said:

 

Can't help feeling that should have  "tuck" on all 4 sides of the upstand. As if you'd put say a 20x20 batten around the shuttering before you cast it. Something for the asphalt to key into. Like my little hand sketch a while back. Then you bed the skylight on whatever goop you're using.

Expand  

Roofer looked at all this before said it wasn’t an issue .

He also suggested the screed to falls .

i’ll try to get him back out to take a look ...

Edited by pocster
Posted

Should you run a course of brickwork around for the bitumen to dress up, or does this upstand get done in timber? Make sure the detail is OKed by SIG.  I used adjustable pedestals from Castle Composites but the minimum height is 30mm.  They also do fixed height ones down to 10mm.